Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 281
    • 282
    • 283
    • …
    • 509
  • Next »

What taps support the MIP

Issue Will all taps support the MIP? Environment I/NET site Cause What taps support the MIP Resolution No. There are some taps not supported such as the 78020 (plastic enclosure).
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1301 Views

PC locks with a GPF error message when modifying a slave time schedule

Issue PC locks with a GPF error message when modifying a slave time schedule Environment I/NET Time Schedule Editor Slave Time Schedule Cause The master time schedule point that this slave time schedule is referenced with, no longer exists. Resolution Delete the Slave ATS Re-add it with an existing point that has a Master ATS attached.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
881 Views

What is the recommended maximum number of Doc to Dif conversions?

Issue What is the recommended maximum number of Doc to Dif conversions? Environment I/NET Cause Configuration Question Resolution Not more than 20.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
2172 Views

Windows crashes after performing a Doc to Dif conversion

Issue Windows crashes after performing a Doc to Dif conversion Environment I/NET Site Cause Why does Windows crash after performing a Doc to Dif conversion? Resolution Do not define more than 164 cells per conversion.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
2166 Views

Why is ATS being performed incorrectly as in executing the weekend routine time schedule on a weekly basis

Issue Why is ATS being performed incorrectly as in executing the weekend routine time schedule on a weekly basis and vice-versa? Environment I/NET site Cause Why is ATS being performed incorrectly as in executing the weekend routine time schedule on a weekly basis Resolution Within Windows Control Panel, Regional Settings, try making the date style a 4-digit year for both short and long date styles.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1004 Views

With an NPR Integrated dial configuration, when trying to add an indirect point, site receives an error message "Bad address or link not defined and online"

Issue With an NPR Integrated dial configuration, when trying to add an indirect point, site receives an error message "Bad address or link not defined and online" Environment I/NET site Cause With an NPR Integrated dial configuration, when trying to add an indirect point, site receives an error message "Bad address or link not defined and online" Resolution In previous revisions of I/NET 2000, you could not add indirect points thru an NPR Direct or NPR Integrated Dial configuration.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1151 Views

The I/disc LED remain red constantly, yet individuals can still correctly access the door?

Issue The I/disc LED remain red constantly, yet individuals can still correctly access the door? Environment I/NET Site Cause Why does the I/disc LED remain red constantly, yet individuals can still correctly access the door? Resolution Make sure the DPU dipswitches 11 & 12 are not in the On position. Both should be Off which represents 2-color LED control.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1314 Views

DPU Restore error: "Failed to download file ACSave.tmb?"

Issue When trying to perform a DPU Restore, why do I receive an error message "Failed to download file ACSave.tmb?" Environment DPU 7910 DPU 7920 I/NET 2000  Cause This file was created when a DPU Restore was trying to be performed to an offline DPU. When now trying to restore any online DPU, this error message is generated. Resolution Make the offline DPU Internal within MCU Configuration Shut down I/NET Delete the Inet2000\data\ACSave.tmb file Restart I/NET Retry the DPU restore
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1259 Views

When performing an update MCI after adding a new ACS controller to an existing sublan, why is a Memory Failure error message generated?

Issue When performing an update MCI after adding a new ACS controller to an existing sublan, why is a Memory Failure error message generated? Environment I/NET site Cause When performing an update MCI after adding a new ACS controller to an existing sublan, why is a Memory Failure error message generated? Resolution Since the existing sublan controllers are ASCs with each containing 20 points within the interface, memory limitation is likely exceeded. Clean-up the interface database by deleting the unused resident I/O points. Make sure ASC controllers are set to Internal before deleting points. Retry performing the MCI update for the newly added controllers.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1202 Views

DC/DM points in subLAN devices

Issue Technical Support Services occasionally receives calls concerning the use of DC/DM points in the Micro Regulator product line. The use of DC/DM points in MRs is possible but only when certain guidelines are followed. Environment SubLAN controllers MRs UCs Cause The functionality of the DC/DM points depends on what is actually controlling the DC point. If you use any of the extensions that reside only in the MRI, MCI or I/SITE LAN, etc., to control the DC point you will not have a problem. These extensions include: Time Scheduling, Temperature Control, Calculations and Event Sequences . As long as one of these editors controls the state of the DC point you should not see a problem with the functionality of the DC/DM points. Where you run into trouble is when an MR resident editor controls the DC point. These include all of the modules found in the MR Resident DDC editor, (PID, Floating, Two Position, Relay, Reset, Calculation module). If the state of a DC point is controlled by any of the MR resident DDC modules the associated DM point will always alarm in one state or the other. The same is true for the UCI/UC product line in that a DC point can not be controlled by a UC resident editor. This includes everything under the Unitary Control editor, (VAV, AHU, PID, FLT, HPMP ). In fact, currently if an attempt is made to enter a DC point in any of these editors an error is generated which will not allow such an entry, (this error is not generated in the MR Resident DDC editor). Resolution If you need positive feedback like that provided by the DC/DM points please follow the guidelines set below: Create Control Description and State Description Parameters: Refer to figure 1 and 2. Create an External DO point for Fan Control. Refer to Figure 3. Create an External DI point for Fan Status. Refer to Figure 4. Create an Internal DA Point for Fan Alarm. Refer to Figure 5.  Create a Calculation for the DA point: Refer to Figure 6. Anytime the Fan Control DO and the Fan Status DI follow each other’s state, the calculation remains True. If the DO does not equal the DI State, then the calculation becomes False. This results in an Alarm after the Time Delay of the DA has been met. The Time Delay acts in the same manner as the Time to State for a DM point. Please note if the DI 0 state was ON (the opposite of the DO), the calculation would be P0=~P1 .   *MSG* 09/21/95 12:34:29 Thu Control descriptions and commands Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798] Enter up to 4 characters:  # Description Command Delay --+-----------+-------+-----  0 STRT 1 0  1 STOP 0 0  2 0 0  3 0 0  4 0 0  5 0 0  6 0 0  7 0 0  8 0 0  9 0 0 10 0 0 11 0 0 12 0 0 13 0 0 14 0 0 15 0 0 Figure 1: Control Description and commands *MSG* 09/21/95 12:35:14 Thu State descriptions Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798] Enter up to 4 characters: # Description # Description --+----------- --+----------- 0 OFF 16 1 ON 17 2 ALRM 18 3 NORM 19 4 20 5 21 6 22 7 23 8 24 9 25 10 26 11 27 12 28 13 29 14 30 15 31 Figure 2: State descriptions *MSG* 09/21/95 12:36:19 Thu Resident I/O points Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798] Point 0000 (02290000 DO) Enter up to 16 characters: Parameter Value Parameter Value ---------------------------------------- ------------------+-------- Point name Fan Control Distribution group 1 Point class Ext Distribution mask -------- Scan interval (seconds) 60 Alarm priority - Global level Local Message priority - State description 0 Cell number 0 Control description 0 Restart control action Reinforce Minimum trip (minutes) 0 Minimum close (minutes) 0 Three-state output N Figure 3: Resident I/O points *MSG* 09/21/95 12:36:19 Thu Resident I/O points Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798] Point 0000 (02290000 DI) Enter up to 16 characters: Parameter Value Parameter Value ---------------------------------------- ------------------+-------- Point name Fan Status Distribution group 1 Point class Ext Distribution mask -------- Scan interval (seconds) 10 Alarm priority - Global level Local Message priority - State description 0 Cell number 0 Number of bits 1 Supervision None Figure 4: Resident I/O points *MSG* 09/21/95 12:38:56 Thu Resident I/O points Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798] Point 0009 (02290009 DA) Enter up to 16 characters: Parameter Value Parameter Value ---------------------------------------- ------------------+-------- Point name Fan Alarm Distribution group 1 Point class Int Distribution mask Y------- Scan interval (seconds) 10 Alarm priority Priority Global level Local Message priority Priority State description 2 Cell number 0 Number of bits 1 Normal state 1 Alarm delay (seconds) 120 Supervision None Figure 5: Resident I/O points *MSG* 09/21/95 12:39:57 Thu Calculations Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798] Point 0009 (Fan Alarm) Enter point address or name: Equation --------------------------------------------------------------------------- P0=P1 Operand Point Operand Constant -------+---------------- -------+---------------- P0 Fan Control P1 Fan Status Figure 6: Calculations   The above calculation will return the following DA conditions depending on the state of the DO and DI DO DI DA OFF OFF NORM ON OFF ALRM OFF ON ALRM ON ON NORM
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1048 Views

Site number added to the icon when adding a point to a graphic page within a DLA system

Issue When adding a point to a graphic page within a DLA system, is the site number added to the icon? Environment I/NET site Cause When adding a point to a graphic page within a DLA system, is the site number added to the icon? Resolution No. Since station addresses on the controller LAN beneath the NPR must have unique addresses, this will be adequate to identify the points.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1067 Views

Viewing DLA AMT data on a non-DLA host

Issue Viewing DLA AMT data on a non-DLA host Environment I/NET Site Cause Need for viewing DLA AMT data on a non-DLA host Resolution Yes. If you copy the InetAMT.mdb file (that was used on a DLA host) into the non-DLA host, you should successfully be able to view the AMT data. The difference will be that the Site column will not be visible and the new Link/Site Name column will be replaced by the Link Name.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1432 Views

What files are affected when performing the Repair function from DLA setup

Issue What files are affected when performing the Repair function from DLA setup? Environment I/NET site Cause What files are affected when performing the Repair function from DLA setup Resolution The files that are repaired when executing the repair function are all EXEs and DLLs only. Corrupt Netcon, AC, Sav, and config.dat files will not be repaired.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
977 Views

Can DLA functionality be used on all I/NET 2000 host revisions?

Issue Can DLA functionality be used on all I/NET 2000 host revisions? Environment I/NET site Cause DLA Functionality on older I/NET sites Resolution No. DLA functionality is not available for systems prior to I/NET 2000 revision 2.12.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1190 Views

Controllers have a Boot ROM revision. What is its purpose?

Issue Controllers have a Boot ROM revision. What is its purpose? Environment I/NET site with controllers Cause Controller in Boot state. Resolution The purpose of the Boot ROM is to allow dial-up capability with 06 emulated controllers when the controller is at the boot-state. This will allow the operator to download the bin file via dial.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1139 Views

If a controller is not being used for 06 emulation, does the Boot ROM revision need to be the same as the host revision?

Issue If a controller is not being used for 06 emulation, does the Boot ROM revision need to be the same as the host revision? Environment I/NET site Cause 06 Emulation Resolution No. Only needs to be the same when 06 emulation is being used.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
976 Views

When upgrading a system, are there any issues with ASC controllers whose revisions date back to pre I/NET 2000?

Issue When upgrading a system, are there any issues with ASC controllers whose revisions date back to pre I/NET 2000? Environment I/NET site Cause ASC Controllers before I/NET 2000 Resolution Should not be any issues. UPD files for all ASC controller revisions are included within I/NET 2000.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1081 Views

NPR and modems set up for integrated NPR dialing do not pose security risks to a network

Issue Can an NPR and modem setup for integrated NPR dial, allow a "back door" into a company's Ethernet lan (i.e. compromising their network security)? Environment I/NET site Cause NPR and modems set up for integrated NPR dialing do not pose security risks to a network Resolution The NPR will not talk to a PC unless it has I/NET running. This eliminates the possibility of using it as a "back door" to bypass network security measures.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1151 Views

There is no need to purchase NPRs in order to put I/NET on the local network

Issue Do I need to purchase NPR's to put I/NET on the local network? Environment I/NET site Cause Do I need to purchase NPR's to put I/NET on the local network? Resolution Your local I/NET host(s) merely need to have NIC (network interface cards) installed and working. You will need to obtain properly assigned, static IP addresses from the network administrator. The only time you will need an NPR, is if you have controllers in stand alone mode, with Ethernet connecting them to I/NET hosts. If you do not wish to have a host near the controllers, you can situate an NPR to act as an Ethernet tap
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1033 Views

How to set momentary duration (pulse duration) on a 7780?

Issue How to set momentary duration (pulse duration) on a 7780? Environment I/NET site Cause How to set momentary duration (pulse duration) on a 7780? Resolution Using a Hand Held Console: Press [Code], then type 07 and press [Enter] to set momentary duration. The current momentary duration in milliseconds displays. Enter the desired delay in milliseconds and press [Enter]. The range is 0-255 (0-2.55 seconds). For example, entering 100 from the HHC results in a one-second pulse to the relay to turn it On or Off. When using a standard 7780, the momentary duration value should be set to a minimum value of 10 (0.1 seconds).
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
1093 Views
  • « Previous
    • 1
    • …
    • 281
    • 282
    • 283
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of