Importance of correct selection / installation of Satchwell 3-port Valve Body to provide Mixing function or Diverting function.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Importance of correct selection / installation of Satchwell 3-port Valve Body to provide Mixing function or Diverting functio...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2469 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Importance of correct selection / installation of Satchwell 3-port Valve Body to provide Mixing function or Diverting function.

Picard Product_Support
‎2018-09-07 11:14 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:48 AM

Issue

Importance of correct selection / installation of Satchwell 3-port Valve Body to provide Mixing function or Diverting function.

Environment

Satchwell 3-port Valve Body to provide Mixing function or Diverting function in heating or cooling circuit.

 

Satchwell MB, MBF, MJF, MZ, MZF, MZX

Cause

Incorrect selection / installation  of Satchwell 3-port Valve Body to provide Mixing function or Diverting function may result in poor control, damage to the Valve Body, damage to the Valve Actuator or damage to the hydraulic installation.

Resolution

  1. Determine which of the following types of hydraulic circuit the Satchwell 3-port Valve Body is to be installed in.
    1. Constant Temperature Variable Volume (CT) circuit e.g. AHU Heating / Cooling Coil or Calorifier Coil 
    2. Variable Temperature Constant Volume (VT) circuit e.g. Radiator System
  2. For Constant Temperature circuit application install Satchwell 3-port Valve Body as follows :-
    1. MJF, MZ, MZF, MZX install in RETURN pipework.
      Port 3 - Connect to Bypass (IN)
      Port 2 - Connect to Coil Return (IN)
      Port 1 - Connect to System Return (OUT)
    2. MB, MBF install in RETURN pipework.
      Port 3 - Connect to Bypass (IN)
      Port 2 - Connect to Coil Return (IN)
      Port 1 - Connect to System Return (OUT)
      OR
    3. MB, MBF may alternatively be installed in FLOW pipework
      Port 3 - Connect to Bypass (OUT)
      Port 2 - Connect to Coil Flow (OUT)
      Port 1 - Connect to System Flow (IN)
  3. For Variable Temperature circuit application install Satchwell 3-port Valve Body as follows :-
    1. MJF, MZ, MZF, MZX install in FLOW pipework.
      Port 3 - Connect to Bypass (IN)
      Port 2 - Connect to Boiler Flow (IN)
      Port 1 - Connect to System Flow (OUT)
    2. MB, MBF install in FLOW pipework.
      Port 3 - Connect to Bypass (IN)
      Port 2 - Connect to Boiler Flow (IN)
      Port 1 - Connect to System Flow (OUT)
      OR
    3. MB, MBF may alternatively be installed in RETURN pipework
      Port 3 - Connect to Bypass (IN)
      Port 2 - Connect to System Return (IN)
      Port 1 - Connect to Boiler Return (OUT)

N.B.

It should be noted that the alternative installation methods are valid for the MB and MBF Valve Bodies due to the ROTARY SHOE construction of the MB and MBF

Similarly it should be noted that the alternative installation methods are not valid for the MJF, MZ, MZF and MZX Valve Bodies due to the PLUG AND SEAT construction of the MJF, MZ, MZF and MZX .

Failure to install MJF, MZ, MZF and MZX Valve Bodies correctly in the pipework may result in VALVE VIBRATION in the pipework caused by WATER HAMMER 

 

INSTALLATION OPTIONS - MJF, MZ, MZF and MZX

3-PORT PLUG AND SEAT VALVES MAY BE INSTALLED TO MIX IN THE FLOW

VALVE BODIES USE TWO “IN” PORTS (Ports 2 & 3) AND ONE “OUT” PORT(Port 1)

 

3-PORT PLUG AND SEAT VALVES MAY BE INSTALLED TO DIVERT (BY MIXING) IN THE RETURN

VALVE BODIES USE TWO “IN” PORTS (Ports 2 & 3) AND ONE “OUT” PORT(Port 1)

 

INSTALLATION OPTIONS - MB, MBF 

3-PORT ROTARY SHOE VALVES MAY BE INSTALLED TO MIX IN THE FLOW USING TWO “IN” PORTS (Ports 2 & 3) AND ONE “OUT” PORT (Port 1)

3-PORT ROTARY SHOE VALVES MAY BE INSTALLED TO MIX IN THE RETURN.USING ONE “IN” PORT (Port 1) AND TWO “OUT” PORTS (Ports 2 & 3))

3-PORT ROTARY SHOE VALVES MAY BE INSTALLED TO DIVERT IN THE RETURN USING TWO “IN” PORTS (Port 2 & 3) AND ONE “OUT” PORT (Port 1)

3-PORT ROTARY SHOE VALVES MAY BE INSTALLED TO DIVERT IN THE FLOW USING ONE “IN” PORT (Port 1) AND TWO “OUT” PORTS (Port 2 & 3)

 

RELATED INFORMATION - DIVERTING IN THE FLOW

It should be noted that some manufacturers produce 3-Port Plug and Seat Valve Bodies specifically designed to DIVERT in the FLOW.  Such Valve Bodies have 1 IN Port and 2 OUT Ports

 

Please check the latest catalog for current equipment.


 

Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • 5074
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore