Unable to commission an I/O module

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to commission an I/O module
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1409 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to commission an I/O module

Picard Product_Support
‎2018-09-06 01:55 PM

Issue

  • I/O modules that cannot be successfully commissioned
  • Is there a procedure to test these or any resets or checks to do before sending the IOU back for repairs?
     

Environment

  • CX96xx
  • I/O Module

Cause

Unable to commission I/O module.

Resolution

FLASHING STATUS LIGHT

This indicates that the Neuron chip in the module has undergone a partial commissioning and that it has calculated an invalid checksum in its flash chip.  This could happen due to communications problems on the IOU bus, either during module commissioning or during a NetController reload (which also de-commissions and re-commissions the modules).

If you are experiencing this problem, do not return the modules to the Repair department. We have added a routine in the NetController to automatically detect and correct this condition. You can download the new NetController flash file and upgrade your NetController in the field. This will automatically correct any IOU modules that have this condition.

To avoid this issue, you should also verify that your controllers and IOU modules are installed per the installation instructions, paying careful attention to bus topology, bus terminations, network cable, and grounding.

Please note when adding multiple IOU modules that exhibit the behavior described above, to add and commission the modules onto the system one at a time.

 SOLID STATUS LIGHT

This indicates that the IOU module application flash is not present in the module. This could happen either due to the conditions described above or by a failure during the flash upgrade process.

 These modules can be corrected in the field using one of the manual procedures described below:

If the module was already commissioned on the NetController

If the NetController has the module information in its memory, you should be able to flash the IOU firmware by editing the IOU object and selecting the “Update IOU” button. Then select the correct flash file for that module.

If the module will not upgrade

  1. Connect the faulty module to a CX9xxx.
  2. With CyberStation online, create an IOU module.  Specify IOU number but not module ID. Save and close  the editor disregarding the error message.
  3. Set CyberStation offline. Edit the IOU module object inserting the module ID. Save and close the editor. Set CyberStation back online.
  4. Open the IOU module object, re-insert the module ID, select the Uprev button, and select a .upd file.
  5. When the uprev completes, commission the module.

TAC product development has made a correction to this issue Click Here  in firmware version 1.530023.

You should also read Technical Bulletin #1041 to make sure that you are using the correct IOU file.


 

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4991
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore