Interfacing with a Trane BCU panel with a 7797-12 ICI
  • Interfacing with a Trane BCU panel with a 7797-12 ICI
  • sesa139513
    sesa139513
  • SESA116857
    SESA116857
‎2018-09-06 03:09 PM
I/NET Seven Site with 7797-12 ICI and TRANE BCU
The 7797-12 ICI is a PTP (Point to Point) RS232 BACnet device which can be used to interface with Trane systems using their BCU panel. The BCU panel can be equipped with an optional Ethernet card. However the presence of this card can modify the addressing structure of the Trane device disabling communication with the ICI.
To resolve this problem simply remove the Ethernet card from the BCU panel.
If the Ethernet card is required then a alternative interface will have to be utilized.
  • TAC INET
  • 1857