Satchwell RM3601 mains voltage Light Duty Actuator split phase capacitor motor rating is 24 volts.
  • Satchwell RM3601 mains voltage Light Duty Actuator split phase capacitor motor rating is 24 volts.
‎2018-09-09 08:57 PM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:58 AM
Satchwell RM3601 mains voltage Light Duty Actuator mounted on Satchwell MB Rotary Shoe Valve Body..
Satchwell RM 3601 mains voltage Light Duty Actuator mounted on Satchwell MB Rotary Shoe Valve Body..
Satchwell RM3601 mains voltage and XRM3201 24 volt Light Duty Actuator both utilise a 24 volt rated split phase capacitor motor.
A dropper resistor installed across the RM3601 input terminals during manufacture is designed to enable this Light Duty Actuator to be utilised in mains voltage applications.
The presence of a 24 volt split phase capacitor motor within a RM3601 mains voltage Light Duty Actuator should not lead an installer to believe that the Actuator has been manufactured incorrectly..