Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2029 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 59
    • 60
    • 61
    • …
    • 102
  • Next »
Label: "TAC Vista" Show all articles

Induced voltage generated by electrical discharges & what we use to protect our hardware systems.

Issue Induced voltage generated by electrical discharges & what we use to protect our hardware systems. Environment I/NET Seven or Vista Site Cause Explanation that I/Net and Vista products utilize a variety of design methods and transient related components/circuits for general isolation and/or suppression of EMC noise/disturbances Resolution The I/Net and Vista products utilize a variety of design methods and transient related components/circuits for general isolation and/or suppression of EMC noise/disturbances. We utilize components such as MOVs, Trans-Zorb TVS suppressors, inductors/ferrites, opto-couplers, relays with >1KV isolation, filter capacitors, RC circuits, etc., to suppress and/or isolate EMI interference along with circuit design and segregation practices to achieve compliance with the EMC immunity (and emission) standards applicable to the CE marking of the products. A number of different specific international standards are applied to this compliance verification.
View full article
Picard Product_Support
‎2018-09-06 03:11 PM

Labels:
  • TAC INET
  • TAC Vista
1217 Views

Xenta 100 high discharge temperature alarm limit can not be set high enough

Issue Xenta 100 has a discharge temperature alarm when in heat but the alarm limit can't be set high enough Environment Xenta 100 Cause In several parameters, the Xenta 100 plug-ins set limits on the range of valid entries which are tighter than the limits for that SNVT type. One example is nciDischAirMax on the 104-A. The plug-in sets the acceptable range at 32-104°F (0-40°C). The heated discharge temperature is likely to exceed 104°F. Resolution Open the LonMaker browser on the device Change the setting for the high alarm limit there. Values much higher than 104°F can be entered (limited only by the SNVT type).
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
989 Views

Upgrading Vista while running Server as a service

Issue Upgrading Vista while running Server as a service Product Line TAC Vista Environment TAC Vista Server Cause The installation directories include the version number (i.e. C:\Program Files\TAC\TAC Vista 4.2.3). If you perform an upgrade before unregistering the service, you will be unable to unregister the service unless you reinstall the previous version to provide the files Windows requires. Resolution If a user is running Vista Server as a service it is recommended that the user unregister the service before performing an upgrade.  
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
1493 Views

FieldServer Bridge in Lon network with more then 15 devices

Issue FieldServer Bridge in Lon network with more then 15 devices Environment I/NET or Vista Site Cause Can a FieldServer bridge communicate with more then 15 Xenta controllers? Resolution A FieldServer bridge can communicate with more then 15 Xenta controllers despite the address table limitation found with implicit addressing. This requires that the bridge be programmed for explicit addressing which requires the knowledge of the controllers node number and SNVT index numbers. This is useful for situations where you are interfacing to a non LonWorks device that needs to communicate values to more then 15 Xenta or LonWorks controllers.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC INET
  • TAC Vista
1405 Views

Deleting a Group from the System Plug-in

Issue Deleting a Group from the System Plug-in Environment TAC Vista System Plugin Cause After adding a controller to the Vista database, the System Plug-in automatically creates a new Group Resolution If you move the new controller to a different Group, make sure the controller you added is not still selected when you try to delete the old group. By default, both the controller you moved and the group you moved it from will be selected. Hitting the delete key will delete both.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
1302 Views

Xenta 511/527/911: Recovering from a bad download

Issue Xenta 511/527/911: Recovering from a bad download Environment Xenta 511, 527, 911 Cause If the 511/527/911 has suffered an error during the download process and the system starts behaving abnormally, then the device needs to be taken back to a boot state. Resolution Connect to the 511/527/911 using the serial connection on port B Use HyperTerminal to log in. Type "format" command to format the device. Once the process has completed, log in as super user (root/root by default) and set the IP address as detailed in the device manual. Verify that you can ping the device from a computer and then run the appropriate system program for the device you are working with. Select option B Install Full System. This will verify the current program is in the device as well as let you change the color scheme. Once this is completed you should be able to download the existing or new XBuilder project to the device.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
1902 Views

Adding Custom Buttons in Vista 4.2

Issue Adding Custom Buttons in Vista 4.2 Environment Vista 4.2 Cause In Vista 4.2 you can add custom buttons to the Tools menu or the Toolbar. This can be useful to make shortcuts to the desktop, your Vista database directory, or WordPad. Resolution Right click on any tool bar and choose Customize. On the Tools tab, insert a new shortcut. Enter a name for the button and the Path for the EXE you wish to execute in the Command box. Click Close and your button should be visible from the Tools menu. You can also drag and drop this button on any tool bar.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
924 Views

How can I get SNVT values from one LonWorks network to another without relying on Vista to do object transfer?

Issue How can I get SNVT values from one LonWorks network to another without relying on Vista to do object transfer? Environment Two LNS Networks LonMaker/NL220 Cause Data cannot be transferred between two separate LON networks unless they share an L-Proxy in the network management tool. Resolution Each port of a Loytec L-Proxy may be commissioned in a different LonWorks network. Any SNVT bound to one port can be transferred by the L-Proxy to its other port(s).
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
1237 Views

Corrupted/Hidden Time Schedule Events

Issue Corrupted/Hidden Time Schedule Events Environment Time Schedule Objects Vista Workstation Cause Sometimes an event will not show up in the Time Schedule window in Vista, but may still be in the object. Resolution To check all Time Schedules in Vista press Ctrl+Shift+D and a table will show up with all events in that Time Schedule. From here you can edit, add, and delete events.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
1237 Views

Configuring Xenta Public Signals

Issue It is possible to browse and bind the public signals while working on MTA files on your hard drive, however this has repeatedly led to problems when downloaded due to differences in controller names between the MTA file and the controller name in the Vista database. Environment TAC Menta TAC Network Variables Xenta programmable controllers Cause Waiting until the application is imported into the network will allow the Vista database to automatically provide you with the correct controller name to the public signal you are wanting to use. You will have a database browse window rather then a file select window which is your indication that you are doing this the correct way. This method to reduces the chance of operator error. Resolution While generating your Menta application, do not set the Network Address while binding Inputs to the Network Variable option Complete the other parts of the application and import the .mta to the Vista Database using the System Plug In. Once the application has been incorporated in the Vista database you can then edit the application and browse the Network Address of the Input.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
2065 Views

"Field Unit Not Configured" error during download

Issue "Field Unit Not Configured" error during download Environment Vista System Plug-In Xenta programmable controllers  Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B Cause If trying to download the application and parameters in a Xenta controller and the error "Field Unit Not Configured" is received, one cause that has been found is when an Xenta base unit is placed in a LonWorks group (even if it appears to be a part of a Xenta group). Resolution The group in question should be deleted from the Vista database pane in the Vista System Plug-In. Update the Vista database and the controllers imported into the Vista Database should be created in proper groups. Verify that the group is tagged correctly and then update the Vista database once more. Verify for the final time in Vista Workstation that the group is a Xenta group before downloading to the controller in the Vista System Plug-In. You may also drag that Xenta unit into an existing Xenta group after it has been re-imported.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
1636 Views

"Error: Device does not refer to a COM port" when downloading an application to a Xenta 400/300/2xx controller

Issue "Error: Device does not refer to a COM port" when downloading an application to a Xenta 400/300/2xx controller Environment Xenta 281, 282, 283, 301, 302, 401 Cause This message means that the LonWorks network in the Vista database doesn’t have any COM port (LNS port) defined. The problem is usually caused when you start a different LonMaker network but forget to change the Vista database directory. When a "update Vista db" is done from the system plug-in instead of adding or updating the correct database, a second network has been added to the Vista db. You now have 2 LonWorks networks in your Vista db but only one communication port. Resolution Delete the incorrect LonWorks network Open the correct LonMaker drawing Update the Vista Db once more to make sure everything is in sync. For the second LonMaker drawing, specify the correct Vista db directory in Vista Server Setup and update the Vista db.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
1138 Views

Space temperature calibration using the Xenta 102-AX plug-in

Issue Space temperature sensor calibration using the Xenta 102-AX plug-in Environment Xenta 102-AX Plug-In Cause The space temperature of a 102-AX can be calibrated in three locations:   M/STAT, service menu OP > CSS, resolution 0.1° Vista Workstation, VAV_Controller.UCPTvavSelection.CSS, resolution as entered Xenta 102-AX Plug-in, Browser tab > UCPTvavSelection, resolution 1° The first two allow resolution at least as fine as 0.1° step sizes on the offset.  The LNS plug-in, however, by default only allows whole integer 1° step sizes. Resolution Read to the end before you try this.  NOTE:  It is recommended to make this fix prior to opening the plug-in on a VAV box that has already had the space temperature calibrated via the M/STAT.  Failure to do so may result in the desired calibration being rounded to the nearest whole degree. From the Xenta 102-AX plug-in, select the browser tab (or open the LonMaker browser if you wish). Navigate to and expand the VAV controller object and select "UCPTvavSelection.CSS". Past all of the "CALIBR_NOT_ACTIVE" statements, you'll find a couple of numbers - the second one being 32. Raising or lowering this value will raise or lower the space temp by the same amount. But, until now, if you try to enter 33 or 31 you'll find that only even numbered integers are accepted. What to do? Open c:\Lonworks\types\user\TAC\Xenta100.fmt in notepad. Locate line 172 which should appear as UCPTvavSelection#US: text("%m,%m,%m,%d,%d,%d,%m,%m,%m,%m,%m", Change the second "%d" to "%f" and save the file and restart the Xenta 102-AX plug-in. Now you can change that value in finer increments than is necessary.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
1684 Views

Xenta Time Charts changes when clicking Edit in Vista 4.2.3

Issue Xenta Time Charts changes when clicking Edit in Vista 4.2.3 Environment TAC Vista 4.2.3 Time Schedules Cause In some cases Xenta Time Charts will change when clicking the Edit button. For example, if you have a time chart running Monday through Saturday and you click Edit the days will change to Tuesday through Sunday. Resolution Upgrade to the latest version of Vista to fix this issue. To work around this without upgrading: Change the First Day of week setting in your registry HKEY_CURRENT_USER\Control Panel\International\iFirstDayOfWeek If you change this to 0, the first day of the week will be considered Monday and editing Time Charts will work.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • TAC Vista
1135 Views

HASP Error when installing Privilege Administrator 2.01 on Windows XP Machine Service Pack 2

Issue HASP Error when installing Privilege Licenser 2.01 on Windows XP Machine Service Pack 2 Environment Aladdin Privilege Administrator 2.01 Windows XP SP2 Vista IV Licensing Cause On the most recent versions of Windows XP with Service Pack 2 installed, there has been a problem installing Privilege Licenser 2.01. Upon installing the software a "HASP" error occurs. This is caused by the version of HASP on the computer not being compatible with one Privilege Licenser is trying to use. Resolution Aladdin does not officially support Windows XP SP2, but there is a fix that usually fixes the problem. Go to the following url and download the "HASP Device Driver Commandline Installation" https://supportportal.gemalto.com/csm/?id=kb_article&sys_id=f7055f20db6207c8fe0aff3dbf9619cc Download the file to your hard drive and use the following steps to install the fix: Unzip file to root of your C: drive. Go to Start/Run and type in ‘cmd’. In the DOS window type in ‘cd\’ This will take you to the root of the ‘C:\’ drive Type in ‘cd hinstall’ This will take you to the program folder Type in ‘hinstall.exe –i’ A window will pop up and let you know when the file has finished installing. Close out of DOS by typing in ‘exit’ Run setup for Privilege Licenser 2.01 Note: Beginning 2012, PSS will no longer support the Privilege License System. The Tamfs26 Server will be retired along with TAC License Server software. It would be wise to inform the customer of this important information to plan for future upgrade in the event that their site license has issues.
View full article
Picard Product_Support
‎2018-09-07 01:23 AM

Labels:
  • TAC Vista
1695 Views

ERROR C:\Program Files\TAC\TAC Menta X.X.X\temp\opdoc.gop Error in line: xx

Issue If there is a " in any of the Xenta OP screens, the application will not compile/download correctly. Error message states "ERROR c":\program files\tac\tac menta 4.2.3\temp\opdoc.gop Error in line: xx " Environment Xenta programmable controllers Menta Xenta OP Tree (.dop) Cause The character " is not allowed in the Xenta OP. Resolution Do not use the character " in the Xenta OP tree.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
3818 Views

Xenta 102-AX Heat cycling off even with rev. 1.11

Issue Xenta 102-AX Heat cycling off even with rev. 1.11 Environment TAC Xenta 102-AX v1.11 Cause If nvi_applicmode is bound to another device, it will revert to hvac_cool for a split second every time it receives a packet. If the controller is in heat mode, this is long enough for the heat to turn off and the terminal load to go to 0 for about 3-5 seconds. If it is time to change modes anyway, this is not a problem but if the mode is re-enforced periodically, your heat output will turn off upon that period. Resolution There is no need to re-enforce this command, so make sure that the output is set to send ONLY on a change. Make sure period is set to 0.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
1312 Views

Stroke time on Xenta 102-AX

Issue Stroke time (throttling range) on Xenta 102-AX VAV controller Environment Xenta 102-AX Cause The stroke time of the actuator differs when the input power is 50Hz versus 60Hz. Since this is not an Imperial vs. Metric issue, LonMaker or Vista does not automatically change this for you according to your regional settings. Resolution The stroke time for the Xenta 102-AX is as follows: 2.4 seconds / degree rotation (50 Hz) 2.0 seconds / degree rotation (60 Hz)   Assuming the damper stroke is 90º: The default setting for damper stroke time is 230 seconds. This is the approximate stroke time when that AC motor is driven with a 50Hz supply. 185 seconds is the approximate time when using a 60Hz supply. The unit will control space temperature regardless but the damper position which is estimated in software will be off when it is anywhere other than 0% or 100%. This will make the damper more aggressive than the program thinks it is. This could make the calibration efforts take longer since the damper might take longer to stabilize the airflow reading. It is recommend to change the damper stroke time to 185 on any site fed by a 60Hz supply. (Unless the damper travel is other than 90°. In that case, set the physical screws accordingly and calculate a new appropriate stroke time based on the seconds per degree values above.)
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
1590 Views

Corrupted LNS Credits

Issue Cannot register LonMaker plugins Product Line TAC Vista Environment LNS, LonMaker, NL220 Cause If you are having difficulty registering plug ins in LonMaker then you may have corrupted LNS credits. Resolution To check your LNS credit status, run the LNS Server License Wizard which is found at C:\LonWorks\bin\LnsLic.exe If you run the wizard and it displays the Max Credits at zero and Credits Available as zero as well, then your LNS credits have become corrupted. To correct this, select Next in the Wizard so that it displays the PC Key. The wizard provides a button titled "Copy to Clipboard" which when selected will allow you to paste a form letter into an email or text editor. After filling your specific contact information you will want to check the "No Charge" box and the "Replacement Use" box. Before you send the form via fax or email, you also need to provide evidence that your LNS credits have been corrupted. Select Start > Run > and type "cmd" to reach a command prompt. This command will check the status of the LNS credits: checklic nsseng.exe The output of this command should either be printed and sent with the fax or included in the email to the address or phone number shown at the top of the form letter. You should then receive instructions or an application key to correct the problem.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
1885 Views

Send out the system date and time as a SNVT_Time_stamp

Issue Send out the system date and time as a SNVT_Time_stamp Environment Time Stamp SNVT type Xenta 511 Cause Send out the system time properties to monitor externally and make sure the time is synchronized. Resolution You can do this by creating signals in the system window for the system variable year, month, day, hour, minute and second. Create an nvo SNVT_time_stamp in the Xenta 511. Create connection objects and connect the signals with the members of the SNVT. Note, you have to change the category and the unit for hour, minute and second to match the SNVT.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
989 Views
  • « Previous
    • 1
    • …
    • 59
    • 60
    • 61
    • …
    • 102
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore