Forta actuator closing direction
  • Forta actuator closing direction
  • SESA150559
    SESA150559
‎2018-09-06 10:12 AM
If the actuator is closing in the wrong direction, how can that be changed?
Forta series actuator:
M300
M400
M750
M800
M1500
M3000
Depending on application, you may want to change the direction of the actuator movement.
Invert the control signal by changing dip switch no 7 settings. For changes to take affect, the power supply needs to cycled or the manual operation handle needs to be lowered and raised back to normal position.