Will a jace-645 run a R2 station more efficiently than a UNC-520?
  • Will a jace-645 run a R2 station more efficiently than a UNC-520?
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 10:12 AM
A UNC-520 is installed at a jobsite and has been programmed over the years with additional controllers and graphics.  The resource count is now over 600,000.  The CPU idle time does not rise any higher than 3-4%.
Since the jace-645 is a more updated (i.e. powerful) hardware platform, will it run this large R2 station more efficiently?
Niagara R2
jace-645
Site UNC-520 can no longer run its installed station efficiently
Tridium tested the jace-645 and rated it capable of running a 600,000 resource-sized station.  It was not tested for anything larger.
Installing and running a larger R2 station is not recommended.