Can the A or B port of a mixing or diverting valve be capped to change the valve to a two-way valve?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Can the A or B port of a mixing or diverting valve be capped to change the valve to a two-way valve?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa139513
    sesa139513
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2044 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Can the A or B port of a mixing or diverting valve be capped to change the valve to a two-way valve?

Picard Product_Support
‎2018-09-06 02:29 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-06-05 01:22 PM

Issue

Can you cap the A port or B port of a mixing or diverting valve to change the valve to a two way (straight through) valve?

Product Line

Field Devices

Environment

VB-9313 series

Cause

Capping A port or B port of a mixing or diverting valve to change the valve to a two way (straight through) valve

Resolution

Schneider Electric does not recommend this modification for the VB-9313 series, because the valves are not equal percentage and therefore will not provide good control. The valve performs as a linear valve when both ports are utilized. These curves are not additive. Total flow is determined with both ports contributing. The valve will perform as a quick acting valve if the B port is plugged and a nominally linear valve if the A port is plugged.

Additional problems that can occur are:

  1. Insufficient force to close off. Two way valves usually require high actuator forces to provide close off.
  2. Valves are not designed to be tight seating. Valves are rated ANSI III therefore flow leakage through the controlled coil can be expected.
  3. Flow direction through the valve can not be reversed. Flow must oppose the plug when closing. Flow aiding the plug may create hammer by causing the plug to overcome the actuator force and slam against the seat.
  4. When converted to a two way control valve for a variable flow system, 3-way valves tend to be extremely over-sized creating poor process control.

After considering the pros and cons of making this type of modification, you may choose to proceed with this modification. The performance penalties should be less in chilled water applications and higher in hot water application.

Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • 3825
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore