Issue
How does the nciSetpts snvt integrate to Niagara R2 for a Viconics Thermostat Model # VT7200C1018E (programID = 80:0:c5:55:0:4:4:1b)
Environment
- Niagara R2
- Viconics Thermostat (Model# VT7200C1018E)
Cause
Information will help configure the Niagara R2 for a Viconics Thermostat.
Resolution
The correct shadow object is T7XFCr. Use the SnvtTempSetptCmd object to link with the nciSetpts snvt. Note that if a setpoint is changed at the thermostat's local display, it will be used as the controlling setpoint regardless of the value provided by the nciSetpts snvt.