Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Field Devices
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "field devices"

View in: "Building Automation Knowledge Base" | Community

721 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 20
    • 21
    • 22
    • …
    • 37
  • Next »
Label: "Field Devices" Show all articles

Can the A or B port of a mixing or diverting valve be capped to change the valve to a two-way valve?

Issue Can you cap the A port or B port of a mixing or diverting valve to change the valve to a two way (straight through) valve? Product Line Field Devices Environment VB-9313 series Cause Capping A port or B port of a mixing or diverting valve to change the valve to a two way (straight through) valve Resolution Schneider Electric does not recommend this modification for the VB-9313 series, because the valves are not equal percentage and therefore will not provide good control. The valve performs as a linear valve when both ports are utilized. These curves are not additive. Total flow is determined with both ports contributing. The valve will perform as a quick acting valve if the B port is plugged and a nominally linear valve if the A port is plugged. Additional problems that can occur are: Insufficient force to close off. Two way valves usually require high actuator forces to provide close off. Valves are not designed to be tight seating. Valves are rated ANSI III therefore flow leakage through the controlled coil can be expected. Flow direction through the valve can not be reversed. Flow must oppose the plug when closing. Flow aiding the plug may create hammer by causing the plug to overcome the actuator force and slam against the seat. When converted to a two way control valve for a variable flow system, 3-way valves tend to be extremely over-sized creating poor process control. After considering the pros and cons of making this type of modification, you may choose to proceed with this modification. The performance penalties should be less in chilled water applications and higher in hot water application.
View full article
Picard Product_Support
‎2018-09-06 02:29 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-06-05 01:22 PM

Labels:
  • Field Devices
2043 Views

TS-58XX 1,000 Ohm Platinum sensors resistance table

Issue TS-58XX 1,000 Ohm Platinum sensors resistance table Environment TS-58XX 1,000 Ohm Platinum Cause Resistance tables are sometimes required for compatibility measures. Resolution Temp (°C) Temp (°F) Ohms -40 -40 842.7 -39 -38.2 846.7 -38 -36.4 850.6 -37 -34.6 854.6 -36 -32.8 858.5 -35 -31 862.5 -34 -29.2 866.4 -33 -27.4 870.4 -32 -25.6 874.3 -31 -23.8 878.3 -30 -22 882.2 -29 -20.2 886.1 -28 -18.4 890.1 -27 -16.6 894 -26 -14.8 898 -25 -13 901.9 -24 -11.2 905.8 -23 -9.4 909.8 -22 -7.6 913.7 -21 -5.8 917.7 -20 -4 921.6 -19 -2.2 925.5 -18 -0.4 929.5 -17 1.4 933.4 -16 3.2 937.3 -15 5 941.3 -14 6.8 945.2 -13 8.6 949.1 -12 10.4 953 -11 12.2 957 -10 14 960.9 -9 15.8 964.8 -8 17.6 968.7 -7 19.4 972.6 -6 21.2 976.5 -5 23 980.5 -4 24.8 984.4 -3 26.6 988.3 -2 28.4 992.2 -1 30.2 996.1 0 32 1000 1 33.8 1003.9 2 35.6 1007.8 3 37.4 1011.7 4 39.2 1015.6 5 41 1019.5 6 42.8 1023.4 7 44.6 1027.3 8 46.4 1031.2 9 48.2 1035.1 10 50 1039 11 51.8 1042.9 12 53.6 1046.8 13 55.4 1050.7 14 57.2 1054.6 15 59 1058.5 16 60.8 1062.3 17 62.6 1066.2 18 64.4 1070.1 19 66.2 1074 20 68 1077.9 21 69.8 1081.8 22 71.6 1085.7 23 73.4 1089.5 24 75.2 1093.4 25 77 1097.3 26 78.8 1101.2 27 80.6 1105.1 28 82.4 1108.9 29 84.2 1112.8 30 86 1116.7 31 87.8 1120.6 32 89.6 1124.4 33 91.4 1128.3 34 93.2 1132.2 35 95 1136.1 36 96.8 1139.9 37 98.6 1143.8 38 100.4 1147.7 39 102.2 1151.5 40 104 1155.4 41 105.8 1159.3 42 107.6 1163.1 43 109.4 1167 44 111.2 1170.8 45 113 1174.7 46 114.8 1178.6 47 116.6 1182.4 48 118.4 1186.3 49 120.2 1190.1 50 122 1194 51 123.8 1197.9 52 125.6 1201.7 53 127.4 1205.6 54 129.2 1209.4 55 131 1213.3 56 132.8 1217.1 57 134.6 1221 58 136.4 1224.8 59 138.2 1228.7 60 140 1232.5 61 141.8 1236.3 62 143.6 1240.2 63 145.4 1244 64 147.2 1247.8 65 149 1251.7 66 150.8 1255.5 67 152.6 1259.3 68 154.4 1263.1 69 156.2 1267 70 158 1270.8 71 159.8 1274.6 72 161.6 1278.4 73 163.4 1282.3 74 165.2 1286.1 75 167 1289.9 76 168.8 1293.7 77 170.6 1297.5 78 172.4 1301.4 79 174.2 1305.2 80 176 1309 81 177.8 1312.8 82 179.6 1316.6 83 181.4 1320.4 84 183.2 1324.2 85 185 1328.1 86 186.8 1331.9 87 188.6 1335.7 88 190.4 1339.5 89 192.2 1343.3 90 194 1347.1 91 195.8 1350.9 92 197.6 1354.7 93 199.4 1358.5 94 201.2 1362.3 95 203 1366.1 96 204.8 1369.9 97 206.6 1373.7 98 208.4 1377.5 99 210.2 1381.3 100 212 1385.1 101 213.8 1388.9 102 215.6 1392.7 103 217.4 1396.4 104 219.2 1400.2 105 221 1404 106 222.8 1407.8 107 224.6 1411.6 108 226.4 1415.3 109 228.2 1419.1 110 230 1422.9 111 231.8 1426.7 112 233.6 1430.5 113 235.4 1434.2 114 237.2 1438 115 239 1441.8 116 240.8 1445.6 117 242.6 1449.4 118 244.4 1453.1 119 246.2 1456.9 120 248 1460.7
View full article
Picard Product_Support
‎2018-09-06 02:30 PM

Last Updated: Administrator CraigEl Administrator ‎2019-06-03 07:07 PM

Labels:
  • Field Devices
2163 Views

TS-59XX 1,000 ohm copper sensors resistance table

Issue TS-59XX 1,000 ohm copper sensors resistance table Environment TS-59XX Cause Converting Resistance to Temperature to characterize the sensor. Resolution Temp (°F) Temp (°C) Ohms -40 -40 759.8 -39 -39.44 762 -38 -38.89 764.2 -37 -38.33 766.4 -36 -37.78 768.6 -35 -37.22 770.8 -34 -36.67 772.9 -33 -36.11 775.1 -32 -35.56 777.3 -31 -35 779.5 -30 -34.44 781.7 -29 -33.89 783.9 -28 -33.33 786 -27 -32.78 788.2 -26 -32.22 790.4 -25 -31.67 792.6 -24 -31.11 794.8 -23 -30.56 797 -22 -30 799.1 -21 -29.44 801.3 -20 -28.89 803.5 -19 -28.33 805.7 -18 -27.78 807.9 -17 -27.22 810.1 -16 -26.67 812.2 -15 -26.11 814.4 -14 -25.56 816.6 -13 -25 818.8 -12 -24.44 821 -11 -23.89 823.2 -10 -23.33 825.3 -9 -22.78 827.5 -8 -22.22 829.7 -7 -21.67 831.9 -6 -21.11 834.1 -5 -20.56 836.3 -4 -20 838.4 -3 -19.44 840.6 -2 -18.89 842.8 -1 -18.33 845 0 -17.78 847.2 1 -17.22 849.2 2 -16.67 851.5 3 -16.11 853.7 4 -15.56 855.9 5 -15 858.1 6 -14.44 860.3 7 -13.89 862.5 8 -13.33 864.6 9 -12.78 866.8 10 -12.22 869 11 -11.67 871.2 12 -11.11 873.4 13 -10.56 875.6 14 -10 877.7 15 -9.44 879.9 16 -8.89 882.1 17 -8.33 884.3 18 -7.78 886.5 19 -7.22 888.7 20 -6.67 890.8 21 -6.11 893 22 -5.56 895.2 23 -5 897.4 24 -4.44 899.6 25 -3.89 901.8 26 -3.33 903.9 27 -2.78 906.1 28 -2.22 908.3 29 -1.67 910.5 30 -1.11 912.7 31 -0.56 914.9 32 0 917 33 0.56 919.2 34 1.11 921.4 35 1.67 923.6 36 2.22 925.8 37 2.78 928 38 3.33 930.1 39 3.89 932.3 40 4.44 934.5 41 5 936.7 42 5.56 938.9 43 6.11 941.1 44 6.67 943.2 45 7.22 945.4 46 7.78 947.6 47 8.33 949.8 48 8.89 952 49 9.44 954.2 50 10 956.3 51 10.56 958.5 52 11.11 960.7 53 11.67 962.9 54 12.22 965.1 55 12.78 967.3 56 13.33 969.4 57 13.89 971.6 58 14.44 973.8 59 15 976 60 15.56 978.2 61 16.11 980.4 62 16.67 982.5 63 17.22 984.7 64 17.78 986.9 65 18.33 989.1 66 18.89 991.3 67 19.44 993.4 68 20 995.6 69 20.56 997.8 70 21.11 1000 71 21.67 1002.2 72 22.22 1004.4 73 22.78 1006.5 74 23.33 1008.7 75 23.89 1010.9 76 24.44 1013.1 77 25 1015.3 78 25.56 1017.5 79 26.11 1019.6 80 26.67 1021.8 81 27.22 1024 82 27.78 1026.2 83 28.33 1028.4 84 28.89 1030.6 85 29.44 1032.7 86 30 1034.9 87 30.56 1037.1 88 31.11 1039.3 89 31.67 1041.5 90 32.22 1043.7 91 32.78 1045.8 92 33.33 1048 93 33.89 1050.2 94 34.44 1052.4 95 35 1054.6 96 35.56 1056.8 97 36.11 1058.9 98 36.67 1061.1 99 37.22 1063.5 100 37.78 1065.5 101 38.33 1067.7 102 38.89 1069.9 103 39.44 1072 104 40 1074.2 105 40.56 1076.4 106 41.11 1078.6 107 41.67 1080.8 108 42.22 1083 109 42.78 1085.1 110 43.33 1087.3 111 43.89 1089.5 112 44.44 1091.7 113 45 1093.9 114 45.56 1096.1 115 46.11 1098.2 116 46.67 1100.4 117 47.22 1102.6 118 47.78 1104.8 119 48.33 1107 120 48.89 1109.2 121 49.44 1111.3 122 50 1113.5 123 50.56 1115.7 124 51.11 1117.9 125 51.67 1120.1 126 52.22 1122.3 127 52.78 1124.4 128 53.33 1126.6 129 53.89 1128.8 130 54.44 1131 131 55 1133.2 132 55.56 1135.4 133 56.11 1137.5 134 56.67 1139.7 135 57.22 1141.9 136 57.78 1144.1 137 58.33 1146.3 138 58.89 1148.5 139 59.44 1150.6 140 60 1152.8 141 60.56 1155 142 61.11 1157.2 143 61.67 1159.4 144 62.22 1161.6 145 62.78 1163.7 146 63.33 1165.9 147 63.89 1168.1 148 64.44 1170.3 149 65 1172.5 150 65.56 1174.7 151 66.11 1176.8 152 66.67 1179 153 67.22 1181.2 154 67.78 1183.4 155 68.33 1185.6 156 68.89 1187.8 157 69.44 1189.9 158 70 1192.1 159 70.56 1194.3 160 71.11 1196.5 161 71.67 1198.7 162 72.22 1200.9 163 72.78 1203 164 73.33 1205.2 165 73.89 1207.4 166 74.44 1209.6 167 75 1211.8 168 75.56 1214 169 76.11 1216.1 170 76.67 1218.3 171 77.22 1220.5 172 77.78 1222.7 173 78.33 1224.9 174 78.89 1227.1 175 79.44 1229.2 176 80 1231.4 177 80.56 1233.6 178 81.11 1235.8 179 81.67 1238 180 82.22 1240.2 181 82.78 1242.3 182 83.33 1244.5 183 83.89 1246.7 184 84.44 1248.9 185 85 1251.1 186 85.56 1253.3 187 86.11 1255.4 188 86.67 1257.6 189 87.22 1259.8 190 87.78 1262 191 88.33 1264.2 192 88.89 1266.4 193 89.44 1268.5 194 90 1270.7 195 90.56 1272.9 196 91.11 1275.1 197 91.67 1277.3 198 92.22 1279.5 199 92.78 1281.6 200 93.33 1283.8 201 93.89 1286 202 94.44 1288.2 203 95 1290.4 204 95.56 1292.6 205 96.11 1294.7 206 96.67 1296.9 207 97.22 1299.1 208 97.78 1301.3 209 98.33 1303.5 210 98.89 1305.7 211 99.44 1307.8 212 100 1310 213 100.56 1312.2 214 101.11 1314.4 215 101.67 1316.6 216 102.22 1318.8 217 102.78 1320.9 218 103.33 1323.1 219 103.89 1325.3 220 104.44 1327.5 221 105 1329.7 222 105.56 1331.9 223 106.11 1334 224 106.67 1336.2 225 107.22 1338.4 226 107.78 1340.6 227 108.33 1342.8 228 108.89 1345 229 109.44 1347.1 230 110 1348.3 231 110.56 1351.5 232 111.11 1353.7 233 111.67 1355.9 234 112.22 1358.1 235 112.78 1360.2 236 113.33 1362.4 237 113.89 1364.6 238 114.44 1366.8 239 115 1369 240 115.56 1371.2 241 116.11 1373.3 242 116.67 1375.5 243 117.22 1377.7 244 117.78 1379.9 245 118.33 1382.1 246 118.89 1384.3 247 119.44 1386.4 248 120 1388.6 249 120.56 1390.8 250 121.11 1393
View full article
Picard Product_Support
‎2018-09-06 02:31 PM

Last Updated: Administrator CraigEl Administrator ‎2019-06-03 07:04 PM

Labels:
  • Field Devices
2284 Views

TS-57XX and TS-67XX 10 K thermistor (no 11 K shunt) sensor resistance table

Issue TS-57XX and TS-67XX 10 K thermistor (no 11 K shunt) sensor resistance table Environment Site with thermistor sensor Cause TS-57XX and TS-67XX 10 K thermistor (no 11 K shunt) sensor resistance table Resolution   Temp (°C) Temp (°F)  Sensor Ohms  -40.0° -40.0° 239,700 -39.0° -38.2° 226,000 -38.0° -36.4° 213,100 -37.0° -34.6° 201,100 -36.0° -32.8° 189,800 -35.0° -31.0° 179,200 -34.0° -29.2° 169,300 -33.0° -27.4° 159,900 -32.0° -25.6° 151,200 -31.0° -23.8° 142,900 -30.0° -22.0° 135,200 -29.0° -20.2° 127,900 -28.0° -18.4° 121,100 -27.0° -16.6° 114,600 -26.0° -14.8° 108,600 -25.0° -13.0° 102,900 -24.0° -11.2° 97,490 -23.0° -9.4° 92,420 -22.0° -7.6° 87,650 -21.0° -5.8° 83,150 -20.0° -4.0° 78,910 -19.0° -2.2° 74,910 -18.0° -0.4° 71,130 -17.0° 1.4° 67,570 -16.0° 3.2° 64,200 -15.0° 5.0° 61,020 -14.0° 6.8° 58,010 -13.0° 8.6° 55,170 -12.0° 10.4° 52,490 -11.0° 12.2° 49,950 -10.0° 14.0° 47,540 -9.0° 15.8° 45,270 -8.0° 17.6° 43,110 -7.0° 19.4° 41,080 -6.0° 21.2° 39,140 -5.0° 23.0° 37,310 -4.0° 24.8° 35,580 -3.0° 26.6° 33,930 -2.0° 28.4° 32,370 -1.0° 30.2° 30,890 0.0° 32.0° 29,490 1.0° 33.8° 28,160 2.0° 35.6° 26,890 3.0° 37.4° 25,690 4.0° 39.2° 24,540 5.0° 41.0° 23,460 6.0° 42.8° 22,430 7.0° 44.6° 21,440 8.0° 46.4° 20,510 9.0° 48.2° 19,620 10.0° 50.0° 18,780 11.0° 51.8° 17,980 12.0° 53.6° 17,210 13.0° 55.4° 16,480 14.0° 57.2° 15,790 15.0° 59.0° 15,130 16.0° 60.8° 14,500 17.0° 62.6° 13,900 18.0° 64.4° 13,330 19.0° 66.2° 12,780 20.0° 68.0° 12,260 21.0° 69.8° 11,770 22.0° 71.6° 11,290 23.0° 73.4° 10,840 24.0° 75.2° 10,410 25.0° 77.0° 10,000 26.0° 78.8° 9,602 27.0° 80.6° 9,226 28.0° 82.4° 8,866 29.0° 84.2° 8,522 30.0° 86.0° 8,194 31.0° 87.8° 7,879 32.0° 89.6° 7,579 33.0° 91.4° 7,291 34.0° 93.2° 7,016 35.0° 95.0° 6,752 36.0° 96.8° 6,500 37.0° 98.6° 6,258 38.0° 100.4° 6,027 39.0° 102.2° 5,805 40.0° 104.0° 5,592 41.0° 105.8° 5,389 42.0° 107.6° 5,194 43.0° 109.4° 5,007 44.0° 111.2° 4,827 45.0° 113.0° 4,655 46.0° 114.8° 4,490 47.0° 116.6° 4,331 48.0° 118.4° 4,179 49.0° 120.2° 4,033 50.0° 122.0° 3,893 51.0° 123.8° 3,758 52.0° 125.6° 3,629 53.0° 127.4° 3,505 54.0° 129.2° 3,385 55.0° 131.0° 3,271 56.0° 132.8° 3,160 57.0° 134.6° 3,054 58.0° 136.4° 2,952 59.0° 138.2° 2,854 60.0° 140.0° 2,760 61.0° 141.8° 2,669 62.0° 143.6° 2,582 63.0° 145.4° 2,498 64.0° 147.2° 2,417 65.0° 149.0° 2,339 66.0° 150.8° 2,264 67.0° 152.6° 2,191 68.0° 154.4° 2,122 69.0° 156.2° 2,055 70.0° 158.0° 1,990 71.0° 159.8° 1,928 72.0° 161.6° 1,868 73.0° 163.4° 1,810 74.0° 165.2° 1,754 75.0° 167.0° 1,700 76.0° 168.8° 1,648 77.0° 170.6° 1,598 78.0° 172.4° 1,550 79.0° 174.2° 1,503 80.0° 176.0° 1,458 81.0° 177.8° 1,414 82.0° 179.6° 1,372 83.0° 181.4° 1,332 84.0° 183.2° 1,293 85.0° 185.0° 1,255 86.0° 186.8° 1,218 87.0° 188.6° 1,183 88.0° 190.4° 1,149 89.0° 192.2° 1,116 90.0° 194.0° 1,084 91.0° 195.8° 1,053 92.0° 197.6° 1,023 93.0° 199.4° 994 94.0° 201.2° 966 95.0° 203.0° 939 96.0° 204.8° 913 97.0° 206.6° 887 98.0° 208.4° 863 99.0° 210.2° 839 100.0° 212.0° 816 101.0° 213.8° 794 102.0° 215.6° 773 103.0° 217.4° 752 104.0° 219.2° 732 105.0° 221.0° 713 106.0° 222.8° 694 107.0° 224.6° 675 108.0° 226.4° 658 109.0° 228.2° 640 110.0° 230.0° 624 111.0° 231.8° 607 112.0° 233.6° 592 113.0° 235.4° 576 114.0° 237.2° 562 115.0° 239.0° 547 116.0° 240.8° 533 117.0° 242.6° 520 118.0° 244.4° 507 119.0° 246.2° 494 120.0° 248.0° 482 121.0° 249.8° 470
View full article
Picard Product_Support
‎2018-09-06 02:31 PM

Last Updated: Administrator CraigEl Administrator ‎2019-06-03 07:00 PM

Labels:
  • Field Devices
3112 Views

TS-8XXX and TS-9XXX 1,000 Ohm Balco sensor, Celsius temperature resistance table.

Issue TS-8XXX and TS-9XXX 1,000 Ohm Balco sensor, Celsius temperature resistance table. Environment TS-8XXX TS-9XXX 1,000 Ohm Balco sensor Cause Unknown Cause Resolution Temp (°C) Ohms -40 779.0 -39 782.3 -38 785.6 -37 788.9 -36 792.3 -35 795.6 -34 799.0 -33 802.3 -32 805.7 -31 809.1 -30 812.5 -29 815.9 -28 819.3 -27 822.7 -26 826.2 -25 829.6 -24 833.1 -23 836.5 -22 840.0 -21 843.5 -20 847.0 -19 850.5 -18 854.1 -17 857.6 -16 861.1 -15 864.7 -14 868.3 -13 871.8 -12 875.4 -11 879.0 -10 882.6 -9 886.2 -8 889.9 -7 893.5 -6 897.1 -5 900.8 -4 904.5 -3 908.1 -2 911.8 -1 915.5 0 919.2 1 923.0 2 926.7 3 930.4 4 934.2 5 937.9 6 941.7 7 945.5 8 949.3 9 953.1 10 956.9 11 960.7 12 964.6 13 968.4 14 972.3 15 976.1 16 980.0 17 983.9 18 987.8 19 991.7 20 995.6 21 999.6 22 1003.5 23 1007.5 24 1011.4 25 1015.4 26 1019.4 27 1023.4 28 1027.4 29 1031.4 30 1035.4 31 1039.4 32 1043.5 33 1047.5 34 1051.6 35 1055.7 36 1059.8 37 1063.8 38 1068.0 39 1072.1 40 1076.2 41 1080.3 42 1084.5 43 1088.6 44 1092.8 45 1097.0 46 1101.2 47 1105.4 48 1109.6 49 1113.8 50 1118.0 51 1122.3 52 1126.5 53 1130.8 54 1135.1 55 1139.4 56 1143.7 57 1148.0 58 1152.3 59 1156.6 60 1160.9 61 1165.3 62 1169.6 63 1174.0 64 1178.4 65 1182.8 66 1187.2 67 1191.6 68 1196.0 69 1200.4 70 1204.9 71 1209.3 72 1213.8 73 1218.3 74 1222.7 75 1227.2 76 1231.7 77 1236.2 78 1240.8 79 1245.3 80 1249.8 81 1254.4 82 1259.0 83 1263.5 84 1268.1 85 1272.7 86 1277.3 87 1282.0 88 1286.6 89 1291.2 90 1295.9 91 1300.5 92 1305.2 93 1309.9 94 1314.6 95 1319.3 96 1324.0 97 1328.7 98 1333.4 99 1338.2 100 1342.9 101 1347.7 102 1352.5 103 1357.3 104 1362.1 105 1366.9 106 1371.7 107 1376.5 108 1381.3 109 1386.2 110 1391.0 111 1395.9 112 1400.8 113 1405.7 114 1410.6 115 1415.5 116 1420.4 117 1425.3 118 1430.3 119 1435.2 120 1440.2 121 1445.2 122 1450.1
View full article
Picard Product_Support
‎2018-09-06 02:31 PM

Last Updated: Administrator CraigEl Administrator ‎2019-06-03 06:53 PM

Labels:
  • Field Devices
2168 Views

Wiring configuration enabling connection of S-E Forta Actuator set in Increase / Decrease mode to early discrete Satchwell Climatronic CSC/CXR/CXT Controller.

Issue Wiring configuration enabling connection of S-E Forta Actuator set in Increase / Decrease mode to early discrete Satchwell Climatronic CSC/CXR/CXT Controller. Environment S-E Forta Actuator set in Increase / Decrease mode connected to early discrete Satchwell Climatronic CSC/CXR/CXT Controller. Cause Obsolescence of previous Actuator connected to early discrete Satchwell Climatronic CSC/CXR/CXT Controller. Resolution 1.  Connect S-E Forta Actuator set in Increase / Decrease mode to early discrete Satchwell Climatronic CSC/CXR/CXT Controller.  It should be noted that when connecting a S-E Forta Actuator set in Increase / Decrease operation mode to an early discrete Satchwell Climatronic CSC/CXR/CXT Controller it may be necessary to wire the Actuator in a 24v OPEN / 24v CLOSE / 0v COMMON configuration instead of the 0v OPEN / 0v CLOSE / 24v COMMON configuration as shown in the S-E Forta Actuator Data Sheets. 2.  With S-E Forta Actuator DIL Switch No.2 set ON in Increase / Decrease mode wire to the S-E Forta Actuator terminals as follows :- 24v Supply – wire to Terminal G 0v   Supply – wire to Terminal G0 24v Open signal – wire to Terminal VH 24v Close signal – wire to Terminal VC N.B. This deviation from the standard S-E Forta Actuator installation method should be recorded in the site Operating & Maintenance manual. A 24v supply must be present across Terminals G / G0 for the S-E Forta Actuator to work satisfactorily. A 4-wire connection must be made to the S-E Forta Actuator, instead of the 3-wire connection made to any Satchwell Actuator it is replacing. It is important to ensure that the 24v Power Supply to both the S-E Forta Actuator and the Satchwell Climatronic Controller share the same 0v potential. It is also important to ensure that the 24v Power Supply is capable of providing the higher level of VA required to operate the S-E Forta Actuator compared to that of any Actuator that it may be replacing. 
View full article
Picard Product_Support
‎2018-09-06 02:42 PM

Labels:
  • Field Devices
1296 Views

S-E L2SV Linkage Kit and S-E L7SV Linkage Kit compatibility with Satchwell Plug and Seat Valve Bodies.

Issue S-E L2SV Linkage Kit and S-E L7SV Linkage Kit compatibility with Satchwell Plug and Seat Valve Bodies. Environment Satchwell 1 series Plug and Seat 2-port and 3-port Valve Bodies. Satchwell 2 series Plug and Seat 2-port and 3-port Valve Bodies. Satchwell 3 series Plug and Seat 2-port and 3-port Valve Bodies. Satchwell 7 series Plug and Seat 2-port and 3-port Valve Bodies. Cause Use the correct S-E Linkage Kit with Satchwell Plug and Seat Valve bodies. Resolution 1.  Observe specification number of Satchwell Plug and Seat Valve Body Generally where a Satchwell AL series Linear Actuator is fitted to a Satchwell plug and seat Valve Body, the Actuator may be replaced by an equivalent S-E Forta or MV15B series Linear Actuator and appropriate S-E Linkage Kit. It should be noted however that neither the S-E L2SV Linkage Kit nor the S-E L7SV Linkage Kit will enable an S-E Forta or MV15B series Linear Actuator to be mounted on a Satchwell 7 series MZ/MZF or a Satchwell 7 series VZ/VZF plug and seat Valve Body. The internal screw threads of the Neck Adaptors included in the S-E L2SV Linkage Kit (880 – 0124 – 000) and S-E L7SV (880 – 0126 - 000) Linkage Kit are compatible with the external screw threads on Satchwell 1, 2 & 3 series Valve Body necks only. The external screw threads on Satchwell 7 series Valve Body necks however differ to those on Satchwell 1, 2 & 3 series Valve Body necks. Consequently neither the S-E L2SV Linkage Kit nor the S-E L7SV Linkage Kit will enable an S-E Forta or MV15B series Linear Actuator to be mounted on a Satchwell 7 series Valve Body. A S-E Forta series Linear Actuator may be mounted on a Satchwell 7 series Valve Body however using Linkage Kit 880 – 0135 – 000.  No equivalent Linkage Kit is currently available for use with the MV15B series Linear Actuator. The Satchwell Valve Body series may be determined from the Valve Body specification number stamped on the Valve Body Identification Collar, where the single middle digit of the specification number denotes the series. In the case of a Satchwell 7 series Valve Body for instance the single middle digit of the specification number will be the number 7 (e.g. 626 – 7 – 402)
View full article
Picard Product_Support
‎2018-09-06 02:40 PM

Labels:
  • Field Devices
2260 Views

How do I select an actuator and valve combination?

Issue How do I select an actuator and valve combination? Environment Actuator Valve Cause Select the correct actuator and valve part numbers. Resolution Refer to the TAC Catalog F-27414-*. Read the section on valve part numbers. Select the valve body needed. Refer to Catalog F-27382-*. Read through the actuator selection for MA, MC, MF, MK, MM, Mp, and MS to identify the desired actuator. Refer to TAC Catalog F-27414-*. find the page with the chosen actuator valve combination. Verify from the close off table that the actuator will meet the valve performance requirements. Turn to the actuator assembly code table and select the assembly code needed to complete the valve assembly number. ie: Vx-XXXX-XXX-X-XX. Order valve. If valve is not available as a factory assembly, order the individual parts and field assemble. The valve close off table provides the correct linkage kit required to couple the actuator and valve body, not all actuators require linkage kits.
View full article
Picard Product_Support
‎2018-09-06 02:36 PM

Labels:
  • Field Devices
1186 Views

Cross Reference of Obsolete Field Devices to Current Schneider Electric Field Devices.

Issue Cross Reference of Obsolete Field Devices to Current Schneider Electric Field Devices. Environment Field device replacement Cause Unknown replacement for obsolete field device part number Resolution There is an Online Cross Reference Guide located on our Schneider Electric Buildings Website. Enter the old part number into the field for part to cross reference & click on the search button not the ENTER key. The ENTER Key clears the part number entry. The Manufacturer's name is not required for a product search. Contact Product Support when no cross reference is found for additional help.
View full article
Picard Product_Support
‎2018-09-07 02:09 AM

Labels:
  • Field Devices
2151 Views

When to use ERIE Replacement motors 30-158-A,B,D,T,U instead of 30-118-A,B,D,T,U?

Issue When to use ERIE Replacement motors 30-158-A,B,D,T,U instead of 30-118-A,B,D,T,U? Environment ERIE Replacement motors 30-158-A,B,D,T,U ERIE Replacement motors 30-118-A,B,D,T,U Cause Find the correct replacement part for the AH/AG Actuator. Resolution Use 30-158-A,B,D,T,U if AH/AG Actuator was made after January of 2003.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • Field Devices
1141 Views

TS-58XXX & TS-81XXX Cover Kits w/inserts

Issue TS-58XXX & TS-81XXX Cover Kits w/inserts Environment TS-58XXX TS-81XXX Cause Compatible cover kits are not noted in the catalog. Resolution AT-80 Cover Kit will work.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • Field Devices
1310 Views

What is the packing Gland for obsolete TAC Globe Valves: VB-9XXX 2" and Smaller.

Issue What is the packing Gland for obsolete TAC Globe Valves: VB-9XXX 2" and Smaller. Environment TAC Globe Valves: VB-9XXX 2" and Smaller Cause Obsolete product. Resolution Part # YBA-616-1 Not listed separately for repair parts.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • Field Devices
1420 Views

Packing Gland Nut for TAC VB-9XXX Globe Valves 2 1/2" and larger.

Issue Packing Gland Nut for TAC VB-9XXX Globe Valves 2 1/2" and larger. Environment TAC VB-9XXX Globe Valves 2 1/2" and larger Cause Not listed in repair parts Resolution NYBA-63
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • Field Devices
1387 Views

Valve Linkage Kits for Hazardous Location Gear Train Actuators that mount on TAC Globe Valves: VB-7XXX & VB-9XXX.

Issue Valve Linkage Kits for Hazardous Location Gear Train Actuators that mount on TAC Globe Valves: VB-7XXX & VB-9XXX. Environment Valve Linkage VB-7XXX VB-9XXX Cause Part number for Valve Linkage Kits. Resolution Linkages are AV-291, AV-293, AV-295, AV-296 Reference literature # F-27441.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • Field Devices
1208 Views

Are there repair parts for the Erie Pop-Top valves?

Issue Are there repair parts for the Erie Pop-Top valves? Environment Erie Pop-Top Valves Cause Parts needed to repair Erie Pop-Top valves. Resolution Repair parts are available for the Erie Current Pop-Top valves. 100-080 = 2-way 1.0 to 5.0Cv 1/2" & 3/4" Swt 100-081 = 2-way 7.0Cv 3/4" Swt & NPT and 1" Swt 100-082 = 2-way 7.0Cv 1" NPT and 1 1/4" Swt 100-083 = 3-way 1.5 to 5.0Cv 1/2" & 3/4" Swt 100-084 = 3-way 7.0Cv 3/4" Swt & NPT and 1" Swt 100-085 = 3-way 7.5Cv 1" NPT and 1 1/4" Swt
View full article
Picard Product_Support
‎2018-09-06 02:33 PM

Labels:
  • Field Devices
1777 Views

Erie Aux Switches for the Current Pop-Top actuators are not field replaceable.

Issue Are the Erie Aux Switches for the Current Pop-Top actuators field replaceable? Environment Pop-Top actuators Cause Replace defeated part without replacing the whole unit. Resolution No they are not. The actuator would have to be replaced.
View full article
Picard Product_Support
‎2018-09-06 02:33 PM

Labels:
  • Field Devices
1173 Views

What is the Thermowell part number for the sensor TT-I-4-1?

Issue What is the Thermowell part number for the sensor TT-I-4-1? Environment TT-I-4-1 Cause Replacing the Thermowell for sensor TT-I-4-1 Resolution The thermowell for sensor TT-I-4-1 is either the W-S-4-1/2-1 for 1/2" MPT 4" long well or W-S-3/4-4-1 for 3/4" MPT and 4" long well
View full article
Picard Product_Support
‎2018-09-06 02:32 PM

Labels:
  • Field Devices
1452 Views

What is the part number for the thermowell for the sensor TT-I-6-1?

