DC/DM points in subLAN devices

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • DC/DM points in subLAN devices
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
963 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

DC/DM points in subLAN devices

Picard Product_Support
‎2018-09-06 03:13 PM

Issue

Technical Support Services occasionally receives calls concerning the use of DC/DM points in the Micro Regulator product line. The use of DC/DM points in MRs is possible but only when certain guidelines are followed.

Environment

  • SubLAN controllers
  • MRs
  • UCs

Cause

The functionality of the DC/DM points depends on what is actually controlling the DC point. If you use any of the extensions that reside only in the MRI, MCI or I/SITE LAN, etc., to control the DC point you will not have a problem. These extensions include: Time Scheduling, Temperature Control, Calculations and Event Sequences . As long as one of these editors controls the state of the DC point you should not see a problem with the functionality of the DC/DM points. Where you run into trouble is when an MR resident editor controls the DC point. These include all of the modules found in the MR Resident DDC editor, (PID, Floating, Two Position, Relay, Reset, Calculation module). If the state of a DC point is controlled by any of the MR resident DDC modules the associated DM point will always alarm in one state or the other.

The same is true for the UCI/UC product line in that a DC point can not be controlled by a UC resident editor. This includes everything under the Unitary Control editor, (VAV, AHU, PID, FLT, HPMP ). In fact, currently if an attempt is made to enter a DC point in any of these editors an error is generated which will not allow such an entry, (this error is not generated in the MR Resident DDC editor).

Resolution

If you need positive feedback like that provided by the DC/DM points please follow the guidelines set below:

  1. Create Control Description and State Description Parameters: Refer to figure 1 and 2.
  2. Create an External DO point for Fan Control. Refer to Figure 3.
  3. Create an External DI point for Fan Status. Refer to Figure 4.
  4. Create an Internal DA Point for Fan Alarm. Refer to Figure 5. 
  5. Create a Calculation for the DA point: Refer to Figure 6.

Anytime the Fan Control DO and the Fan Status DI follow each other’s state, the calculation remains True. If the DO does not equal the DI State, then the calculation becomes False. This results in an Alarm after the Time Delay of the DA has been met. The Time Delay acts in the same manner as the Time to State for a DM point. Please note if the DI 0 state was ON (the opposite of the DO), the calculation would be P0=~P1 .

 

*MSG* 09/21/95 12:34:29 Thu Control descriptions and commands
Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798]
Enter up to 4 characters:
 # Description Command Delay
--+-----------+-------+-----
 0 STRT 1 0
 1 STOP 0 0
 2 0 0
 3 0 0
 4 0 0
 5 0 0
 6 0 0
 7 0 0
 8 0 0
 9 0 0
10 0 0
11 0 0
12 0 0
13 0 0
14 0 0
15 0 0

Figure 1: Control Description and commands

*MSG* 09/21/95 12:35:14 Thu State descriptions
Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798]
Enter up to 4 characters:
 # Description # Description
--+----------- --+-----------
 0 OFF 16
 1 ON 17
 2 ALRM 18
 3 NORM 19
 4 20
 5 21
 6 22
 7 23
 8 24
 9 25
10 26
11 27
12 28
13 29
14 30
15 31

Figure 2: State descriptions

*MSG* 09/21/95 12:36:19 Thu Resident I/O points
Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798] Point 0000 (02290000 DO)
Enter up to 16 characters:
Parameter Value Parameter Value
---------------------------------------- ------------------+--------
Point name Fan Control Distribution group 1
Point class Ext Distribution mask --------
Scan interval (seconds) 60 Alarm priority -
Global level Local Message priority -
State description 0 Cell number 0
Control description 0
Restart control action Reinforce
Minimum trip (minutes) 0
Minimum close (minutes) 0
Three-state output N

Figure 3: Resident I/O points

*MSG* 09/21/95 12:36:19 Thu Resident I/O points
Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798] Point 0000 (02290000 DI)
Enter up to 16 characters:
Parameter Value Parameter Value
---------------------------------------- ------------------+--------
Point name Fan Status Distribution group 1
Point class Ext Distribution mask --------
Scan interval (seconds) 10 Alarm priority -
Global level Local Message priority -
State description 0 Cell number 0
Number of bits 1
Supervision None

Figure 4: Resident I/O points

*MSG* 09/21/95 12:38:56 Thu Resident I/O points
Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798] Point 0009 (02290009 DA)
Enter up to 16 characters:
Parameter Value Parameter Value
---------------------------------------- ------------------+--------
Point name Fan Alarm Distribution group 1
Point class Int Distribution mask Y-------
Scan interval (seconds) 10 Alarm priority Priority
Global level Local Message priority Priority
State description 2 Cell number 0
Number of bits 1
Normal state 1
Alarm delay (seconds) 120
Supervision None

Figure 5: Resident I/O points

*MSG* 09/21/95 12:39:57 Thu Calculations
Host 00 (CSI) Link 02 [78020] DCU 29 [DCU 7798] Point 0009 (Fan Alarm)
Enter point address or name:
 Equation
---------------------------------------------------------------------------
P0=P1
Operand Point Operand Constant
-------+---------------- -------+----------------
P0 Fan Control
P1 Fan Status

Figure 6: Calculations

 

The above calculation will return the following DA conditions depending on the state of the DO and DI

DO DI DA
OFF OFF NORM
ON OFF ALRM
OFF ON ALRM
ON ON NORM
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1666
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of