Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,851
  • TAC IA Series 1,825
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 149
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 379
    • 380
    • 381
    • …
    • 508
  • Next »

Getting error messages when attempting to add a BACnetNetwork to an ENC.

Issue The message "Could not invoke the command "New"" is displayed when attempting to right-click in the Drivers View Pane and add a BACnetNetwork. Also, the message "Cannot perform the drop" is displayed when attempting to drag and drop a BACnetNetwork driver from the Palette into the Drivers folder. Environment Niagara G3, Enterprise Network Sever, ENC-520, ENC-410 Cause NA Resolution Uninstall WorkBench Delete remaining folders and files from Niagara build directory Reinstall WorkBench
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • TAC IA Series
1191 Views

What is the maximum cable length for Continuum I/O bus (IOU Module)?

Issue What is the maximum cable length for Continuum I/O bus (IOU Module)? Environment IOU Module Cause Need verification of cable length. Resolution Maximum Length of I/O Bus The Andover I/O Bus is a network. Networks are limited by cable lengths because electrical signals lose power and distort as they travel along wire. The longer the wire, the lower the signal strength. The following are the maximum cable length specifications: RS-485 2000 ft. (610 m) FTT-10A 8858 ft. (2700 m) double termination 1640 ft. (500 m) free topology
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • Andover Continuum
949 Views

Does Continuum provide a way to monitor the 61850 protocol?

Issue Does Continuum provide a way to monitor the 61850 protocol? Environment Continuum Cyberstation 61850 protocol Cause Protocol support Resolution Continuum does not provide a means to communicate with the 61850 protocol either directly or xdriver.
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • Andover Continuum
1019 Views

Can not add additional histories to an existing Niagara G3 SQL database. The error messages "javax.baja.sys.BajaRuntimeException" and "Caused by: java.sql.Batch...

Issue The following error messages are displayed in the Application Director output windows when attempting to add additional histories to a existing SQL database. javax.baja.sys.BajaRuntimeException at javax.baja.rdb.history.BRdbmsHistoryExport.insertMetaRecord(BRdbmsHistoryExport.java:679) at javax.baja.rdb.history.BRdbmsHistoryExport.exportRecords(BRdbmsHistoryExport.java:279) at javax.baja.rdb.history.BRdbmsHistoryExport.doExecute(BRdbmsHistoryExport.java:202) at auto.com_tridium_rdb_sqlserver_history_BSqlServerHistoryExport.invoke(AutoGenerated) at com.tridium.sys.schema.ComponentSlotMap.invoke(ComponentSlotMap.java:1232) at com.tridium.sys.engine.EngineUtil.doInvoke(EngineUtil.java:49) at javax.baja.sys.BComponent.doInvoke(BComponent.java:1050) at javax.baja.util.Invocation.run(Invocation.java:46) at javax.baja.util.ThreadPoolWorker$WorkerThread.run(ThreadPoolWorker.java:266) Caused by: java.sql.BatchUpdateException: Invalid column name 'INTERVAL_'. at net.sourceforge.jtds.jdbc.JtdsStatement.executeBatch(JtdsStatement.java:944) at org.apache.commons.dbcp.DelegatingStatement.executeBatch(DelegatingStatement.java:297) at javax.baja.rdb.history.BRdbmsHistoryExport.insertMetaRecord(BRdbmsHistoryExport.java:673) ... 8 more Environment G3 Niagara, 3.4 and later, SQL Cause The term INTERVAL was a keyword in some SQL dialects, so the column name was changed from INTERVAL to INTERVAL_ in the database schema. The database schema changed between 3.3 and 3.4. Resolution The following changes needed to be made to the SQL database. Altered the existing HISTORY_CONFIG table in the SQL database to change the column to INTERVAL_. Altered the HISTORY_CONFIG table, added a column called SYSTEMTAGS, set up as VARCHAR(500). Changed SOURCE column length to VARCHAR(500) in the HISTORY_CONFIG table  
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • TAC IA Series
1944 Views

How to remove a Security Level from Continuum

Issue If a Security Level has been created in Cyberstation and is no longer required how can it be removed? Environment Cyberstation all versions Cause It may be required to remove a Security level from a system or to remove its action from an object. Resolution It is not possible to delete a Security Level after it has been created in Cyberstation. You can however remove the security level action from an object: in the Security Level tab; to de-select the security level right click and choose "Clear Selection".
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • Andover Continuum
1193 Views

Sigma - Displayed temperatures are seen to increase suddenly.

Issue Sigma AI objects could be seen to suddenly change in value through the system logging. Environment AI Objects Temperature Sigma controllers Cause This is caused by a fault on the processor card. Resolution Replace the CPU card.
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • Satchwell BAS & Sigma
807 Views

Need to replace the GCMA-136-2 repeater circuit board.

Issue Need to replace the GCMA-136-2 repeater circuit board. Environment Network 8000 devices on an RS-485 bus (ASD, LCM, or GCS) with fiber-optic repeater(s). Cause Failure of the repeater. Resolution The GCMA-136-2 printed circuit board is the major component of the fiber optic repeater RPTR-FIBER. It is not available separately. Order the RPTR-FIBER to replace the complete repeater.
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • TAC IA Series
1251 Views

What is the maximum distance an xP expansion module can be installed?

Issue What is the maximum distance an xP expansion module can be installed? Environment xP Expansion Module Cause Maximum cable length Resolution Modules can be connected to the bottom of the controller with the built-in expansion port connector or they may be connected remotely via a 3-foot (~1m) or 10-foot (~3m) ribbon cable. A total of 10 feet of cable may be used for all Expansion Modules. Mounting and securing of the xP modules is provided through four mounting holes in the base plate.
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • Andover Continuum
942 Views

How do configure a SNVT in Xbuilder to send only on change?

Issue How do configure a SNVT in Xbuilder to send only on change? Environment TAC Xbuilder Cause Having a SNVT that you only want to send on change Resolution Set the period to 0 (zero). This will configure the SNVT to send only on change.
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • TAC Vista
875 Views

What is the DC1100 strap on sensor spec number?

Issue Information Environment Optimiser/compensator Controller Cause Requirement Resolution Specification No. STC600D Part No. 5126020000
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • Field Devices
  • Satchwell BAS & Sigma
2197 Views

Workstation Program disables when Continuum is logged off.

Issue Workstation program functions while logged on to Continuum but stops functioning when the user logs off. The program disables with the error ''You do not have sufficient access to do the requested operation.'' being displayed in the Run Time tab of the program properties. Environment Continuum Cyberstation Cause When Continuum is logged off, the access rights of the default ACC user are used for things such as when Workstation programs run. If the ACC user has had its security settings restricted then these restrictions are applied when the correct user (who may not have these restrictions) is logged off of Continuum. This could then result in a workstations program trying to read / write or do some other action that it is not allowed to do under the current restriction. Resolution Modify your security restrictions on the ACC user to allow for actions that your Workstation Program is trying to perform.
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • Andover Continuum
1001 Views

How to show camera from a DVR in Pinpoint Graphic panel.

Issue Unable to select DVR when selecting Video source device in Video Object control in a Pinpoint Graphic. Environment Continuum Cyberstation Pinpoint Graphics Endura DVR Cause The Video Object control in Pinpoint is not able to have an external DVR as the source. It is only able to show images from internal cameras connected to the Workstation such as by USB or the older Integral Flashbus card.   Resolution The Video Object control only supports cameras connected to the Cyberstation through the means of USB or an Integral Flashbus card. Alternatively, there are two options available to show video from an external DVR/camera in a Pinpoint Graphic. Configure a VideoLayout or Video Monitor object and link this to the DVR and camera you wish to view. Create a button on the graphic to launch the required camera. If the camera is an IP camera and supports streaming, use the embedded Webpage control on the Pinpoint graphic to link to the webpage streaming the camera image. Note: This is a resource heavy way of displaying video in Cyberstation and isn't recommended. The integration that is offered to Endura or Digital Sentry are the best solutions for displaying video in Cyberstation.
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • Andover Continuum
  • CCTV
1551 Views

How do I get the part numbers and datasheets for Continuum products?

Issue Need information and help deciding on the correct product and part numbers. Product Line Andover Continuum Environment All current Continuum products Cause Customers do not always know how to find sales and product information on the various websites. (i.e. Catalogue, datasheets) Resolution For EMEA & Asia Pacific markets the Continuum Catalogue defines all current products and associated part numbers, see Andover Continuum Product Catalogue For the Americas information is available from the iPortal website for product selection and part numbers: http://iportal2.schneider-electric.com   Continuum datasheets are available from the Schneider Exchange Extranet link: https://ecobuilding.schneider-electric.com/search#keyword/Andover%20Continuum%20Specification%20Sheets/tab/documents
View full article
Picard Product_Support
‎2018-09-10 02:53 AM

Labels:
  • Andover Continuum
2085 Views

Xenta 555 is not getting the parameters from MicroNet controllers (Tx/Rx LEDs are not blinking). The values are always zero.

Issue When exporting a pointslist from VisiSat 2.1 build 148 to XBuilder (See pdf link in Resolution below), the format of the TACXBuilder.xmlm is not aligned in a manner that XBuilder fully understands. Environment Xenta VisiSat Points list Export Cause TACXBuilder.xmlm is not aligned in a manner that XBuilder fully understands. Resolution Install service pack 1 for VisiSat 2.1 build 148. For further information see TPA-LOND-08-0006.00 The Service pack for VisiSat 2.1 build 148 can be downloaded here. The current version of VisiSat is version 2.1 build 201 (September 2018) VisiSat 2.1 Build 196 can be download here. Two service packs are available: - for information and a download link for service pack 1 software click here. for information and a download link for service pack 2 software click here.
View full article
Picard Product_Support
‎2018-09-10 03:04 AM

Labels:
  • Satchwell MicroNet
1014 Views

What is the life expectancy of the LCD display of smart sensors with available display?

Issue What is the life expectancy of the LCD display of smart sensors with available display? Environment Smart sensor with LCD display Cause Display life expectancy. Resolution The Life expectancy of an LCD Display is 50K hours. Note: Life is reduced if LCD works under direct sunlight. If you use a LED backlight in a LCD module the life expectancy of the LED is 30K to 50K hours, depending on the forward current. EL backlights are available but we don’t recommend them because of their short life (3K hours) and EMC problems. The AC voltage is generated by the DC to AC inverter.  
View full article
Picard Product_Support
‎2018-09-06 01:19 PM

Labels:
  • Andover Continuum
  • Field Devices
1136 Views

When installing UltiVist on a new OS/2 computer it fails to begin stating there's not enough space on c: drive.

Issue When installing UltiVist on a new OS/2 computer, it fails to begin stating there's not enough space on c: drive.  However, c: drive has plenty of free space. Pop-up error message reads as follows: Setup is unable to copy the installation support file a:\~ins0762.lib to a temporary location.  Error 420 Environment UltiVist Cause The primary partition size is an issue for UltiVist. OS/2 can support partition sizes greater than 2 gigabytes if HPFS is selected over FAT.  UltiVist will NOT support a primary partition size of 2 gigabytes or greater and, as a result, it will think that there's insufficient capacity for writing data to the partition. To confirm, open a Win-OS/2 window, go to file manager, and check the drive space.  If a partition of greater than 2 gigabytes has been created, the available drive space will display as zero. Resolution Create a primary partition size of 1.99 gigabytes.  It can be HPFS or FAT. Best practice:  Install only OS/2 on the primary partition.  Install UltiVist on an extended partition (typically d: drive).
View full article
Picard Product_Support
‎2018-09-06 01:19 PM

Labels:
  • TAC IA Series
924 Views

When integrating a Network 8000 LCM with a Niagara R2 UNC, what firmware revision level must the LCM have for proper operation?

Issue A Network 8000 LCM-84x10 or LCM-88x10 will be integrated with a Niagara R2 UNC.  What firmware revision level must the LCM have for proper operation? Environment Network 8000 LCM Niagara R2 UNC-520 Cause The integration requires the LCM to have at least Year 2000 firmware installed.  The shadow objects in the Niagara station will not update or function properly. Resolution Upgrade the LCM using EPROM kit # LCMA-138-54. This kit is to be used with the LCM-84x10 or LCM-88x10 and it will upgrade the firmware level to 5.4, Year 2000 compliancy. It is available for purchase via iPortal.
View full article
Picard Product_Support
‎2018-09-06 01:19 PM

Labels:
  • TAC IA Series
1178 Views

What is the replacement for an IAC-420-P or the IAC-420-F

Issue Product Rationalisation Environment Global Cause The IAC-420-F part number for an IAC-420 with fixed terminals has been made obsolete. The IAC-420-P specification number should be used. The only difference between the two devices is fixed (F) terminals against plug in (P) terminals. Resolution The replacement for either an IAC 420-F or an IAC-420-P is the IAC-420-P
View full article
Picard Product_Support
‎2018-09-06 01:19 PM

Labels:
  • Satchwell MicroNet
1171 Views

We have got old CX9400 Eclipse controllers which we need to replace on an Infinity SX8000 installation.

Issue We have spare Continuum CX9400 controllers which we need to replace the damaged Infinity ones on a old SX8000 installation.   Environment CX9400 Eclipse Continuum, Infinity SX8000 Cause SX8000 Flash files are not posted on the Extranet and the product is obsolete. Resolution It is not possible to downgrade a CX9400 Eclipse from Continuum back to Infinity in the field, this is a one way process to upgrade using a Continuum Flash file in SX8000. There are no Infinity flash files that would allow you to go backwards. Your only option would be to contact your local Repairs department and arrange to have the controller shipped back to the factory where they should be able to re-load in the Infinity Operating system.  
View full article
Picard Product_Support
‎2018-09-06 01:19 PM

Labels:
  • Andover Continuum
1249 Views

Getting the message "Cannot display page" and "Access Denied: Remote host does not accept brand "Webs"" while trying to access the Platform of...

Issue Getting the message “Cannot display page” and “Access Denied: Remote host does not accept brand “Webs”” while trying to access the Platform of an ENC-520 with Niagara G3 WorkBench. Environment G3 Niagara all version, ENC-410, ENC-520 Cause Honeywell WEBs (Honeywell’s version of Ax) on the same PC as Niagara G3. WEBS was installed and licensed first. G3 was installed after WEBs, but never licensed. Since a license for G3 was never obtained, G3 was attempting to use the Honeywell license to connect to the ENC-520. This results in a license brand incompatibility. Resolution The Niagara G3 WorkBench has to be licensed to connect to an ENC.   All TIP and end customer Niagara G3 / R2 license requests are emailed to:IASeries.License@buildings.schneider-electric.com  
View full article
Picard Product_Support
‎2018-09-10 03:07 AM

Labels:
  • TAC IA Series
1636 Views
  • « Previous
    • 1
    • …
    • 379
    • 380
    • 381
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of