Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 470
    • 471
    • 472
    • …
    • 509
  • Next »

b3 Controller error log reports 0x00001427.

Issue Points from on b3 controller will not update on pinpoint graphics.  Environment b3 0x00001427 HardwareErr__ Bad RTC chip RTC Cause Error 0x00001427 denotes a hardware failure of the real time clock.  Resolution Return controller to Schneider Electric for repair.
View full article
Picard Product_Support
‎2018-09-06 10:13 AM

Labels:
  • Andover Continuum
969 Views

Continuum 1.94 SP1 Service Pack to address accdataserices.exe crashes and other issues

Issue See "mismatch xxxxxxxx" in the Continuum Error Listview. Product Line Andover Continuum Environment Continuum Windows XP Windows 7 Windows Server 2003 Windows Server 2008 Cause An Error logging feature was added with 1.94 SP1. If the Continuum Error Listview has "mismatch xxxxxxxx" errors, then SP1 for Cyber has been installed, but the controllers are posting errors. Resolution Use the updates below or the most recent version and the errors will no longer post. A Cyberstation 1.94 service pack released to address accdataservices crashes and other issues. The list of corrected issues is the release notes. The files are available on https://ecobuilding.schneider-electric.com/ 
View full article
Picard Product_Support
‎2018-09-11 12:47 PM

Labels:
  • Andover Continuum
2420 Views

Are lnml files required to remain with the Niagara G3 station?

Issue The LON XML tool was used to create a lnml file.  Does it need to remain with the station at all times? Environment Niagara G3 Cause General database housekeeping Resolution Once the LON controller has been imported, the lnml file is no longer required and can be removed. Note:  If the LON controller's profile changes slightly (i.e. one or two SNVTs), a Learn Nv is sufficient to update the device in the station.  The Learn Nv command will not execute unless the reference to the lnml file is removed.
View full article
Picard Product_Support
‎2018-09-06 10:13 AM

Labels:
  • TAC IA Series
1178 Views

Is it possible to customize the email message body of Reports that are emailed using ReportCmdLine.exe?

Issue Is it possible to customize the email message body of Reports that are emailed using ReportCmdLine.exe? Environment Continuum Cyberstation Outlook Cause Want to modify the email message body to include more information about the Report. The message in an Alarm that is being emailed can be changed with an email format file using XML tags, can the same thing be done with Reports being emailed? Resolution It's not possible to modify the email message body of an emailed Report.
View full article
Picard Product_Support
‎2018-09-06 10:13 AM

Labels:
  • Andover Continuum
1079 Views

Access events not being reported for one controller.

Issue All controllers are reporting access events except one. Environment SystemStatus Access Events Cause The InfinitySystemVariable SystemStatus was set to No Database. Resolution Once SystemStatus was set to equal Normal access events began to be reported from the controller.
View full article
Picard Product_Support
‎2018-09-06 10:13 AM

Labels:
  • Andover Continuum
991 Views

Email alarm redundancy on the AS and ES and their interaction

Issue Email alarms can be configured in the AS and ES and understanding that interaction is needed Environment SmartStruxure Windows 7 Windows Server 2008 Cause There is a need to know what happens when creating email alarms in the AS and ES Resolution The server (AS or ES) that has the email notification object will send the email. So if you want to be sure that the AS alarms still send emails even if the ES is offline, then you should have email notifications configured on the AS and not rely on a global email notification on the ES. If notifications are configured on both the ES and AS which triggers on the same alarm, then two emails will be sent. One when its triggered on the AS and one when the ES fetches the alarm from the AS. You may be able to manage the triggering of the AS alarm by a program that checks the online status or alarm indication of the ES being offline.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • EcoStruxure Building Operation
1678 Views

Unable to connect to b3xxx controllers with RoamIO.

Issue Unable to connect to b3xxx controllers with RoamIO. Environment RoamIO-1 RoamIO-2 Cause The RoamIO-1 is not able to communicate with BACnet controllers. It only supports Infinet controllers. Resolution The RoamIO will not be able to communicate with the BACnet controllers (bCX4040, b3xxx, etc...) you will need to use the RoamIO-2 that is able to communicate to both Infinet and BACnet.  
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1180 Views

Can I install the Java7u25 patches in 3.5.25?

Issue Can I install the Java7u25 patches in 3.5.25? Environment I/A Series G3 with multiple browsers Cause JAVA 7u25 prevents the Java applet from loading Resolution You must be at a level specified in the TPA before applying these patches.  See TPA-IA-13-0007.01 Java 7 Update 25 May Cause I/A Series G3 Niagara Applet to Fail.
View full article
Picard Product_Support
‎2018-09-11 06:30 AM

Labels:
  • TAC IA Series
1325 Views

ACX5740 does loses comm after power failure.

Issue Following a power failure, ACX 5740 controller loses communication. Cycling power with the controller battery removed recovers some but not all controllers. Environment ACX5740 ACX5720 1.1000037 Comm Loss Power failure Cause This problem was fixed in firmware version 1.100037. Resolution Upgrade ACX firmware to 1.100037 
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1531 Views

Errors when save to database -- error inserting into table

Issue Continuum throws  the following error when a save to database is performed on a controller -- Error inserting row into table. Environment SQL ContinuumDB Cause Duplicate Tables in the database. Resolution Restore backup of last known working database.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1173 Views

How to swap two infinet controller on the same system.

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue What is the proper procedure to use when swapping two previously installed Infinet controllers on the same Continuum network. Environment ACCID Infinet Controllers Cause Must prove determine whether an Infinet Controllers flow sensor is damaged. Resolution It is important to recommission Infinet controllers before relocating them in the same system. Recommissioning the Infinet controller purges all object handles and ensures that the controller will be brought on line virtually as a new "out of the box" controller. Infinet controllers are recommissioned by setting the InfinetID to 0 using a RoamIO. Using a RoamIO, set the InfinetID of both Infinet controllers to zero. Verify that the controllers InfinetID has been set to 0. With the workstation in OffLine mode, change the serial number of each controllers to a fictional serial number that does not exist in Continuum. Remove both controllers and install them in place of each other with out powering the controller. Before the controllers are powered, connect them to the Infinet bus while the bus is connected to the infinet port. Switch the workstation to Online Mode. Power up the controllers. Enter the correct serial number for each controller in the controller editor. Both controllers should come online. Reload both controllers.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1201 Views

Sigma low level alarm - Operlist.txt file missing

Issue 'Operlist.txt file missing' alarms are seen in the Sigma Alarm Manager. Operlist.txt files have been downloaded to the controllers and the controller's contents show that the operlist.txt file exist.  Environment Sigma 4.07 build 3.45.48 (upgraded from BAS2800+ or Sigma versions prior to 4.04) Cause The operlist.txt file is required for Sigma controllers. Starting from Sigma 4.04, the Sigma controllers uses a dummy operlist.txt file. There is no longer the need to create this file manually. The Sigma server automatically creates a suitable dummy operlist.txt file for downloading to the controller. However, if an operlist.txt file exists in the controller / outstation folder, then that file will be sent to the controller and not the dummy one. In this case, the existing operlist.txt files still exists in the controller / outstation folders.  Resolution Delete the existing operlist.txt files from the controllers / outstation folders. A quick way to do this is to use the Windows Search function to search for the file name 'operlist.txt' inside the C:\Sigma\Data folder and delete all the files together.    In Sigma System Diagnostics, download the operlist.txt file to all controllers. A dummy operlist.txt file will be created in each controller / outstation folder and the file will be downloaded to the controller. 
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Satchwell BAS & Sigma
1132 Views

Will a jace-645 run a R2 station more efficiently than a UNC-520?

Issue A UNC-520 is installed at a jobsite and has been programmed over the years with additional controllers and graphics.  The resource count is now over 600,000.  The CPU idle time does not rise any higher than 3-4%.  Since the jace-645 is a more updated (i.e. powerful) hardware platform, will it run this large R2 station more efficiently? Environment Niagara R2 jace-645 Cause Site UNC-520 can no longer run its installed station efficiently Resolution Tridium tested the jace-645 and rated it capable of running a 600,000 resource-sized station.  It was not tested for anything larger. Installing and running a larger R2 station is not recommended.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • TAC IA Series
1133 Views

Switching Windows Users

Issue Acc Data Service error when we switch users on a workstation with multiple user accounts. Environment Windows 7 Windows XP Windows 2008 Server Continuum  1.XX Cause You cannot open multiple Continuum instances simultaneously on a system. You cannot switch users and leave the cyber station running on one session and open another instance of Continuum under a different user on the same system without errors. Resolution You must close Continuum and log off of the system before another user opens another session.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1176 Views

What is the default BACnet Priority of the SmartStruxure Lite.

Issue What is the default BACnet Priority of the SmartStruxure Lite. Environment SmartStruxure Lite Cause Different BACnet devices write in different priority. Resolution The default priority is 10 in firmware version 2.4.x and newer. The default priority is 08 in firmware version 2.3.x and older.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • EcoStruxure Building Expert
1095 Views

Zelio relay family

Issue Where can the Zelio relay family be ordered? Environment Zelio relay Cause Unable to order through Schneider Electric Buildings organisation. Resolution The Zelio relays are available through the Schneider Electric Power business organisation. Please contact the regional Schneider Electric front office for more information.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Field Devices
1153 Views

Anti-Passback Protection option is not available

Issue The Anti-Passback Protection is not editable on Entry or Exit options page of door editor. Product Line Andover Continuum Environment Access control Anti-passback Cause In order to configure anti passback protection on either side of a door the door must have both an entry area and an exit area selected. Resolution Once an exit area is selected, the Anti-Passback protection option becomes selectable.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1491 Views

Unable to find Part number for a ATV 21 Variable Speed Drive

Issue I'm looking for a part number for the ATV 21 Variable Speed Drive but it does not appear on the part number list Environment ATV 21 ATV 212 Altivar  Variable Speed Drive Cause Part number has been discontinued Resolution There is now a new name for the ATV 21 Variable Speed Drive as this old version has now been updated The new name for the ATV 21 is ATV 212 or Altivar 212 the below is a link to the Schneider Electric web site where all documentation, part numbers, distributors and Support can be found Altivar 212
View full article
Picard Product_Support
‎2018-09-11 04:40 AM

Labels:
  • Field Devices
1169 Views

Forta actuator closing direction

Issue If the actuator is closing in the wrong direction, how can that be changed? Environment Forta series actuator: M300 M400 M750 M800 M1500 M3000 Cause Depending on application, you may want to change the direction of the actuator movement. Resolution Invert the control signal by changing dip switch no 7 settings. For changes to take affect, the power supply needs to cycled or the manual operation handle needs to be lowered and raised back to normal position.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Field Devices
1062 Views

The I/A Series G3 GCM driver does not process and route the COS block alarm to the alarm console when the alarm activates.

Issue When the GCM has been configured to send a COS alarm, a null pointer exception similar to the one shown below is seen in the output window when an alarm is activated. “ERROR [17:15:39 16-May-13 CDT][gcm.unsolicited.com1] Exception java.lang.NullPointerException in Unsolicited message processing” The alarm is not processed by the ENC nor sent to the alarm console with the COS alarm’s message. The return from alarm is processed and seen in the alarm console. The return from alarm does not have a COS message associated within the GCM COS block. Environment I/A Series G3, GCM driver Cause The alarm is not being processed and routed properly by the tacGcm driver. Resolution The tacGcm 3.6.47.4 module corrects driver's alarm processing.  The tacGcm 3.6.47.4 module can be downloaded from The Exchange Download Center.
View full article
Picard Product_Support
‎2018-09-11 05:57 AM

Labels:
  • TAC IA Series
1370 Views
  • « Previous
    • 1
    • …
    • 470
    • 471
    • 472
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of