Data is visible on a report preview but not when printed
  • Data is visible on a report preview but not when printed
  • sesa139513
    sesa139513
  • Tom_Poovey
    Tom_Poovey
‎2018-09-07 01:26 AM
Data can be seen when previewing the report, but when printed nothing happens.
TAC INET
I/NET Site
No printer is selected or the no printer option is checked.
  1. Open the I/NET Seven report that has the issue.
  2. Choose the Design yellow tab.
  3. Go into the Main REport area on the left side of this report. Place the mouse cursor in the white area below the Tree List. Right-click in the blank space to bring up the options menu.
  4. From the context menu select Designer > Printer Setup.
  5. In the upper left corner of the Printer Setup dialog confirm that the "No Printer" option is unchecked. This should allow you to select a printer.
  6. Remember to save this corrected report back in the I/NET Sven reports list.
  • TAC INET
Tags (3)
  • 1851
  • ok
  • seven