Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2197 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 87
    • 88
    • 89
    • …
    • 110
  • Next »
Label: "Andover Continuum" Show all articles

Random "'Bit count not supported by system" access events reported.

Issue Valid card swipes sometimes successfully unlock the door and other times result in invalid attempts with the message "Bit count not supported by system" Environment CyberStation ACX7xx CX9900 CX9702 CX9680 ACX5740 ACX5720 Cause Random bit count not supported by system events typically indicate that the signal from the card swipe at the reader got corrupted on its way to the panel, this happens on very long runs (reader is too far from panel) or due to wiring issues and/or electrical noise interfering with the signal. Resolution Make sure the max distance from reader to panel has not been exceeded. (A Wiegand signal repeater may be used) Make sure the reader wire conforms to the specs in the controller's installation guide. Eliminate any source of electrical noise that may be interfering with the card swipe signal on its way to the panel.
View full article
Picard Product_Support
‎2018-09-06 12:31 PM

Labels:
  • Andover Continuum
1934 Views

Password Reset ACX 57XX

Issue Unable to log into the Controllers web page. How do I reset the Password on  a ACX5740 from the Continuum front end? Environment Continuum  1.8X Continuum 1.9X ACx57XX Cause Password Unknown Resolution Open Continuum Explorer Expand the Network Select the ACX 57XX Select the Controller User folder Edit the ACC user and reset the password. 
View full article
Picard Product_Support
‎2018-09-06 12:31 PM

Labels:
  • Andover Continuum
3232 Views

How to test an Infinet bus using a volt meter.

Issue What voltage should be seen across conductors on an Infinet bus? Environment Infinet RS-485 Cause Communication issues on RS-485 bus. Resolution  Measuring Ground Potential Signal Potential refers to the horizontal plane along which signals are sent and received with respect to ground.  RS-485 requires that all devices communicating with each other be at a reasonable ground potential. Measuring the ground potential of any Infinet controller Use a voltmeter to measure between the earth ground connection (for power) and the Infinet shield connection.   Measuring the ground difference between the Infinet controller and the ground at the InfiLink or CX/NetController (shield grounding point). Set the multi meter to measure AC voltage; measure and record the AC voltage (ACV) between + and -. A reading higher than 2-3 volts indicates a grounding problem. Set the multi meter to measure DC voltage; measure and record the DC voltage (DCV) between +and -. A reading higher than 2 to 3V on either voltage indicates a grounding problem. Calculate the combined voltage using the following formula. (1.4 X ACV) + DCV = Combined Voltage. If the combined voltage is greater than 7 a grounding problem exists
View full article
Picard Product_Support
‎2018-09-06 12:31 PM

Labels:
  • Andover Continuum
1961 Views

Output turns ON uncommanded

Issue InfinityOutput that has been set to ON by a schedule and then set to OFF manually (or from a Graphics) randomly turns back to ON Environment All CXs All i2s All b3s Cause Anything that causes the schedule to get re-evaluated will set the output value from the schedule. Resolution To take control of the output away from the schedule set the output state to disabled. To return the output to schedule control set its value backup to the schedule value and re-enable it.
View full article
Picard Product_Support
‎2018-09-06 12:31 PM

Labels:
  • Andover Continuum
1160 Views

Upgrading from SX8000 to Cyberstation 1.93

Issue When upgrading from SX8000 to Cyberstation 1.93,  with over 600 reports for SX8000 that need to be upgraded to Cyberstation. Environment Cyberstation LAN or StandAlone Cause A site has been running SX8000 and is upgrading to Cyberstation 1.93. There are over 600 reports that the customer wants upgraded to Cyberstation. Resolution There is no auto-conversion program that will upgrade the reports from SX8000 to Cyberstation. Keywords will be an issue. There are over 600 reports that must be upgraded manually. There is no automatic upgrade for reports.
View full article
Picard Product_Support
‎2018-09-06 12:31 PM

Labels:
  • Andover Continuum
1099 Views

Epibuilder Dynamic Text fields are not displaying the correct attribute values.

Issue The DynamicText fields on the card are not displaying the correct attribute information.   The DynamicText fields that displays Info1 information is displaying the value from another attribute. Environment Continuum EpiBuilder Cause Data fields mislabeled in Personnel Manager. Resolution Correct the labeling of the data fields in Personnel Manager > Configure > Customize attributes.
View full article
Picard Product_Support
‎2018-09-06 12:30 PM

Labels:
  • Andover Continuum
1141 Views

SQL Server errors when installing Cyberstation.

Issue Installing Cyberstation on a Standalone workstation results in SQL Server errors. Environment Cyberstation Standalone. Cause Installing Cyberstation on a StandAlone workstation returns the error "Another version of SQL is installed." The Standalone had Windows 7 installed. Resolution On the Windows 7 workstation, select  Start  > All Programs > System Tools > System Restore.   Select a restore point that pre-dates the Cyberstation install. Once the system has been successfully returned to that restore point, reinstall Cyberstation.
View full article
Picard Product_Support
‎2018-09-06 12:30 PM

Labels:
  • Andover Continuum
1311 Views

Unknown Error received when searching records using the Personnel Manager

Issue On a database with a large number of personnel records, an 'Unknown error' is received when searching personnel using Personnel Manager Environment Continuum Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause There is a default maximum limitation to the number of records that can be display when searching for records using Personnel Manager. The default maximum is set to 50. If you attempt to increase this number in the New Search screen in Personnel Manager it reverts back to 50. Resolution In order to allow a higher number to work around this error, perform the following steps: Shut down Cyberstation Make a copy of the existing PersonnelManagerCtrlDll.Config (C:\Program Files\Continuum\Common) Use Textpad or Notepad and open the PersonnelManagerCtrlDll.Config file Change the number in the line SearchSection MaxSearchResult=50 (Change this to a larger number closer to the max search results you would expect from the site) Too large of a number can affect system performance of the search. Restart Cyberstation Note: Repeat this procedure for each Cyberstation as needed.
View full article
Picard Product_Support
‎2018-09-06 12:30 PM

Labels:
  • Andover Continuum
1084 Views

Continuum Security Key Failure.

Issue LED on Continuum Security Key goes out after it has been running for a hours or days. Cyberstation shuts down sometime after the LED has stopped illuminating. Environment Cyberstation Continuum Security Key USB Cause Computer hardware failure. Continuum Security Key failure. Resolution Test the Security Key in another Cyberstation PC.
View full article
Picard Product_Support
‎2018-09-06 12:29 PM

Labels:
  • Andover Continuum
1309 Views

Can not see BACnet IP XDriver points in the BACnet view

Issue After doing a "Find new BACnet" devices (or device discovery) none of the BACnet IP X Driver points can be found. Environment BACnet IP X-Driver As used in ACX5740, ACX5720, NC2 (Netcontroller II) to map data between Continuum points and BACnet. Cause The X Driver has 2 modes of operation: Client mode or Server mode, points can only be viewed externally in Server mode. Resolution When using the BACnet IP XDriver you must always first create a Device Self object point as a type 200, this will define the parameters for the BACnet device itself. This allows the device itself to be found in the BACnet view of any BACnet Operator Workstation.   For points with type 0 (BACnet Client), these are not seen in the BACnet view as they are Continuum points that have the BACnet data mapped into them for use within Continuum. For points to be seen in the BACnet view they have to be Type 1 or 2 in a BACnet Server mode.
View full article
Picard Product_Support
‎2018-09-06 12:29 PM

Labels:
  • Andover Continuum
1343 Views

Password Encryption in Continuum

Issue Need to know if Continuum account passwords are encrypted Environment Cyberstation and webClient (all versions) Cause No cause - information only. Resolution Continuum passwords are encrypted with an algorithm. Being salted and hashed before being saved in the Continuum Database.
View full article
Picard Product_Support
‎2018-09-06 12:29 PM

Labels:
  • Andover Continuum
1006 Views

Find new BACnet devices from the root does not find bCX or b3 devices.

Issue Find new BACnet devices from the root does not find bCX or b3 devices. ACCTrace reveals CyberStation is not sending WHOIS message even though Cyber is enabled for BACnet. Environment CyberStation bCX b3s Cause CyberStation not sending WHOIS message. Resolution After rebooting, CyberStation sent out WHOIS message and found the devices.
View full article
Picard Product_Support
‎2018-09-06 12:29 PM

Labels:
  • Andover Continuum
1309 Views

Commissioning first generation Continuum Controllers

Issue When NC9900 is commissioned it does not hold the configuration settings even though the changes have been saved to the controllers configuration page. Environment 1st Generation Controllers CMX 9924 CX 9900, 9901, 9940 Cause Proper controller commissioning procedure was not followed. Resolution When commissioning a first generation network controller, the controller must be rebooted (power shut off and then power restored) once the changes have been made to the controller configuration via a PC using a terminal emulation application.
View full article
Picard Product_Support
‎2018-09-06 12:29 PM

Labels:
  • Andover Continuum
1551 Views

Controller goes offline randomly.

Issue Communications from CyberStation to controller is flaky, controller goes offline during reload or while an object is under edit. Controller can be pinged consistently and access via the configuration web page works fine. Opening/editing objects randomly result in communication timeout errors. Environment CyberStation All CXs Cause Controller is online with two Continuum databases at the same time. Example: In a LAN system  with the controller is configured in the SQL server DB, a lap top running stand alone Continuum is connected to perform some troubleshooting, the controller exists in the SA database residing in the lap top. Resolution The controller MUST only be online with one ContinuumDB. Close Continuum on the machine that is looking at the second database.
View full article
Picard Product_Support
‎2018-09-06 12:29 PM

Labels:
  • Andover Continuum
2316 Views

Opening Video Monitor without an alarm

Issue At times there is a need to see video monitor without triggering an alarm Environment Continuum Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause Video Monitor is triggered by an alarm Resolution There is a work around solution to this issue that is provided as is without any additional support. By default, Video Monitor is launched by triggering an alarm. Work around: 1. Use TAC.VideoLaunch.exe arguments being the objectidhi and objectidlo. It can be launched from the Continuum shell or a graphic. The following example is from a button on a graphic. 2. Locate the objectidhi and objectidlo by right clicking on the door or point and select properties (This can be copied and pasted) 3. In the case of a graphic, paste the objectidhi and objectidlo into the text field. 4. Save the button and run the graphic.  5. Click on the button and video will be launched, but not playback an event. You will be able to search on video by time and see live video for 2 cameras.
View full article
Picard Product_Support
‎2018-09-06 12:28 PM

Labels:
  • Andover Continuum
1117 Views

"Select CASE" function will not check in a Plain English program.

Issue Can not save a PE Program in Continuum controller. Environment Cyberstation and CX controllers BasedOn and Case statements Cause Not all keywords and functions are supported in all controllers. Resolution When using keywords and inbuilt Plain English functions always verify it is supported by the controller you are using. The "Select CASE" statement is only supported by the Cyberstation programs, if programming a controller use the BASEDON function that has a similar format and is supported by all controllers.
View full article
Picard Product_Support
‎2018-09-06 12:28 PM

Labels:
  • Andover Continuum
1829 Views

Issue capturing personnel photo from USB camera in Create/Edit badge dialog.

Issue In the 'Make/Edit Badge' dialog of the personnel manager/editor, selecting 'Capture Photo' but nothing happens. USB camera device works fine from an application other than Continuum. Environment CyberStation Cause The photo image source has not been properly selected. Resolution In the 'Tools' menu select 'Set Photo Image Source' menu item then select the camera device and click OK. Clicking the 'Capture Photo' button works once the camera has been selected as the source.
View full article
Picard Product_Support
‎2018-09-06 12:28 PM

Labels:
  • Andover Continuum
1535 Views

Getting Access errors when editing objects in controller (i.e. system variables) after controller converted from 9900 to 9680

Issue Immediately after conversion from 9900 to 9680 an attempt to edit a system variable from the Continuum Explorer causes an access denied error Environment CyberStation CX9680 Cause Conversion process was not completely successful Resolution In the Continuum Explorer change the controller type to 9681, when the warning comes up that this is irreversible click OK Change the controller type backup to 9680, when the warning comes up that this is irreversible click OK
View full article
Picard Product_Support
‎2018-09-06 12:28 PM

Labels:
  • Andover Continuum
1041 Views

Multiple OPC servers configuration

Issue Can two (or more) OPC servers be configured to get information from the same Continuum system? Environment CyberStation OPC Server Infinity CX controller. Cause General configuration Resolution Yes, multiple OPC servers can be configured to get information from the same Continuum system. It is recommended that each OPC server runs in its own computer and uses a different CX as its primary controller.
View full article
Picard Product_Support
‎2018-09-06 12:28 PM

Labels:
  • Andover Continuum
1586 Views

What are the minimal CyberStation user rights to see video in a VideoLayout?

Issue Need to know minimal CyberStation user rights for security guards to be able to see video in a VideoLayout object launched from Pinpoint. Environment CyberStation VideoLayouts (as opposed to VideoMonitor) Cause When trying to give security officers the right to click on a graphic object to open up a video layout. What Continuum security rights do they need to do this? Resolution Tested with v1.93. The minimal rights (keys in the Security editor application) to see video in a VideoLayout appears to be the following: 1. Run Graphics Editor. 2. VideoServer, View . 3. VideoLayout, View 4. VideoLayout, General Page You need a hotspot on a menu page to open a Pinpoint graphic. That graphic has a button to open a VideoLayout.
View full article
Picard Product_Support
‎2018-09-06 12:27 PM

Labels:
  • Andover Continuum
1291 Views
  • « Previous
    • 1
    • …
    • 87
    • 88
    • 89
    • …
    • 110
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore