Offline License Activation in Device Administrator

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Offline License Activation in Device Administrator
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • StephenYang
    StephenYang

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
526 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Offline License Activation in Device Administrator

Picard RobertAndriolo Picard
‎2025-10-23 06:03 PM

Last Updated: Admiral StephenYang Admiral ‎2025-11-21 12:52 PM

Issue

Customers using Device Administrator for offline license activation in EBO 7.0.3 face challenges due to changes in how entitlements are delivered via Software Companion.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Device Administrator (v7)
  • Software Companion Portal
  • FlexNet Licensing Portal
  • Offline systems (no internet access)

Cause

The current Software Companion tool does not generate an HTML entitlement certificate compatible with Device Administrator. Instead, it provides a PDF summary, which the Device Administrator cannot read or import.

Resolution

The simplest way is to enable Internet access for Device Administrator and add the entitlement ID.

To activate licenses offline in Device Administrator:

  1. Do not use the PDF summary generated by Software Companion — it is not compatible with Device Administrator.
  2. There are several options available, each differing in complexity and time requirements.
    1. Webhelp(Adding an Entitlement without the HTML file when a Field Server is not Connected to License Server (...), users can follow the follwing steps:
      • In Device Administrator, click Entitlements.
      • Click the Add Entitlement down arrow and click Manually Enter the entitlement ID.
      • Click Next.
      • Click Skip. If you know that you do not have any server connected to internet in the list, click Skip. If you do not click Skip, Device Administrator goes through all servers in your list until it finds one that is connected to internet.
      • In the Entitlement Products - Enter Manually list , enter the Activation ID, Description and seat count for the product.
      • Click Add Product , to add more products.
      • Click Add.
        Note: It is recommended to verify the Activation ID, Description, and seat count in FlexNet Operations End-User Portal before proceeding with the steps. When there is no connection between the EcoStruxure BMS Server and License Activation Server, Device Administrator cannot synchronize the number of licenses in the entitlement that are available for activation. Instead, Device Administrator assumes that all licenses that was purchased can be activated. 
    2. Access the FlexNet Licensing Portal: FlexNet Operations End-User Portal
      • Log in using the Entitlement ID.
      • List all Entitlements.
      • Select one Activation ID
      • Use the View Certificate option.
      • Download and save the certificate locally in HTML format.
        • When using Save As - ensure you select the "Webpage, complete (*htm;*html) option 
          RobertAndriolo_0-1761255697961.png
      • Repeat for each Activation ID listed in the Entitlement
      • Import each HTML certificate into Device Administrator to load the entitlement offline.
    3. Create a server list away from the site, using Device Administrator, that has Internet access.

      Caution: this will wipe the current server list, remove all certificates (if used), and remove all servers added to Device Administrator.

      • If the server list has already been created on site, save and export this list.

      • Off-site or on a PC with Internet access, import (from step 1) or create a new server list in Device Administrator.

      • Add the necessary entitlement IDs.

      • Save and export the server list.

      • Back on the on-site PC, import the exported server list to Device Administrator.

      • If using a new server list (that is, no servers added from Step 1), add the required certificates and servers.

      • Save this new list. It is advisable to export it as a backup in case of any issues.

      • Proceed with the offline activation. EcoStruxure BMS Server Licensing on Servers not Connected to Internet Workflow.

      • Once activated, remember to save and export the list for safekeeping.

Comment:
Investigation into why Software Companion does not generate HTML certificates is ongoing.  Device Administrator still requires either the HTML certificate or manual entry of activation IDs.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • RobertAndriolo25
  • StephenYang25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore