Supervised input reads only reads trouble.
  • Supervised input reads only reads trouble.
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 10:17 AM
With a 10K Ohm resistor wired across the controller input (at the controller) the supervised input reads trouble with the door switch in either the closed or open position.
  • UI
  • Supervised Input
  • IO Modules
  • 10K Ohm resistor
The input voltage selector switch was set to 5 volts instead of 10 volts.
Changed the voltage selector switch from 5 to 10 volts and power cycled the IO module.