The specification sheet for the UNC-510 (F-27001) lists the power supply input voltage as 24 Vac or 24 Vdc. Can this UNC use a DC power supply source?
  • The specification sheet for the UNC-510 (F-27001) lists the power supply input voltage as 24 Vac or 24 Vdc. Can this UNC use ...
  • sesa119747
    sesa119747
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 02:51 PM
 UNC-510
The spec sheet listed 24vdc as a supported power source but the installation manual instructs to use AC power source.
No. It was originally intended to use both AC and DC but it was never UL-listed or FCC-tested as a DC device. The UNC-510 installation instructions (F-27033) clearly indicates the use of an AC power source.