Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,854
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 11
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2045 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 53
    • 54
    • 55
    • …
    • 103
  • Next »
Label: "TAC Vista" Show all articles

Significance of initial value settings in Menta

Issue What is the significance of initial value settings for some blocks in Menta? Environment Menta PVR, PVB, PVI Cause Initial value settings are used on the first program cycle after a download or the first program cycle after power has been off for more than 72 hours. Resolution The most common error in programming a value for the "initial value" is programming a value that causes some unique aspect of the program to execute. For example, if the initial value of the mixed air temperature is programmed at 0°F and a low limit alarm value of 40°F is part of the logic, a mixed air alarm will be generated on the first program cycle and the fan may be locked in the off position. Always program "safe" initial values.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1277 Views

Execution of the application in a programmable controller has stopped

Issue It is possible to stop the execution of the application in a programmable controller. Typically, this is done accidentally. Environment Xenta programmable controllers Directly connected Menta Cause When you are connected to a controller using the RS232 cable and you are in the online mode you can stop the application by pressing and then releasing the execution button. Resolution  If the application has been stopped while directly connected through a serial cable, and the cable is then disconnected, the application will remain paused. When directly connected to view a Menta application it is best practice not to use the execution button. If an application has been stopped, you must connect directly to the controller again to start the execution.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1323 Views

Keep others from using local TAC Vista IV licenses

Issue How do you keep others from using my TAC Vista IV licenses? Environment Vista IV Licensing Cause Networked PCs will look for licenses outside of their local drives. On a shared engineering drive, this can cause problems. Resolution In order to have your PC set up so that it does not share its license over a network: Go to Start > Run > Type in regedit Click OK Go to HKEY_LOCAL_MACHINE > SOFTWARE > Aladdin Knowledge Systems > Privilege Licenser > Applications Click on PLServe Double click on Network Change the 1 to a 0
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1151 Views

Disable TAC Vista IV license sharing over a network

Issue Disable TAC Vista IV license sharing over a network Environment TAC Vista IV Licensing Vista Server on an open network Cause Sharing licenses across a network can be a cost effective mechanism to enable several users to use a pool of seats. However, if yours is the only license on the network, it can accidentally be "stolen" by someone else running Vista Server on the same network and you will be unable to connect, or will have to wait a long time for your PC to find an available license elsewhere on the network. Especially in an engineering setting, it is better to disable this feature. Resolution In order to have your PC set up so that it does not share its license over a network: Go to Start > Run Type in regedit, Click OK Go to HKEY_LOCAL_MACHINE > SOFTWARE > Aladdin Knowledge Systems > Privilege Licenser > Server Addresses Enter the computer name in the TCP/IP Change Broadcast to NO.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1127 Views

In Vista, alarms are not appearing in the alarm handling window.

Issue In Vista, alarms are not appearing in the alarm handling window. Environment Vista Workstation Alarm Queue Cause If the alarm is set up for a priority of Zero the alarms will not shown in Vista alarm window. Resolution If you are online in Vista, you can change the priority directly in Vista. The changes will be done in your MTA file when you export the file. Go back into Menta change the priority level in the alarm block Redownload the Menta file. Go into Vista Open the object selection box Double click on the alarm object Click on the button Status button Change the priority level Click OK
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1526 Views

Preserve Configuration Parameters when recommissioning a device in LonMaker

Issue Recommission a device in LonMaker causes the loss of Configuration Parameter setting that were changed in the browser. Environment Echelon LonMaker Cause These values exist in the device, but not in the database. Resolution When recommissioning, select use Current Values in Device instead of Default. After you have Made all the changes to the CPs in the browser that you want: Close the browser Right click on the device Go to Resynch CPs Select the Option – Upload values from the device Click OK. This will upload the Value that you just sent to the device and insert those values a CP defaults into Lon Maker’s browser. This way every time you recommission a device it will not lose any of these changes.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1179 Views

What can be connected to a UI on an Xenta controller?

Issue What can be connected to a UI on an Xenta controller? Environment Xenta programmable Xenta I/O modules Universal Inputs Cause The name "universal input" implies that anything can be connected to it. In reality, it just accepts several different types of inputs (not all). Resolution Thermistor 0-10 volts Open/Close contact
View full article
Picard Product_Support
‎2018-09-06 03:23 PM

Labels:
  • TAC Vista
1293 Views

Can you use the thermistor inputs on a 451 for Digital Inputs?

Issue Can you use the thermistor inputs on a 451 for Digital Inputs? Environment Xenta 451 Cause Thermistors can only be used on B inputs and U inputs, not X inputs.  Resolution The associated software does not allow anything with an X input to report anything but an on/off based on a voltage or no voltage.
View full article
Picard Product_Support
‎2018-09-06 03:23 PM

Labels:
  • TAC Vista
938 Views

In LonMaker, how do I get rid of multiple message tags within a base unit virtual function block?

Issue In LonMaker, how do I get rid of multiple message tags within a base unit virtual function block? Environment Vista Site Cause In LonMaker, how do I get rid of multiple message tags within a base unit virtual function block? Resolution Right click on the VFB and select to delete NVs & MTs. All unconnected message tags will then be deleted.
View full article
Picard Product_Support
‎2018-09-06 03:22 PM

Labels:
  • TAC Vista
807 Views

In the event of an alarm can TAC Vista Server dial out using RAS to another TAC Vista workstation?

Issue In the event of an alarm can TAC Vista Server dial out using RAS to another TAC Vista workstation? How does a local site call a remote Service Center? Using RAS? Environment TAC Vista Server IV RAS Cause In the event of an alarm, a service technician can be paged using an email service paging system and then call up the remote location using RAS or PC Anywhere. Resolution Service centers will need to use the mail receiver functionality within TAC Vista.
View full article
Picard Product_Support
‎2018-09-06 03:22 PM

Labels:
  • TAC Vista
1158 Views

Should we recommend Message tag bindings be performed after the commissioning of the device?

Issue Should we recommend Message tag bindings be performed after the commissioning of the device? Environment I/NET Site Cause Should we recommend Message tag bindings be performed after the commissioning of the device? Resolution No, this should not be necessary. It may be preferable, however, for a dialed network as the 901 device must be added to the network when connected to the network.
View full article
Picard Product_Support
‎2018-09-06 03:22 PM

Labels:
  • TAC INET
  • TAC Vista
812 Views

901 modem is dialing multiple times before successfully registering a change on the alarm window.

Issue The 901 modem is dialing multiple times (6-8) before successfully registering a change on the alarm window. Environment 901 Modem Cause Normally it only takes one dial-up attempt to establish the communication link. If it takes 6-8 times, it indicates modem or telephone line problems. Resolution In the dial-up parameters, define the number of dial up attempts before line block. 10 is the default value.
View full article
Picard Product_Support
‎2018-09-06 03:20 PM

Labels:
  • TAC Vista
850 Views

901 dialing once for each trip/reset of the alarm

Issue Why is the 901 dialing once for each time the alarm is tripped or reset? Is there a way to request that the alarm queue be emptied with one call? Environment 901 Modem Cause This is because the dial up parameters have been configured to do this. Resolution Check the "Alarm delay" parameters where tripped/reset/ack is specified. If you don't want the TAC Xenta 901 to dial up when an alarm is reset or acked, just uncheck the options. Note that the options are per alarm priority.
View full article
Picard Product_Support
‎2018-09-06 03:20 PM

Labels:
  • TAC Vista
970 Views

How do you get the system information of a Xenta Server from a web browser?

Issue How do you get the system information of a Xenta Server from a web browser? Environment Xenta Server Xenta 511, 527, 701, 711, 721, 731, 913 Cause View the most up to date system information for the firmware version loaded into a Xenta Server. Resolution Getting system information using a web browser: Menu Utilities-System Information Displays all system information such as software versions etc. Use cut/paste to save information. Menu Utilities-Error-Error-System Error Log Displays system information and all error messages in the system error log. Use cut/paste to save information.
View full article
Picard Product_Support
‎2018-09-06 03:17 PM

Labels:
  • TAC INET
  • TAC Vista
1635 Views

On a Xenta 301 controller, what is the 0-10v output impedance?

Issue On a Xenta 301 controller, what is the 0-10v output impedance? Environment Xenta 301 programmable controller Cause Electric characteristics of the controller can be used to determine if field devices are compatible. Resolution The 0-10v output impedance is approximately 50 ohm, and in the datasheet it supplies maximum 2 mA.
View full article
Picard Product_Support
‎2018-09-06 03:17 PM

Labels:
  • TAC Vista
1118 Views

Formatting the file system to remove all files and information on a Xenta 5xx, 7xx, or Xenta 9xx

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue A system Format of the file system will remove all files to return device to a factory condition. Product Line TAC Vista Environment TAC Xenta 5xx TAC Xenta 7xx TAC Xenta 9xx Xenta Server Cause A need to reset to factory defaults exists Resolution These actions clears the filesystem and remove all files and information in it. Make sure you have IP and any other information you need to save from the file system. All files and configurations will be lost. Access Xenta using a serial interface via the RS232 port and a HyperTerminal program. obtain a connection to the dsh> prompt Type format. Wait for formatting to be ready , then enter command setip to enter DHCP enable ,ip-address , subnet mask , default gateway , DNS , local name. Default user/password will then be root/root. Remember to change password. Restart system to accept new ip-address. Install Xenta using the install kit. Use ftp transfer and alternative A (We have just formatted the system). Download WebTool project and user defined files. Update bindings using LonMaker.
View full article
Picard Product_Support
‎2018-09-06 03:17 PM

Labels:
  • TAC Vista
3026 Views

How many LonWorks Units can one Vista system have?

Issue How many LonWorks Units can you have on Vista system? Environment TAC Vista LNS network LON devices Cause Understanding the LON device maximum limit prior to designing a new system can avoid problems later on. Resolution The official limit is 1000 LWUs on a TAC Vista system. But there are several plants that are using many more. It depends on the amount of communication there is between TAC Vista and the LWUs TAC Vista can support 3200 (50*64) LWUs on each LonWorks network. A TAC Vista system can contain 65535 objects (sum of Logical and Physical).
View full article
Picard Product_Support
‎2018-09-06 03:17 PM

Labels:
  • TAC Vista
1171 Views

TAC Xenta 901/401/30x won't dial up to TAC Vista system

Issue TAC Xenta 901/401/30x won't dial up to TAC Vista system Environment Xenta 901, 401, 30x Cause Incorrectly formatted parameters. Resolution Check that the correct phone number is downloaded to the TAC Xenta. Define network object and click on modem params.
View full article
Picard Product_Support
‎2018-09-06 03:17 PM

Labels:
  • TAC Vista
1097 Views

Download a new .ndb file to a TAC Xenta Unit in TAC Vista 3

Issue Download a new .ndb file to a TAC Xenta Unit in TAC Vista 3 Environment Vista 3 Cause Updating the network database structure for a Xenta unit. Resolution Browse the new .ndb file in Vista (in the $ndb object select file). Open the status dialogue Right click on the desired level (network, TAC Xenta group or TAC Xenta) Select download application and parameters.
View full article
Picard Product_Support
‎2018-09-06 03:16 PM

Labels:
  • TAC Vista
1135 Views

How many trendlogs can the Xenta 511 handle? How many log values can be stored?

Issue How many trendlogs can the Xenta 511 handle? How many log values can be stored? Environment Xenta 511 Cause Knowing limitations on the maximum number of trends and trend data helps engineer the system properly. Resolution 150 trendlogs are supported. Total 100,000 values are possible to store.
View full article
Picard Product_Support
‎2018-09-06 03:16 PM

Labels:
  • TAC Vista
904 Views
  • « Previous
    • 1
    • …
    • 53
    • 54
    • 55
    • …
    • 103
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of