Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2197 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 86
    • 87
    • 88
    • …
    • 110
  • Next »
Label: "Andover Continuum" Show all articles

Pin Code or general code not working from access control keypad

Issue Pin Code or general code not working from access control keypad Environment Continuum access control Keywords: Pin Code, general code, #, 8 bit burst Cause Pin Code or general code not working from access control keypad. Resolution The 4 numbers in the PIN code or General Code need to be followed by the # key When personnel are created with no PIN number they are allocated "0" but this does not work at a PIN code. The PIN number must be changed from non "0" before it will work. The PIN number does not need to be 4 digits long (ACX57 only fully tested) The keypad/ reader used must provide an 8 bit burst wiegand output.
View full article
Picard Product_Support
‎2018-09-06 12:36 PM

Labels:
  • Andover Continuum
1598 Views

CyberStation can not connect to the database.

Issue Launching Continuum results in error "This workstation is currently unable to connect to the database. Click OK to exit." Also, running Continuum DB initialization results in error: SQL Server [server name] does not exist or access denied. Workstation Setup Failed! Please try again or click Cancel to exit. Environment CyberStation LAN system Cause Fire wall on the server machine is blocking TCP port 1433 Another cause for this happening is a Windows firewall or McAfee firewall being enabled and blocking the IP of the 2nd Cyberstation that is trying to connect. Resolution Disable fire wall at the server or add an exception for TCP port 1433 (or the port used by the client to get access to the server if different).
View full article
Picard Product_Support
‎2018-09-06 12:36 PM

Labels:
  • Andover Continuum
2624 Views

Recovering a Continuum database without a SQL Backup (BAK) from the ContinuumDev.MDF and ContinuumLog.LDF files.

Issue A hard drive failure on the LAN SQL server or on a Stand Alone workstation is preventing Cyberstation from starting. Environment LAN Server and StandAlone workstations Cause A hard drive failure on the LAN SQL server or on a Stand Alone workstation is preventing Cyberstation from starting. The site does not have a verified SQL backup of the database. The raw data files, typically named ContinuumDev.mdf and ContinuumLog.ldf, can be recovered. Resolution For a standalone, use the Microsoft SQL Server 2005 Management Studio Express. The freeware SQL front end is much easier to use than the command line. The Microsoft SQL Server 2005 Management Studio Express will also allow you to administer SQL 2000 MSDE databases. The Management Studio Express can be downloaded for free from Microsoft using the link below. http://www.microsoft.com/downloads/details.aspx?FamilyID=c243a5ae-4bd1-4e3d-94b8-5a0f62bf7796&DisplayLang=en  This procedure assumes that the Continuum database no longer exists on the SQL Server. It is also critical that SQL is up and running.  If the SQL Server or StandAlone workstation hard drive has crashed, SQL must be reinstalled on a functioning workstation before attempting to attach the raw data files. See the link below for the steps to attach the db using the SQL Management Studio Express http://msdn.microsoft.com/en-us/library/ms190209.aspx  This links to an article that describes how to attach the data files and of the log files for a database running Microsoft SQL Server 2005, SQL Server 2000, or SQL Server 7.0 database. http://support.microsoft.com/kb/224071
View full article
Picard Product_Support
‎2018-09-10 07:54 AM

Labels:
  • Andover Continuum
1441 Views

WebPinpoint cannot be installed on client machine.

Issue WebPinpoint is not successfully installing on client machine during initial graphic launch. Environment WebClient WebPinpoint Cause Client PC has been locked down by customers IT department. Resolution Ask the customers IT department to open up security on the client machine until the WebPinpoint installation is completed.  Once WebPinpoint has installed the security setting on the client machine can be restored. On Windows 7 machines, set User Account Settings to minimum until WebPinpoint has completed its initial installation. 
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • Andover Continuum
1263 Views

Alarms are not clearing from the Active Alarm View when they Return To Normal and are Acknowledged.

Issue Alarms are not clearing from the Active Alarm View when they Return To Normal and are Acknowledged. Environment Continuum Cyberstation Cause The "To Normal" Transition is not being sent to the recipient Workstation. Resolution Confirm that the "To Normal" transition events are configured to be sent to the recipient Workstation. In your EventNotification objects: Go to the Recipients tab. For each recipient Workstation, check the "To Normal" transition entry.
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • Andover Continuum
1623 Views

Alarm printer is printing one alarm per page.

Issue Even though the "Suppress form feeds when printing alarms" option is selected in the Workstation Preferences, alarm printer is printing only one alarm per page. Environment CyberStation Alarms Printer Cause The alarm printer is issuing a form feed at the end of every alarm message. Resolution If the "Suppress form feeds when printing alarms" option is set to true in the Workstation Preferences, this issue has to be handled at the printers internal settings by adjusting the page length and other settings. 
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • Andover Continuum
1468 Views

"Improper Use of Operand error" in a Plain English Program.

Issue A program turns on an output based on a comparison of a door's forced entry attribute and the value of a schedule numeric.  The program is disabling and throws an error. Environment AC1 AC1 Plus Plain English CyberStation Continuum Cause An Infinity Numeric and the Forced Entry attribute of a Continuum door object are incompatible value types.  Resolution Use an If/Then/Else expression to evaluate the value of the doors Forced Entry attribute, and the Infinity Numeric's value separately.  Then Switch the state of the output based on the result of the evaluation. Original Code   If (AHCASECACC100A ForcedEntry and PerimeterDoors) then Goto AlarmOutputOn Corrected Code   If (AHCASECACC100A ForcedEntry = True) and (PerimeterDoors = On) then Goto AlarmOutputOn
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • Andover Continuum
1623 Views

Maximum Import Export entries in Infinet or a CX controller

Issue How many IE entries can Continuum controllers have? Environment CX controllers Infinet controllers Cause Limitations of IE entries in Continuum controllers Resolution Infinet controllers = 255 CX level controllers = 65535
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • Andover Continuum
1011 Views

WebPinpoint tries to install again with each new client session.

Issue WebClient installs and runs normally until the client session is terminated.  On the next client session WebClient goes through an install process as if WebClient had never been installed. Environment WebClient WebPinpoint Cause WebPinpoint appears to uninstall at the end of each client session.  Deleting WebPinpoint folders and registry keys do not resolve this issue. Resolution This issue was resolved by uninstalling WebClient on the webserver, including deleting the folder structure and associated registry keys and then reinstalling WebClient.
View full article
Picard Product_Support
‎2018-09-06 12:33 PM

Labels:
  • Andover Continuum
1605 Views

AAON VAV bacnet device will not come online

Issue Cannot being AAON bacnet device online in Continuum Environment Continuum Bacnet AAON Cause The baud rate wasn't being detected by the AAON device Resolution Set the baud rate in the AAON device to auto detect
View full article
Picard Product_Support
‎2018-09-06 12:33 PM

Labels:
  • Andover Continuum
1324 Views

Unable to add second Workstation to Single-user installation. Receive SQL error "SQL Server PC_Name\SQLEXPRESS does not exist or access denied"

Issue Unable to add second Workstation to Single-user (SU) installation. Receive SQL error "SQL Server PC_Name\SQLEXPRESS does not exist or access denied" Environment Continuum Cyberstation SQL Express Cause SQL Server was not configured properly for remote connections. Resolution Follow the steps in the Microsoft article on how to enable the correct protocols and open the firewall to allow these connections. http://msdn.microsoft.com/en-us/library/ms345343.aspx
View full article
Picard Product_Support
‎2018-09-10 11:05 AM

Labels:
  • Andover Continuum
1507 Views

Eaton IP BACnet Lighting Panels go offline with error "Communications failure due to routing device not available"

Issue Eaton IP BACnet Lighting Panels are successfully discovered via the Find BACnet Devices but then go offline with error "Communications failure due to routing device not available" Product Line Andover Continuum Environment CyberStation Cause IP BACnet level Eaton devices configured with network number other than zero Resolution Set the network number to zero for all Eaton lighting panels. Then they will stay online.
View full article
Picard Product_Support
‎2018-09-06 12:33 PM

Labels:
  • Andover Continuum
2214 Views

How to log data in Continuum only when a point changes

Issue Instead of logging a value on a set time interval, can I only log the value when it changes? Product Line Andover Continuum Environment Logging - all controller types. Time Interval = 0 Log value on change. Semi Automatic logging. Cause When working with strings, date times or Plain English comms drivers, it is often required to only log a value on change. How can this be achieved? Resolution Create the point in the usual way. On the "Logs" tab, enter the number of log entries required. Select "Log Instantaneous." Leave all of the Time intervals at 0. The controller will now log a new value every time the point value changes and all log entries move down 1 position. This is often called Semi Automatic logging. Note: This logging method is not related to time in any way, however creating an Infinity DateTime point and writing to that with the Date system variable when the point is updated would allow the time / date of the change to be recorded.
View full article
Picard Product_Support
‎2018-09-06 12:32 PM

Labels:
  • Andover Continuum
1683 Views

Cyberstation Locks Up

Issue Cyberstation locks up and becomes unresponsive. Environment CyberStation WebClient Cause Problem with OS or computer hardware. Resolution Reformat the workstations hard drive and or install a new operating system that is supported by the current version of Cyberstation. Backup the Continuum Database. Reinstall Cyberstation. Run Continuum Database Initialization an initialize the workstation. 
View full article
Picard Product_Support
‎2018-09-06 12:32 PM

Labels:
  • Andover Continuum
1152 Views

How to keep a door unlocked until after the door closes.

Issue After a valid door unlock, Continuum, by default, turns off the door lock output one second after the door opens when a door switch is used. How can this sequence be modified? Environment ACX AC1 Cause Due to the locking hardware used, sometimes it is necessary to make sure the door is closed before energizing the maglock. Resolution Use a Plain English program as follows: ' File Name: LONGLOCK.TXT ' Program name: LongLockProgram ' '   This program keeps the door strike energized until after the door '   closes. This is needed for certain types of door hardware. Normally, '   the door strike is de-energized 1 second after the door is physically '   opened. ' ' Flowtype: Looping, Autostart 1:   If Door1 ValidAccess is On then Goto 3   If Door1 ExitRequest is On then Goto 2 2:   If Door1 DoorSwitch is Opened then Goto 3   If TS > Door1 DoorStrikeTime then Goto 1    ' in case the door doesn't get opened 3:   Door1 = UnLocked   If Door1 DoorSwitch is Closed then Goto 4   If TS > 60 then Goto 4    ' safety 4:   If TS >=1 then    Door1 = Locked    Goto 1   Endif
View full article
Picard Product_Support
‎2018-09-06 12:32 PM

Labels:
  • Andover Continuum
1165 Views

Cyberstation is sluggish or freezes with AUDIOP~1.EXE at or near 100% CPU usage.

Issue Following upgrade of CyberStation, two of the workstations freeze up.  Task Manager shows AUDIOP~1.EXE at 99% CPU utilization. Environment Cyberstation WebClient WebServer Cause CyberStation cannot resolve an audio file link in an AlarmEnrollment or EventNotification. Resolution Review all AudioFile references linked in all AlarmEnrollments and EventNotifications. Verify files referenced on the PC exist in the path location shown in the object editor. Repair or remove invalid audio file references from all AlarmEnrollments and all EventNotifications.
View full article
Picard Product_Support
‎2018-09-06 12:32 PM

Labels:
  • Andover Continuum
1267 Views

Comm issues between BCX and a remote controller (guard shack).

Issue Communication between the guard shack controller was working after installation but the controller has since lost communication with the master controller.  Communication to controller could not be reestablished. Environment BCX Wireless Cause Weak wireless mesh due to the quantity and proximity of nearest controllers. Resolution Install wireless repeaters to strengthen the wireless mesh.
View full article
Picard Product_Support
‎2018-09-06 12:32 PM

Labels:
  • Andover Continuum
1472 Views

What is the part number ( part# ) of the i2814's output fuse?

Issue The output fuse of the i2814 is replaceable at the site and want to purchase them from our iPortal website. Environment i2814 Infinet controller Cause The output fuse blows out at the site and want to replace the fuse at the site. Resolution The i2814's output fuse is " FUSE NANO W/SOCKET 1/8A 125V ", and its part# ( part number / part # ) in Schneider Electric iPortal website is 01-2180-005 . 
View full article
Picard Product_Support
‎2018-09-06 12:32 PM

Labels:
  • Andover Continuum
1411 Views

Photographs for personnel in webclient

Issue Can photos be added to personnel using webclient? Environment Continuum Webclient Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause Webclient is mainly a viewer and doesn't have the ability with some features for editing.  There isn't a way from a Webclient browser PC to add or edit photos for personnel. Resolution Personnel photos must be added using Cyberstation personnel editor or personnel manager and may then be viewed in a webclient browser session.
View full article
Picard Product_Support
‎2018-09-06 12:32 PM

Labels:
  • Andover Continuum
1029 Views

Net Controller UTC offset

Issue Net Controller time is off by 5 hours. Environment Continuum LAN and StandAlone Cause Network object UTC offset did not match the Net Controller UTC offset. Resolution Ensure the Network object UTC offset matches the Net Controller UTC offset when both are in the same time zone. Right click on the Network object in the Cyberstation Object Tree to set the Network
View full article
Picard Product_Support
‎2018-09-06 12:31 PM

Labels:
  • Andover Continuum
1657 Views
  • « Previous
    • 1
    • …
    • 86
    • 87
    • 88
    • …
    • 110
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore