Convert a true/false output from a Boolean object to a numeric 0 or 100 in Niagara G3
  • Convert a true/false output from a Boolean object to a numeric 0 or 100 in Niagara G3
  • sesa116871
    sesa116871
‎2018-09-06 02:53 PM
How can the true/false output from a Boolean object (i.e. Tstat) be changed to a numeric 0 or 100 in Niagara G3?
Niagara G3
Represent a boolean on/off value with a numeric that can be used to drive other logic.
  1. Open the kitControl palette under the Util folder
  2. Use an object called NumericSwitch
  3. Link the output of the Boolean object into the InSwitch property of the NumericSwitch
  4. In the properties of the NumericSwitch object, set the "in true" value to 100 and "in false" value to 0 (or vice versa if reverse acting).
  5. The output of the NumericSwitch will be a numeric type.
  • TAC IA Series
  • 2827
100% helpful (1/1)