Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Field Devices
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,838
  • TAC IA Series 1,821
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "field devices"

View in: "Building Automation Knowledge Base" | Community

720 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 20
    • 21
    • 22
    • …
    • 36
  • Next »
Label: "Field Devices" Show all articles

What is the correct packing Kit for the MZX valve range

Issue Need to order packing Kit for the MZX valve Environment MZX Valve packing kit Cause Valve leaking Resolution The specification number for the packing kit for valve size half inch to two inches is 626-9-204 
View full article
Picard Product_Support
‎2018-09-06 01:21 PM

Labels:
  • Field Devices
891 Views

What is the DC1100 strap on sensor spec number?

Issue Information Environment Optimiser/compensator Controller Cause Requirement Resolution Specification No. STC600D Part No. 5126020000
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • Field Devices
  • Satchwell BAS & Sigma
2109 Views

What is the life expectancy of the LCD display of smart sensors with available display?

Issue What is the life expectancy of the LCD display of smart sensors with available display? Environment Smart sensor with LCD display Cause Display life expectancy. Resolution The Life expectancy of an LCD Display is 50K hours. Note: Life is reduced if LCD works under direct sunlight. If you use a LED backlight in a LCD module the life expectancy of the LED is 30K to 50K hours, depending on the forward current. EL backlights are available but we don’t recommend them because of their short life (3K hours) and EMC problems. The AC voltage is generated by the DC to AC inverter.  
View full article
Picard Product_Support
‎2018-09-06 01:19 PM

Labels:
  • Andover Continuum
  • Field Devices
1108 Views

Enabling / Disabling the WoW64 optional feature in Windows Server 2008 R2 - R4 (Windows 32-bit on Windows 64-bit)

Issue Even though Windows Server 2008 R2 is exclusively a 64-bit operating system, 32-bit applications are supported by enabling the WoW64 optional feature. NOTE: These are general instructions for utilizing the WoW64 function. Not all Schneider Software will be able to run in an emulated environment. If uncertain, please check with Product Support Services to ensure proper installation. Product Line Andover Continuum, Field Devices, Other, Satchwell MicroNet, Satchwell Sigma, TAC INET, TAC Vista Environment Windows Server 2008 R2 WoW64 feature. All 64bit OS Cause If the WoW64 feature is not enabled and you try to run a 32-bit application, the application will fail to execute. WoW64 option in in undesired state. Resolution If the WoW64 feature is not enabled and you try to run a 32-bit application, the application will fail to execute. The WoW64 execution layer is an optional component that is installed by default on R2 releases. You can save resources by removing the feature if you are not going to be running 32-bit applications on your Server Core install. Install the WoW64 Execution Layer using the following command: dism /online /enable-feature /featurename:ServerCore-WOW64 If your solution has a .NET 32-bit dependency, then also invoke the following sequence: dism /online /enable-feature /featurename:NetFx2-ServerCore dism /online /enable-feature /featurename:NetFx2-ServerCore-WOW64 Note: In Windows Server 2008 R2 RC1, WoW64 is enabled by default. If you don't want WoW64 enabled, just disable the feature as follows:  dism /online /disable-feature /featurename:ServerCore-WOW64
View full article
Picard Product_Support
‎2018-09-06 01:14 PM

Labels:
  • Andover Continuum
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
15163 Views

What wall module (room sensor) to use for the TAC Vista series controllers

Issue What wall module (room sensor) to use for the TAC Vista series controllers Environment TAC Xenta 101, Xenta 102, Xenta 103, Xenta 104 TAC Xenta 301, Xenta 302, TAC Xenta281,  Xenta 282, Xenta 283 TAC Xenta 401 Cause Need to know what sensors to use Resolution Use the Sensor selection tool
View full article
Picard Product_Support
‎2018-09-10 05:05 AM

Labels:
  • Field Devices
  • TAC Vista
1003 Views

V321 (DN65 to DN100), M800, M1500, MV15B, M3000

Issue The Forta range actuator does not fit onto the V321 Valve. Environment V321 M800 M1500 MV15B M3000 Cause The actuator has a 10mm fitting, the valve (DN65 to DN100 only) spindle has a 8mm stem. Resolution On V321 valves size DN65 to DN100 an adaptor piece is supplied with the valve part no. 880-0133-000 to adapt the valve spindle to the actuator drive. The part no. 880-0133-000 can be ordered separately.
View full article
Picard Product_Support
‎2018-09-06 01:06 PM

Labels:
  • Field Devices
1802 Views

Replacing a M15 actuator when mounted to a VTRA.

Issue Which actuator should be used as replacement to a M15 actuator that is mounted on a VTRA Valve? Environment VTRA DN65 M15 24V / 12VA 15 Nm 300s / 180° Cause Currently used actuator is no longer available. Resolution Use EM9/180 (part no 8601110000) together with Linkage kit E/M9-VTRA (part no 8600990000).
View full article
Picard Product_Support
‎2018-09-06 01:05 PM

Labels:
  • Field Devices
1045 Views

Is the DC1100C still available? Is the DCCOMMS software still available?

Issue Is the DC1100C still available? Is the DCCOMMS software still available? Environment DC1100C DC1100 C DCCOMMS DC COMMS DC1100 DC1400 DC1000C DC1000 C Cause Is the DC1100C and the DCCOMMS software still available? Resolution The DC1100C had the communication module so that the controller could be interrogated remotely. This controller is no longer available. The DCCOMMS software ran in a DOS environment and is also obsolete. The DC1000C or DC1100C must not be confused with the DC1100 or the DC1400, these are the same controllers but without the communication interface and are still available.
View full article
Picard Product_Support
‎2018-09-06 01:04 PM

Labels:
  • Field Devices
880 Views

Valve, Actuator, Sensor, Field Device, Peripheral, HVAC Control Devices Datasheets and Catalogues, Selection Tool.

Issue Valve Datasheet & Catalogue Actuator Datasheet & Catalogue Sensor Datasheet & Catalogue Field Device Datasheet & Catalogue Peripheral Datasheet & Catalogue HVAC Control Devices Selection Tool Environment Actuator Valve Sensor Field Device Peripheral HVAC Control Device Selection Tool Cause Need for valve and actuator information. Need for sensor information. Resolution For European and American Field Device and Valve datasheets/technical publications and catalogues click here to go to the website and select which range that is required. Or the EMEA  sensor catalogue  or the valve and actuator catalogues can be download from the Download Center For the Sensor selection tool click here. For the Heat Meter selection tool click here. For the Cross Reference selection tool click here. 
View full article
Picard Product_Support
‎2018-09-10 07:32 AM

Labels:
  • Field Devices
1895 Views

Configuring a Multical 601 meter.

Issue What is necessary to do in order to change settings in the Kamstrup Multical 601 meter? Environment Kamstrup Multical 601 Cause How to change the basic settings in pulse calculations from MWhrs to kWhrs, and also other settings.   Resolution Metertool software (part no: MAHWSWTOOL) together with the Optical eye USB hardware (part no: MAOPTICUSB) is required for this type of configuration. For more information, please take a look at MeterTool for Multical 601 presentation.
View full article
Picard Product_Support
‎2018-09-10 04:58 AM

Labels:
  • Field Devices
1428 Views

Veris CO Sensor Hasn't DIP Switch for Voltage Adjustment

Issue According to the datasheet, there should be a DIP switch for output voltage adjustment for Veris CO sensor. But some of them haven't such DIP switch. Environment Veris Sensor Cause There are several models for Veris CO sensor. For example, GWVAS is the wall mount sensor with voltage output signal, while GDMAS is the duct mount sensor with current output signal. The sensor with current output signal hasn't such DIP switch for voltage output. Resolution This model of product hasn't such DIP switch.
View full article
Picard Product_Support
‎2018-09-06 12:59 PM

Labels:
  • Field Devices
824 Views

Running Forta series actuators on 24VDC

Issue Is it possible to run a Forta series actuator on 24VDC? Environment TAC Forta series actuators: M300 M310 M400 M750 M800 M1500 M3000 Cause The TAC Forta series actuators older documentation suggests it can only be run on 24VAC only. Resolution The TAC Forta series actuators can run on 24VAC +/- 25% or 24Vdc +/- 10%. For more specific details on tolerances, please see the data sheet for each product.
View full article
Picard Product_Support
‎2018-09-06 12:58 PM

Labels:
  • Field Devices
1128 Views

Controlling a Forta actuator from PLC system

Issue Controlling a Forta actuator from PLC system using 0-10V output. Environment TAC Forta actuator  PLC controller Cause The PLC system is using a 0-10V control output to control the TAC Forta (MX and X1 input), powering the TAC Forta (G and G0 input)using a separate transformer. Resolution As long as the PLC system and TAC forta units are fed from separate transformers, this should cause no problem, and galvanic isolators on the control signal should not be required. Make sure to not mix up G and G0 in case several TAC Forta actuators are fed through the same transformer.
View full article
Picard Product_Support
‎2018-09-06 12:58 PM

Labels:
  • Field Devices
847 Views

Cross reference on Belimo actuator LMQU24-SR .

Issue Schneider Electric part number equivalent to Belimo LMQU24-SR  Environment Belimo LMQU24-SR Cause Internal purchasing instead of external. Resolution No cross reference is available. The Belimo actuator in question is not represented in our portfolio and needs to be purchased from the manufacturer directly.
View full article
Picard Product_Support
‎2018-09-06 12:53 PM

Labels:
  • Field Devices
924 Views

Actuator MD20 gearbox materials

Issue Requesting material specifications used in gear box on actuators MD20 in its different versions. Environment Actuator MD20 Cause Possible exposure to heat (desert climate). Resolution The gear box has a mix of plastic and steel plate gears. 5 in total. Experience from manufacturer states that there should be no issues in using them in a desert climate like Dubai or similar.
View full article
Picard Product_Support
‎2018-09-06 12:53 PM

Labels:
  • Field Devices
961 Views

Motor type used in MD20 actuator

Issue Motor type used in MD20 actuator Environment Desert/warm climate MD20 actuator Cause Motor configuration Resolution A brushless type, designed by Belimo is used in all MD 20 actuators.
View full article
Picard Product_Support
‎2018-09-06 12:53 PM

Labels:
  • Field Devices
988 Views

Different Forta versions.

Issue There are different versions of TAC Forta actuators available on the global market. Environment Forta actuators on the global market. M400 M400A M800 M800A M1500 M1500A Cause There are different types of Fortas available. Resolution The "A" version of the Forta actuators are designed to be used on the US market. There are several differences between the "A" series and the regular type, but the key ones are: UL approval Electrical connections designed to conform to US standards The VB version is equipped with a short yoke to fit directly on the VB series of valves used on the US market.
View full article
Picard Product_Support
‎2018-09-06 12:52 PM

Labels:
  • Field Devices
1173 Views

SE 7300 override/°C-°F button choice.

Issue When defining configuration on SE7300 part no, your choice is between "0" (override) and "5" (possibility to change between °C and °F in interface). Environment SE7300 Cause its not possible to have both override and °C/°F feature Resolution When defining the part number, you will have to choose. The override feature is usually the preferred choice in industrial applications, while the °C/°F feature is used for Hotels and similar, where users are given the possibility to change unit of desired temperature.
View full article
Picard Product_Support
‎2018-09-06 12:51 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
1554 Views

SE7300 specification choice

Issue When specifying the configuration of the SE7300 you can choose between "50" and "55" in step 5 of the part number. Product Line EcoStruxure Building Expert, Field Devices Environment SE7300 Cause Different options of configuration when defining the part no for the SE7300 Resolution The difference is that the "50" option is PIR Ready, but PIR cover of unit is not included. Option "55" is with the PIR cover already mounted upon delivery. 
View full article
Picard Product_Support
‎2018-09-06 12:51 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
1466 Views

Actuator with position feedback signal for V321 (V292, V222) DN125-DN150

Issue Looking for actuator with position feedback signal for V321 (V292, V222) DN125-DN150 since M22/M50 does not provide this option. Environment V222 DN125 V222DN150 V292 DN125 V292 DN150 V321 DN125 V321 DN150 M22 M50 Cause Actuator with positioning feedback signal for DN125 - DN150 valves Resolution There are currently no suitable actuators available that gives the Forta features on the M22/M50 actuators. Also, there is no linkage kit that would make the Forta series actuators fit on the DN125 and DN150 size valves, due to its different design.
View full article
Picard Product_Support
‎2018-09-06 12:51 PM

Labels:
  • Field Devices
1646 Views
  • « Previous
    • 1
    • …
    • 20
    • 21
    • 22
    • …
    • 36
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of