Direct Connect Xenta 527-NPR or 527 Web Server through I/NET

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Direct Connect Xenta 527-NPR or 527 Web Server through I/NET
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2191 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Direct Connect Xenta 527-NPR or 527 Web Server through I/NET

Picard Product_Support
‎2018-09-07 01:03 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:38 AM

Issue

Direct Connect Xenta 527-NPR or 527 Web Server through I/NET

Environment

I/NET site

Cause

Direct Connect a Xenta 527-NPR or 527 Web Server through I/NET

Resolution

Are you using a Xenta 527-NPR or 527 Web Server and want to direct connect to it through I/NET and not having any luck? There are a couple of things that you need to set up in the unit for serial communication to I/NET through Port A (RS 232). The Xenta 527 NPR is set at factory default (RS232 Port A). The following steps should get you through this:

  1. Start I/Net and create a profile for the NPR (Net Plus Router) in I/O Server, then make this active.
  2. Verify that you have the correct cable to hook up from the serial port of the PC to Port A (RS 232) on the unit. (L1: RJ45 to RJ45 part # 0-073-0817). Connect them together.
  3. At this time you will need to start X Builder, if you don’t have it already, then you need to download it from the Exchange Extranet.
  4. The path is TAC Vista > Engineering Tools > TAC XBuilder > TAC XBuilder 1.5 (or latest revision). Download this to the PC.
  5. Start XBuilder through Programs > TAC > TAC Tool > XBuilder.
  6. Once started, select File\ New Project\(Project Name)\Location (default)\Project Template (select 527 Project), call it 527 NPR or whatever makes sense to you.
  7. At the settings Editor, just hit the OK button.
  8. Once the Editor comes up, in the Network frame, expand the TAC_Xenta_527. Right Click on the RS232-485A selection, click on Add then select I/NET.
  9. If you click on the TAC_Xenta_527, you will see all the settings that you have originally set up through Hyper Terminal or you can put those in at this time.
  10. Now select the Generate Icon or press F10 to generate the file. In the bottom of your project you would see a message that says Xbuilder – 0 error(s), 0 warning (s). This indicates that your project is now complete without errors.
  11. Now select the Rocket Ship Icon or press F11 to transfer the file to the unit.
  12. Once completed, restart or cycle power on the 527.
  13. Go to I/Net\Edit\Host Computer\Network Configuration and your 527 will show up in the Link Summary. At this time you can save the link, penetrate it and save the controllers etc. the old fashioned way.

At this time you should be able to work on your system through a direct connect on a Xenta 527 NPR/Webserver unit.

Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 2067
  • Direct Connect Xenta 527-NPR or 527 Web Server through INET
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore