Do the MRs have the ability to run a time schedule without a MRI, MCI or I/SIT LAN?
  • Do the MRs have the ability to run a time schedule without a MRI, MCI or I/SIT LAN?
‎2018-09-06 08:58 PM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:38 AM
I/NET MRs
If communications are lost to the MRI, MCI, or LAN, a stand alone time schedule will continue to work at the controller level.
Yes, you can build a Standalone ATS in the MR functions editor or I/STAT.
Standalone ATS (Automatic Time Schedule) is an MR-resident ATS schedule programmed into the MRs that allows a single start stop time for each day of the week for the point designated as the master Device Control point in the MR Parameters editor. These commands are only issued if the MR and MRI/MCI are NOT communicating.
Refer to our System Operator Guide TCON 207 or TCON 236 for more details.
  • TAC INET
  • 1062