Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Wiring configuration enabling connection of S-E Forta Actuator set in Increase / Decrease mode to early discrete Satchwell Climatronic CSC/CXR/CXT Controller.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Wiring configuration enabling connection of S-E Forta Actuator set in Increase / Decrease mode to early discrete Satchwell Cl...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Gary
    Gary
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1297 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Wiring configuration enabling connection of S-E Forta Actuator set in Increase / Decrease mode to early discrete Satchwell Climatronic CSC/CXR/CXT Controller.

Picard Product_Support
‎2018-09-06 02:42 PM

Issue

Wiring configuration enabling connection of S-E Forta Actuator set in Increase / Decrease mode to early discrete Satchwell Climatronic CSC/CXR/CXT Controller.

Environment

S-E Forta Actuator set in Increase / Decrease mode connected to early discrete Satchwell Climatronic CSC/CXR/CXT Controller.

Cause

Obsolescence of previous Actuator connected to early discrete Satchwell Climatronic CSC/CXR/CXT Controller.

Resolution

1.  Connect S-E Forta Actuator set in Increase / Decrease mode to early discrete Satchwell Climatronic CSC/CXR/CXT Controller. 

It should be noted that when connecting a S-E Forta Actuator set in Increase / Decrease operation mode to an early discrete Satchwell Climatronic CSC/CXR/CXT Controller it may be necessary to wire the Actuator in a 24v OPEN / 24v CLOSE / 0v COMMON configuration instead of the 0v OPEN / 0v CLOSE / 24v COMMON configuration as shown in the S-E Forta Actuator Data Sheets.

2.  With S-E Forta Actuator DIL Switch No.2 set ON in Increase / Decrease mode wire to the S-E Forta Actuator terminals as follows :-

24v Supply – wire to Terminal G
0v   Supply – wire to Terminal G0

24v Open signal – wire to Terminal VH
24v Close signal – wire to Terminal VC

N.B.

This deviation from the standard S-E Forta Actuator installation method should be recorded in the site Operating & Maintenance manual.

A 24v supply must be present across Terminals G / G0 for the S-E Forta Actuator to work satisfactorily.

A 4-wire connection must be made to the S-E Forta Actuator, instead of the 3-wire connection made to any Satchwell Actuator it is replacing.

It is important to ensure that the 24v Power Supply to both the S-E Forta Actuator and the Satchwell Climatronic Controller share the same 0v potential.

It is also important to ensure that the 24v Power Supply is capable of providing the higher level of VA required to operate the S-E Forta Actuator compared to that of any Actuator that it may be replacing. 

Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • 3231
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore