Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,826
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 443
    • 444
    • 445
    • …
    • 509
  • Next »

Chinese Characters cannot be shown correctly in Seven Reports

Issue Chinese Characters cannot be shown correctly in Seven Reports. Odd characters will be shown instead. Environment I/NET Seven Reports Chinese Operation System Cause The default font in Seven Reports cannot be shown correctly for Chinese characters. Resolution The default font in Seven Report is Tahoma. Change to any Chinese font, and it will work fine.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • TAC INET
1366 Views

Unable to associate TGML files with TGML editor after installing Vista.

Issue Unable to associate TGML files with TGML editor after installing Vista. After right-clicking on the TGML file and selecting "Open With" it is not possible to browse in the graphics editor's .exe file. The file can be located but it doesn't appear in the dialogue. Environment Vista 5.1.X Windows 7 Cause The TGML editor application hasn't been correctly registered. Resolution Try the following steps. Check between each step to see if it's possible to associate the TGML editor with TGML files. Reinstall Vista using "Run as administrator" In regedit: Navigate to HKEY_LOCAL_MACHINE\SOFTWARE\Wow6432Node\TAC\TAC Graphics Editor\5.1.8 ( HKEY_LOCAL_MACHINE\SOFTWARE\TAC\TAC Graphics Editor\5.1.8 on 32bit PCs) Check that the path given is correct under "ExecutablePath" Navigate to HKEY_CURRENT_USER\Software\Microsoft\Windows\CurrentVersion\Explorer\FileExts\.tgml and delete .tgml Reinstall Vista as an administrator
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • TAC Vista
1022 Views

Getting error FiringOrder error when sending data to a controller

Issue Getting error FiringOrder error when sending data to a controller "Unable to reload object Network\Controller\FiringOrder.           You do not have sufficient access to do the requested operation" Environment Continuum Cause Firing Order is a Group Object, so if Group Objects are not open to the user then they can not be sent to a controller. Resolution Firing Order is a Group Object thus when reloading a controller (send to controller) the user requires security rights for Groups.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • Andover Continuum
1033 Views

How can a deleted Pinpoint graphic be restored?

Issue How can a deleted Pinpoint graphic be restored that was mistakenly deleted. Environment Pinpoint Graphic Cause A Pinpoint graphic was mistakenly deleted. Resolution In order to restore a deleted graphic and hope to have it restored with all the points from the database attached, in addition to the PIN file and background being in the correct drive and folder, you will need either a text export (.dmp) of the graphic file (which you would import) or you would need to restore the database from before the deletion. The PIN file has all the control objects but no link to the points that were attached on a certain graphic file. The database has the links to the points in the ObjectList of the Panel table. This is how you could have just one VAV.pin file and use it for hundreds of VAV boxes in a building. If you cannot restore a backup of the database and you do not have a text export of the graphic you will need to use the PIN file and background (if applicable) and manually attach the points to the control objects in the graphic.  To do this create a New >> Graphics in the location of your choice in ContinuumExplorer. Then using the menus go to File >> Import Panel File... and navigate to the PIN file and import it. This will bring in all the control objects in the locations they were before the deletion. Then add the background to the graphic by going to File >> Configuration and the Canvas tab. You then have to attach the points to the controls.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • Andover Continuum
1043 Views

How to create personnel on a webClient user's PC

Issue On the webClient interface, it is not easy to find a way to create personnel. Environment Continuum webClient Cause No manuals describe how to create personnel via webClient user PC Resolution Log onto webClient Click "Search" on the top of the interface. From the left side of the interface click "All Objects" From the drop down list, select "Personnel" On the top of the new window, click "New Personnel", A personnel editor appears Following the same steps required for creating personnel objects in CyberStation, completing the necessary items. Click "Save " at the bottom of the editor Note: webClient does not support adding or editing photos for personnel objects. Go to CyberStation to do this.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • Andover Continuum
1027 Views

Periodic Report is not printed

Issue Periodic Report is not printed. Environment TAC Vista 5.1.7 Cause If the box "Automatically set printing area" is checked in the properties for the report, the report is not printed. If it is left unchecked, the report will print. Resolution Uncheck the box "Automatically set printing area" in the properties for the report .
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • TAC Vista
1305 Views

B4920 does not have the Send to Database option.

Issue While rebuilding a database by bringing controllers online then initiating a Send to Database we find that the B4920 controllers do not offer a send to database option. Environment B4920 Send to Database Cause Send to database option was never added to the B4920. Resolution The controller will have to be rebuilt manually.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • Andover Continuum
1310 Views

Microsmart controllers not following commands from a Niagara R2 schedule

Issue Microsmart controllers not following commands from a Niagara R2 schedule Environment Niagara R2 (all versions) Microsmart controllers (all versions) Cause Power failure in building The UNC does a 'graceful' shutdown, using its backup battery, 60 seconds after main AC power is lost.  If the power failure in the building lasts less than 60 seconds, the Microsmart controllers come back online.  The UNC never shuts down and thinks the Microsmart controllers are online.  Meanwhile the Microsmart shadow objects in the station are no longer updating.  The link between them and the points in the Microsmart was lost (during the power failure) and does not automatically recover. Resolution Reboot the UNC
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • TAC IA Series
1110 Views

Command Request / Command Response window not available in the Niagara G3 DMS driver

Issue Command Request / Command Response window not available in the Niagara G3 DMS driver Environment Niagara G3 Microsmart driver Cause Not carried over from the Niagara R2 driver Resolution Only option is to tunnel to the Microsmart controllers with OPRIF
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • TAC IA Series
1168 Views

An unknown automation error occurred while upgrading the application [-1:-1]

Issue An unknown automation error occurred while upgrading the application [-1:-1] Environment WorkPlace Tech 3.2 service pack 1 Visio 2000 Cause File corrupt File opened with a different version of Visio (than the one used with WorkPlace Tech 3.2sp1 which is Visio 2000) Resolution Use a backup file or rebuild application from scratch. Copy paste anything that can be re-used.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • TAC IA Series
1518 Views

An unknown automation error occurred while upgrading the application [-1:-1]

Issue An unknown automation error occurred while upgrading the application [-1:-1] Environment WorkPlace Tech 3.2 service pack 1 Visio 2000 Cause Corrupt file (perhaps opened/saved with a different version than Visio 2000) Resolution Use a backup copy or build a new application file from scratch (copy/paste any programming from existing file -- if possible -- to save time)
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • TAC IA Series
1356 Views

Vista - List all alarms in the system

Issue Need to generate a list of all alarms in the system. Environment Vista Cause Vista has a search function to find out what alarm objects exist in the system. Resolution To search for all the alarm object in the system: In Workstation, click on Search Go to Type of devices and objects and click on the button right of view Search for "Event"  and then "Message" mark "Alarm" and click ok All objects are now listed and can be copied and pasted to an Excel sheet.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • TAC Vista
986 Views

What product changes have been made to the SCR range of sensors?

Issue SCR sensors working with AC Voltages Environment SCR Series Sensors Cause An issue was found with AC voltages below 22.8VAC Resolution Any SCR units that have been shipped since 1 March 2012 will be fine with the full AC supply range (as per their datasheet), however we had an issue with older units that require the AC supply to be above 22.8 Volts to ensure there are no problems. DC supply voltages operate correctly on all SCR sensors. See TPA-FD-12-0002.00 and TPA-FD-12-0003.00 for full details of the issue and changes made to the sensors.
View full article
Picard Product_Support
‎2018-09-10 01:20 PM

Labels:
  • Field Devices
1377 Views

Controller configured with an XDriver interface keeps resetting and dumping its database.

Issue Controller resets sporadically, when it comes back online there is no database found in the controller (all points have been deleted) and it needs to be reloaded. After reloading, the Controller responds very slowly and time SystemVariables such as Date, Minute, Hour, are not updating. Environment Netcontroller II (CX9680) Cause The problem ended up being traced down to some XDriver points that were configured with an annex point that was also configured as an XDriver point. They were fighting each other. Resolution Removed the XDriver point configured as an annex point in another XDriver point and the Controller started to respond normally.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • Andover Continuum
1021 Views

Sigma - The "Run" function in the programmable Object editor causes the editor to crash.

Issue The "Run" function in the programmable Object editor causes the editor to crash. Environment Programmable point Run option Cause When a programmable point is edited and the "Run" option chosen, the editor crashes. Resolution This issue is caused by the controller object number being used. Sigma X96 controllers have traditionally used object numbers in the range of 1 to 250, but with the introduction of Integrated Controllers which use the range of 1 to 1000, the issue will arise. If a controller object number in the range of 251 to 1000 is used for a programmable object, and the "Run" option is required, then the object text should be copied into a spare object with a number in the range of 1 to 250. Once tested the object text can be copied back to its correct object number. Note: this issue does not effect the object operation in the controller itself.
View full article
Picard Product_Support
‎2018-09-06 11:00 AM

Labels:
  • Satchwell BAS & Sigma
1257 Views

Remote Alarm Manager - What TCP ports are used?

Issue Remote Alarm Manager - What TCP ports are used? Environment RAM TCP Ports Cause Customers RAM Console is unable to communicate with the RAM Engine. Customer cannot communicate with RAM webserver. Resolution Remote Alarm Manager uses TCP ports 8090 and 8091 between the RAM Console and RAM Engine. Remote Alarm Manager uses TCP port 80, but also recommends this to be changed to 781 - 785 as defined in the settings page.  
View full article
Picard Product_Support
‎2018-09-06 11:00 AM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
1251 Views

Template for TAC Xenta 102-B, Xenta 102-VF and TAC Xenta 102-EF

Issue What template to use for TAC Xenta 102-B What template to use for TAC Xenta 102-VF What template to use for TAC Xenta 102-EF Environment TAC Xenta 102-B TAC Xenta 102-VF TAC Xenta 102-EF Cause The Xenta 102-B TAC Xenta 102-VF and TAC Xenta 102-EF uses the same template. Resolution Use the TAC Xenta 102 template
View full article
Picard Product_Support
‎2018-09-06 11:00 AM

Labels:
  • TAC Vista
976 Views

Control signal Xenta102B.

Issue What is the control signal to the actuator for a Xenta 102B? Environment Xenta 102B Cause The 102B is designed to be used with a Belimo actuator. This is why the out signal is not specified anywhere in the documentation.   Resolution The out control signal to the actuator is 0-10V.  
View full article
Picard Product_Support
‎2018-09-06 11:00 AM

Labels:
  • TAC Vista
910 Views

Sigma Server crashes soon after startup. Anti-Virus is also on the same machine.

Issue Sigma Server failure Environment Sigma Site Cause Sigma has worked OK previously but now the Sigma server fails every time and quickly after starting. Resolution A new anti-virus definitions file has been downloaded either manually or automatically and has detected that a Sigma file may be suspect, this will normally be a fault of the definitions file. There will be a report in the Windows event viewer that Sigma services has failed. Anti-Virus software is often set to move suspect files into a "quarantined" directory.  There will be a log to show this. Check these for any Sigma files quarantined. Anti-Virus software can also be set to automatically delete suspect files.  There will be a log to show this. Check this for any Sigma files shown as deleted. 1. Disable the Anti-Virus software on either the whole of c:\sigma\data or c:\sigma\bin. Note: The site IT may need to be involved and approval may be required. 2. Either re-instate the files from the quarantined folder or re-install Sigma.
View full article
Picard Product_Support
‎2018-09-06 11:00 AM

Labels:
  • Satchwell BAS & Sigma
948 Views

Where can I purchase a replacement battery for a CSC5352 Compensator

Issue Replacing battery Environment Wall mounted   Cause Old age Resolution RS Order number=         201-9438 Type LS14500 Click here to be linked to the RS page
View full article
Picard Product_Support
‎2018-09-10 01:23 PM

Labels:
  • Field Devices
1315 Views
  • « Previous
    • 1
    • …
    • 443
    • 444
    • 445
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of