Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,853
  • TAC IA Series 1,826
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 286
    • 287
    • 288
    • …
    • 509
  • Next »

SQL Server Failed to Initialize when Trying to Run Reports

Issue When Reports are opened and the user selects a Report then tries to run the report, an error comes up that says “Server Failed to Initialize” and nothing happens. Environment I/NET Seven Site Cause error comes up that says “Server Failed to Initialize" Resolution There is a fix for this but an IT individual will need to be present or the user must have admin rights to do this. Shut down I/NET and Seven Reports. Go to Start, Run and type Regedit at the prompt. Go to Local_Machine, Software, Microsoft, MSSQL Server, Super Socket Net Lib. Expand this and there should be two folders listed in here, NP and TCP. Highlight the Super Socket Net Lib and a Protocol file appears. Right Click this file and modify it to display the Hex addresses in there and verify that one exists for NP and TCP. Value data: 0000 74 00 63 00 70 00 00 00 t.c.p... 0008 6e 00 70 00 00 00 00 00 n.p..... 0010 Note: If you are not sure please contact an IT professional to assist you.  
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC INET
1470 Views

Stroke time on Xenta 102-AX

Issue Stroke time (throttling range) on Xenta 102-AX VAV controller Environment Xenta 102-AX Cause The stroke time of the actuator differs when the input power is 50Hz versus 60Hz. Since this is not an Imperial vs. Metric issue, LonMaker or Vista does not automatically change this for you according to your regional settings. Resolution The stroke time for the Xenta 102-AX is as follows: 2.4 seconds / degree rotation (50 Hz) 2.0 seconds / degree rotation (60 Hz)   Assuming the damper stroke is 90º: The default setting for damper stroke time is 230 seconds. This is the approximate stroke time when that AC motor is driven with a 50Hz supply. 185 seconds is the approximate time when using a 60Hz supply. The unit will control space temperature regardless but the damper position which is estimated in software will be off when it is anywhere other than 0% or 100%. This will make the damper more aggressive than the program thinks it is. This could make the calibration efforts take longer since the damper might take longer to stabilize the airflow reading. It is recommend to change the damper stroke time to 185 on any site fed by a 60Hz supply. (Unless the damper travel is other than 90°. In that case, set the physical screws accordingly and calculate a new appropriate stroke time based on the seconds per degree values above.)
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
1246 Views

Dependencies for Vista Server running as a service

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue Dependencies for Vista Server running as a service Product Line TAC Vista Environment Vista Server Cause The Vista server can run into issues if it starts up before other services. Resolution Ensure that Vista Server does not start up before Aladdin Privilege Server by making some changes to the registry. Select the start menu, select run, and type “regedt32”. Once the program opens you should browse to the following path: HKEY_LOCAL_MACHINE\SYSTEM\ControlSet001\Services\TACOS\ The key named DependOnService should by default contain the value RPCSS. To add a dependency to this service just modify the value of the key and add the name of the service you wish to start before this one. In the case of Aladdin Privilege Server just add the text “Privilege Win32 Server” to the registry key. Close the registry editor and the dependency will be visible in the services properties window for TACOS. Note: If you need Vista to start late in the boot cycle but you do not have a specific service dependency, as explained above, then choose one of the services which startup last as the data value for the value "Depends on Service". Services commonly selected are Spooler and Messenger.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
2068 Views

Corrupted LNS Credits

Issue Cannot register LonMaker plugins Product Line TAC Vista Environment LNS, LonMaker, NL220 Cause If you are having difficulty registering plug ins in LonMaker then you may have corrupted LNS credits. Resolution To check your LNS credit status, run the LNS Server License Wizard which is found at C:\LonWorks\bin\LnsLic.exe If you run the wizard and it displays the Max Credits at zero and Credits Available as zero as well, then your LNS credits have become corrupted. To correct this, select Next in the Wizard so that it displays the PC Key. The wizard provides a button titled "Copy to Clipboard" which when selected will allow you to paste a form letter into an email or text editor. After filling your specific contact information you will want to check the "No Charge" box and the "Replacement Use" box. Before you send the form via fax or email, you also need to provide evidence that your LNS credits have been corrupted. Select Start > Run > and type "cmd" to reach a command prompt. This command will check the status of the LNS credits: checklic nsseng.exe The output of this command should either be printed and sent with the fax or included in the email to the address or phone number shown at the top of the form letter. You should then receive instructions or an application key to correct the problem.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
1722 Views

Synchronizing time with a DVR

Issue Synchronizing time with a DVR Environment DVR CCTV I/NET Cause PC time on the DVR is behind the PC time on the I/NET Seven system.   Resolution When an event occurs in a Digital Video Recorder that is interfaced with I/NET Seven and you want to see the associated video with this event it is possible that no video will appear without searching manually. This occurs when the PC time on the DVR is behind the PC time on the I/NET Seven system. During configuration of the interface it should be verified that both computers are using the same time settings to include current time and time zone. These can be set either manually or if additional precision is necessary through the use of a NTP server.  
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC INET
1088 Views

MRs going to Sleep

Issue MRs going to Sleep Environment I/NET Seven site with MR's Cause When certain DDC Modules are being used in an MR it uses both the NOV RAM and RAM Memory Resolution When certain DDC Modules are being used in an MR it uses both the NOV RAM and RAM Memory. When writing DDC care should be taken so as to not exceed the amount of memory that is within the device itself. It has 130 Bytes of RAM and 1024 Bytes of NOVRAM. The MR supports six DDC module types and an interconnected control configuration up to 16, depending upon the types. It may appear that the memory is not maxed out, when it is all added up but it causes the MR to “go to sleep”. The user will have to go to the MCU Configuration and turn that MR Internal and then External again, to “wake it up”. Depending upon the application, if there are more than 4 PID modules, the first 4 work, but the others do not. This can also occur if there is a huge calculation on one of the points, the same symptom and result will apply. Please be selective as to which module and function you’re using for your application. Note: MR-resident DDC modules only reside in the MR (not in the MCI, MRI or I/Site LAN. Therefore, these modules are not available for use in any MR tagged as Internal in the MCU configuration editor.) The following table shows the amount of memory that each item uses:     Points   Point NOVRAM Bytes RAM Bytes DI Point 4 1 DA Point 4 1 DM Point 4 1 DO Point (Internal) 4 1 DO Point (External) 4 3 DC Point (Internal) 4 1 DC Point (External) 4 3 AI Point (Internal) 16 3 AI Point (External) 16 5 AO Point (Internal) 16 3 AO Point (External) 16 5 PI Point 4 2         Modules   Module NOVRAM Bytes RAM Bytes PID Module (Without Filter) 40 14 PID Module (With Filtering) 40 19 Floating Module (Without Filter) 40 12 Floating Module (With Filter) 40 17 Two Position Module (W F) 28 2 Two Position Module (W/O F) 28 7 Relay Module (Standard) 20 2 Relay Module (DBB, DBM, INT) 20 4 Reset Module 48 2         Calculations   Calculation NOVRAM Bytes RAM Bytes Calculation Modules Overhead Module (fixed) 6 2 Each Operator (+, -, *, /, etc) 1 N/A Each Point Address (P0, P1, etc) 2 N/A Each Constant (C0, C1, etc) 4 N/A Each Line (L0, L1, etc) 1 N/A Calculation Module Total * 2         Lines   Lines NOVRAM Bytes RAM Bytes MR-DDC Lines N/A 4 Note: Verify that you are using the most current EPROM for the revision of software that you are running.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC INET
1474 Views

Memory Usage on a 7793 Controller.

Issue User upgraded their systems to I/NET Seven from I/NET 2000 rev X.XX and noticed that their databases cannot be downloaded to the controller anymore. Environment I/NET Seven upgraded from I/NET 2000 Cause If dial is not being used at this site, then the controller should be set up as a 779301. Resolution To check how the controller is configured: Use an HHC (Hand Held Console) Plug it into the port Press CODE 90 Enter. If it is set up for a 779301, the bytes available after the bin file is downloaded are 140439 and for a 779306 the bytes available are 95639. The reason for this difference is that the memory is allocated for the Messages Queue. If for some reason the database does not get downloaded then the problem lies in the database itself where there could be a lot of Trended Data that needs to be discarded or Archived to create more room.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC INET
1378 Views

Send out the system date and time as a SNVT_Time_stamp

Issue Send out the system date and time as a SNVT_Time_stamp Environment Time Stamp SNVT type Xenta 511 Cause Send out the system time properties to monitor externally and make sure the time is synchronized. Resolution You can do this by creating signals in the system window for the system variable year, month, day, hour, minute and second. Create an nvo SNVT_time_stamp in the Xenta 511. Create connection objects and connect the signals with the members of the SNVT. Note, you have to change the category and the unit for hour, minute and second to match the SNVT.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
932 Views

Input alarms in a 7797-15

Issue Input alarms in a 7797-15 Environment I/NET Seven Site Cause If a 7797-15 running revisions 1.01 of the binary file has alarming configured on an input point the alarm text will be sent to the message window in AMT every time the point is scanned. This can cause an enormous load on your controller LAN as well as flood your message window making it unusable depending on the number of input points being used.  Resolution If a 7797-15 running revisions 1.01 of the binary file has alarming configured on an input point the alarm text will be sent to the message window in AMT every time the point is scanned. This can cause an enormous load on your controller LAN as well as flood your message window making it unusable depending on the number of input points being used. The only current work around is to turn off the message masking and alarm priority for the input point that has the Modbus address associated with it. Then create a secondary point that has the alarming configured and use a P0 calculation to transfer the value. Any event definitions, trend sampling, or other controller functions can still operate on the original input point. These steps are not necessary for output points since they can be set as internal points and still communicate their values to the Modbus network while the inputs must be external to function.  
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC INET
1268 Views

Steps to properly remove a door from I/NET Seven

Issue Several doors need to be removed in an existing I/NET Seven System. What is the proper way to do this? Product Line TAC INET Environment I/NET Seven with Access Control Cause Steps to remove Doors in an existing I/NET Seven System Resolution It should be sufficient to just deselect the door from the tenant and then NETCON on one equalized client, the file master, or Standalone PC. If the door physically goes away, the next time an operator enters an individual or group that had that door it will display a * for the offline/deleted door. At that time just select "Unselected" option and that door will be removed from that list. If all trace of the door needs to be removed: Remove all access privileges from a door. Be sure to check System View to verify they are all removed. Remove the door from all tenants Connect to the Controller and select Edit>Controller>Doors Delete the Door Close of the Door editors and select Edit>Host Computer>Network Configuration Penetrate to the Door level and delete the door objects. Next, In the Resident I/O editor delete any points associated.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC INET
1838 Views

Conversion utilities location on the I/NET Seven CD.

Issue Conversion utilities location on the I/NET Seven CD. Environment I/NET 2000 - I/NET Seven Cause Location of the Conversion utilities on the I/NET Seven CD. Resolution The location of these files are on the I/NET Seven CD in this location: Program Files > INET Seven > Conversion Files
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC INET
1338 Views

Data is visible on a report preview but not when printed

Issue Data can be seen when previewing the report, but when printed nothing happens. Product Line TAC INET Environment I/NET Site Cause No printer is selected or the no printer option is checked. Resolution Open the I/NET Seven report that has the issue. Choose the Design yellow tab. Go into the Main REport area on the left side of this report. Place the mouse cursor in the white area below the Tree List. Right-click in the blank space to bring up the options menu. From the context menu select Designer > Printer Setup. In the upper left corner of the Printer Setup dialog confirm that the "No Printer" option is unchecked. This should allow you to select a printer. Remember to save this corrected report back in the I/NET Sven reports list.
View full article
Picard Product_Support
‎2018-09-07 01:26 AM

Labels:
  • TAC INET
1344 Views

Using reference shapes to clean up a LonMaker drawing

Issue Using reference shapes to clean up a LonMaker drawing Environment LonMaker Visio Cause A Xenta 401 controller can have as many as 125 SNVT inputs and 125 SNVT outputs visible on a LonMaker drawing. If every one of these signals is connected with a SNVT binding with graphical lines connecting the source and destination signals it can be rather difficult to differentiate between the connections. Resolution One way to clean up your drawing is to select the "Use References" option when you are in the process of creating your SNVT bindings. This will graphically display a line to a numbered balloon at the source and a numbered balloon with a line drawn to the destination. Since the balloons will contain the same number you can easily identify these as bound together. If for some reason you need to revert a referenced binding to a graphical line, right click on the reference object and select the "Don't Use Reference" option and a normal graphical line will be added. If you have a large network, the destination of the binding is on another page, or the destination is not easily visible, right click on the reference object and select "Go To Reference" to have LonMaker take you directly to the destination.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
936 Views

Interfacing with a Trane BCU panel with a 7797-12 ICI

Issue Interfacing with a Trane BCU panel with a 7797-12 ICI Environment I/NET Seven Site with 7797-12 ICI and TRANE BCU Cause The 7797-12 ICI is a PTP (Point to Point) RS232 BACnet device which can be used to interface with Trane systems using their BCU panel. The BCU panel can be equipped with an optional Ethernet card. However the presence of this card can modify the addressing structure of the Trane device disabling communication with the ICI. Resolution The 7797-12 ICI is a PTP (Point to Point) RS232 BACnet device which can be used to interface with Trane systems using their BCU panel. The BCU panel can be equipped with an optional Ethernet card. However the presence of this card can modify the addressing structure of the Trane device disabling communication with the ICI. To resolve this problem simply remove the Ethernet card from the BCU panel. If the Ethernet card is required then a alternative interface will have to be utilized.  
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC INET
1629 Views

Connecting to Controllers using Dial.

Issue Connecting to Controllers using Dial. Environment I/NET Seven Site Cause How to connect to remote sites using Integrated Dial Resolution If the user is connecting to remote sites using Integrated Dial and the site controllers are not visible, please check the following settings: Open I/O Server, modify the dial profile Uncheck the Dial Box Shut down and restart I/O server Connect again If the user is connecting to remote sites using ADAA and the site controllers are not visible, check the following setting: 1.DTE (Host)--------DCE (Modem)-------DTE (Controller)-----9600 (Baud) All these need to be at 9600 Baud, otherwise the lights on the I/O Server would only show Red and no Green. This indicates that there is a Transmit but no receive between one of the above components. For I/NET Seven, only the US Robotics 56K Modems are supported.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC INET
888 Views

Wildcard Filtering in AMT.

Issue Wildcard Filtering in AMT. Environment I/NET Seven Site Cause How to use Wild Card Filtering Resolution In AMT when filtering is being done on devices for data within the Device Name field, there are several characters that can be used to accomplish this task: % The % character is like the * character in windows find files. Searching for a device name of %device% would return any device name containing the string “device” _ The underscore character allows any single character. For example, searching for a device name of “device_” would return “device1”, “device2”, “devices” etc. () The left and right closed brackets allow a single character to be within a specified range (for example: (a-c) or within a set of characters (for example (abcd). Searching for a device name of “device (a-f) would return “device a” through to “device f” but not to “device g”. (^) This is the negation of the previous wildcard. It specifies that a single character should not be within a set of characters (for example, (^a-c) or (^abcd)).  
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC INET
1149 Views

Displaying SNVT Switch on a Graphic in Vista

Issue Displaying SNVT Switch on a Graphic in Vista Environment TAC Vista IV Workstation OGC Graphics Cause When displaying a point of type SNVT Switch on a graphic page in Vista Workstation it's common for the user to see the value of zero when they are expecting the analog value of the SNVT . The reason that this is seen; is due to the fact that when a digital presentation is created on the graphic page and the SNVT Switch signal is browsed in, the attribute field is by default set as "Authenticated." Resolution Proper selection of the attribute field will allow the correct values to be see in the graphic page. To display the analog portion of the SNVT Switch the attribute field should be selected as "Value_(%)" To display the binary portion of the SNVT Switch the attribute field should be selected as "State"  
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
1222 Views

Xenta 101 LonMaker stencils

Issue Which Xenta 101 stencil should be use in LonMaker? Environment Xenta 101-1VF, 101-1VFC, 101-2VF, 101-2VFC, 101-VF Cause Adding a Xenta 101 to a LonMaker drawing. Resolution Please use the following chart when deciding which Xenta 101 stencil to use in LonMaker:   Xenta Unit Stencil 101-1VF 101 101-1VFC 101 101-2VF 101 101-2VFC 101 101-VF 101-VF
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
932 Views

Error: "There is no folder for this object" when creating an object in Workstation

Issue I get an Error message saying, "There is no folder for this object" when I try to create an object. Environment Vista Workstation Cause This error occurs if there is a dash or hyphen (–) in the name of the object being created. Vista uses the dash to define folder paths in the database, e.g. a graphic named RTU-1. Vista sees this as a graphic "1" in the folder "RTU." Resolution Do not use dashes or hyphens in the naming convention for Vista objects. Either eliminate it altogether, or use underscores (_) instead.
View full article
Picard Product_Support
‎2018-09-06 03:08 PM

Labels:
  • TAC Vista
1129 Views

Why Vista Workstation Remote is not supported for Internet Use

Issue Why Vista Workstation Remote is not supported for Internet Use Environment Vista Servers not in the same network Cause Technically Vista Workstation Remote can communicate to a Vista Server over the internet but this is not a supported practice due to the network requirements for the Vista Server. Resolution The Vista Server must be on a PC that is not behind a firewall which utilizes address translation. The IP address of the computer must be the same IP address that Vista Workstation Remote will use to communicate with it. Due to the nature of DCOM (Distributed Common Object Model) which is used by Vista Workstation Remote many ports would have to be left open on the PC and the network firewalls. Vista Workstation Remote connects to DCOM's Service Control Manager (SCM) on port 135 which will dynamically assign a port for the programs to communicate on. Since this requires ports 135 and the entire range of ports that the SCM utilizes to be open on the PC and the firewalls the risk to the network is significant. Most IT departments will not be willing to leave their network so open and exposed. Therefore, Vista Workstation Remote is not supported for Internet use. To use Vista over the internet please look into a web server (Xenta 511/527) or Vista Webstation.
View full article
Picard Product_Support
‎2018-09-06 03:08 PM

Labels:
  • TAC Vista
1062 Views
  • « Previous
    • 1
    • …
    • 286
    • 287
    • 288
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of