Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 16
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 504
    • 505
    • 506
    • 507
    • 508
  • Next »

Updated a Sigma system to 4.05 SEB and the graphics have changed

Issue Graphics updated to Sigma 4.05 SEB contain objects and text that has offset from its original position Environment Sigma 4.05 SEB Sigma 3 Cause Sigma 4.05 SEB introduces and fixes previous graphic bugs that now results in some graphic elements being offset when displayed. Resolution A hot fix is available from Product Support London. 1.  If upgrading from Sigma v3 then zip up and send the C:\Sigma\data\Sgi location to Product Support 2. if upgrading from Sigma 4 or 4.05 then zip up and send the C:\Sigma\data\graphics location to Product Support
View full article
Picard Product_Support
‎2018-09-11 08:42 AM

on ‎2018-09-11 08:42 AM

Labels:
  • Satchwell BAS & Sigma
1462 Views

The Lonworks Trunk Connector Plug (Orange) for ENC's and UNC's, can they be purchased separately?

Issue The Lonworks Trunk Connector Plug (Orange) for ENC's and UNC's, can they be purchased separately? Environment UNC-410 UNC-520 ENC-410 ENC-520 Cause Part Number description Resolution LON connector ( p/n E24-1555-2) is available though the iPortal. For other Standard Replacement Parts see the Installation Instruction sheet of the UNC or ENC model.
View full article
Picard Product_Support
‎2018-09-10 02:41 AM

on ‎2018-09-10 02:41 AM

Labels:
  • TAC IA Series
1168 Views

Replacement of Satchwell Sunvic control devices.

Issue Replacement of Satchwell Sunvic control devices. Environment On / Off temperature control applications  Domestic installations. Cause Satchwell Sunvic control device requires replacement.. Resolution Satchwell Sunvic Ltd. was a sister company of Satchwell Control Systems Ltd. Satchwell Sunvic Ltd. primarily manufactured domestic Thermostats and Central Heating Programmers etc. Satchwell Sunvic Ltd. was sold to another group of companies and left the Satchwell Group of Companies. At that time all Satchwell Sunvic Ltd. ON/OFF control devices were transferred to that group of companies.   There are currently no equivalent products in the Schneider Electric / TAC / Satchwell range of products. Satchwell Sunvic Ltd. now trade as Sunvic Controls Ltd. and may be contacted as follows :- Sunvic Controls Ltd. General Enquiries :- T: +44 (0) 1698 812 944 F: +44 (0) 1698 813 637 Email. enquiries@sunvic.co.uk Technical Helpline :- T: +44 (0) 1698 810 945 Email.  technical@sunvic.co.uk
View full article
Picard Product_Support
‎2018-09-10 12:10 AM

on ‎2018-09-10 12:10 AM

Labels:
  • Field Devices
1731 Views

Satchwell RM3601 mains voltage Light Duty Actuator split phase capacitor motor rating is 24 volts.

Issue Satchwell RM3601 mains voltage Light Duty Actuator split phase capacitor motor rating is 24 volts. Environment Satchwell RM3601 mains voltage Light Duty Actuator mounted on Satchwell MB Rotary Shoe Valve Body.. Satchwell RM 3601 mains voltage Light Duty Actuator mounted on Satchwell MB Rotary Shoe Valve Body.. Cause Satchwell RM3601 mains voltage and XRM3201 24 volt Light Duty Actuator both utilise a 24 volt rated split phase capacitor motor. A dropper resistor installed across the RM3601 input terminals during manufacture is designed to enable this Light Duty Actuator to be utilised in mains voltage applications. Resolution The presence of a 24 volt split phase capacitor motor within a RM3601 mains voltage Light Duty Actuator should not lead an installer to believe that the Actuator has been manufactured incorrectly.. A dropper resistor installed across the RM3601 input terminals during manufacture is designed to enable this Light Duty Actuator to be utilised in mains voltage applications.   Please check the latest catalog for current equipment.  
View full article
Picard Product_Support
‎2018-09-09 08:57 PM

on ‎2018-09-09 08:57 PM

Labels:
  • Field Devices
2109 Views

Satchwell MBF 3-port Rotary Shoe Valve Body Open / Close status determination from Spindle position.

Issue Satchwell MBF 3-port Rotary Shoe Valve Body Open / Close status determination from Spindle position. Environment Satchwell MBF 3-port Rotary Shoe Valve Body installations. Cause Satchwell MBF 3-port Rotary Shoe Valve Body is installed in pipework and Open / Close status cannot be determined by observing Valve Body Shoe positions. Resolution The Satchwell MBF 3-port Rotary Shoe Valve Body Spindle protrudes through the side of the Valve Body. The position of the Valve Body Shoes may be determined by observing the position of a hole drilled through the Valve Body Spindle. If the hole is ( l ) then Valve Body is fully open to Port 2 If the hole is ( -- ) then Valve Body is fully open to Port 3 If the hole is ( / ) then Valve Body is half open to Port 2 and half open to Port 3   When the hole through the Valve Body Spindle is VERTICAL having turned the Valve Body Spindle fully Anticlockwise, then the Valve Body is fully open to flow and fully closed to bypass. When the hole through the Valve Body Spindle is HORIZONTAL having turned the Valve Body Spindle fully Clockwise, then the Valve Body is fully closed to flow and fully open to bypass. When the hole through the Valve Body Spindle is at an ANGLE of say 45 degrees, then the Valve Body is half open to flow and half open to bypass.   Please check the latest catalog for current equipment.  
View full article
Picard Product_Support
‎2018-09-09 08:56 PM

on ‎2018-09-09 08:56 PM

Labels:
  • Field Devices
1632 Views

Satchwell MBX 3-port Rotary Shoe Valve Body Open / Close status determination from Spindle position.

Issue Satchwell MBX 3-port Rotary Shoe Valve Body Open / Close status determination from Spindle position. Environment Satchwell MBX 3-port Rotary Shoe Valve Body installations. Cause Satchwell MBX 3-port Rotary Shoe Valve Body is installed in pipework and Open / Close status cannot be determined by observing Valve Body Shoe positions. Resolution The Satchwell MBX 3-port Rotary Shoe Valve Body Spindle protrudes through the side of the Valve Body. The position of the Valve Body Shoes may be determined by observing the angle of the Slot in the end of the Valve Body Spindle. If the slot is ( \ )  then Valve Body is fully open to Port 2 If the slot is ( / )  then Valve Body is fully open to Port 3 If the slot is ( | )  then Valve Body is half open to Port 2 and half open to Port 3 With the Spindle Slot in the 10 o'clock position the Valve Body is fully open to flow and fully closed to bypass. With the Spindle Slot in the 2 o'clock position the Valve Body is fully open to bypass and fully closed to flow.   With the Spindle Slot in the Vertical position the Valve Body is half open to flow and half open to bypass.   Please check the latest catalog for current equipment.
View full article
Picard Product_Support
‎2018-09-09 08:55 PM

on ‎2018-09-09 08:55 PM

Labels:
  • Field Devices
2039 Views

Satchwell MB 3-port Rotary Shoe Valve Body Open / Close status determination from Spindle position.

Issue Satchwell MB 3-port Rotary Shoe Valve Body Open / Close status determination from Spindle position. Environment Satchwell MB 3-port Rotary Shoe Valve Body installations. Cause Satchwell MB 3-port Rotary Shoe Valve Body is installed in pipework and Open / Close status cannot be determined by observing Valve Body Shoe positions. Resolution The Satchwell MB 3-port Rotary Shoe Valve Body Spindle protrudes through the side of the Valve Body. The position of the Valve Body Shoes may be determined by observing the angle of the Slot in the end of the Valve Body Spindle. If the slot is ( \ )  then Valve Body is fully open to Port 2 If the slot is ( / )  then Valve Body is fully open to Port 3 If the slot is ( l )  then Valve Body is half open to Port 2 and half open to Port 3          With the Spindle Slot in the 10 o'clock position the Valve Body is fully open to flow and fully closed to bypass.        With the Spindle Slot in the 2 o'clock position the Valve Body is fully open to bypass and fully closed to flow.        With the Spindle Slot in the Vertical position the Valve Body is half open to flow and half open to bypass.   Please check the latest catalog for current equipment.  
View full article
Picard Product_Support
‎2018-09-09 08:55 PM

on ‎2018-09-09 08:55 PM

Labels:
  • Field Devices
1391 Views

Satchwell RM series Rotary Actuator does not open or close Satchwell MB series Rotary Shoe Valve Body due to incorrect wiring connections.

Issue Satchwell RM series Rotary Actuator does not open or close Satchwell MB series Rotary Shoe Valve Body due to incorrect wiring connections. Environment Satchwell RM series Rotary Actuator installed on Satchwell MB series 3-port Rotary Shoe Valve Body. Cause Satchwell RM series Rotary Actuator incorrect wiring connections. Resolution 1.  Check Satchwell RM series Actuator wiring connections. Wiring connections should comply with the following :- Actuator Terminal 1 = Live to OPEN Actuator Terminal 2 = Live to CLOSE Actuator Terminal 3 = Neutral N.B. The Satchwell RM series Actuator must be connected to a controlling switching device such as a Thermostat, Switch, Relay or Programmer providing CHANGEOVER CONTACT switched outputs rated at mains voltage.  2.  Ensure no other electrical device is connected between controlling switching device and Satchwell RM series Actuator. N.B. In such circumstances back feeds can cause the Satchwell RM series Actuator to stall which in turn may result in the electric motor within the Actuator burning out. 3.  Rewire Satchwell RM series Actuator as necessary and observe direction of operation is relative to control signal applied. 4.  Transfer Switches installed within the Satchwell RM series Actuator enable a Pump or Boiler etc. to be switched via the Actuator. Terminal 1 signal transfers to Terminal 1T when Satchwell RM series Actuator is fully OPEN Terminal 2 signal transfers to Terminal 2T when Satchwell RM series Actuator is fully CLOSED    Please check the latest catalog for current equipment.  
View full article
Picard Product_Support
‎2018-09-09 08:53 PM

on ‎2018-09-09 08:53 PM

Labels:
  • Field Devices
1335 Views

Using the TAC I/A BACnet WorkPlace Balance Tool to balance a VAV, when requesting the box drive to Maximum flow, get error "Controller was temporarily busy. Please rest...

Issue Using the TAC I/A BACnet WorkPlace Balance Tool to balance a VAV, when requesting the box drive to Maximum flow, get error "Controller was temporarily busy. Please restart this balancing step” message. What does this mean and how to solve it? Environment BACnet  WorkPlace Flow Balance Tool MNB-V1 MNB-V2 Cause Multiple tools connected to the same VAV controller.  Resolution "Controller was temporarily busy. Please restart this balancing step” message means one of two things – One tool has control of the VAV while another is attempting to connect or the VAV is in the process of completing a balancing step while another balancing function is attempted. Flow balancing should be  accomplished with a single tool connected to a VAV controller.  
View full article
Picard Product_Support
‎2018-09-06 01:36 PM

Labels:
  • TAC IA Series
1354 Views

Satchwell MB series 3-port Rotary Shoe Valve Body conversion for use as a 2-port Zone Valve.

Issue Satchwell MB series 3-port Rotary Shoe Valve Body conversion for use as a 2-port Zone Valve. Environment HVAC heating and cooling installations requiring a 2-port Zone Valve having pipework connection size in excess of 3/4" B.S.P. Cause HVAC heating or cooling installations requiring a 2-port Zone Valve Body having a connection sizes in excess of the usual 3/4" B.S.P. HVAC heating or cooling installations requiring a 2-port Valve Body to be installed in place of a 3-port Valve Body originally installed.  Resolution 1  Install plumber's plug in Port 3 of MB series 3-port Rotary Shoe Valve Body. 2. Tighten plumber's plug sufficiently to ensure PN 10 rating of Valve Body is not compromised. IMPORTANT Careful consideration should be given to the use of this conversion method with 3-port Valve Bodies of Plug and Seat construction. Here only "dish nosed" or "hollow ended" plumber's plugs should be installed in Port 3 of the Valve Body. The purpose of this is to prevent fouling of the Plug / Seat assembly within the Valve Body. N.B. In preference a Satchwell VZ 2-port Plug and Seat Valve Body should be replaced by a Satchwell MZ 3-port Plug and Seat Valve Body.
View full article
Picard Product_Support
‎2018-09-06 01:47 PM

Labels:
  • Field Devices
1241 Views

Can an existing UNC-600 serve graphics for a new UNC-520, without adding an Enterprise Server?

Issue Can an existing UNC-600 serve graphics for a new UNC-520, without adding an Enterprise Server? Environment I/A Series (Niagara) UNC-600 I/A Series (Niagara) UNC-520 Cause Application for serving graphics without adding Enterprise Server. Resolution Yes you can without adding a Enterprise Server. It is recommended that native Niagara objects in the UNC-600 be liked to data points in the UNC-520. This will optimize communication speed and database modifications if need. Remember to set-up the address book and select PEER to PEER. And to watch the resource count of the UNC-600
View full article
Picard Product_Support
‎2018-09-06 01:45 PM

Labels:
  • TAC IA Series
1316 Views

S-E Forta M700 Actuator unable to be mounted on S-E VGS211F Valve Body due to absence of S-E VGS211F Valve Body Spindle Adaptor.

Issue S-E Forta M700 Actuator unable to be mounted on S-E VGS211F Valve Body . Environment S-E Forta M700 Actuator mounted on S-E VGS211F Valve Body  Cause S-E Forta M700 Actuator unable to be mounted on S-E VGS211F Valve Body due to absence of S-E VGS211F Valve Body Spindle Adaptor. Resolution 1.  Install S-E VGS211F Valve Body Spindle Adaptor prior to installation of S-E Forta M700 Actuator. The S-E VGS211F Valve Body is supplied with a Valve Spindle Adaptor. The Adaptor is illustrated in the S-E Forta M700 Installation Instruction (OFL – 4340 – 001). It is particularly important to ensure that this Adaptor is fitted to the Valve Spindle, as its absence will prevent the M700 Actuator from being mechanically connected to the Valve Body Spindle.
View full article
Picard Product_Support
‎2018-09-06 02:37 PM

Labels:
  • Field Devices
1651 Views

USB-serial adapter recommended for use with DMS Operator interface (OPRIF) version 11.6

Issue USB-serial adapter recommended for use with DMS Operator interface (OPRIF)  version 11.6.  Environment DMS OPRIF 11.6, DMS-350A and DMS-3500 Cause Lack of serial port on PC. Resolution We recommend the IOGEAR model GU232A. (This is the same adapter we recommend for use with other devices, such as the MSC-LIM, MN-CIM and CBL-002 (DB-9S>DB-9S). NOTE: When using the converter with the MSC-LIM, launch the OPRIF from the LINKERGL.EXE in the DMS folder.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • TAC IA Series
1279 Views

DC1100 / DC1400 displays message "No Sensors Connected" or displays temperature values that are not representative of the temperatures being sensed...

Issue DC1100 / DC1400 displays message "No Sensors Connected" or displays temperature values that are not representative of the temperatures being sensed. Environment DC1100 / DC1400 Discrete Controller and associated Sensors. Cause DC1100 / DC1400 is connected to Sensors having incompatible resistance range. The resistance range of those Sensors compatible with the DC1100 differs to that of the resistance range of those Sensors compatible with the DC1400 "No Sensors Connected" message may appear in the Controller display as a result of the Sensors connected having a resistance that is out of range compared to that of the resistance range that the Controller Sensor Inputs are designed to recognise.  Resolution Check Sensor type connected to Controller. DC1100 Controller is compatible with the following Sensors :- STC 600 D Contact Temperature Sensor                               (Original Drayton Sensor = A704) STO 600 D Outside Air Temperature Sensor                          (Original Drayton Sensor = A702) STP 600 D Pipe Temperature Sensor                                     (Original Drayton Sensor = A703) STR 600 D Room Temperature Sensor                                  (Original Drayton Sensor = A701)   DC1400 Controller is compatible with the following Sensors :- STC 600 Contact Temperature Sensor                                   (Original Satchwell Sensor = DST) STO 600 Outside Air Temperature Sensor                             (Original Satchwell Sensor = DOT)    STP 660 Pipe Temperature Sensor                                        (Original Satchwell Sensor = DWT) STR 600 Room Temperature Sensor                                     (Original Satchwell Sensor = DRT)
View full article
Picard Product_Support
‎2018-09-06 02:06 PM

Labels:
  • Field Devices
1581 Views

AVUE 5304, AVUE 5354, AVUE 5305 or AVUE 5355 Light Duty Actuator does not respond to changes in control signal.

Issue AVUE 5304, AVUE 5354, AVUE 5305 or AVUE 5355 Light Duty Actuator does not respond to changes in control signal. Environment AVUE 5304 or AVUE 5354 Light Duty Actuator installed on VZX or MZX Valve Body.. AVUE 5305 or AVUE 5355 Light Duty Actuator installed on Satchwell VEU, MEU or FEU Unit Valve Body.. Cause AVUE 5304, AVUE 5354, AVUE 5305 or AVUE 5355 Light Duty Actuator may not respond to changes in control signal due to self stroking / auto stroking procedure failing to occur when originally installed, or due to manual override having been undertaken without subsequent reset procedure having been applied. Resolution 1.  Check that 0v of 0-10v dc control signal and 0v of 24v ac power supply originate from same source. 2.  Undertake Manual Override Reset. The Manual Override Reset Button is located on the underside of the AVUE Actuator. The purpose of the Manual Override Reset Button is to cause the Actuator to self reference. A reset is required only in the following circumstances. A.  If the Manual Override Access screw on the top of the Actuator has been operated when the Actuator is powered up. B.  If it is necessary to re-align the Actuator to a point of self reference during periods of system maintenance. N.B. The AVUE is designed to reset automatically on restoration of power following a power failure.  It should be noted that it will take approximately 85 seconds (AVUE 5305 and AVUE 5355) or 110 seconds (AVUE 5304 and AVUE 5354) for the self reference procedure to be completed. 
View full article
Picard Product_Support
‎2018-09-06 01:47 PM

Labels:
  • Field Devices
2305 Views

Sigma remote client software has been added to new PC and the client will not connect to the Sigma server properly.

Issue Sigma remote client software has been added to new PC and the client will not connect to the Sigma server properly.  On some occasions the connection occurs but the Sigma Client Menu options are not available. Environment Sigma remote client (up to version 4.04), Windows XP, Windows 2000. Cause Sigma Software up to version 4.04 uses the Windows Share to allow the Sigma Remote Client to connect to the Sigma server.  The Windows share is not working correctly. Resolution 1.  Upgrade to Sigma 4.05 or above as this no longer uses the Windows Share to connect remote clients to the server. 2.1  If the software can't be upgraded then enable file Sigma file sharing between the PC’s by using a common Windows username and password on all the Sigma server/client PC’s. 2.2  Check the firewall/network will allow TCP port 3614 to be passed, unblock if necessary. 2.3 If the PC’s are on a client network then you may have to discuss this with the sites IT people to allow TCP port 3614 to pass through their routers/firewalls. 2.4 If the Sigma communications needs to pass through a firewall then port UPD 49152 will need to be unblocked.
View full article
Picard Product_Support
‎2018-09-06 02:42 PM

Labels:
  • Satchwell BAS & Sigma
1611 Views

S-E VZ29, VZ39 and VZ49 Unit Control Valve Open / Close status required relative to spindle position.

Issue S-E VZ29, VZ39 and VZ49 Unit Control Valve Open / Close status required relative to spindle position. Environment S-E VZ29, VZ39 and VZ49 Unit Control Valve installations. Cause Open / Close status of S-E VZ29, VZ39 and VZ49 Unit Control Valve is not visually apparent Resolution Observe S-E VZ29, VZ39 and VZ49 Unit Control Valve spindle position. S-E VZ29, VZ39 and VZ49  =  Spindle DOWN OPEN / Spindle UP CLOSE   Please check the latest catalog for current equipment.
View full article
Picard Product_Support
‎2018-09-08 12:03 AM

on ‎2018-09-08 12:03 AM

Labels:
  • Field Devices
1161 Views

Importance of correct selection / installation of Satchwell 3-port Valve Body to provide Mixing function or Diverting function.

Issue Importance of correct selection / installation of Satchwell 3-port Valve Body to provide Mixing function or Diverting function. Environment Satchwell 3-port Valve Body to provide Mixing function or Diverting function in heating or cooling circuit.   Satchwell MB, MBF, MJF, MZ, MZF, MZX Cause Incorrect selection / installation  of Satchwell 3-port Valve Body to provide Mixing function or Diverting function may result in poor control, damage to the Valve Body, damage to the Valve Actuator or damage to the hydraulic installation. Resolution Determine which of the following types of hydraulic circuit the Satchwell 3-port Valve Body is to be installed in. Constant Temperature Variable Volume (CT) circuit e.g. AHU Heating / Cooling Coil or Calorifier Coil  Variable Temperature Constant Volume (VT) circuit e.g. Radiator System For Constant Temperature circuit application install Satchwell 3-port Valve Body as follows :- MJF, MZ, MZF, MZX install in RETURN pipework. Port 3 - Connect to Bypass (IN) Port 2 - Connect to Coil Return (IN) Port 1 - Connect to System Return (OUT) MB, MBF install in RETURN pipework. Port 3 - Connect to Bypass (IN) Port 2 - Connect to Coil Return (IN) Port 1 - Connect to System Return (OUT) OR MB, MBF may alternatively be installed in FLOW pipework Port 3 - Connect to Bypass (OUT) Port 2 - Connect to Coil Flow (OUT) Port 1 - Connect to System Flow (IN) For Variable Temperature circuit application install Satchwell 3-port Valve Body as follows :- MJF, MZ, MZF, MZX install in FLOW pipework. Port 3 - Connect to Bypass (IN) Port 2 - Connect to Boiler Flow (IN) Port 1 - Connect to System Flow (OUT) MB, MBF install in FLOW pipework. Port 3 - Connect to Bypass (IN) Port 2 - Connect to Boiler Flow (IN) Port 1 - Connect to System Flow (OUT) OR MB, MBF may alternatively be installed in RETURN pipework Port 3 - Connect to Bypass (IN) Port 2 - Connect to System Return (IN) Port 1 - Connect to Boiler Return (OUT) N.B. It should be noted that the alternative installation methods are valid for the MB and MBF Valve Bodies due to the ROTARY SHOE construction of the MB and MBF Similarly it should be noted that the alternative installation methods are not valid for the MJF, MZ, MZF and MZX Valve Bodies due to the PLUG AND SEAT construction of the MJF, MZ, MZF and MZX . Failure to install MJF, MZ, MZF and MZX Valve Bodies correctly in the pipework may result in VALVE VIBRATION in the pipework caused by WATER HAMMER    INSTALLATION OPTIONS - MJF, MZ, MZF and MZX 3-PORT PLUG AND SEAT VALVES MAY BE INSTALLED TO MIX IN THE FLOW VALVE BODIES USE TWO “IN” PORTS (Ports 2 & 3) AND ONE “OUT” PORT(Port 1)   3-PORT PLUG AND SEAT VALVES MAY BE INSTALLED TO DIVERT (BY MIXING) IN THE RETURN VALVE BODIES USE TWO “IN” PORTS (Ports 2 & 3) AND ONE “OUT” PORT(Port 1)   INSTALLATION OPTIONS - MB, MBF  3-PORT ROTARY SHOE VALVES MAY BE INSTALLED TO MIX IN THE FLOW USING TWO “IN” PORTS (Ports 2 & 3) AND ONE “OUT” PORT (Port 1) 3-PORT ROTARY SHOE VALVES MAY BE INSTALLED TO MIX IN THE RETURN.USING ONE “IN” PORT (Port 1) AND TWO “OUT” PORTS (Ports 2 & 3)) 3-PORT ROTARY SHOE VALVES MAY BE INSTALLED TO DIVERT IN THE RETURN USING TWO “IN” PORTS (Port 2 & 3) AND ONE “OUT” PORT (Port 1) 3-PORT ROTARY SHOE VALVES MAY BE INSTALLED TO DIVERT IN THE FLOW USING ONE “IN” PORT (Port 1) AND TWO “OUT” PORTS (Port 2 & 3)   RELATED INFORMATION - DIVERTING IN THE FLOW It should be noted that some manufacturers produce 3-Port Plug and Seat Valve Bodies specifically designed to DIVERT in the FLOW.  Such Valve Bodies have 1 IN Port and 2 OUT Ports   Please check the latest catalog for current equipment.  
View full article
Picard Product_Support
‎2018-09-07 11:14 PM

on ‎2018-09-07 11:14 PM

Labels:
  • Field Devices
2274 Views

Replacement of Satchwell ALM series Linear Actuator by S-E MV15B-230 Linear Actuator due to obsolescence. (Actuator Wiring)

Issue Satchwell ALM series Linear Actuator requires replacement. Environment Satchwell ALM series Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF Series Plug and Seat Valve Body.    Satchwell ALM series Linear Actuators. Cause Obsolescence of Satchwell ALM series Linear Actuator. Resolution Replace Satchwell ALM series Linear Actuator with MV15B-230 Linear Actuator and Linkage Kit and wire as follows :- ALM = MV15B-230 + L7SV (880-0126-000) Linkage Kit. Actuator wiring :- ALM Terminal Number 1  =  MV15B-230 Terminal Number Y2  ALM Terminal Number 2  =  MV15B-230 Terminal Number Y1  ALM Terminal Number 3  =  MV15B-230 Terminal Number N N.B. ALM power consumption  =  4.5 VA          MV15B-230 power consumption  =  12 VA operating and 15 VA Transformer sizing Should the Satchwell ALM series Actuator include a wired Auxiliary Switch (ALA1211) then the following Accessory should also be installed on the MV15B-230 Actuator as appropriate and should be wired as follows :- S2 - MV15B = Two independent 250 volt 10 amp / 3 amp rated SPDT Auxiliary End Point Switches. Auxiliary Switch wiring :- ALA1211 Terminal S1  =  S2 - MV15B Switch 1 Terminal C ALA1211 Terminal S2  =  S2 - MV15B Switch 1 Terminal B ALA1211 Terminal S3  =  S2 - MV15B Switch 1 Terminal A ALA1211 Terminal S4  =  S2 - MV15B Switch 2 Terminal C ALA1211 Terminal S5  =  S2 - MV15B Switch 2 Terminal B ALA1211 Terminal S6  =  S2 - MV15B Switch 2 Terminal A   Please check the latest catalog for current equipment.  
View full article
Picard Product_Support
‎2018-09-07 11:13 PM

on ‎2018-09-07 11:13 PM

Labels:
  • Field Devices
1719 Views

SVT Controller will not operate plant under Auto control following Clock replacement due to lack of re-commissioning.

Issue SVT Controller will not operate plant under Auto control following Clock replacement Environment SVT 4201 Optimiser Controller  SVT 4251 Optimiser Controller  Cause SVT Controller will not operate plant under Auto control following Clock replacement due to lack of re-commissioning. Resolution Re-commission SVT Controller using Test method. The absence of plant control may normally be confirmed by lack of illumination of Burner L E D (bottom left corner of SVT)  Test method of re-commissioning may be undertaken as follows: Ensure SVT 4201 Analogue Clock override button is set to AUTO condition and Clock is in an ON period. Ensure SVT 4251 Digital Clock status is set to AUTO condition and Clock is in an ON period. Ensure SVT Manual Override Switch (lower left of SVT) is set to AUTO Note SVT Preheat Selector Switch (lower centre of SVT) setting (scaled 1,2,3,4,5,T) Turn Preheat Selector Switch fully clockwise from Preheat number setting to letter T Turn Manual Override Switch fully anti-clockwise from AUTO setting to O (Off)  Turn Manual Override Switch fully clockwise from O (Off) setting to + (ON) Burner L E D should illuminate and plant should start. Turn Manual Override Switch anti-clockwise from + (ON) setting to AUTO Burner L E D should remain illuminated and plant should continue to run. If plant continues to run then proceed to action L.  If plant remains OFF then return to action A. Turn Preheat Selector Switch anti-clockwise from T position to previously noted SVT Preheat Selector Switch setting.  
View full article
Picard Product_Support
‎2018-09-07 02:16 PM

on ‎2018-09-07 02:16 PM

Labels:
  • Field Devices
1288 Views
  • « Previous
    • 1
    • …
    • 504
    • 505
    • 506
    • 507
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of