Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2045 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 52
    • 53
    • 54
    • …
    • 103
  • Next »
Label: "TAC Vista" Show all articles

Communication failures of multiple LNS databases due to duplicate Domain IDs

Issue Multiple LNS databases under i.Lons or Loytec L-IPs which use the same ethernet network and the same domain ID can cause communication failures. Routers stop communicating in random order until some user intervention is taken. Environment LNS LonMaker, NL220 Cause It seems that packets intended for the Operator Unit/Host PC (or from it to other routers) will be received by the other routers and passed down to their Lon networks. This may cause unexpected or duplicated messages to be generated and put back on the ethernet to be received by who knows which device. Resolution Configure all of the networks under multiple i.Lons or L-IPs as a single LNS database If that is not an option, ensure that each LNS network has a unique domain ID.
View full article
Picard Product_Support
‎2018-09-06 03:29 PM

Labels:
  • TAC Vista
1114 Views

Using Full Screen mode in Vista Workstation

Issue In Vista Workstation 4.20 or 4.21, when using full screen mode (F11), if all windows are closed, a gray screen is displayed. Environment Vista Workstation 4.2.0 or 4.2.1 Cause Closing all windows results in an empty display, but it is still taking up the whole screen. Resolution The only way to exit full screen mode is to use the ESC key.
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Labels:
  • TAC Vista
951 Views

Creating custom Multi-state Text definitions

Issue Creating custom Multi-state Text definitions Environment Vista 4.2x Workstation Cause "Value-Multi-state" objects in Vista have a property called Multi-state Text which provides the definitions to enumerated signals. This is similar to the paired text in a "Value-Binary" signal. However you cannot add a new entry in the Vista 4.2x workstation. Resolution To add a new entry to the drop down list: Navigate to C:\Program Files\TAC\TAC Vista\ Find the old workstation program tamain.exe Use the object selection dialog to select the Object Type filter of "Multi-state Definition" Add a new definition by following the naming convention of the existing definitions. Once you have added the definition, edit the object and enter the text values in the “MSTXTS” field separated by comma in the order that match the enumerated signal. Example: OFF, ON SECR, UNLK, LOCK
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Labels:
  • TAC Vista
1448 Views

Modifying protection status of Vista 4.2x database objects

Issue Modifying protection status of Vista 4.2x database objects Environment Vista Workstation 4.2.X Cause Vista allows you to enable protection of database objects which restricts your ability to change the object or delete it. Protected database objects are displayed with grey text and unprotected objects are displayed in black text. While the majority of protected objects are those created by the system there are times when a user has elected to make an object protected. Resolution The method used to enable protection is: Right click on the object and selecting "Authority" Inside the "Authority" dialog box is a check box labeled "Protected database object" Check this box and select OK. You will see no change in the Vista Workstation. To make the change go into effect, refresh the display by pressing F5 or right clicking and selecting "Refresh"
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Labels:
  • TAC Vista
1200 Views

Serial Communication with Xenta Units (511, 527, 911, 913):

Issue Serial Communication with Xenta Units (511, 527, 911, 913): Environment Xenta Servers Xenta 511, 527, 701, 711, 721, 731, 913 Cause Incorrect cables can cause improper ground references between the PC and the Xenta unit, which will disable serial communication. Resolution The Xenta units that utilize a web interface all have a certain amount of setup that is done with a direct serial connection via HyperTerminal. This communication however can be problematic at times due to grounding between the Xenta unit and the computer. If both devices do not share a common earth ground reference, then communication will not occur at all. There will be no indication that either side is receiving the transmissions from other device. This is most commonly encountered when using the incorrect cable since the proper cable provides a conductor for ground and thus a common ground reference. An OP panel cable is not the proper cable to use in such a situation. Instead you should be using the cables found in the TAC Xenta programming Serial Kit. If you are using a cable made by someone other then TAC the most likely cause is your cable having the improper or insufficient connections. When stuck in a situation where the proper cable is not available and working with a laptop computer we recommend that you plug the computer’s power supply in preferably to the same power supply as the controller to try to establish the common earth ground. Any other attempts to stabilize the differing grounds will be at your own risk.
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Labels:
  • TAC Vista
1976 Views

LonMaker 3.1 "Re-synch CPs" corrupts template configuration parameters and some Xenta 100s

Issue LonMaker 3.1 re-synch CPs causes the template configuration parameter settings & some Xenta 100s to be corrupted. Controllers subsequently modified by LonMaker can also be corrupted. Environment LonMaker 3.1 Xenta 100 series controllers, Revision 1.2X Cause LonMaker 3.1 handles this operation differently than 3.0. At one point we recommended that you avoid "Reset device to default values" and "Set device template defaults from device" commands, but "Upload values from device" was ok. We've since learned that any resynch CPs command can cause problems. Resolution Until this is changed in a future revision, don't do ANY resynch CPs command. (This does not refer to resynching the Lonmaker drawing and the database. Those operations work correctly and are necessary to construct your LNS network.)
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Labels:
  • TAC Vista
1092 Views

"Completion event failure" or "Waiting for device to restart" when downloading a commissioned Xenta controller

Issue "Completion event failure" and/or "Waiting for unit to restart" errors are received when attempting to download a controller which has already been commissioned and contains an existing Menta application. Product Line TAC Vista Environment LNS Network Xenta Programmable controllers Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B System Plug-in Cause The controller is busy responding to all other requests for communication and is not able to focus solely on the download. Resolution Before downloading, right-click on the controller and select Manage Set the node status to offline Download the controller Set the node status back to online. Alternatively, Before downloading, de-commission the unit. Select “Preserve neuron ID" to allow the plug-in to communicate with the controller and to avoid having to re-enter the ID or service pin. Download the controller Re-commission the device. This will prevent the controller from performing other communication while trying to receive the download and thus being unable to keep up.
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Labels:
  • TAC Vista
2320 Views

Find all defined Holiday charts using the TAC Vista 4.20 editor

Issue Problems finding all defined Holiday charts using the TAC Vista 4.20 editor Environment TAC Vista 4.2 Time Schedules Holiday Charts Cause Find all holiday charts to review scheduled holidays for the year. Resolution There is a feature in the time schedule editor that shows all schedules in a table format instead of a the calendar format. Press CTRL + SHIFT + D keys while the editor is open you will be able to edit all time schedules in one table.
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Labels:
  • TAC Vista
1169 Views

Intermittent "Completion Event Failure"

Issue Intermittent "Completion Event Failure" Xenta controllers go offline and come back online randomly Environment Vista Workstation LNS Database LonMaker / NL220 Cause Completion event failure can occur for many reasons: not using Lon cable terminators, too much network traffic, "acknowledged" type SNVT bindings to a node, etc. Resolution "One to many" bindings set as acknowledged can cause data storms, download failures, completion event failures, X'ed values in graphics, and communication problems because controllers are busy re-sending information. The reason the controllers might be resending is because they did not get a response from one of the recipients or did not get a response in time. It then resends the packet to all of the recipients, not just the unresponsive node, and waits for acknowledgments from all of them. If one of them is offline, there will be a lot of unnecessary network traffic being generated. When "one to many" bindings are required it is almost always preferable to select unacknowledged or repeated as the binding type. Note that the default binding type for programmable controllers is acknowledged. If you still have problems with completion event failures after making sure that the network is correct, you can change the number of retries in the Network object. In TAC Vista Workstation, right click on the Lonworks Network object, go to Properties, select the Timer tab, under Networks timer change the retry from 2 (default) to 4. If using LonMaker, right click on the LNS Network Interface, go to Properties, select the time tab, set the Non Group Receive Timer to the recommended 6144ms. If NL220 is being used, double click the LNS Network Interface, go to the Network tab, change the Non Group Timer to the recommended selection 11 - 6.144s.
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Labels:
  • TAC Vista
1902 Views

Problems can occur if LonMaker is not installed in the default directory

Issue There have been some reports of problems encountered when LonMaker is installed in locations other then the default directory. These problems can include failure of LonMaker .dll files to register as well as plug-in registration failure. Environment Echelon LonMaker Cause LonMaker is not installed in default directory. Typically this refers to the C:\ drive, but it doesn't necessarily have to. Resolution Restrict the LonMaker installation to the default directory and the default LonWorks folder. Example: C:\LonWorks
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Labels:
  • TAC Vista
1237 Views

Does Configuration Server for an i.Lon 1000 have to be running all of the time?

Issue Does Configuration Server for an i.Lon 1000 have to be running all of the time? Environment i.LON 1000 Cause The Config Server provides the path for communication to the iLon when used as an RNI. Resolution If using the i.Lon 1000 as an RNI to communicate with the LonWorks network, then the Config Server must be open.   If the i.Lon 1000 is being used as a router (not RNI), it is not necessary to have Config Server running unless you are in the configuration process for the router.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
1114 Views

Dial Network and LNS Network in the same Vista Network

Issue Is it possible to have a Dial Network and LNS Network in the same Vista Network? Environment Vista Network Dial Network LNS Network Cause  A dial up network communicates via the PC comport directly (no LTA driver), therefore there is no conflict with LTA card drivers (like the conflict that occurs between Classic and LNS networks). Resolution There is no problem having both types of communication in a single Vista network.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
1296 Views

When will the connection in a Dial network disconnect?

Issue When will the connection in a Dial network disconnect? Environment Xenta 901 Cause The 901 connection will continue as long as live values are being viewed. Resolution If the Status window is open (for example), the connection will continue until that window (and any other window viewing live data) is closed.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
855 Views

Using the Xenta 511, will value pages only show temperatures in Celsius? How do you get them to display in Fahrenheit?

Issue Using the Xenta 511, will value pages only show temperatures in Celsius? How do you get them to display in Fahrenheit? Environment XBuilder Cause Regional settings can be project wide or per point. Resolution When creating a new TAC Xenta 511 project, select to use US values. You can also select conversions to occur per object.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
912 Views

Is it not possible to have multiple Xenta 901s from multiple sites in a single LNS network

Issue Is it possible to have multiple Xenta 901 controllers from multiple sites in a single LNS network and access the remote sites as needed? This would leave any controllers not connected offline. Environment TAC Xenta 901 LNS Network Cause TAC Xenta 901 is an "LTA" and in TAC Vista there can only be one per LonWorks network. Resolution Create one LNS database per TAC Xenta 901. You can have up to 240 TAC Xenta 901 networks per TAC Vista Server (all can dial up the same TAC Vista Modem(s)). Add another TAC Vista Server if you need more dial up connections.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
958 Views

Xenta controller Universal Inputs

Issue What does it mean when a TAC controller is said to have a Universal Input? Environment Xenta Programmable Controllers Xenta I/O modules Cause Universal typically means all types; however, this definition does not apply to TAC Xenta controllers. Resolution With respect to TAC Xenta controllers, the term "Universal" means more than one type of input. It is important that the project planner review the data sheet to determine the exact definition for "Universal" as it applies to any TAC Xenta device.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
2190 Views

What network troubleshooting tools are available for use with Lon systems.

Issue What network troubleshooting tools are available for use with Lon systems. Environment Vista LON systems Cause Option in tools to monitor error tracking in packets. Resolution We recommend the LoyTec network data analyzer as a very important tool. It is available from Engenuity.com. It is a very user friendly tool that is windows based.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
908 Views

Version control issues with Echelon LonMaker

Issue Version control issues with Echelon LonMaker Environment LonMaker Cause When a LonMaker database is opened by a PC using a version of LonMaker that is more current that the version used to create the database, the database will be automatically updated. The previous version of LonMaker can no longer be used to open the database. Resolution Control the version of LonMaker being used by all of your personnel. Keep all PCs on a project at the same revision to avoid problems and loss of efficiency.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
943 Views

File management for Menta applications

Issue Are there any special concerns I should have with respect to making changes in Menta applications on my installations? Environment Menta programming Vista database Cause After a Menta application is downloaded to a controller, the file is imported into the Vista database. The file also typically remains on the technicians laptop. If the technician makes a change and downloads a new load to the controller but does not update Vista problems will occur. Resolution It is good practice to let Vista be the file cabinet. When a change is required, export the application from Vista, make the changes, download to the controller and then re-import to Vista. This will keep your field environment in concert with the operator interface.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1085 Views

How does a Menta application execute?

Issue How does a Menta application execute? Environment Menta Cause Menta applications use parallel computing. All updates are simultaneous. There is no order by object name or number. Location of objects on the page has nothing to do with execution. Resolution Menta applications update all objects simultaneously. On the first program cycle, the outputs of all objects are updated based on initial values within all of the blocks. On the next sweep, all inputs are updates from external values or outputs from upstream objects. All outputs are then updated from the new inputs. This process then continues.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Labels:
  • TAC Vista
1376 Views
  • « Previous
    • 1
    • …
    • 52
    • 53
    • 54
    • …
    • 103
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now