Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 15
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2209 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 101
    • 102
    • 103
    • …
    • 111
  • Next »
Label: "Andover Continuum" Show all articles

When moving files to a new PC user can no longer edit them

Issue User has a backup of my files that they have restored onto a new workstation PC but now they are unable to edit the files.  For example: A Continuum graphic needs to be edited and cannot save changes but can save as a new graphic. Environment Window OS Windows XP Windows 7 8 8.1 10 Windows Vista Cause This is caused by Microsoft Windows OS. Windows will automatically make a file "Read only" if it has been moved from another PC  Resolution The solution is to change the files back to read / write. Example: Open Windows Explorer and find the folder you want to change, for this example it is "Continuum graphics." Right click on the folder and select properties, which shows a tab that will be ticked next to "read only" deselect this tab and then select apply. Once windows has finished changing the folder and its contents to read/write the user will be able to go into continuum and edit graphics.
View full article
Picard Product_Support
‎2018-09-06 10:14 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1165 Views

Command Window is flashing up when Continuum is running

Issue Command Window is flashing up when Continuum is running, the window has some text but flashes too quick to read Environment Windows 7 XP Command Dos Window Cause Following an upgrade (include new PCs) from a Stand Alone, pre v1.82 installation the Workstation within Continuum retains it's PE Programs Resolution Following an upgrade (include new PCs), Workstations PE Programs should be checked to see if they are still required. Stand Alone Utilities could be used for a number of tasks on pre v1.82 installations and included a number of PE programs calling batch files and SQL queries. If these PE Programs are still running following an upgrade, then they will be calling batch files and SQL queries that do not exist on the new PC. Disable or delete these programs NOTE: One way of seeing what is in the Command Window is to record the screen using a simple Screen recording program.
View full article
Picard Product_Support
‎2018-09-11 08:58 AM

Labels:
  • Andover Continuum
1406 Views

What is an ObjectID.

Issue What is the significance of the ObjectID number that appears under the properties of a Continuum object. Environment SQL Continuum ObjectID ObjectIDHi ObjectIDLo Cause Customer enquiry Resolution The ObjectID is a combined string that includes the SQL ObjectIDHi and the ObjectIDLo separated by a decimal. 
View full article
Picard Product_Support
‎2018-09-06 10:14 AM

Labels:
  • Andover Continuum
1222 Views

b3 Controller error log reports 0x00001427.

Issue Points from on b3 controller will not update on pinpoint graphics.  Environment b3 0x00001427 HardwareErr__ Bad RTC chip RTC Cause Error 0x00001427 denotes a hardware failure of the real time clock.  Resolution Return controller to Schneider Electric for repair.
View full article
Picard Product_Support
‎2018-09-06 10:13 AM

Labels:
  • Andover Continuum
956 Views

Continuum 1.94 SP1 Service Pack to address accdataserices.exe crashes and other issues

Issue See "mismatch xxxxxxxx" in the Continuum Error Listview. Product Line Andover Continuum Environment Continuum Windows XP Windows 7 Windows Server 2003 Windows Server 2008 Cause An Error logging feature was added with 1.94 SP1. If the Continuum Error Listview has "mismatch xxxxxxxx" errors, then SP1 for Cyber has been installed, but the controllers are posting errors. Resolution Use the updates below or the most recent version and the errors will no longer post. A Cyberstation 1.94 service pack released to address accdataservices crashes and other issues. The list of corrected issues is the release notes. The files are available on https://ecobuilding.schneider-electric.com/ 
View full article
Picard Product_Support
‎2018-09-11 12:47 PM

Labels:
  • Andover Continuum
2372 Views

Is it possible to customize the email message body of Reports that are emailed using ReportCmdLine.exe?

Issue Is it possible to customize the email message body of Reports that are emailed using ReportCmdLine.exe? Environment Continuum Cyberstation Outlook Cause Want to modify the email message body to include more information about the Report. The message in an Alarm that is being emailed can be changed with an email format file using XML tags, can the same thing be done with Reports being emailed? Resolution It's not possible to modify the email message body of an emailed Report.
View full article
Picard Product_Support
‎2018-09-06 10:13 AM

Labels:
  • Andover Continuum
1021 Views

Access events not being reported for one controller.

Issue All controllers are reporting access events except one. Environment SystemStatus Access Events Cause The InfinitySystemVariable SystemStatus was set to No Database. Resolution Once SystemStatus was set to equal Normal access events began to be reported from the controller.
View full article
Picard Product_Support
‎2018-09-06 10:13 AM

Labels:
  • Andover Continuum
980 Views

Unable to connect to b3xxx controllers with RoamIO.

Issue Unable to connect to b3xxx controllers with RoamIO. Environment RoamIO-1 RoamIO-2 Cause The RoamIO-1 is not able to communicate with BACnet controllers. It only supports Infinet controllers. Resolution The RoamIO will not be able to communicate with the BACnet controllers (bCX4040, b3xxx, etc...) you will need to use the RoamIO-2 that is able to communicate to both Infinet and BACnet.  
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1126 Views

ACX5740 does loses comm after power failure.

Issue Following a power failure, ACX 5740 controller loses communication. Cycling power with the controller battery removed recovers some but not all controllers. Environment ACX5740 ACX5720 1.1000037 Comm Loss Power failure Cause This problem was fixed in firmware version 1.100037. Resolution Upgrade ACX firmware to 1.100037 
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1434 Views

Errors when save to database -- error inserting into table

Issue Continuum throws  the following error when a save to database is performed on a controller -- Error inserting row into table. Environment SQL ContinuumDB Cause Duplicate Tables in the database. Resolution Restore backup of last known working database.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1156 Views

How to swap two infinet controller on the same system.

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue What is the proper procedure to use when swapping two previously installed Infinet controllers on the same Continuum network. Environment ACCID Infinet Controllers Cause Must prove determine whether an Infinet Controllers flow sensor is damaged. Resolution It is important to recommission Infinet controllers before relocating them in the same system. Recommissioning the Infinet controller purges all object handles and ensures that the controller will be brought on line virtually as a new "out of the box" controller. Infinet controllers are recommissioned by setting the InfinetID to 0 using a RoamIO. Using a RoamIO, set the InfinetID of both Infinet controllers to zero. Verify that the controllers InfinetID has been set to 0. With the workstation in OffLine mode, change the serial number of each controllers to a fictional serial number that does not exist in Continuum. Remove both controllers and install them in place of each other with out powering the controller. Before the controllers are powered, connect them to the Infinet bus while the bus is connected to the infinet port. Switch the workstation to Online Mode. Power up the controllers. Enter the correct serial number for each controller in the controller editor. Both controllers should come online. Reload both controllers.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1164 Views

Switching Windows Users

Issue Acc Data Service error when we switch users on a workstation with multiple user accounts. Environment Windows 7 Windows XP Windows 2008 Server Continuum  1.XX Cause You cannot open multiple Continuum instances simultaneously on a system. You cannot switch users and leave the cyber station running on one session and open another instance of Continuum under a different user on the same system without errors. Resolution You must close Continuum and log off of the system before another user opens another session.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1149 Views

Anti-Passback Protection option is not available

Issue The Anti-Passback Protection is not editable on Entry or Exit options page of door editor. Product Line Andover Continuum Environment Access control Anti-passback Cause In order to configure anti passback protection on either side of a door the door must have both an entry area and an exit area selected. Resolution Once an exit area is selected, the Anti-Passback protection option becomes selectable.
View full article
Picard Product_Support
‎2018-09-06 10:12 AM

Labels:
  • Andover Continuum
1462 Views

What is the operating environment of Continuum controllers

Issue What is the operating temperature / humidity of Continuum controllers Environment Continuum B3xxx i2xxx IO module ACX52xx ACX54xx CX9xxx Cause The operating Environment for the Continuum controller range Resolution The operating Environment for the Continuum controller range is as follows:   Temperature 32°-120°F (0-49°C)   Humidity 10-95% RH (non-condensing) This is the maximum Temperature and Humidity within the controller(s) enclosure, if the room is at 49°C then the temperature within the enclosure may be much warmer.
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Labels:
  • Andover Continuum
1319 Views

BCX1 goes offline when reloading the controller

Issue There are many BCX1 on the site. All of the BCX1s go offline when reloading the controller. Environment BCX1-CR B3 Continuum Cause Checking the system configuration and programming. The reasons listed below may cause significant traffic on the network. A lot of Polling value of points across controllers COV increment is set to zero Check all the numeric points' setpoint attribute including Runtime, DamperPosition, etc. as these change all the time. Points under b3 controllers are referenced by more than 32 devices. Device in the BACnet Device folder doesn't match the controller in infinity side.(Not deleted device from BACnet folder after replace the controller) When the special trunk with low quality cable  connect to BLink also cause this issue. Remove the problem trunk, the issue will be  gone When the heavy traffic happens on the network or some other issues , it will cause unexpected issues. Resolution Change the programs way, create a program in the BCX1 to mirror the referenced points in b3s Uncheck the setpoint attribute of all numerics except  temperature setpoint. Change the polling program flow type from looping to fall thru and trigger every minute or trigger by other digital point. Set the COV increments to a non-zero value After device replacement, delete the device from BACnet Device folder and find new BACnet device again, then send to database Remove the problem trunk from Blink or try to change the terminal resistor will  resolve this issue  After the steps above are done, the network should be stable and the BCX1 will no longer go offline when reloading.
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Labels:
  • Andover Continuum
1659 Views

Continuum may not start if McAfee Intrusion Detection is installed

Issue Continuum Workstation initialization resolved but will not start normally. Only a few executables start Environment Continuum Windows 7 McAfee Enterprise and Intrusion Detection Cause McAfee Intrusion Detection was installed and updated and after that Continuum would no longer start Resolution Removed McAfee Intrusion Detection, rebooted and then Continuum started normally
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Labels:
  • Andover Continuum
1429 Views

Software Licensing for Continuum 2.0 and StruxureWare Solution

Issue Software Licensing for Continuum 2.0 & StruxureWare Solution Product Line Andover Continuum, EcoStruxure Building Operation Environment Continuum Site integration with the StruxureWare Solution Continuum Cyberstation software & Licensing Cause Request for Software Licensing compared to the Hardware key.  Resolution There is a Ordering and Activation document available on the Buildings Exchange Download Center. A link is provided below: Ordering and Activation of Software License for Continuum v2.0 Software license is a dedicated license per workstation and locked to both the hardware and the operating system. Recommended not to install on old hardware. Software licensing is available for both new and existing installations after Continuum 2.0.  A Hardware key is required in order purchase a software license.  This is because the Continuum features and options are purchased with the physical Hardware key, not with the keyless license.   When purchasing the Keyless license, the serial number of the Hardware key is submitted along with a License Information file (c2v) that has been created on the workstation that is to be licensed.  The License Information file is created using the Hasp Key Utility.   Continuum installations pre version 2.0 (e.g. v1.94) who wish to upgrade to v2.0 and would like to benefit from Software Licensing feature must download and install the required files. Those are outlined in the document above. Note: For Continuum Interface for SmartStruxure Solution the demo StruxureWare Building Operation license has all required features. Your Continuum 2.0 key must have the Advanced Webserver feature enabled.You can use the Continuum Interface Server for any Continuum installation: Standalone or Multi-User (LAN). All existing Andover Continuum configurations are supported in the Continuum Interface Server.  
View full article
Picard Product_Support
‎2018-09-11 04:38 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
3865 Views

Unable to communicate with controller after correctly configuring and enabling Network Security.

Issue Controller comm is lost after enabling Network Security after properly configuring the Controller and Workstation. Environment Network Security NCII CX9680 ACX5740 ACX5780 Cause Network security activation was being inhibited by the domain user security policies. Resolution In this case both the controllers and Windows network security policies had been configured properly for Continuum.  This fact was confirmed when the IT department got involved.  Once they relaxed some of the security policies on this machine Continuum network security began to work as expected, both from the controller and Cyberstation point of view. The customers IT personnel did not share with us what policies were responsible for the activation issues.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1071 Views

Unable to reload or upgrade firmware on a controller.

Issue Controller drops offline when reloaded or when an attempt to flash firmware is made. Environment Infinet MSTP Cause Massive CRC errors on the MSTP bus due to a bad controller on one leg of blink. Resolution In this case the problem was due to a bad controller on the bus.  The offending controller was located by segmenting the bus to determine which legs were introducing this problem. Once it was determined which controller was causing this issue, the controller was removed and a replacement installed.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1163 Views

Infinity controller goes offline every five to ten minutes.

Issue BCX9680 controller goes offline every five to ten minutes then returns online. Environment Infinity Controller BCX NC CX Cause Duplicate IP address on the network. Resolution Give the controller a unique IP address.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1387 Views
  • « Previous
    • 1
    • …
    • 101
    • 102
    • 103
    • …
    • 111
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now