Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2029 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 57
    • 58
    • 59
    • …
    • 102
  • Next »
Label: "TAC Vista" Show all articles

Using the Xenta 511, will value pages only show temperatures in Celsius? How do you get them to display in Fahrenheit?

Issue Using the Xenta 511, will value pages only show temperatures in Celsius? How do you get them to display in Fahrenheit? Environment XBuilder Cause Regional settings can be project wide or per point. Resolution When creating a new TAC Xenta 511 project, select to use US values. You can also select conversions to occur per object.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
1072 Views

Is it not possible to have multiple Xenta 901s from multiple sites in a single LNS network

Issue Is it possible to have multiple Xenta 901 controllers from multiple sites in a single LNS network and access the remote sites as needed? This would leave any controllers not connected offline. Environment TAC Xenta 901 LNS Network Cause TAC Xenta 901 is an "LTA" and in TAC Vista there can only be one per LonWorks network. Resolution Create one LNS database per TAC Xenta 901. You can have up to 240 TAC Xenta 901 networks per TAC Vista Server (all can dial up the same TAC Vista Modem(s)). Add another TAC Vista Server if you need more dial up connections.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
1114 Views

What network troubleshooting tools are available for use with Lon systems.

Issue What network troubleshooting tools are available for use with Lon systems. Environment Vista LON systems Cause Option in tools to monitor error tracking in packets. Resolution We recommend the LoyTec network data analyzer as a very important tool. It is available from Engenuity.com. It is a very user friendly tool that is windows based.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1050 Views

Version control issues with Echelon LonMaker

Issue Version control issues with Echelon LonMaker Environment LonMaker Cause When a LonMaker database is opened by a PC using a version of LonMaker that is more current that the version used to create the database, the database will be automatically updated. The previous version of LonMaker can no longer be used to open the database. Resolution Control the version of LonMaker being used by all of your personnel. Keep all PCs on a project at the same revision to avoid problems and loss of efficiency.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1116 Views

File management for Menta applications

Issue Are there any special concerns I should have with respect to making changes in Menta applications on my installations? Environment Menta programming Vista database Cause After a Menta application is downloaded to a controller, the file is imported into the Vista database. The file also typically remains on the technicians laptop. If the technician makes a change and downloads a new load to the controller but does not update Vista problems will occur. Resolution It is good practice to let Vista be the file cabinet. When a change is required, export the application from Vista, make the changes, download to the controller and then re-import to Vista. This will keep your field environment in concert with the operator interface.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1346 Views

How does a Menta application execute?

Issue How does a Menta application execute? Environment Menta Cause Menta applications use parallel computing. All updates are simultaneous. There is no order by object name or number. Location of objects on the page has nothing to do with execution. Resolution Menta applications update all objects simultaneously. On the first program cycle, the outputs of all objects are updated based on initial values within all of the blocks. On the next sweep, all inputs are updates from external values or outputs from upstream objects. All outputs are then updated from the new inputs. This process then continues.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1640 Views

Significance of initial value settings in Menta

Issue What is the significance of initial value settings for some blocks in Menta? Environment Menta PVR, PVB, PVI Cause Initial value settings are used on the first program cycle after a download or the first program cycle after power has been off for more than 72 hours. Resolution The most common error in programming a value for the "initial value" is programming a value that causes some unique aspect of the program to execute. For example, if the initial value of the mixed air temperature is programmed at 0°F and a low limit alarm value of 40°F is part of the logic, a mixed air alarm will be generated on the first program cycle and the fan may be locked in the off position. Always program "safe" initial values.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1590 Views

Execution of the application in a programmable controller has stopped

Issue It is possible to stop the execution of the application in a programmable controller. Typically, this is done accidentally. Environment Xenta programmable controllers Directly connected Menta Cause When you are connected to a controller using the RS232 cable and you are in the online mode you can stop the application by pressing and then releasing the execution button. Resolution  If the application has been stopped while directly connected through a serial cable, and the cable is then disconnected, the application will remain paused. When directly connected to view a Menta application it is best practice not to use the execution button. If an application has been stopped, you must connect directly to the controller again to start the execution.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1436 Views

Keep others from using local TAC Vista IV licenses

Issue How do you keep others from using my TAC Vista IV licenses? Environment Vista IV Licensing Cause Networked PCs will look for licenses outside of their local drives. On a shared engineering drive, this can cause problems. Resolution In order to have your PC set up so that it does not share its license over a network: Go to Start > Run > Type in regedit Click OK Go to HKEY_LOCAL_MACHINE > SOFTWARE > Aladdin Knowledge Systems > Privilege Licenser > Applications Click on PLServe Double click on Network Change the 1 to a 0
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1255 Views

Disable TAC Vista IV license sharing over a network

Issue Disable TAC Vista IV license sharing over a network Environment TAC Vista IV Licensing Vista Server on an open network Cause Sharing licenses across a network can be a cost effective mechanism to enable several users to use a pool of seats. However, if yours is the only license on the network, it can accidentally be "stolen" by someone else running Vista Server on the same network and you will be unable to connect, or will have to wait a long time for your PC to find an available license elsewhere on the network. Especially in an engineering setting, it is better to disable this feature. Resolution In order to have your PC set up so that it does not share its license over a network: Go to Start > Run Type in regedit, Click OK Go to HKEY_LOCAL_MACHINE > SOFTWARE > Aladdin Knowledge Systems > Privilege Licenser > Server Addresses Enter the computer name in the TCP/IP Change Broadcast to NO.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1241 Views

In Vista, alarms are not appearing in the alarm handling window.

Issue In Vista, alarms are not appearing in the alarm handling window. Environment Vista Workstation Alarm Queue Cause If the alarm is set up for a priority of Zero the alarms will not shown in Vista alarm window. Resolution If you are online in Vista, you can change the priority directly in Vista. The changes will be done in your MTA file when you export the file. Go back into Menta change the priority level in the alarm block Redownload the Menta file. Go into Vista Open the object selection box Double click on the alarm object Click on the button Status button Change the priority level Click OK
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1632 Views

Preserve Configuration Parameters when recommissioning a device in LonMaker

Issue Recommission a device in LonMaker causes the loss of Configuration Parameter setting that were changed in the browser. Environment Echelon LonMaker Cause These values exist in the device, but not in the database. Resolution When recommissioning, select use Current Values in Device instead of Default. After you have Made all the changes to the CPs in the browser that you want: Close the browser Right click on the device Go to Resynch CPs Select the Option – Upload values from the device Click OK. This will upload the Value that you just sent to the device and insert those values a CP defaults into Lon Maker’s browser. This way every time you recommission a device it will not lose any of these changes.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1308 Views

What can be connected to a UI on an Xenta controller?

Issue What can be connected to a UI on an Xenta controller? Environment Xenta programmable Xenta I/O modules Universal Inputs Cause The name "universal input" implies that anything can be connected to it. In reality, it just accepts several different types of inputs (not all). Resolution Thermistor 0-10 volts Open/Close contact
View full article
Picard Product_Support
‎2018-09-06 03:23 PM

Labels:
  • TAC Vista
1419 Views

Can you use the thermistor inputs on a 451 for Digital Inputs?

Issue Can you use the thermistor inputs on a 451 for Digital Inputs? Environment Xenta 451 Cause Thermistors can only be used on B inputs and U inputs, not X inputs.  Resolution The associated software does not allow anything with an X input to report anything but an on/off based on a voltage or no voltage.
View full article
Picard Product_Support
‎2018-09-06 03:23 PM

Labels:
  • TAC Vista
1066 Views

In LonMaker, how do I get rid of multiple message tags within a base unit virtual function block?

Issue In LonMaker, how do I get rid of multiple message tags within a base unit virtual function block? Environment Vista Site Cause In LonMaker, how do I get rid of multiple message tags within a base unit virtual function block? Resolution Right click on the VFB and select to delete NVs & MTs. All unconnected message tags will then be deleted.
View full article
Picard Product_Support
‎2018-09-06 03:22 PM

Labels:
  • TAC Vista
910 Views

In the event of an alarm can TAC Vista Server dial out using RAS to another TAC Vista workstation?

Issue In the event of an alarm can TAC Vista Server dial out using RAS to another TAC Vista workstation? How does a local site call a remote Service Center? Using RAS? Environment TAC Vista Server IV RAS Cause In the event of an alarm, a service technician can be paged using an email service paging system and then call up the remote location using RAS or PC Anywhere. Resolution Service centers will need to use the mail receiver functionality within TAC Vista.
View full article
Picard Product_Support
‎2018-09-06 03:22 PM

Labels:
  • TAC Vista
1256 Views

Should we recommend Message tag bindings be performed after the commissioning of the device?

Issue Should we recommend Message tag bindings be performed after the commissioning of the device? Environment I/NET Site Cause Should we recommend Message tag bindings be performed after the commissioning of the device? Resolution No, this should not be necessary. It may be preferable, however, for a dialed network as the 901 device must be added to the network when connected to the network.
View full article
Picard Product_Support
‎2018-09-06 03:22 PM

Labels:
  • TAC INET
  • TAC Vista
928 Views

901 modem is dialing multiple times before successfully registering a change on the alarm window.

Issue The 901 modem is dialing multiple times (6-8) before successfully registering a change on the alarm window. Environment 901 Modem Cause Normally it only takes one dial-up attempt to establish the communication link. If it takes 6-8 times, it indicates modem or telephone line problems. Resolution In the dial-up parameters, define the number of dial up attempts before line block. 10 is the default value.
View full article
Picard Product_Support
‎2018-09-06 03:20 PM

Labels:
  • TAC Vista
920 Views

901 dialing once for each trip/reset of the alarm

Issue Why is the 901 dialing once for each time the alarm is tripped or reset? Is there a way to request that the alarm queue be emptied with one call? Environment 901 Modem Cause This is because the dial up parameters have been configured to do this. Resolution Check the "Alarm delay" parameters where tripped/reset/ack is specified. If you don't want the TAC Xenta 901 to dial up when an alarm is reset or acked, just uncheck the options. Note that the options are per alarm priority.
View full article
Picard Product_Support
‎2018-09-06 03:20 PM

Labels:
  • TAC Vista
1171 Views

How do you get the system information of a Xenta Server from a web browser?

Issue How do you get the system information of a Xenta Server from a web browser? Environment Xenta Server Xenta 511, 527, 701, 711, 721, 731, 913 Cause View the most up to date system information for the firmware version loaded into a Xenta Server. Resolution Getting system information using a web browser: Menu Utilities-System Information Displays all system information such as software versions etc. Use cut/paste to save information. Menu Utilities-Error-Error-System Error Log Displays system information and all error messages in the system error log. Use cut/paste to save information.
View full article
Picard Product_Support
‎2018-09-06 03:17 PM

Labels:
  • TAC INET
  • TAC Vista
2270 Views
  • « Previous
    • 1
    • …
    • 57
    • 58
    • 59
    • …
    • 102
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore