Issue
Xenta 100 has a discharge temperature alarm when in heat but the alarm limit can't be set high enough
Environment
Xenta 100
Cause
In several parameters, the Xenta 100 plug-ins set limits on the range of valid entries which are tighter than the limits for that SNVT type. One example is nciDischAirMax on the 104-A. The plug-in sets the acceptable range at 32-104°F (0-40°C). The heated discharge temperature is likely to exceed 104°F.
Resolution
- Open the LonMaker browser on the device
- Change the setting for the high alarm limit there. Values much higher than 104°F can be entered (limited only by the SNVT type).