Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1827 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 39
    • 40
    • 41
    • …
    • 92
  • Next »
Label: "TAC IA Series" Show all articles

A UNC-5x0 fails to start its station and reports the error "Driver failed to load license". How can this be corrected?

Issue A UNC-5x0 fails to start its station and reports the error "Driver failed to load license". How can this be corrected? Environment UNC-5x0 Cause The error indicates a failure in the flash memory. Resolution Field repair of the UNC-5x0 is not possible. Contact Product Support Services to obtain a return authorization (RA) number.
View full article
Picard Product_Support
‎2018-09-06 02:54 PM

Labels:
  • TAC IA Series
852 Views

In a Niagara R2 / MicroSmart integration, what's the optimal method to transfer data from a UNC station to all the MicroSmart controllers connected to its RS-485 port?

Issue In a Niagara R2 / MicroSmart integration, what's the optimal method to transfer data from a UNC station to all the MicroSmart controllers connected to its RS-485 port? Environment Niagara R2, Niagara G3 MicroSmart controllers (versions 10 & 11) Cause Sharing data between controllers Resolution The MSGlobalDataOut object will transmit data, from a UNC station, onto the MicroSmart (RS-485) bus using a MicroSmart global broadcast channel. Then, within each controller, a point can be programmed to access the data from that specific channel number. Only controllers with firmware revision 10 & 11 support MicroSmart global broadcast channels. MicroSmart controllers with a capacity of 64 points, like the MSC-MPC, can receive information on all 122 global channels. MicroSmart controllers with a capacity of 48 points, like the MSC-P1500 series, can only receive information on global channels 1 – 24. See the MicroSmart Driver Engineering Guide (F-27327) for more details on the MSGlobalDataOut object. See the DMS Operator Interface User’s Guide (F-25467) for more details on MicroSmart Global Broadcasting.
View full article
Picard Product_Support
‎2018-09-06 02:53 PM

Labels:
  • TAC IA Series
1229 Views

How can BACnet objects be learned as "full" objects and not "lite" objects in a Niagara R2?

Issue How can BACnet objects be learned as "full" objects and not "lite" objects in Niagara R2? Environment Niagara R2 Cause "Use lite objects" is enabled and need to be disable (uncheck the box) "Use Lite Objects" setting using BACnet Utilities. Resolution From the BACnet Utilities window, when performing either a "network - learnNetwork" or "device - learnDevice" command, clicking the Execute button will generate a pop-up window. In this window, uncheck "Use lite objects", and click OK to proceed.
View full article
Picard Product_Support
‎2018-09-06 02:53 PM

Labels:
  • TAC IA Series
936 Views

How can an AI object be scaled to display to 4 decimal places in Workplace Tech?

Issue How can an AI object be scaled to display to 4 decimal places in Workplace Tech? Environment MNL controller MNB controller Workplace Tech Cause The AI object in a MNL or MNB controller can only display to 2 decimal places and this cannot be increased. Resolution Change the "scaled high value" and "scaled low value" represented by the input signal. For example: Given a transmitter that provides 0 to 5 VDC representing 0.0 to 0.1 inches of water column. Rather than putting in a "scaled low value" of 0.0 and a "scaled high value" of 0.1 make the "scaled high value" 100. Then take that value up to a Niagara station and divide it by 1000 to convert it back to inches of water column.  This will display it to 4 decimal places.
View full article
Picard Product_Support
‎2018-09-06 02:53 PM

Labels:
  • TAC IA Series
985 Views

Can an alarm be generated if a Niagara R2 Enterprise Server loses connectivity to the Vykon Alarm Service (VAS)?

Issue Can an alarm be generated if a Niagara R2 Enterprise Server loses connectivity to the Vykon Alarm Service (VAS)? Environment Niagara R2 VAS client Cause To trigger an alarm when VAS connection changes, create a program object and link to clientActive. Resolution In order to alarm on the status of a VAS connection, do the following: Create a program object in WorkPlace Pro, and paste in the following code: //////////////////////////////////////////////////////////////// // VAS Active clients // This object monitors the number of active VAS clients. // Revision History: // 07 August, 2007 ////////////////////////////////////////////////////////////////// // Inputs // flex input int ActiveClients // // Outputs // output FloatStatusType Clients // Processing Clients.value = ActiveClients Link the clientActive property of the VykonAlarmService to the ActiveClients property of the program object Create a comparison object, and link the output of the program object to Input A of the comparison object In the comparison object, configure the function so that A < B, and set defaultB to 1 Create a BI object, and link the status out of the comparison object to the status in of the BI Configure the alarm properties of the BI
View full article
Picard Product_Support
‎2018-09-06 02:53 PM

Labels:
  • TAC IA Series
964 Views

Which BACnet (MNB) and Micronet (MNL) controllers are half-wave rectified and which are full-wave rectified?

Issue Which BACnet (MNB) and Micronet (MNL) controllers are half-wave rectified and which are full-wave rectified? Environment BACnet (MNB) controllers Micronet (MNL) controllers Cause Information about products rectifier helps avoid equipments damage connected with improperly wiring. Resolution In the current MNB controller line, the MNB-1000 is full-wave rectified. The MNB-300, MNB-70, and MNB-Vx are half-wave rectified. In the current MNL controller line, the MNL-800 is full-wave rectified. The MNL-5Rxx, MNL-1xRxx, MNL-20Rxx, and MNL-VxRxx are half-wave rectified. An early version of the MNL controllers were full-wave rectified: MNL-Pxx, MNL-Uxx, and MNL-Vxx (firmware V1.x). The same controllers were upgraded to firmware V2.x and re-designed for half-wave rectification. Both firmware versions of this controller line are obsolete.
View full article
Picard Product_Support
‎2018-09-06 02:53 PM

Labels:
  • TAC IA Series
1738 Views

Convert a true/false output from a Boolean object to a numeric 0 or 100 in Niagara G3

Issue How can the true/false output from a Boolean object (i.e. Tstat) be changed to a numeric 0 or 100 in Niagara G3? Environment Niagara G3 Cause Represent a boolean on/off value with a numeric that can be used to drive other logic. Resolution Open the kitControl palette under the Util folder Use an object called NumericSwitch Link the output of the Boolean object into the InSwitch property of the NumericSwitch In the properties of the NumericSwitch object, set the "in true" value to 100 and "in false" value to 0 (or vice versa if reverse acting). The output of the NumericSwitch will be a numeric type.
View full article
Picard Product_Support
‎2018-09-06 02:53 PM

Labels:
  • TAC IA Series
4182 Views

Can a Niagara R2 station be started from a command prompt?

Issue Can a Niagara R2 station be started from a command prompt? Environment Niagara R2 Cause Another option to start Niagara R2 station. Resolution Add the Niagara bin folder to the computer path or change directories to be in that folder. Then run "station ". The command window can be minimized, but closing it will stop the station. When the station is started in this method, it will not show "running" in the admin tool. An example of a batch file to start station "Lon522" is shown below: C:\cd\Niagara\r2.301.522\nre\bin station Lon522  
View full article
Picard Product_Support
‎2018-09-06 02:53 PM

Labels:
  • TAC IA Series
1345 Views

Is there surge protection available for a BACnet/MSTP or RS-485 trunk?

Issue Is there surge protection available for a BACnet/MSTP or RS-485 trunk? Environment BACnet/MSTP RS-485 trunk Surge protector Cause Install surge protector to prevent devices from abnormal electrical spike, which might damage devices. Resolution In the Network 8000 Hardware Installation Practices manual (F-23061) pages 21-26, the GCMA-131-1 is used for data line surge protection in conjunction with the AS-8969-21 capacitor grounding the shields as shown. The same components and procedures apply to BACnet/MSTP or RS-485 trunks. If there are power line issues, review the PAS-29901-400 lightning arrestors. The GCMA-131-1 and its associated installation shown on pages 22-23 of the above manual can be used.  Also, the E-1001-111 transzorb shown on page 26 can be used. It is important to have a GOOD earth ground when applying these devices.
View full article
Picard Product_Support
‎2018-09-06 02:52 PM

Labels:
  • TAC IA Series
2371 Views

How many ASD buses can exist on a Niagara R2 UNC 520?

Issue How many ASD buses can exist on a Niagara R2 UNC 520? Environment Niagara R2 UNC 520 Cause Knowing the total number of ASD bus supported helps with system architecture. Resolution The ASD driver only supports 2 ASD buses on a single UNC-520.
View full article
Picard Product_Support
‎2018-09-06 02:52 PM

Labels:
  • TAC IA Series
977 Views

What are the rules for linking objects between Niagara R2 Stations?

Issue What are the rules for linking objects between Niagara R2 Stations? Environment Niagara R2 stations Cause Additional information on linking rules to correctly linked objects between Niagara R2 Resolution The following are the Niagara R2 link rules for inter-station and external station links:   Link as many inputs to a single output as needed (“one-to-many”). For any input property that is already linked, no further link to it is permitted unless the property is a priorityArray type or trigger type (or certain types of Lon properties). Only then is a “many-to-one” link allowed. External links (between stations) have further restrictions. The following types of external links are not permitted (nor are they shown in the Link Editor): Links between prioritizedOutputs and priorityArray input properties. Links between properties using triggerType data species. Links from a GxText object to an internal property of another object (only inputs or outputs are available).
View full article
Picard Product_Support
‎2018-09-06 02:52 PM

Labels:
  • TAC IA Series
1110 Views

The following error appears in the Niagara R2 UNC Standard Output Window: Duplicate Server Sessions - kill (Enterprise Server Name).

Issue The following error appears in the Niagara R2 UNC Standard Output Window: Duplicate Server Sessions - kill (Enterprise Server Name). Environment Niagara R2 UNC Cause Running multiple R2 stations can cause issue with the subscription of the UNCs in the address book of the Enterprise Server station. Resolution An Enterprise Server has the ability to run multiple R2 stations at one time. Under normal circumstances only one station should be running on a server.
View full article
Picard Product_Support
‎2018-09-06 02:52 PM

Labels:
  • TAC IA Series
1102 Views

When accessing MNL VAV boxes from a computer running Workplace Pro, the following error appears: ERROR.E_INVALID_ENUM_ORDINAL.(6)

Issue When accessing MNL vav boxes from a computer running Workplace Pro, the following error appears:   ERROR.E_INVALID_ENUM_ORDINAL.(6) Environment Workplace Pro MNL VAV boxes Cause This is an indicator of a jar mismatch. Resolution Ensure the UNC has the same lonSiebe and lonWorks jars as the computer running WorkPlace Pro.
View full article
Picard Product_Support
‎2018-09-06 02:52 PM

Labels:
  • TAC IA Series
1117 Views

Where can the specifications for the MNB-300-ENC be found?

Issue Where can the specifications for the MNB-300-ENC be found? Environment MNB-300-ENC Cause There is no separate specification sheet for the MNB-300-ENC. Resolution See the Installation Instructions for the MNB-300 (F-27345).
View full article
Picard Product_Support
‎2018-09-06 02:52 PM

Labels:
  • TAC IA Series
894 Views

Specifications of the internal battery of a UNC-6x0

Issue What are the specifications of the internal battery of a UNC-6x0? Environment UNC600 UNC610 Cause When the battery is replaced, follow Technical Bulletin TB06-05 to restore the BIOS settings. Resolution The internal battery is a CR2032 (3 Vdc) and is available from any retail technology outlet store.
View full article
Picard Product_Support
‎2018-09-06 02:51 PM

Labels:
  • TAC IA Series
802 Views

The specification sheet for the UNC-510 (F-27001) lists the power supply input voltage as 24 Vac or 24 Vdc. Can this UNC use a DC power supply source?

Issue The specification sheet for the UNC-510 (F-27001) lists the power supply input voltage as 24 Vac or 24 Vdc. Can this UNC use a DC power supply source? Environment  UNC-510 Cause The spec sheet listed 24vdc as a supported power source but the installation manual instructs to use AC power source. Resolution No. It was originally intended to use both AC and DC but it was never UL-listed or FCC-tested as a DC device. The UNC-510 installation instructions (F-27033) clearly indicates the use of an AC power source.
View full article
Picard Product_Support
‎2018-09-06 02:51 PM

Labels:
  • TAC IA Series
1172 Views

How long will a UNC-520 hold the date &amp; time on a power loss?

Issue How long will a UNC-520 hold the date & time if AC power and the backup battery are disconnected? How long will a UNC-520 hold the date & time if AC power is disconnected but the backup battery remains connected? Environment UNC-520 Universal Network Controller Cause UNC-520 provide real-time clock and need to maintain the information during power failures. Resolution Approximately one hour. This is done by a 1200 µF 10 Vdc capacitor that backs up the real-time clock chip. Over one month.
View full article
Picard Product_Support
‎2018-09-06 02:51 PM

Labels:
  • TAC IA Series
833 Views

The Niagara Schedule object was created in a Niagara R2 UNC station. The schedule events display in Workplace Pro but do not display in a web browser.

Issue The Niagara Schedule object was created in a Niagara R2 UNC station. The schedule events display in Workplace Pro but do not display in a web browser. Environment Niagara R2 UNC Workplace Pro Web browser Cause To display in a web browser, it require the UNC to have the WebUIService and WebUI licensing. Resolution The schedule events are graphically-based views. In order to make them web browser-accessible, the UNC station requires the WebUIService and the UNC must be licensed for web browser support.
View full article
Picard Product_Support
‎2018-09-06 02:51 PM

Labels:
  • TAC IA Series
998 Views

How can a graph displaying two points in WorkPlace Pro be created?

Issue How can a graph displaying two points in WorkPlace Pro be created? Environment Workplace Pro Trend log graph Cause Displaying two points' trend data on a single graph allows the user to compare two values over time. Resolution Using return air temperature and supply air temperature as an example: In the logic folder, link these two objects to an analog log object using status output to status input. Open a web browser and type the SWID http://IPaddress/chart/log. In the log window, hold down the CTRL key and select multiple logs and click on ADD and click Chart. This will create a chart with multiple points. Continue the following steps to access it from the browser: In the chart window, copy the URL address and create a gx text on a gxpage. Go to the properties of the gxtext and select the visual tab. On the hyperlink URL paste the address in the space. On hyperlinkonclick select URL, go to the configure tab and type text in the box that will display in the browser. Open a web browser and type in this SWID http://IPaddress/gx/index. This will display the list of graphics, select one and select the gxtext. This will launch to the graphics page.
View full article
Picard Product_Support
‎2018-09-06 02:51 PM

Labels:
  • TAC IA Series
950 Views

What information is required in requesting an RMA for any model of Niagara R2 UNC / Niagara G3 ENC?

Issue What information is required in requesting an RMA for any model of Niagara R2 UNC / Niagara G3 ENC? Environment Niagara R2 UNC Niagara G3 ENC Cause Return a defected product to service. Resolution The Serial Number and Symptom (Description of Issue) are required. If advance replacement equipment is required, or if the unit is out of warranty, a purchase order number will also be required. Call and provide this information to Product Support Services at 1-888-444-1311,  Note, there may be additional information required to aid in resolving the difficulty.
View full article
Picard Product_Support
‎2018-09-06 02:51 PM

Labels:
  • TAC IA Series
1164 Views
  • « Previous
    • 1
    • …
    • 39
    • 40
    • 41
    • …
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.