Issue What is the part number for the thermowell for the sensor TT-I-6-1? Environment TT-I-6-1 Cause Replacing the thermowell for sensor TT-I-6-1. Resolution The thermowell for sensor TT-I-6-1 is either W-S-6-1/2-1 for 1/2" mpt and 6" long well OR W-S-6-3/4-1 which is for 3/4" mpt and 6" long well.
View full article
Picard Product_Support
‎2018-09-06 02:32 PM

Labels:
  • Field Devices
1172 Views

Erie controllers SR-201, 301,601, 201-AT, 301-AT, and 601-AT. Voltage apparent on unpowered Relay Terminals.

Issue Erie controllers SR-201, 301,601, 201-AT, 301-AT, and 601-AT. Voltage apparent on unpowered Relay Terminals. Environment SR-201 SR-301 SR-601 SR201AT SR301AT SR601AT Cause The large foil surfaces used to carry the high currents of the switched loads of these control boards act as antennas causing the DMM to read a voltage signal. Resolution The voltage as read L2 to X1 approximately 12 VAC and L2 to X2 approximately 25 VAC is not harmful to humans or equipment and will not affect the operation of the unit. When determining if these induced voltages are present, all wiring except power wiring to L1 and L2 should be disconnected.
View full article
Picard Product_Support
‎2018-09-06 02:31 PM

Labels:
  • Field Devices
1596 Views

TS-7222 and TS-6722 30K thermistor sensor (no 11K shunt) resistance table

Issue TS-7222 and TS-6722 30K thermistor sensor (no 11K shunt) resistance table Environment TS-7222 TS-6722 Cause Specification on the sensing element. Resolution   Temp (°C) Temp (°F) Ohms    25.0°     77.0°    30,000    26.0°     78.8°    28,806    27.0°     80.6°    27,678    28.0°     82.4°    26,598    29.0°     84.2°    25,566    30.0°     86.0°    24,582    31.0°     87.8°    23,637    32.0°     89.6°    22,737    33.0°     91.4°    21,873    34.0°     93.2°    21,048    35.0°     95.0°    20,256    36.0°     96.8°    19,500    37.0°     98.6°    18,774    38.0°     100.4°    18,081    39.0°     102.2°    17,415    40.0°     104.0°    16,776    41.0°     105.8°    16,167    42.0°     107.6°    15,582    43.0°     109.4°    15,021    44.0°     111.2°    14,481    45.0°     113.0°    13,965    46.0°     114.8°    13,470    47.0°     116.6°    12,993    48.0°     118.4°    12,537    49.0°     120.2°    12,099    50.0°     122.0°    11,679    51.0°     123.8°    11,274    52.0°     125.6°    10,887    53.0°     127.4°    10,515    54.0°     129.2°    10,155    55.0°     131.0°    9,813    56.0°     132.8°    9,480    57.0°     134.6°    9,162    58.0°     136.4°    8,856    59.0°     138.2°    8,562    60.0°     140.0°    8,280    61.0°     141.8°    8,007    62.0°     143.6°    7,746    63.0°     145.4°    7,494    64.0°     147.2°    7,251    65.0°     149.0°    7,017    66.0°     150.8°    6,792    67.0°     152.6°    6,573    68.0°     154.4°    6,366    69.0°     156.2°    6,165    70.0°     158.0°    5,970    71.0°     159.8°    5,784    72.0°     161.6°    5,604    73.0°     163.4°    5,430    74.0°     165.2°    5,262    75.0°     167.0°    5,100    76.0°     168.8°    4,944    77.0°     170.6°    4,794    78.0°     172.4°    4,650    79.0°     174.2°    4,509    80.0°     176.0°    4,374    81.0°     177.8°    4,242    82.0°     179.6°    4,116    83.0°     181.4°    3,996    84.0°     183.2°    3,879    85.0°     185.0°    3,765    86.0°     186.8°    3,654    87.0°     188.6°    3,549    88.0°     190.4°    3,447    89.0°     192.2°    3,348    90.0°     194.0°    3,252    91.0°     195.8°    3,159    92.0°     197.6°    3,069    93.0°     199.4°    2,982    94.0°     201.2°    2,898    95.0°     203.0°    2,817    96.0°     204.8°    2,739    97.0°     206.6°    2,661    98.0°     208.4°    2,589    99.0°     210.2°    2,517    100.0°     212.0°    2,448    101.0°     213.8°    2,382    102.0°     215.6°    2,319    103.0°     217.4°    2,256    104.0°     219.2°    2,196    105.0°     221.0°    2,138    106.0°     222.8°    2,081    107.0°     224.6°    2,026    108.0°     226.4°    1,973    109.0°     228.2°    1,921    110.0°     230.0°    1,871    111.0°     231.8°    1,822    112.0°     233.6°    1,775    113.0°     235.4°    1,729    114.0°     237.2°    1,685    115.0°     239.0°    1,642    116.0°     240.8°    1,600    117.0°     242.6°    1,560    118.0°     244.4°    1,520    119.0°     246.2°    1,482    120.0°     248.0°    1,445    121.0°     249.8°    1,409 
View full article
Picard Product_Support
‎2018-09-06 02:31 PM

Labels:
  • Field Devices
1805 Views
  • « Previous
    • 1
    • …
    • 20
    • 21
    • 22
    • …
    • 37
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore