How to set momentary duration (pulse duration) on a 7780?
  • How to set momentary duration (pulse duration) on a 7780?
  • sesa139513
    sesa139513
‎2018-09-06 03:13 PM
I/NET site
Using a Hand Held Console:
  1. Press [Code], then type 07 and press [Enter] to set momentary duration.
  2. The current momentary duration in milliseconds displays. Enter the desired delay in milliseconds and press [Enter]. The range is 0-255 (0-2.55 seconds). For example, entering 100 from the HHC results in a one-second pulse to the relay to turn it On or Off.
  3. When using a standard 7780, the momentary duration value should be set to a minimum value of 10 (0.1 seconds).
  • TAC INET