Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 462
    • 463
    • 464
    • …
    • 501
  • Next »

Controller TAC213

Issue TAC213 is obsolete and needs replacement Environment TAC213 0803097005 Cause Obsolete controller needs replacement Resolution TAC213 is obsolete since many years. No replacement product is available.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • Field Devices
  • TAC Vista
1049 Views

"ERROR: Non-activation-capable daemon activation invoked with non-client-request event type"

Issue The license log from the license server can occasionally display the following message: "ERROR: Non-activation-capable daemon activation invoked with non-client-request event type" Environment Vista and Flexnet Licensing Cause There is no known cause. Typically, it is logged once daily in the Debug.log file right after midnight. Resolution Acresso support has recognised this as a bug in FLEXnet. There is no implication that this error message impacts your license server usage or performance. This error is benign and not known to cause licensing problems.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1339 Views

Logs in the UNC are not archiving to the Enterprise Server

Issue Logs in the UNC are not archiving to the Enterprise Server Environment I/A Series R2 Universal Network Controller (UNC) and Enterprise Server Cause The UNC station and the Enterprise Server station have their LogService 'archiveMode' property set to 'archive_disabled'.  Resolution Change the LogService 'archiveMode' in both the UNC station and the Enterprise Server station.  1. Set the UNC station's LogService 'archiveMode' to 'archive_remote'. The 'archiveAddress' property should have 'Supervisor' checked.  2. Set the Enterprise Server station's LogService 'archiveMode' to 'archive_local'. (The “archive_local” selection is valid only if the station is running the DatabaseService) The following have to be also correct in order for log archiving to happen: AddressBook entries should be properly setup in the Enterprise Server and UNC stations. Refer to Page 1-15 and 1-16 of the Niagara Standard Programming Reference for further information.  Supervisor checkbox in the UNC's LogService 'archiveAddress' property should be checked. In the Niagara Log Object properties, the 'archiveSetup' property should have 'nearFull' or 'daily' checked. It is recommended that both of these be checked. 
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • TAC IA Series
927 Views

Not possible to log on to Enterprise Server from Workstation when regional settings are Arabic or Saudi Arabia

Issue When using a Windows 7 PC with regional settings set to Arabic or Saudi Arabia it is not possible to log on to ES from Workstation Environment StruxureWare Building Operation Workstation 1.3 Cause On a Windows 7 PC with .NET 4.0 installed if the regional settings are Arabic or Saudi Arabia a user cannot log on to the Enterprise Server from Workstation. This is not a problem with Webstation. Resolution This is only an issue with Windows 7 with .NET 4.0 which is the currently supported configuration (April 2013). The solution is to upgrade to .NET 4.5 or if required use Windows XP SP3 operating system. This has been tested on released version 1.3 and also 1.3.0 SP1 (build 1.3.0.10104-SP1).
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • EcoStruxure Building Operation
1528 Views

DC1100 / DC1400 with more than 2 boilers

Issue Can the DC1100 / DC1400 serve more than 2 boilers Environment DC1100 DC1400 Cause Can the DC1100 / DC1400 serve more than 2 boilers? Resolution The DC1100 or DC1400 is primarily designed for a 1 or 2 boiler installation. However in the case of 3 boilers. Note, 2 additional relays are required: Wire Boiler 1 to Boiler 1 terminals. Wire Boiler 2 to Boiler 2 terminals. Wire the coil of the 1st 230Vac relay to Boiler 1 terminals. Wire the coil of the 2nd 230Vac relay to Boiler 2 terminals. Either wire the relay contacts in parallel or in series, the feed for each contact will be wired from the Boiler 1 and Boiler 2 terminals respectively on the controller, the output of the relay contacts will be wired to Boiler 3. This is a workaround and does have its disadvantages: Boiler 3, when wired in parallel will always be a Lead Boiler and will do more work or when wired in series it will always be a Lag Boiler and will do the least work. In the case of 4 boilers: Wire the boilers in pairs to each boiler output on the controller. Note, the boilers will lead or lag in pairs. In the case of 5 boilers: Adapt both the solutions above.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • Field Devices
3471 Views

Aux Switch for MDx and MFx0 series actuators

Issue In some applications, auxiliary switches on the actuator are requested. Environment MD-S1 MD-S2 MD5 MD10 MD20 MD40 MF20 MF40 Cause Aux switches are not included and needs to be ordered separately if application requires them. Resolution MD-S1(1 switch) and MD-S2(2 switches) are suitable add-ons for all MD5/10/20/40 damper actuators.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • Field Devices
1348 Views

Display uptime of Automation Server

Issue How long has an Automation Server been running since the last power cycle or reboot? Environment Automation Server SmartStruxure Device Administrator Cause The uptime of an Automation Server indicates how long the server has been operational since the last power cycle or system reboot. This is not currently visible in the StruxureWare Building Operation Workstation, but it is available through the Console interface in Building Operation Device Administrator. By monitoring the uptime of the device this can be a valuable diagnostic tool to determine if power loss occurred, crashes in Automation Server occurred, or other situations that might have resulted in a reboot and what time this occurred. Resolution In the Building Operation Device Administrator connect to an Automation Server (IP or USB) and select the "Open Console" option. Once logged into the Console issue the "uptime" command in the prompt. The uptime will be listed in Days, Hours, and Minutes as visible below: admin@AS-B-RKFDMW:~> uptime  14:18:20 up 1 day,  1:01, load average: 1.26, 1.16, 1.06   If you are using Report Server, this information is also available using SQL Server Management Studio from the Report Server PC. Enter the following query and the "Runtime" column will provide the current uptime for the specified ES or AS. SELECT Top (1) CAST(CURRENT_TIMESTAMP - DateTimeStamp AS Time) AS 'Runtime' ,DateDiff(Day, DateTimeStamp, CURRENT_TIMESTAMP) AS 'Days Up' ,DateDiff(HOUR, DateTimeStamp, CURRENT_TIMESTAMP) AS 'Hours Up' ,DateDiff(MINUTE, DateTimeStamp, CURRENT_TIMESTAMP) AS 'Minutes Up' ,DateDiff(SECOND, DateTimeStamp, CURRENT_TIMESTAMP) AS 'Seconds Up' ,[DateTimeStamp] ,[TYPE] ,[OriginatedServer] ,[OriginatedDevice] ,[SystemEventId] FROM [StruxureWareReportsDB].[dbo].[tbEvents] WHERE SystemEventId = 'Server initialized' AND OriginatedServer = '/Server 1' ORDER BY DateTimeStamp Desc   NOTE: Change the WHERE statement "OriginatedServer = '/Server 1'" so that '/Server 1' become '/yourServerName'
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • EcoStruxure Building Operation
1794 Views

How can a TreeTech database be moved from one computer to another?

Issue How can a TreeTech database be moved from one computer to another? Environment TreeTech - all versions Cause New pc purchase Resolution The project backups are stored in a "Jobs" folder.  The folder location in Windows 7 is:  C:\ProgramData\Schneider Electric\TreeTech\JOBS The folder location in Windows XP is:  C:\Documents and Settings\All Users\Schneider Electric\Jobs Use any compression utility to create a .zip or .rar of this folder.  Unzip the file in the destination computer in the same folder path.
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • TAC IA Series
961 Views

SNVT is not propagated from TAC Xenta 121-FC

Issue Why is not nvoSpaceCO2 propagated in TAC Xenta 121-FC? Environment TAC Vista TAC Xenta 121-FC Cause You must have a binding for the SNVT to be propagated. Also, not all SNVT are sent by heartbeat (please note that the tooltip text in ZBuilder was corrected in version 5.1.7). Resolution Make sure that you have a binding from the actual SNVT. Make sure that the value is changed more than the actual setting for propagation.
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • TAC Vista
1303 Views

How to generate a report of personnel that have not accessed the site via the Access Control system in X days/months.

Issue Need a report of personnel that have not accessed the facilities in some specified time. Environment CyberStation Cause Documentation Resolution Create a List View of the Personnel class Add desired columns (Name, Card Number etc) In the Qualifiers tab add the following advanced qualifiers TimeEntered <= MyCyberStation\Date - xxx where MyCyberStation is the name of the workstation object and xxx is a number that represents the number of seconds going back in time. For example to generate a list view report of all personnel that have not accessed the facilities in a day enter the following qualifier TimeEntered <= MyCyberStation\Date - 86400  (86400 is the number of seconds in a day) For a qualifier for a month enter... TimeEntered <= MyCyberStation\Date - 86400 * 30
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • Andover Continuum
1159 Views

Host bindings does not show up in TAC Vista

Issue Why does not my Host bindings show up in TAC Vista? Environment TAC Vista Echelon LonMaker Cause Host Bindings in TAC Vista could only be from other devices in to TAC Vista, to be able to show values in TAC Vista. It is not possible to have Host Bindings from TAC Vista to other devices, because these points do not have any information holder in TAC Vista, it is only virtual points. Resolution Host Bindings in TAC Vista could only be from other devices in to TAC Vista, to be able to show values in TAC Vista. It is not possible to have Host Bindings from TAC Vista to other devices, because these points do not have any information holder in TAC Vista, it is only virtual points. From the manual: You should not use group bindings when binding to the host. Important To make the host SNVTs available in the Vista database, the check box Export Host Bindings to TAC Vista Database must be selected. The check box is found in Vista System Plug-In in the Settings dialog on the TAC Network menu. Note Digital and multistate SNVTs should be sent as soon as a change of state occurs and analog SNVTs should be sent as soon as they reach a defined limit. All SNVTs should be sent with a heartbeat determined by the priority of the information. For more information about how to set these parameters, see the LonWorks device documentation.  
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • TAC Vista
1132 Views

Spare stuffing box for VG321, VG311F and VG222

Issue Replacement stuffing box/stem seal Environment stuffing box 100108100 VG321 VG222 VG311F Cause When leaking by the gland, a stuffing box replacement may sometimes help. Resolution Replacement/spare stuffing box for VG321, VG311F and VG222 DN65-DN150 is part no 100108100.
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • Field Devices
1142 Views

How to Export a Trend Log List as a .csv File

Issue Need to Export a Trend log file without using Reports Server Product Line EcoStruxure Building Operation Environment SmartStruxure Workstation Cause Customer needs a log file, but does not have Report Server Resolution In Workstation, right click on a Trend and create a new Trend Log List View Once the List populates, click on the Icon showing a green arrow labeled .csv Save the file to an appropriate location. If this is a frequent action, save the Trend Log List View Please Note that this feature is not available in WebStation  At v2.0 WebStation introduced the option to export to Excel, creating an XLSX file, this can be opened in Excel and saved as a CSV if required (this option is not available if WebStation is directly logged on to the AS/P/B)
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • EcoStruxure Building Operation
4144 Views

The folder name is included in the binding even when using relative path.

Issue When doing a binding using relative path the folder name is included in the binding. When clicking on the relative path button the binding looks like it should without the folder name but it is no possible to save it like that. Environment StruxureWare version 1.3 Cause In the folder name a space was used.   Resolution When taking away the space in the name the relative bindings looked like the should, no folder name in them.
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • EcoStruxure Building Operation
947 Views

SmartStat gives faulty reading.

Issue The temperature reading randomly  fluctuates between 69.5 deg and 327 deg. Environment Controllers with SPWR / Smart  Sensor support. Cause This situation can be the result of running one 6 conductor cable for all of the wiring to the thermostat; including the 24 VAC for the LED light.  The 24 VAC is causing interference with the temperature  input . Resolution Use a different cable for the LED light 24 volt.  Use 0-5 VDC to feed the LED Light.
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • Andover Continuum
1287 Views

V241 valve size availability

Issue Which valves sizes are available for the V241 valve? Environment V241 Cause Size specifications for V241 valves. Resolution The V241 valve is available in the following sizes: DN15, DN20, DN25, DN32, DN40, DN50. Some of these are available in different Kvs values. For more information and details, please see the V241 data sheet available on the Extranet.
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • Field Devices
1077 Views

TAC200 controller replacement

Issue Obsolete heat controller Environment TAC200 TA200 2001000000 2001000009 Cause Obsolete product, no longer available for ordering Resolution The TAC200 controller was made obsolete in the end of 2011. No replacement product is available in the TAC range.  The Satchwell DC1100 and DC1400 offer similar functionality, but require Satchwell sensors.
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • Field Devices
  • TAC Vista
1051 Views

Configuring door access using keypad without access card.

Issue Is it possible to configure a door so that a card holder can gain access using only his unique pin number. Environment Continuum Access control Personnel objects unique PIN Cause Cardholders often lose their cards and need access to an area. Resolution For PIN only validation to work the Unique PIN option under Allowed Credentials must be selected. * On door object Deselect all Access Validation. Under General Access Validation, select Validate PIN. *  If Unique PIN is not selected, cardholders using a valid pin will be able to gain access through the door, but Continuum will be able to provide reliable cardholder information for access events at this door. There are security issues that make it necessary for the badging personnel to issue a predetermined and available pin number to the cardholder. 
View full article
Picard Product_Support
‎2018-09-06 10:26 AM

Labels:
  • Andover Continuum
1600 Views

SmartStruxure integration to StruxureWare Data Center Expert via EcoStruxure WebServices

Issue SmartStruxure integration to StruxureWare Data Center Expert via EcoStruxure WebServices Environment StruxureWare Building Operation EcoStruxure Web Services StruxureWare Data Center Expert 7.2.0 Cause There is a need to have StruxureWare Building Operation pass data to StruxureWare Data Center Expert using EcoStruxure Web Services. StruxureWare Building Operation Web Services is capable of both 'Serve' and 'Consume' functionality. However, StruxureWare Data Center Expert (version 7.2.0) is only capable of Web Services 'Serve' function. Resolution Use Modbus TCP instead of EcoStruxure Web Services if StruxureWare Data Center Expert is required to read from StruxureWare Building Operation. 
View full article
Picard Product_Support
‎2018-09-06 10:26 AM

Labels:
  • EcoStruxure Building Operation
2337 Views

When deleting and re-creating an I/NET point using a different point type, the changes do not update in SmartStruxure

Issue Changing an I/NET DI to a DA does not show up in StruxureWare Building Operation Workstation Environment I/NET SmartStruxure Integration Cause After integrating I/NET to SmartStruxure the designed intent is to allow all point name changes and alarming to be done in SmartStruxure workstation.  If you delete a point and re-create it using the same point address, point name but a different point type, the change will not show up in SmartStruxure. Resolution To successfully change an I/NET point from DI to DA: Delete the Point using the I/NET Resident I/O Editor Re-create the Point using the I/NET Resident I/O Editor using the new point extension DA. YOU MUST change the point name in some way. Perform a Station Save Open Building Operation Workstation Right Click on the Controller and select Update.
View full article
Picard Product_Support
‎2018-09-06 10:26 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1354 Views
  • « Previous
    • 1
    • …
    • 462
    • 463
    • 464
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore