Getting error FiringOrder error when sending data to a controller
  • Getting error FiringOrder error when sending data to a controller
  • Dave_Shore
    Dave_Shore
‎2018-09-06 11:01 AM
"Unable to reload object Network\Controller\FiringOrder.
          You do not have sufficient access to do the requested operation"
Continuum
Firing Order is a Group Object, so if Group Objects are not open to the user then they can not be sent to a controller.
Firing Order is a Group Object thus when reloading a controller (send to controller) the user requires security rights for Groups.
  • 11367