Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 11
    • 12
    • 13
    • …
    • 500
  • Next »

How to configure an analog input on a DMS MicroSmart controller as a voltage input.

Issue How to configure an analog input on a DMS MicroSmart controller to function as a voltage input. Environment MSC-MPC (Revision 10) MSC-MPC-001 (Revision 11) Product Line TAC IA Series Cause The controller needs to accept voltage signals from sensors, but analog inputs must be configured correctly to interpret voltage rather than other signal types. Resolution To configure an analog input as a voltage input: Reference: MSC-MPC Install Instructions (F-24804-4)
View full article
Picard Product_Support
‎2018-09-11 12:12 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 06:39 PM

Labels:
  • TAC IA Series
1388 Views

Modify Microsmart Mode Control Point (PVALU) in Niagara G3 DMS Driver

Issue When integrating Microsmart controllers with Niagara G3 using the DMS driver, Mode Control points learned as Numeric Points cannot be modified directly. How can the stage setpoints (PVALU elements) be changed from the Niagara G3 station? Product Line TAC IA Series Environment Niagara G3 Microsmart driver Microsmart controllers Cause Mode Control points are learned into Niagara G3 as Numeric Points without writable options, preventing direct modification of stage setpoints (PVALU elements) from the station interface. Resolution Add PVALU Element to Database: Locate the Mode Control point and add the PVALU element for the specific stage to the Niagara G3 database. Update Command String and Index: Modify the Command String to include the PVALU element. Set the Index value to match the PVALU element (e.g., Index = 6 corresponds to PVALU,6 ). Enable Writable Action: After configuration, right-click on the Numeric Point in Niagara G3 to access an action item allowing modification of the PVALU element. Result: You can now adjust stage setpoints for Mode Control points directly from the Niagara G3 station interface.
View full article
Picard Product_Support
‎2018-09-10 10:59 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 06:29 PM

Labels:
  • TAC IA Series
1626 Views

Configure Analog Input as Contact Input on DMS MicroSmart MSC-MPC Controller

Issue How to configure an analog input on a DMS MicroSmart controller to function as a contact input when no dedicated contact inputs are available. Product Line TAC IA Series Environment MSC-MPC (Revision 10) MSC-MPC-001 (Revision 11) Cause No contact inputs available on the MSC-MPC Resolution Below are illustrations and explanations on how to configure an analog input as a contact input.  
View full article
Picard Product_Support
‎2018-09-10 01:32 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 06:24 PM

Labels:
  • TAC IA Series
1343 Views

Connecting a TS-58011-774 Platinum RTD Sensor to a DMS Microsmart MSC-MPC controller.

Issue When wiring a TS-58011-774 Platinum RTD sensor to a DMS Microsmart MSC-MPC controller, what are the acceptable offset values for accurate temperature readings? Can the wire length exceed 200 feet? Product Line TAC IA Series Environment DMS Microsmart controllers TS-58011-774 Platinum RTD sensor Cause A significant offset (approximately 6°F) was required to match readings with a handheld calibration device, raising concerns about wiring length and sensor accuracy. Resolution Offset Values: There is no fixed maximum or minimum offset value. Proper wiring minimizes the need for large offsets. Wire Length: Do not exceed 200 feet. Recommended Cable: Belden #9501 (AWG24). Calibration Steps: Review the sensor installation guide (F-24874) for Software Setup (page 3). Use the temperature/resistance table (page 5) to verify sensor accuracy. Apply appropriate offset values to correct wire-induced error. If necessary, use SOCALC (page 4) to create custom SCALE and OFSET values. Reference: TS-58000 Series Platinum RTD Room Sensor Installation Guidelines (F-24874)
View full article
Picard Product_Support
‎2018-09-10 05:05 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 06:21 PM

Labels:
  • TAC IA Series
3640 Views

ENC Licensed for DMS Shows “FeatureNotLicensedException: tac_llc:tacdms”

Issue An ENC licensed for DMS displays the error: Unlicensed: javax.baja.license.FeatureNotLicensedException: tac_llc:tacdms when attempting to access the DMS Network property sheet in Workbench. Product Line TAC IA Series Environment I/A Series G3, ENC-520 with TAC-LLC license installed Cause Although the TAC_LLC.license file is installed, the corresponding TAC_LLC.certificate is missing. The license will not be recognized without its certificate. Example of correct configuration: Licenses: TAC_LLC.license (never expires), Tridium.license Certificates: TAC_LLC.certificate, Tridium.certificate Resolution Two options to resolve the issue: If public Ethernet connectivity is available: Open Workbench and connect to the ENC. Navigate to Platform → License Manager. Select Import → Import licenses from license server. This will download and install all available licenses and certificates automatically. If public connectivity is not available: Download the attached TAC_LLC.certificate. Use Workbench to import the downloaded certificate file.
View full article
Picard Product_Support
‎2018-09-10 04:14 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 06:17 PM

Labels:
  • TAC IA Series
1168 Views

SAI Controller in DMS Does Not Appear as Microsmart Controller

Issue In a DMS installation, a controller listed as SAI in OPRIF does not appear as a Microsmart controller, even though its points update correctly. Users are unsure how to save its database. Product Line TAC IA Series Environment DMS (all revisions) Cause The SAI controller is an early-generation device designed for the DMS product line. It is a Slave AI Module (part number N604-003) with six analog inputs and firmware revision 8.x. Unlike Microsmart controllers, the SAI is not a smart controller and does not store or require a database. Resolution The SAI controller does not support database storage; therefore, there is no need to back up its database. All analog input points for the SAI must be created and managed directly in the DMS system. Identification tips: Look for part number N604-003 on the controller sticker. Check the PCB for an IC labeled with firmware 8.x. Reference diagram: SAI Module Figure. 
View full article
Picard Product_Support
‎2018-09-10 04:09 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 06:09 PM

Labels:
  • TAC IA Series
1926 Views

Troubleshooting DMS-Microsmart Bus Communication Issues

Issue Communication failures with Microsmart controllers on the DMS bus network. Product Line TAC IA Series Environment Microsmart controllers (all models installed with revision 9.x, 10.x, or 11.x firmware) Cause Common causes include: Incorrect power supply wiring or insufficient voltage Shared power between controllers and field devices Exceeding maximum controller count per RS-485 segment Improper network topology or cable type Missing or incorrectly installed End-of-Line (EOL) modules Ground loops or shield continuity issues Duplicate or illegal point names in controller database Faulty line drivers or incorrect address switch settings Resolution The following checklist provides several settings/configurations to review when faced with a communication problem at the controller level. The content was compiled from different resources, summarized, and laid out in an easy-to-use manner so as to provide a quick-reference document. Do all controllers have a power supply? Each takes 24 VAC from a Class 2 transformer ACTION: Confirm with a voltmeter. If no voltage present, check on-board fuse and then the local circuit breaker. Note: Do NOT ground the transformer’s secondary when powering a MSC-MPC-001. With other controller types, the secondary is grounded. If voltage is present, must be within tolerances (20.4 to 30 VAC) Confirm power (VA) requirements. Varies per controller (see installation instructions) Do the affected controllers share a common power supply? The MSC-MPC-001 must have its own DEDICATED power supply Other controller types can share the same AC transformer provided the VA rating is adequate ACTION: Review power wiring (see installation instructions) Do the affected controllers share a common power supply with output field devices? Power for the controllers and power for the output devices MUST REMAIN SEPARATE ACTION: Review controller and field device power wiring (see installation instructions) In addition, avoid wiring any half-wave and fullwave powered devices to the same transformer. How many MicroSmart controllers exist? Firmware revision 9, 10, & 11 family controllers can communicate on the same RS-485 wire segment simultaneously Maximum per RS-485 segment = 30 (31 if no repeater is installed) ACTION: Determine controller count If there are more than 31, a repeater/router is required If there are more than 62, only firmware revision 11 family controllers can be physically addressed higher than 62 Connect the first 30 controllers (isolate any additional nodes) and attempt/stabilize communications. Any repeaters installed? Allows the connection of two or more RS-485 wire segments Extends the maximum controller count by 30 (maximum of 124 addressable nodes supported) ACTION: Identify model number Review settings using its installation instructions Replace line drivers with known, good ones (Part# E21-1144) How rapidly is the Watch Dog Timer (WDT) LED blinking? Once / second = proper network communication A controller’s logical address is always one higher than the number calculated by the switch settings. For example, if all switches are OFF (binary equivalent of 0), the controller’s logical address is 1. If switches 1 & 2 are ON (binary equivalent of 3), the controller address is 4. Network wire connections ARE polarity sensitive. ACTION: Review LED activity No blinking but illuminated Verify proper power requirements & wiring (see installation instructions) Perform a hardware clear (place all address switches in the ON position and power cycle the controller) No blinking & not illuminated Check the on-board fuse Blinking faster than once / second Check the address switch for proper position. Verify address is not duplicated on the network Check the network connector and ensure it is properly inserted Ensure the + wire and – wire are properly identified and the shield wire is also connected. What is the length and topology of the controller trunk? Bus Topology Daisy-chain (no tees) 4000ft/1219m maximum wire length Trunk wiring is polarity sensitive Recommended cable: 24 AWG twisted-pair, shielded General Purpose: Under 1000ft, Belden#9501 Over 1000ft, Alpha#9823C Plenum & Riser-Rated: Under 1000ft, Belden#89503 Over 1000ft, Belden#89182 ACTION: Review the following: Ensure two EOL modules are installed. Each module must be installed correctly (black dot on module in the same corner as the white dot on the circuit board) Remove each EOL and check for following resistances: Pins 1-8: 3.3 kohms Pins 3-6: 150 ohms Pins 4-5: 3.3 kohms Ensure there are no ground loops in the + and – wires. To do this, use a multi-meter & measure the + and – wires, separately to earth ground Ensure the shield wire is continuous throughout the entire length of the trunk and connected to a solid earth ground in only one location Replace line drivers on the controllers (Part# E21-661). Check trunk voltages: + to earth ground: 2.2 – 2.6 Vdc – to earth ground: 2.2 – 2.6 Vdc If 0 Vdc or 5 Vdc is detected, check other controllers for bad line drivers. Determine cable used. If it is shielded, connect it to earth ground in ONE location through a 470 kK, ¼ watt resistor. The shield must be continuous throughout the wire segment. What is the condition of the controller database? ACTION: Review the controller database Illegal point names must be corrected. Illegal characters are: / # * : ; $ = | &. Duplicate point names must be corrected Will Operator Interface (Part# PS-OPRIF) communicate to the controller? Direct connection to a controller can only be done with the Firmware Revision 10 & 11 Families Accessing a networked controller through a direct connection using a MSC-LIM is possible but very slow (300 baud maximum). It is only recommended for checking communication status and not for application programming. It will also require a master controller (DMS35/350A/3500) ACTION: Attempt an upload of the controller database Requires a Laptop Interface Module (Part# MSC-LIM) Operator Interface version 11.41 and 11.6 both support direct connection to a controller If communication fails to work, try another controller to eliminate the pc and interface cabling from the troubleshooting process
View full article
Picard Product_Support
‎2018-09-10 03:36 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 06:05 PM

Labels:
  • TAC IA Series
1150 Views

DMS-35 Physical Appearance and Connector Details for Power and Communications

Issue A mothballed building is being recommissioned. It uses a DMS-35 with Microsmart controllers for building automation. The customer needs to know what the DMS-35 looks like, its dimensions, and the appearance of the power and communications connectors, which are missing. Product Line TAC IA Series Environment DMS-35 Cause Connectors for power and communications cables are missing, and the customer requires visual identification for installation. Resolution Digital photos of the DMS-35 unit are provided for reference. Scanned images of the obsolete installation guideline (portions thereof) are included to show connector details. Refer to the attached files: DMS35images.pdf dms35installguide.pdf
View full article
Picard Product_Support
‎2018-09-10 03:24 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 05:24 PM

Labels:
  • TAC IA Series
1357 Views

Modify Panel Unit Title in DMS Database Using OPRIF

Issue A panel unit’s title (description) in a DMS database needs to be updated. How can this be done using OPRIF? Product Line TAC IA Series Environment DMS Operator Interface (OPRIF) All revisions of DMS 35, DMS 350A, and DMS 3500 Cause Equipment naming has changed, requiring updates to the DMS database to maintain consistency. Resolution   Access the Message Text Table in OPRIF. Locate the Panel Unit Descriptor Message that needs modification. Use the following steps: Cursor down to the descriptor requiring modification. Press the “=” key. Type the new text for the title. Press Enter to save changes. For detailed instructions, refer to Chapter 4 – “Setting Up Tables” in the DMS Operator Interface User’s Guide (F-25467).
View full article
Picard Product_Support
‎2018-09-09 11:52 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 05:18 PM

Labels:
  • TAC IA Series
1277 Views

Offline License Activation in Device Administrator

Issue Customers using Device Administrator for offline license activation in EBO 7.0.3 face challenges due to changes in how entitlements are delivered via Software Companion. Product Line EcoStruxure Building Operation Environment Building Operation Device Administrator (v7) Software Companion Portal FlexNet Licensing Portal Offline systems (no internet access) Cause The current Software Companion tool does not generate an HTML entitlement certificate compatible with Device Administrator. Instead, it provides a PDF summary, which the Device Administrator cannot read or import. Resolution The simplest way is to enable Internet access for Device Administrator and add the entitlement ID. To activate licenses offline in Device Administrator: Do not use the PDF summary generated by Software Companion — it is not compatible with Device Administrator. There are several options available, each differing in complexity and time requirements. Webhelp(Adding an Entitlement without the HTML file when a Field Server is not Connected to License Server (FNO)), users can follow the follwing steps: In Device Administrator, click Entitlements. Click the Add Entitlement down arrow and click Manually Enter the entitlement ID. Click Next. Click Skip. If you know that you do not have any server connected to internet in the list, click Skip. If you do not click Skip, Device Administrator goes through all servers in your list until it finds one that is connected to internet. In the Entitlement Products - Enter Manually list , enter the Activation ID, Description and seat count for the product. Click Add Product , to add more products. Click Add. Note: It is recommended to verify the Activation ID, Description, and seat count in FlexNet Operations End-User Portal before proceeding with the steps. When there is no connection between the EcoStruxure BMS Server and License Activation Server, Device Administrator cannot synchronize the number of licenses in the entitlement that are available for activation. Instead, Device Administrator assumes that all licenses that was purchased can be activated.  Access the FlexNet Licensing Portal: FlexNet Operations End-User Portal Log in using the Entitlement ID. List all Entitlements. Select one Activation ID Use the View Certificate option. Download and save the certificate locally in HTML format. When using Save As - ensure you select the "Webpage, complete (*htm;*html) option  Repeat for each Activation ID listed in the Entitlement Import each HTML certificate into Device Administrator to load the entitlement offline. Create a server list away from the site, using Device Administrator, that has Internet access. Caution: this will wipe the current server list, remove all certificates (if used), and remove all servers added to Device Administrator. If the server list has already been created on site, save and export this list. Off-site or on a PC with Internet access, import (from step 1) or create a new server list in Device Administrator. Add the necessary entitlement IDs. Save and export the server list. Back on the on-site PC, import the exported server list to Device Administrator. If using a new server list (that is, no servers added from Step 1), add the required certificates and servers. Save this new list. It is advisable to export it as a backup in case of any issues. Proceed with the offline activation. EcoStruxure BMS Server Licensing on Servers not Connected to Internet Workflow. Once activated, remember to save and export the list for safekeeping. Comment: Investigation into why Software Companion does not generate HTML certificates is ongoing.  Device Administrator still requires either the HTML certificate or manual entry of activation IDs.
View full article
Picard RobertAndriolo Picard
‎2025-10-23 06:03 PM

Last Updated: Admiral StephenYang Admiral ‎2025-11-21 12:52 PM

Labels:
  • EcoStruxure Building Operation
582 Views

EH Series Humidity Sensors – Specifications, Setup, and Documentation

Issue Users need specifications, setup details, and documentation for EH Series Humidity Sensors. Product Line  Field Devices Environment EH Series Humidity sensors Cause  Lack of readily available technical details and installation guidance for EH Series sensors. Resolution Refer to the following resources for complete specifications and installation instructions: EH Series Specification Sheet EH Series Humidity Sensor Installation and Operation Instructions Legacy EH Series Installation Guide (for models with two dip switch sets) Key Specifications: Power Supply: +15 to 36 VDC or 24 VAC Output Options (Field-selectable): 4–20 mA, 0–5 VDC, 0–10 VDC Measurement Range: 0–100% RH Accuracy: ±2% RH (model dependent) Operating Temperature: -40°C to +70°C Applications: HVAC systems, clean rooms, humidity-controlled environments. Additional Notes: Ensure correct dip switch settings for output signal selection. For legacy models, use the “Old EH Series” guide.
View full article
Picard Product_Support
‎2018-09-06 10:02 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 04:48 PM

Labels:
  • Field Devices
10963 Views

Windows 10-Compatible Legacy Tools for DMS and NETWORK 8000

Issue Where can Windows 10-compliant legacy tools be obtained for use with DMS and NETWORK 8000 products? Product Line TAC IA Series Environment DMS NETWORK 8000 Cause Legacy tools require updated versions to ensure compatibility with Windows 10 environments. Resolution Windows 10-compliant versions of the following tools are available for download: OPRIF 11.6 (for DMS products) PSI 4.1 (for NETWORK 8000 products) The PSIv4.1.zip package includes: XPSI PSI MF2 AirBalance MicroNet-CI MicroNet AirBalance Important Notes: Direct ASD connection is supported when using the recommended SerialComm USB to RS485 Adapter (Model USB-485B) for use with PSI.  MNet-CI and MNet-Air Balance require the use of an MN-CIM converter. This is an RS-232 to U-Link adapter that connects between the laptop and MicroNet 2000 U-Link sensor bus. The MN-CIM adaptor is obsolete and no longer manufactured. This will also require either a laptop with an RS-232 port or a USB to RS-232 serial adapter capable of working with the MN-CIM. The recommendation is to purchase a Keyspan USB to RS-232 serial adapter from Tripp-Lite. These tools are not compatible with 64-bit Windows natively, but can operate in XP Mode. Operating System Compatibility Table: Tool Win 10 32-bit Win 10 32-bit XP Mode Win 10 64-bit XP Mode Win 10 64-bit PSI/XPSI 4.1 Yes Yes Yes No MNCI 4.0 Yes Yes Yes No Microflo Balance 4.0 Yes Yes Yes No PSOPRIF 11.6 No Yes Yes No
View full article
Picard Product_Support
‎2018-09-07 04:31 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 12:27 AM

Labels:
  • TAC IA Series
1365 Views

Network 8000, DMS, and Signal Manuals – Electronic Format Availability

Issue Are the Network 8000, DMS, and Signal product manuals available in an electronic format? Product Line TAC IA Series Environment Network 8000 DMS Signal Cause Customers and support teams need access to legacy product manuals in electronic format for reference and operational purposes. Resolution The attached Legacy.zip file includes Network 8000, I/A Series MicroNet 2000, DMS and SIGNAL product data, installation, user, and engineering documents.
View full article
Picard Product_Support
‎2018-09-07 03:01 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-20 11:51 PM

Labels:
  • TAC IA Series
2326 Views

Cannot Add or Link Points to DMS Panel Using Operator Interface (OPRIF)

Issue When connected serially to a DMS panel using Operator Interface (OPRIF), symbolic points cannot be added to the DMS, and Microsmart points fail to link. Product Line TAC IA Series Environment UltiVist server networked with multiple DMS panels via Ethernet DMS350A, DMS3500 (all firmware versions) Local serial connection to DMS panel using OPRIF software Cause The PSWRD element in the DMS database restricts point creation and linking when the panel is flagged as networked with an UltiVist server. If PSWRD contains an “N” flag (e.g., PSWRD = 159 03 2 N ), commands for creating, linking, or deleting points are blocked via serial OPRIF connection. Resolution Modify the PSWRD element to remove the “N” flag, allowing full database manipulation via serial connection: Example: PSWRD = 159 03 2 This enables point additions, deletions, and linking through OPRIF. Refer to Commands and Elements Reference (F-25469) for detailed instructions.
View full article
Picard Product_Support
‎2018-09-06 01:35 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-20 11:20 PM

Labels:
  • TAC IA Series
1457 Views

License activation or repair without Internet access

Issue License needs to be activated or repaired, but there is no Internet access on the computer hosting the license. Product Line EcoStruxure Building Operation Environment Building Operation License Administrator  Cause The computer cannot be moved to a location with Internet access for activation or repair. IT policies prohibit temporary Internet access for licensing purposes. Resolution SBO Offline Activation Tool Use the SBO Offline Activation Tool for offline license activation. Access the tool here: SBO Offline Activation Tool. Click Instruction and Help in the tool for step-by-step guidance and helpful videos/charts. SBO Offline License Repair The same tool can repair offline licenses. Access the tool here: SBO Offline Activation Tool. After launching the tool, go to Special Operations → Repair License. If repair fails, contact Support for further troubleshooting.
View full article
Picard Product_Support
‎2018-09-06 11:16 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-20 04:10 AM

Labels:
  • EcoStruxure Building Operation
18891 Views

USRobotics 5686 Modem Settings for DMS Panel Communication

Issue USRobotics 5686 series modems fail to connect properly with DMS panels. Product Line TAC IA Series Environment USRobotics 5686 series DMS panel Cause The V.92 protocol is enabled by default on USRobotics 5686 modems, which prevents compatibility with older modems used in DMS panels. Resolution Disable the V.92 protocol on the USRobotics 5686 modem by entering the following setup string (without quotation marks) in addition to any required strings from the referenced bulletin, then save the settings: AT +PIG=1 +PMH=1 +PQC=3 Refer to Bulletin 00-19 for additional configuration details.
View full article
Picard Product_Support
‎2018-09-07 02:04 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-19 11:45 PM

Labels:
  • TAC IA Series
1161 Views

Reusing NETWORK 8000 (ASD) or DMS (MicroSmart) Wiring for BACnet MS/TP Communication

Issue Can existing communication wiring from a NETWORK 8000 (ASD) or DMS (MicroSmart) system be reused for a BACnet MS/TP trunk? Product Line TAC IA Series Environment NETWORK 8000 (ASD) cable DMS (MicroSmart) cable BACnet MS/TP Cause ASD and MicroSmart cables were designed for lower baud rates. BACnet MS/TP networks often require higher speeds, which these cables may not reliably support beyond 9600 or 19200 baud, especially over extended distances. Resolution Reuse Conditions: ASD and MicroSmart wiring can be reused for BACnet MS/TP only at 9600 baud, and possibly 19200 baud under limited conditions. For higher baud rates or longer cable runs, replace with BACnet-compliant cable. Recommended Cable Specifications for BACnet MS/TP: Type: Shielded twisted pair Gauge: 18 AWG or 22 AWG Impedance: 100–120 Ω Capacitance: ≤ 30 pF/ft (98 pF/m) Maximum Length: 9600 baud: up to 1200 m (4000 ft) 38400 baud: up to 1200 m (4000 ft) with proper cable Examples: Belden 3105A, 3106A or equivalent Ensure proper network biasing and termination when reusing existing wiring. If communication issues persist, migrate to recommended cabling standards for BACnet MS/TP. Cable Specification Comparison Parameter ASD / MicroSmart Typical Cable BACnet MS/TP Recommended Cable Type Unshielded or basic twisted pair Shielded twisted pair Gauge 22–24 AWG 18–22 AWG Impedance ~70–90 Ω 100–120 Ω Capacitance ~50 pF/ft (164 pF/m) ≤ 30 pF/ft (98 pF/m) Shielding Often none Foil or braided shield Max Segment Length Designed for ASD baud rates 1200 m (4000 ft) at 9600–38400 baud Examples Legacy ASD/DMS cable Belden 3105A, 3106A or equivalent
View full article
Picard Product_Support
‎2018-09-06 02:57 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-19 11:28 PM

Labels:
  • TAC IA Series
1683 Views

Restore Factory Default Level 3 Password and Serial Port Settings on DMS-3500

Issue How can the factory default settings for the Level 3 password and the two serial ports be restored on a DMS-3500? Product Line TAC IA Series Environment DMS-3500 Cause The Level 3 password and serial port settings were changed and need to be reset to factory defaults for system access. Resolution To restore factory defaults for the Level 3 password and serial ports: Power On the DMS-3500. Remove the cover to expose the circuit board. Locate the CONFIG 2-pin connector near the green LED labeled SYS. Move the jumper from one pin to short both pins. Cycle power to the DMS-3500. This clears NOVRAM and restores default password and port assignments without affecting the rest of the configuration or database. After reboot, return the jumper to its original position (one pin). If not returned, new settings will be lost on the next power cycle. Default Settings After Reset: Level 3 Password: 170 Serial Port 1: 9600 1 7 E P N Serial Port 2: 2400 1 7 E P M ⚠ Caution: Always return the jumper to its original position after the reset.
View full article
Picard Product_Support
‎2018-09-06 02:50 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-19 11:17 PM

Labels:
  • TAC IA Series
1277 Views

Remove All or Part of the E: Segment in UltiVist/DMS

Issue How to delete all or specific parts of the E: Segment in an UltiVist/DMS database. Product Line TAC IA Series Environment UltiVist/DMS Cause The E: Segment database needs to be removed or cleaned up due to outdated or incorrect configuration data. Resolution Use the KILBRNCH tool to delete the required segment. Backup the database before proceeding. Open an OS/2 window and navigate to the FI directory. Disable communications by typing: SET NOFCS=TRUE (This ensures KILBRNCH only deletes offline elements.) At the x:\\FI prompt, run the KILBRNCH command: KILBRNCH FI Example: KILBRNCH \\FI\\FI E:001.12.01.023 E: = Segment 001 = Network ID 12 = Panel ID 01 = DCM ID 023 = Controller ID After completion, re-enable communications: SET NOFCS=FALSE Refresh the E: Segment in UltiVist.
View full article
Picard Product_Support
‎2018-09-06 02:49 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-19 11:14 PM

Labels:
  • TAC IA Series
1068 Views

Override Command on SIGNAL Graphic Does Not Apply to Network 8000/DMS Point

Issue An override command was applied to a Network 8000/DMS standard point on a SIGNAL graphic. The graphic shows the point in override, but the actual point in the field panel is not overridden. Product Line TAC IA Series Environment Network 8000 SIGNAL Cause The override command in SIGNAL does not properly update the field panel point due to a corrupted or outdated override data file. Resolution Clear the override data file and reapply the commands: Shutdown SIGNAL. Open Windows Explorer and navigate to: C:\Windows\Override Delete the file: override.dat Restart SIGNAL. Apply the override commands again. (The override.dat file will be recreated automatically.)
View full article
Picard Product_Support
‎2018-09-06 02:49 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-19 11:11 PM

Labels:
  • TAC IA Series
1080 Views
  • « Previous
    • 1
    • …
    • 11
    • 12
    • 13
    • …
    • 500
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore