Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2197 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 67
    • 68
    • 69
    • …
    • 110
  • Next »
Label: "Andover Continuum" Show all articles

Continuum controllers and Remote Access Communication.

Issue Which Continuum controllers support RAS via modem connection? Environment CyberStation CX9900 CX9940 CX9680 CX9640 CX9200 CX9924 Cause Not all Continuum controllers support modem connection. Resolution The access point for a remote site is the controller that is configured with a modem that is used to establish a communication link with the remote CyberStation. Only the following Continuum controllers can act as access points for remote sites. CX9900, CX9940, CX9680, CX9640, CX9200, CX9924. Note that other controllers communicating with the access point controller via ethernet can fully participate in RAS communications as the access point controller will route messages to/from its peers.
View full article
Picard Product_Support
‎2018-09-06 01:57 PM

Labels:
  • Andover Continuum
2966 Views

Card Numbers: Truncating Zeros

Issue Is there a way to stop the beginning zeros from being truncated off  in a card number? 00123  becoming 123 when saved and refreshed. Environment Continuum 1.93 PIM FIPs. Wiegand 26 Cause Exporting and Importing card data into 3rd. Party system. Resolution The beginning zeros automatically get truncated off in a card number They get removed in all the user fields in Continuum. This is by design and cannot be altered
View full article
Picard Product_Support
‎2018-09-06 01:57 PM

Labels:
  • Andover Continuum
1342 Views

Adding nodes to a controller

Issue How do I add nodes to my controller? Environment Netcontroller CX99xx Netcontroller II ACX57xx BCX Series Cause Adding more nodes to a controller Resolution First you will need to contact upgrades department to obtain a node upgrade flash file for your controller.  Upgrades can be reached at upgrades.continuum@schneider-electric.com Once you have received your flash file you will being the process of updating your OS. 1.  Rick Click and Edit the controller 2.  Click update OS 3.  Path to file and select file 4.  Verify controller updated 5.  Reload Controller
View full article
Picard Product_Support
‎2018-09-07 02:33 PM

Labels:
  • Andover Continuum
1645 Views

What type of termination resistors should be used for ACC-LON or FTT-10A remote I/O modules.

Issue Wants to know the correct termination specification for each different I/O modules and different IOU networks. Environment NC1 - CX9900, CX9940 NC2 - CX9680 IOU modules Cause Different type of terminations are required for different type of I/O modules (ACC-LON and FTT-10A) and different topologies (Bus topology, Free topology and Doubly terminated Bus topology). Resolution ACC-LON  requires two 120 ohm resistors at both ends of the bus. One between pin 1&2 of the I/O module on the NetController side and the other one between pin 1&2 of the I/O module at the last node of the bus. FTT-10A Free topology requires one 52.3 ohm resistor between pin 1&2 at any place on the bus. FTT-10A Doubly terminated bus topology requires two 105 ohm resistors.  One between pin 1&2 of the I/O module on the NetController side and the other one between pin 1&2 of the I/O module at the last node of the bus.
View full article
Picard Product_Support
‎2018-09-06 01:56 PM

Labels:
  • Andover Continuum
4534 Views

Bacnet object rejected generated in response to a confirmed request... when creating a schedule

Issue Creating a bacnet schedule to control a 3rd party device generates the error:  “Bacnet operation rejected generated in response to a confirmed request apdu in which the service choice field specifies an unknown or unsupported service”  Environment Continuum 3rd party bacnet device Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause The bacnet error occurs when dynamic creating of schedules is not supported in the 3rd party device and the packet gets rejected. Resolution An ethereal capture from the Cyberstation will show the packet getting rejected. A work around for this is to use a BCX to create the schedule and communicate to the 3rd party device.
View full article
Picard Product_Support
‎2018-09-06 01:56 PM

Labels:
  • Andover Continuum
2064 Views

BCX 9640 not able to communicate Bacnet MSTP on Comm1

Issue Is there an Xdriver for the purpose of using comm1 as an BACnet over MSTP for this netcontroller BCX 9640 and still use comm2 as Infinet?   Environment BCX 4040 BCX 9640 Cause Supported feature to use Bacnet MSTP on a BCX 9640 on Comm1 via x-driver Resolution There is no x-driver to allow MSTP Bacnet communications on a BCX 9640 NOTE: Suggestion would be to use a BCX 4040 and Comm2 for MSTP Bacnet Communications.
View full article
Picard Product_Support
‎2018-09-06 01:56 PM

Labels:
  • Andover Continuum
1367 Views

Receiving error "Invalid Handle ID" on controller reload

Issue Reloading controller and receiving "Invalid Handle ID" error Environment Continuum Cyberstation BCX 4040 B3 controllers CX controllers i2 controllers Cause Most common cause is points already in the controller and/or bring controller from a different site/location and trying to reload while controller already has points in it. Resolution Reset controller Reload controller Backup controller flash memory
View full article
Picard Product_Support
‎2018-09-06 01:55 PM

Labels:
  • Andover Continuum
1778 Views

9702 not communicating

Issue CX9702:  appears to be powered up but showing offline in infinity programming Environment Continuum Cyberstation CX 9702 Cause Cannot communicate with 9702. Resolution Burn marks on then controller indicating overvoltage Send to repair.
View full article
Picard Product_Support
‎2018-09-06 01:55 PM

Labels:
  • Andover Continuum
1578 Views

Receiving "Invalid Object context" error when saving a program

Issue Receiving "Invalid Object context" error when saving a program Environment BCX 4040 B3 8xx -V Plain English Cause Receiving "Invalid Object context" error when saving a program Resolution Update B3 controllers with latest firmware version for Continuum Cyberstation version
View full article
Picard Product_Support
‎2018-09-06 01:55 PM

Labels:
  • Andover Continuum
1315 Views

Bacnet communications issues, cannot find 3rd party bacnet gateway devices

Issue Cannot find third party bacnet gateway devices Environment BCX 3rd party bacnet gateway devices Cause Configuration issue will not allow proper communications on Bacnet protocol Resolution The third party Bacnet Gateway devices were setup as foreign device registration and not properly configured. Foreign Device registration is not needed on a single subnet bacnet setup. Disabled foreign device registration and Bacnet communications is now properly established. Also check that the correct subnet mask has been entered for the network
View full article
Picard Product_Support
‎2018-09-06 01:55 PM

Labels:
  • Andover Continuum
1794 Views

Unable to commission an I/O module

Issue I/O modules that cannot be successfully commissioned Is there a procedure to test these or any resets or checks to do before sending the IOU back for repairs?   Environment CX96xx I/O Module Cause Unable to commission I/O module. Resolution FLASHING STATUS LIGHT This indicates that the Neuron chip in the module has undergone a partial commissioning and that it has calculated an invalid checksum in its flash chip.  This could happen due to communications problems on the IOU bus, either during module commissioning or during a NetController reload (which also de-commissions and re-commissions the modules). If you are experiencing this problem, do not return the modules to the Repair department. We have added a routine in the NetController to automatically detect and correct this condition. You can download the new NetController flash file and upgrade your NetController in the field. This will automatically correct any IOU modules that have this condition. To avoid this issue, you should also verify that your controllers and IOU modules are installed per the installation instructions, paying careful attention to bus topology, bus terminations, network cable, and grounding. Please note when adding multiple IOU modules that exhibit the behavior described above, to add and commission the modules onto the system one at a time.  SOLID STATUS LIGHT This indicates that the IOU module application flash is not present in the module. This could happen either due to the conditions described above or by a failure during the flash upgrade process.  These modules can be corrected in the field using one of the manual procedures described below: If the module was already commissioned on the NetController If the NetController has the module information in its memory, you should be able to flash the IOU firmware by editing the IOU object and selecting the “Update IOU” button. Then select the correct flash file for that module. If the module will not upgrade Connect the faulty module to a CX9xxx. With CyberStation online, create an IOU module.  Specify IOU number but not module ID. Save and close  the editor disregarding the error message. Set CyberStation offline. Edit the IOU module object inserting the module ID. Save and close the editor. Set CyberStation back online. Open the IOU module object, re-insert the module ID, select the Uprev button, and select a .upd file. When the uprev completes, commission the module. TAC product development has made a correction to this issue Click Here  in firmware version 1.530023. You should also read Technical Bulletin #1041 to make sure that you are using the correct IOU file.  
View full article
Picard Product_Support
‎2018-09-06 01:55 PM

Labels:
  • Andover Continuum
1412 Views

Enable XDriver on a CX9200

Issue How to enable Xdriver on a CX9200 Environment Continuum Cyberstation CX9200 Cause When Infinity chips are installed on a CX9200 controller, it will not accept the XDriver upgrade cookie.  Attempting to change the commport configuration to Xdriver will return an error "Invalid Mode." Continuum chips are needed to properly apply the cookie. The controller can then be returned to Infinity by replacing the Continuum chip set. The Xdriver can then be used. Most commonly, the issue is due to the Infinity chip set not allowing the XDriver upgrade, but the chip set is not properly identified before the Xdriver upgrade is attempted. Resolution Enable an XDriver on an Infinity CX9200 must be accomplished from a dumb terminal connection: Log on to the controller via Hyperterminal Load -o -m with the XDriver cookie file provided by the repair department. Go to the Hyperterminal Transfer pull down menu and select "Send to Text File" and select the file as provided by Repair. Hit Enter to start the transfer. Send to database from the Continuum Explorer and only select the specific CX9200 controller. When the upgrade has completed, power down the controller, then repower the controller. Verify that the ACCSetEEVal string point in the CX9200 has been created. Check the Options tab of the Continuum controller editor and verify that the commport has been properly enabled for XDriver.
View full article
Picard Product_Support
‎2018-09-06 01:55 PM

Labels:
  • Andover Continuum
2312 Views

Does WebClient Pinpoint use Active-X controls?

Issue Does Web Pinpoint user ActiveX Controls? Environment WebClient Cause On some projects the customer IT department will require that you let them know when Active X controls are being used over the internet. Resolution WebClient Pinpoint uses no ActiveX controls.
View full article
Picard Product_Support
‎2018-09-06 01:54 PM

Labels:
  • Andover Continuum
1361 Views

Issues reloading b3 device From CyberStation

Issue Under certain unknown scenario reloading a b3 device may result in CyberStation hanging when setting the attributes of the first object to be reloaded. A buffer overrun error may also appear. Environment CyberStation bCX4040 b3 Cause Invalid BACnet device configuration in database. Resolution In CyberStation go to the BACnet Devices folder and delete the BACnet device for the b3. Perform a Find New BACnet Devices. Send the BACnet device for the b3 to the database The reload operation should now complete successfully.
View full article
Picard Product_Support
‎2018-09-06 01:54 PM

Labels:
  • Andover Continuum
1259 Views

Emailing Reports

Issue When emailing reports there is no attachment. Environment Windows XP Continuum 1.7X, 1.8X. 1.90 Cause A Product defect. Resolution Contact PSS and request the Email Reports Patch. # 21527 1-978-975-9508
View full article
Picard Product_Support
‎2018-09-06 01:54 PM

Labels:
  • Andover Continuum
2018 Views

UL 916

Issue Is the I2/B3 865/866/885 UL 916 Listed Environment  I2/B3 865/866/885 Cause  I2/B3 865/866/885 UL 916 Listed Resolution Yes the  I2/B3 865/866/885 are UL 916 Listed Download the complete list of UL916 listed products.
View full article
Picard Product_Support
‎2018-09-07 02:35 PM

Labels:
  • Andover Continuum
8775 Views

Controller always indicates that a backup to flash is needed.

Issue Shortly after a successful backup to flash the exclamation point appears again on the controller's icon in the Continuum explorer indicating that a backup to flash is needed. Environment CyberStation bCX9640 bCX4040 CX9680 ACX5740 ACX5720 Cause PE program changing configuration attributes. A setpoint changes value. Resolution Any changes to a configuration attribute will cause the database in the controller to be marked as needing backup up to flash. Also, if an object is configured as a setpoint, changing its value causes the database to be marked as needing backup to flash. Find and modify any PE programs that change configuration attributes (i.e. description, format)  and/or setpoint values.
View full article
Picard Product_Support
‎2018-09-06 01:54 PM

Labels:
  • Andover Continuum
2149 Views

Cyberstation workstation programs become disabled when user logs in to the workstation

Issue Cyberstation workstation programs become disabled when user logs in to the workstation Environment Continuum Cause If a Plain English program is running on a workstation and a user logs on to that workstation, who does not have the rights to perform the operations within the program, then the program may become disabled. Resolution 1. Always try to keep the programs on a workstation to a minimum. Controllers should always be used for programs where possible. 2. Add a Line E to keep the program enabled. 3. Security rights for all users can be increased to keep the programs running. 4. If a program on a workstation is trying to do something that the user does not have permission to do, then the program will disable Therefore the user rights for doing what the program is doing need to be increased for that user
View full article
Picard Product_Support
‎2018-09-06 01:54 PM

Labels:
  • Andover Continuum
1095 Views

Continuum controller goes offline, controller error log shows LAN_ERR_BUFFER_TOO_SMALL_ERROR and/or LAN_ERR_ALLOCATION_ERROR.

Issue Controller randomly goes offline and add entries in its error log indicating LAN_ERR_BUFFER_TOO_SMALL_ERROR and/or LAN_ERR_ALLOCATION_ERROR. Environment CX9680 ACX5740/20 Cause Typically this is caused by a problem with the link partner (hub or switch) or some kind of CAT5 issue. Resolution If you have other ACX controller on this switch that is working fine try swapping the ports (or move the controller to a different port) and see if the problem follows the port or the controller. If the switch is a smart switch that gives an error log, get the log from the switch and analyze it or send in for analysis. There is also a possibility that the NIC card in the controller is bad but that assumption can only be made after everything else has been eliminated.
View full article
Picard Product_Support
‎2018-09-06 01:53 PM

Labels:
  • Andover Continuum
3060 Views

DCX250 Touch Screen compatibility with main board.

Issue I have an older model DCX-250 that the touchscreen has dead spots on the screen but the main board and power supply are working fine. It was wondering if the newer touch screen is compatible with the main board and power I have for the older model DCX-250 Environment DCX - 250 Cause When replacing DCX250 Touch Screen in the field you must check compatibility of your Main board. Resolution The black inverter located on "U6" of the Main Boards PCB was changed out to a newer inverter.  The old style inverter will not work with the Touch screen. If you have the older inverter labeled E205-E821D then this will need to go back to repair to fix because the Touch Screen will not work with this older style inverter. If you have the black inverter that is labeled E2536 it is newer and you can just order a new touch screen from customer care.   Customer Care ordering website http://iportal2.schneider-electric.com Repair Department Contact Information Email: industrialrepair@schneider-electric.com
View full article
Picard Product_Support
‎2018-09-07 10:54 PM

Labels:
  • Andover Continuum
1104 Views
  • « Previous
    • 1
    • …
    • 67
    • 68
    • 69
    • …
    • 110
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore