Issue
Why is not nvoSpaceCO2 propagated in TAC Xenta 121-FC?
Environment
TAC Vista
TAC Xenta 121-FC
Cause
You must have a binding for the SNVT to be propagated.
Also, not all SNVT are sent by heartbeat (please note that the tooltip text in ZBuilder was corrected in version 5.1.7).
Resolution
Make sure that you have a binding from the actual SNVT.
Make sure that the value is changed more than the actual setting for propagation.