Controller always indicates that a backup to flash is needed.
  • Controller always indicates that a backup to flash is needed.
  • AbeMeran
    AbeMeran
‎2018-09-06 01:54 PM
Shortly after a successful backup to flash the exclamation point appears again on the controller's icon in the Continuum explorer indicating that a backup to flash is needed.
  • CyberStation
  • bCX9640
  • bCX4040
  • CX9680
  • ACX5740
  • ACX5720
  1. PE program changing configuration attributes.
  2. A setpoint changes value.
Any changes to a configuration attribute will cause the database in the controller to be marked as needing backup up to flash.
Also, if an object is configured as a setpoint, changing its value causes the database to be marked as needing backup to flash.
Find and modify any PE programs that change configuration attributes (i.e. description, format)  and/or setpoint values.
  • 5025
0% helpful (0/1)