TS-7222 and TS-6722 30K thermistor sensor (no 11K shunt) resistance table

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • TS-7222 and TS-6722 30K thermistor sensor (no 11K shunt) resistance table
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1811 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

TS-7222 and TS-6722 30K thermistor sensor (no 11K shunt) resistance table

Picard Product_Support
‎2018-09-06 02:31 PM

Issue

TS-7222 and TS-6722 30K thermistor sensor (no 11K shunt) resistance table

Environment

  • TS-7222
  • TS-6722

Cause

Specification on the sensing element.

Resolution

 

Temp (°C) Temp (°F) Ohms 
  25.0°     77.0°    30,000 
  26.0°     78.8°    28,806 
  27.0°     80.6°    27,678 
  28.0°     82.4°    26,598 
  29.0°     84.2°    25,566 
  30.0°     86.0°    24,582 
  31.0°     87.8°    23,637 
  32.0°     89.6°    22,737 
  33.0°     91.4°    21,873 
  34.0°     93.2°    21,048 
  35.0°     95.0°    20,256 
  36.0°     96.8°    19,500 
  37.0°     98.6°    18,774 
  38.0°     100.4°    18,081 
  39.0°     102.2°    17,415 
  40.0°     104.0°    16,776 
  41.0°     105.8°    16,167 
  42.0°     107.6°    15,582 
  43.0°     109.4°    15,021 
  44.0°     111.2°    14,481 
  45.0°     113.0°    13,965 
  46.0°     114.8°    13,470 
  47.0°     116.6°    12,993 
  48.0°     118.4°    12,537 
  49.0°     120.2°    12,099 
  50.0°     122.0°    11,679 
  51.0°     123.8°    11,274 
  52.0°     125.6°    10,887 
  53.0°     127.4°    10,515 
  54.0°     129.2°    10,155 
  55.0°     131.0°    9,813 
  56.0°     132.8°    9,480 
  57.0°     134.6°    9,162 
  58.0°     136.4°    8,856 
  59.0°     138.2°    8,562 
  60.0°     140.0°    8,280 
  61.0°     141.8°    8,007 
  62.0°     143.6°    7,746 
  63.0°     145.4°    7,494 
  64.0°     147.2°    7,251 
  65.0°     149.0°    7,017 
  66.0°     150.8°    6,792 
  67.0°     152.6°    6,573 
  68.0°     154.4°    6,366 
  69.0°     156.2°    6,165 
  70.0°     158.0°    5,970 
  71.0°     159.8°    5,784 
  72.0°     161.6°    5,604 
  73.0°     163.4°    5,430 
  74.0°     165.2°    5,262 
  75.0°     167.0°    5,100 
  76.0°     168.8°    4,944 
  77.0°     170.6°    4,794 
  78.0°     172.4°    4,650 
  79.0°     174.2°    4,509 
  80.0°     176.0°    4,374 
  81.0°     177.8°    4,242 
  82.0°     179.6°    4,116 
  83.0°     181.4°    3,996 
  84.0°     183.2°    3,879 
  85.0°     185.0°    3,765 
  86.0°     186.8°    3,654 
  87.0°     188.6°    3,549 
  88.0°     190.4°    3,447 
  89.0°     192.2°    3,348 
  90.0°     194.0°    3,252 
  91.0°     195.8°    3,159 
  92.0°     197.6°    3,069 
  93.0°     199.4°    2,982 
  94.0°     201.2°    2,898 
  95.0°     203.0°    2,817 
  96.0°     204.8°    2,739 
  97.0°     206.6°    2,661 
  98.0°     208.4°    2,589 
  99.0°     210.2°    2,517 
  100.0°     212.0°    2,448 
  101.0°     213.8°    2,382 
  102.0°     215.6°    2,319 
  103.0°     217.4°    2,256 
  104.0°     219.2°    2,196 
  105.0°     221.0°    2,138 
  106.0°     222.8°    2,081 
  107.0°     224.6°    2,026 
  108.0°     226.4°    1,973 
  109.0°     228.2°    1,921 
  110.0°     230.0°    1,871 
  111.0°     231.8°    1,822 
  112.0°     233.6°    1,775 
  113.0°     235.4°    1,729 
  114.0°     237.2°    1,685 
  115.0°     239.0°    1,642 
  116.0°     240.8°    1,600 
  117.0°     242.6°    1,560 
  118.0°     244.4°    1,520 
  119.0°     246.2°    1,482 
  120.0°     248.0°    1,445 
  121.0°     249.8°    1,409 
Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • 3775
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore