Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC INET
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac inet"

View in: "Building Automation Knowledge Base" | Community

1444 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 10
    • 11
    • 12
    • …
    • 73
  • Next »
Label: "TAC INET" Show all articles

How long is the battery backup on the 7716?

Issue How long is the battery backup on the 7716? Environment I/NET site Cause How long is the battery backup on the 7716? Resolution The battery backup of a 7716 will last 30 Days. Refer to TCON 096.
View full article
Picard Product_Support
‎2018-09-07 12:34 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:44 AM

Labels:
  • TAC INET
1141 Views

How long does PSS support a product after it is released?

Issue How long does PSS support a product after it is released? Product Line Andover Continuum, EcoStruxure Building Operation, TAC IA Series, TAC INET, TAC Vista Environment All Schneider Electric Buildings Business software platforms Cause After a few years, the majority of issues with a release product are documented in the Knowledge Base.  At this point, if the customer is having issues requiring Product Support, we ask that they upgrade to the current version. Resolution Please read the following Product Announcements: PA_00271 Software Support Policy - General Overview.pdf PA_00272 Software Support Policy - Supplementary info for_Andover_Continuum.pdf PA_00274 Software Support Policy - Supplementary info for TAC Vista.pdf PA_00279 Software Support Policy - Supplementary info for TAC INET.pdf PA_00280 Software Support Policy - Supplementary info for TAC IA Series.pdf
View full article
Picard Product_Support
‎2018-09-07 02:30 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:44 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC INET
  • TAC Vista
1753 Views

How does the SNMP agent in TAC Xenta Server work and what are the limitations?

Issue Can I send live data over SNMP? How many trap pages can I define? Environment Xenta Servers Xenta 511, 527, 555, 701, 711, 721, 731 Cause All Xenta Servers (except Xenta 913 and Xenta 527-NPR) have a built in SNMP agent. However, the SNMP protocol in them cannot handle sending live data over SNMP. It can only send alarms along with specific fields of those alarms.   Resolution The Xenta Server supports SNMP version 1 and SNMP Traps. It can only be used to send SNMP and not to receive. The first step to setting up SNMP is to create alarms in XBuilder and link the points to the alarms that are to be monitored. Then, the filters used by the SNMP traps should be defined. This is done using SNMP trap pages. SNMP Trap Page The SNMP trap page is where you define a set of rules in Xbuilder of when to send a trap to the SNMP manager. This includes severity of the alarm or a wildcard string based on the address of the point.  In XBuilder you can create up to 10 SNMP trap pages, which will give you possibilities to define 10 different alarm filters. An SNMP trap page is created by right-clicking a folder in the System pane of XBuilder and then selecting New > Page > SNMP Trap Page. (It is recommended that a separate folder be created for SNMP trap pages and that this folder be restricted to only system administrators.) Once the SNMP trap page has been created it is then configured by right-clicking on the SNMP trap page object and selecting SetupSNMP Trap Filter.   SNMP Field Configuration The SNMP field configuration is where you define what 8 pieces of data will be sent to the SNMP manager (due to the UDP limit of 8 fields). That data consists of things like date/time, type, address, priority, description, etc. The SNMP field configuration is accessed by clicking on the Tools menu and selecting SNMP Field Configuration.     For more information on SNMP in Xenta Servers please see the TAC Xenta Server - TAC Networks Technical Manual, section 16. Note: SNMP is only supported by Xenta Server devices and is not supported by TAC Vista.  
View full article
Picard Product_Support
‎2018-09-10 01:02 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:44 AM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
1754 Views

How do Controller LANs connect to Host LANs?

Issue How do Controller LANs connect to Host LANs? Product Line TAC INET Environment I/NET Site Cause Understanding network architecture can help design and servicing of networks. Resolution Controller LANs connect to Host LANs through Link Taps. (TCON209, 1-5). Refer to Explain and define I/NET Ethernet, C-LAN, and Sub-LAN communication for further explanation.
View full article
Picard Product_Support
‎2018-09-07 12:25 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC INET
1346 Views

How can I know when new products are released?

Issue How can I know when new products are released? Environment I/NET Site Cause How can I know when new products are released? Resolution Visit the Building Business Extranet. Email a request to the Buildings Business ExchangeMail marketingadmin@buildings.schneider-electric.com
View full article
Picard Product_Support
‎2018-09-06 11:33 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC INET
1429 Views

HHC cable to connect to LTS80U Space Sensor Assemblies (maintenance) port

Issue What HHC cable do I need to connect to a LTS80U Space Sensor Assemblies (maintenance) port? Environment LTS80U Space Sensor Assembly Hand Held Console Cause Connecting the HHC allows for configuration. Resolution The part number is 602135-0002. It is a two foot (or 60 cm) straight, silver modular cable; Console-3. Refer to TCON 073 for more details.
View full article
Picard Product_Support
‎2018-09-06 09:27 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC INET
1179 Views

Guidelines for using large numbers in Access Control

Issue Are there any documented guidelines for using large number in Access Control? Product Line TAC INET Environment I/NET Site Cause Are there any documented guidelines for using large number in Access Control? Resolution Begin by referencing TCON 300. All SLIs and DPUs must use I/NET Seven revision 1.x (or later) compatible binary software. All DPUs must have DIP switch 7 set to ON. Within a single tenant, you can assign a large key/card number directly to an individual, or translate the number using the Key/Card Translation table, but not both (i.e., you cannot have duplicate key/card numbers or individual numbers within a single tenant). Use compatible EPROMs in the DPUs Note: If you directly assign a key/card to an individual, and later translate the same key/card for another individual, only the translated key/card will be operational within I/NET. Other useful articles: SCU dip switch 6 for dual station addressing How to convert existing Idisc to large numbers (Hex) DPU memory allotment in a 7910A and a Non-mipped 7920
View full article
Picard Product_Support
‎2018-09-06 11:03 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC INET
1381 Views

Firefighters Smoke Control Station Interface (FSCSI) database should consist entirely of internal points and point extensions

Issue Why is it recommended that the Firefighters Smoke Control Station Interface (FSCSI) database consists entirely of internal points and point extensions? Environment Firefighters Smoke Control Station Interface (FSCSI) Cause This allows the same database to be used regardless of whether the FSCSI is an ICI PCU or even an MRI. Resolution This allows the same database to be used regardless of whether the FSCSI is an ICI PCU or even an MRI. For more information see TCON 231, Smoke Control Systems Manual, Database Logic.
View full article
Picard Product_Support
‎2018-09-06 11:26 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:42 AM

Labels:
  • TAC INET
986 Views

File equalization is not available on the workstation if the link type is NetPlus Router, Integrated Dial, or Integrated NPR dial.

Issue Although site operation appears normal, there are problems with file equalization when the desktop PC is direct connected to the NPR. Active Configuration Profile, Link type is NetPlus Router. Environment I/NET Seven NetPlus Router Integrated Dial Integrated NPR dial Cause File equalization is not available on the workstation if your link type is NetPlus Router, Integrated Dial, or Integrated NPR dial. Resolution File equalization is not available on the workstation if your link type is NetPlus Router, Integrated Dial, or Integrated NPR dial. Refer to TCON 298, 3-13 for more information.
View full article
Picard Product_Support
‎2018-09-06 10:41 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:42 AM

Labels:
  • TAC INET
1266 Views

Fiber Optic Interfaces (FOI) in I/NET 2000

Issue What are the dip switch settings for each Fiber Optic Interface (FOI) in I/NET 2000 Controller LAN and subLAN? Can FOI communications be alarmed? How do you test them? Does the FOI need to be addressed in I/NET? Environment I/NET 2000 Fiber Optic Interface Cause Configure the network to work on FOI. Resolution Controller LAN Settings: SubLAN Settings: 1 = Off 2 = Off 3 = On 4 = Off 5 = Off (If no CRR) 6 = Off 7 = Off 8 = On 9 = Off 10 = On 11 = On 12 = On 1 = Off 2 = Off 3 = On 4 = Off 5 = Off (If no CRR) 6 = Off 7 = Off 8 = On 9 = On (9600 subLAN speed) 10 = On 11 = On 12 = On Notes: When testing the fiber optic section of the network, tests can be done in "Single-Mode" or "Multi-Mode." All testing must be performed in "Multi-Mode." Fault alarms can be sent from the FOI to a remote location using fiber line faults. You need to have Counter Rotating Rings (CRR) to get this feature. FOIs are not addressable. The FOI is transparent or invisible when viewed through a workstation or viewcon screen of the 7728 or 7798. Refer to TCON087, Fiber Optic Interface for more details.
View full article
Picard Product_Support
‎2018-09-06 03:37 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:42 AM

Labels:
  • TAC INET
1326 Views

Explaining Masking in an I/NET System

Issue What is Masking? Environment I/NET site Cause What is Masking? Resolution Masking is a filtering process for sending data based on the distribution group and active mask position(s) of both the originating and destination equipment. This applies to messages, alarms, and other data. Read TCON210 and TCON300 for further explanation.
View full article
Picard Product_Support
‎2018-09-07 12:55 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:41 AM

Labels:
  • TAC INET
1462 Views

European Intrusion Certification

Issue Intrusion Alarm System for TAC I/NET Building Automation Systems Environment I/NET Site using Intrusion Alarm System for TAC I/NET Building Automation Systems Cause Certification Requests Certification Requests including Grade 3 Resolution The I/NET Access Control security products are certified and Listed under Underwriters Laboratories standard UL294. We do not have certification with NSI or SSAIB. Reference to NSI and SSAIB suggest a probable European security application. If that is the case, the application may be a candidate for our recently released TAC I/NET security products listed below - ICPB - Intrusion Control Panel Base ICPE - Intrusion Control Panel Expander ICPD - Intrusion Control Panel Distributed OP5 - Operator Terminal The above system panels were certified to the European Security System Standard EN50131 and the Swedish standard SSF1014 by - SP Sveriges Tekniska Forskningsinstitut SP Technical Research Institute of Sweden Box 857, SE-501 15 Borås, Sweden Tel: +46 (0)10 516 50 00 Telefax: +46 (0)33 12 50 38 Internet: www.sp.se The Security system panels and their functional performance were tested and certified to the following standards - EN50131-3:2009 Alarm systems - Intrusion and hold-up systems - Part 3: Control and indicating equipment EN50131-6:2008 Alarm systems - Intrusion and hold-up systems - Part 6: Power supplies The above two standards are used to test/evaluate intrusion systems for compliance with EN50131-1 SSF1014:2005 System components – Intruder Alarm Systems Requirements and test methods EN60950-1:2001+A11:2004 Information technology equipment - Safety EN61000-6-3:20007 Electromagnetic compatibility (EMC) - Generic Standards - Emission standard EN50130-4:1996/A1:1998/A2:2003 - Electromagnetic Compatibility - Product family standard: Immunity requirements for components of fire, intruder and social alarm systems. The TAC I/NET EN50131 compliant system is documented in TCON314 Installation Manual and TCON315 operators Manual. The security system detailed above was certified and registered with the organization - SBSC SBSC is Sweden’s leading organization for certifying companies, products, management processes and personnel within fire protection and crime prevention. This is covered under SBSC Certificate number 10-523 (copy available at link provided) PA-00148 Vista Security Intrusion Certification.
View full article
Picard Product_Support
‎2018-09-11 04:33 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:41 AM

Labels:
  • TAC INET
1505 Views

Door selection is not possible in Tenant editor

Issue Error: "Tenant X individuals for door LLSSPPBB DO exceeds 24,000" when attempting to select additional doors within Tenant Editor Product Line TAC INET Environment I/NET Seven 2.15 and above DPU / SCU Firmware 3.23 and below Cause SCU / DPU firmware revision 3.3 and lower only supports 24,000 individuals per door, even though the I/NET Software (I/NET Seven 2.15 and above) allows you to allocate 32,000 per tenant.  This is why it is important to maintain consistency between I/NET Software Revisions and Hardware firmware. The I/NET Seven 2.xx Compatibility Matrix lists this information. Resolution To allow the controllers to support more than 24,000 individuals per door the firmware in the DPU / SCU must be at revision 3.24 or above. This firmware is included with I/NET Seven Revision 2.15 or above. Although TAC I/NET supports up to 32,000 individuals per tenant, the model type and revision date of a tenant's door controllers will ultimately determine how many individuals will be supported. The following table shows the capacity of various door controllers. For any door controller with revision 2.2x or later firmware, you would have to define multiple tenants in order to reach the door controller’s maximum storage capacity. Firmware Revision Door Controller Maximum Number of Individuals 2.1x and earlier  DPU7910, DPU7920 Up to 24,000 per door 2.2x to 3.23 DPU7910, DPU7920 without DPU48K Up to 48,000 per controller   DPU7910, DPU7920 with DPU48K Up to 48,000 per door 1 3.24 and later DPU7920 with DPU48K, SCU 1284 Up to 64,000 per door 1   1 Typically, the total number of individuals for a selected door cannot exceed 32,000. However, if one of the two doors controlled by a DPU is not being used (that is, no individuals are assigned to the door), you can assign up to 64,000 individuals to the door that is being used. This also requires the use of more than one tenant since no single tenant can have more than 32,000 individuals.  Refer to TCON300-06/11 Chapter 9-62 for further information.
View full article
Picard Product_Support
‎2018-09-10 03:21 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:39 AM

Labels:
  • TAC INET
1896 Views

Does the NPR have a Diagnostic Utility?

Issue Does the NPR have a Diagnostic Utility? Environment I/NET site Cause Does the NPR have a Diagnostic Utility? Resolution Yes. The NPR is equipped with a self-diagnostic function that runs every time the unit is powered up. Four LEDs on the upper right side of the unit provide feedback of the progress of this test, and indicate any error conditions. See TCON209, 2-31 and TCON184 NPR Installation Guide.
View full article
Picard Product_Support
‎2018-09-07 12:22 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:39 AM

Labels:
  • TAC INET
1283 Views

Does a site need to define a Link in the Configuration Profile for Integrated Dial?

Issue Does a site need to define a Link in the Configuration Profile for Integrated Dial? Environment I/NET Site Cause Does a site need to define a Link in the Configuration Profile for Integrated Dial? Resolution Yes, a site does need to define a Link in the Configuration Profile for Integrated Dial? Refer to TCON 226.
View full article
Picard Product_Support
‎2018-09-07 12:04 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:39 AM

Labels:
  • TAC INET
1108 Views

Documentation on memory usage for the 7910 and 7920 DPUs

Issue Documentation on memory usage for the 7910 and 7920 DPUs Product Line TAC INET Environment I/NET site Cause Documentation on memory usage for the 7910 and 7920 DPUs Resolution Yes. TCON 237 pages 9-4 through 9-6 refers to INET 2000, 2.xx systems. Tech tips 039 and 035 were written for older I/NET systems.
View full article
Picard Product_Support
‎2018-09-06 03:44 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:39 AM

Labels:
  • TAC INET
2004 Views

Do the MRs have the ability to run a time schedule without a MRI, MCI or I/SIT LAN?

Issue Do the MRs have the ability to run a time schedule without a MRI, MCI or I/SIT LAN? Environment I/NET MRs Cause If communications are lost to the MRI, MCI, or LAN, a stand alone time schedule will continue to work at the controller level. Resolution Yes, you can build a Standalone ATS in the MR functions editor or I/STAT. Standalone ATS (Automatic Time Schedule) is an MR-resident ATS schedule programmed into the MRs that allows a single start stop time for each day of the week for the point designated as the master Device Control point in the MR Parameters editor. These commands are only issued if the MR and MRI/MCI are NOT communicating. Refer to our System Operator Guide TCON 207 or TCON 236 for more details.
View full article
Picard Product_Support
‎2018-09-06 08:58 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:38 AM

Labels:
  • TAC INET
1133 Views

Do I need to replace the EPROM on the MIP in my 7760?

Issue Do I need to replace the EPROM on the MIP in my 7760? Environment I/NET site Cause Do I need to replace the EPROM on the MIP in my 7760? Resolution No. (TCON 209, 2-14,15)
View full article
Picard Product_Support
‎2018-09-07 12:26 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:38 AM

Labels:
  • TAC INET
1380 Views

Do I need a HHC to set up a 7798 (SLI) (ISITE)?

Issue Do I need a Handheld Console (HHC) to set up a 7798 (SLI) (ISITE)? Environment 7798 SLI ISITE Cause The 7798 does not have ports for a HHC. Resolution No. In fact, the 7798 does not have ports for a HHC. The 7798 is setup using its touch pad. Refer to 7798 TCONs for more details.
View full article
Picard Product_Support
‎2018-09-06 09:22 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:38 AM

Labels:
  • TAC INET
1051 Views

Direct Connect Xenta 527-NPR or 527 Web Server through I/NET

Issue Direct Connect Xenta 527-NPR or 527 Web Server through I/NET Environment I/NET site Cause Direct Connect a Xenta 527-NPR or 527 Web Server through I/NET Resolution Are you using a Xenta 527-NPR or 527 Web Server and want to direct connect to it through I/NET and not having any luck? There are a couple of things that you need to set up in the unit for serial communication to I/NET through Port A (RS 232). The Xenta 527 NPR is set at factory default (RS232 Port A). The following steps should get you through this: Start I/Net and create a profile for the NPR (Net Plus Router) in I/O Server, then make this active. Verify that you have the correct cable to hook up from the serial port of the PC to Port A (RS 232) on the unit. (L1: RJ45 to RJ45 part # 0-073-0817). Connect them together. At this time you will need to start X Builder, if you don’t have it already, then you need to download it from the Exchange Extranet. The path is TAC Vista > Engineering Tools > TAC XBuilder > TAC XBuilder 1.5 (or latest revision). Download this to the PC. Start XBuilder through Programs > TAC > TAC Tool > XBuilder. Once started, select File\ New Project\(Project Name)\Location (default)\Project Template (select 527 Project), call it 527 NPR or whatever makes sense to you. At the settings Editor, just hit the OK button. Once the Editor comes up, in the Network frame, expand the TAC_Xenta_527. Right Click on the RS232-485A selection, click on Add then select I/NET. If you click on the TAC_Xenta_527, you will see all the settings that you have originally set up through Hyper Terminal or you can put those in at this time. Now select the Generate Icon or press F10 to generate the file. In the bottom of your project you would see a message that says Xbuilder – 0 error(s), 0 warning (s). This indicates that your project is now complete without errors. Now select the Rocket Ship Icon or press F11 to transfer the file to the unit. Once completed, restart or cycle power on the 527. Go to I/Net\Edit\Host Computer\Network Configuration and your 527 will show up in the Link Summary. At this time you can save the link, penetrate it and save the controllers etc. the old fashioned way. At this time you should be able to work on your system through a direct connect on a Xenta 527 NPR/Webserver unit.
View full article
Picard Product_Support
‎2018-09-07 01:03 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:38 AM

Labels:
  • TAC INET
2197 Views
  • « Previous
    • 1
    • …
    • 10
    • 11
    • 12
    • …
    • 73
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore