Issue
- If there is a " in any of the Xenta OP screens, the application will not compile/download correctly.
- Error message states "ERROR c":\program files\tac\tac menta 4.2.3\temp\opdoc.gop Error in line: xx "
Environment
- Xenta programmable controllers
- Menta
- Xenta OP Tree (.dop)
Cause
The character " is not allowed in the Xenta OP.
Resolution
Do not use the character " in the Xenta OP tree.