Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2029 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 93
    • 94
    • 95
    • …
    • 102
  • Next »
Label: "TAC Vista" Show all articles

How many imported projects may you have in TAC XBuilder?

Issue How many imported projects may you have in TAC XBuilder? Environment TAC XBuilder Cause There is a limit set in the software Resolution You can not have more than 10 other projects imported into Xbuilder.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • TAC Vista
1271 Views

Alarm Message stating "TACSERVER-______: Offline" comes into the Vista server regularly

Issue Alarm Message stating "TACSERVER-______: Offline" comes into the Vista server regularly Environment Vista Server Xenta Server Vista Classic network Cause When a site has multiple Xenta Server or Vista Server revisions, this alarm will periodically occur as result. Resolution Upgrade all Xenta controllers to the same revision Ensure that this revision matches the revision of the Vista Server.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • TAC Vista
1490 Views

License requirement for Excel Reports in Vista 5.1.X

Issue A specific license module is required for running reports in Excel from TAC Vista Environment Microsoft Excel 2003 / 2007 / XP Report generator : Report Generator...........................000882231 Report Generator – Upgrade..................000883231 Report Generator – 1 year subscription ..........000884230 TAC Vista version 5.1.X  Cause A separate license module for Vista Reports Generator is included in some license packages, but is sometimes required to be ordered separately if Reports are required as a feature. Resolution Part no 000882231 is for the Report Generator license in Vista version 5.1.X.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • TAC Vista
1370 Views

Is it possible to use an analog valve on the TAC Xenta 121-FC even if I want to have the LED mode indicator on a STR-101 through STR-107?

Issue When using STR101 to STR-107 connected to a TAC Xenta 121-FC, the LED Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC, which is the only analog output on the TAC Xenta 121-FC device. Environment TAC Xenta 120-FC STR-101 STR-102 STR-103 STR-104 STR-105 STR-106 STR-107 Cause When using any of STR-101 to STR-107 connected to a TAC Xenta 121-FC, the LED Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC device, which is the only analog output on the TAC Xenta 121-FC device. Resolution In ZBuilder, it is possible to move the Status LED from the default location at Y1 to K1-4. In this case you also need to have an external power supply with 5 Volt DC for the LED indicator. It is also possible to use 24 Volt AC power supply for the LED indicator, however this will make an incorrect temperature reading of about 0.5 degree C. In this case, add a 5 kΩ resistance (4.7 - 5,1 kΩ) ¼W in one of three possible positions: Between G and KC1 Between K1 and LED 16 Between Mx 15 and M. The resistor must be placed outside the STR device.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • TAC Vista
1211 Views

Is it possible to change the colors for the alarm list in Webstation?

Issue Is it possible to change the colors for the alarm list in Webstation? Environment TAC Vista Webstation 5.1.x   Cause The colors for the alarm list in Webstation are inherited from Vista Workstation.  Resolution To change the colors for the alarm list in Webstation change the colors for the alarm list in Workstation and Webstation will inherit the colors. Change the colors in workstation: Right click on a alarm in the alarm list and open the properties for it. Go to "Customize". Click on the "Text" tab. Change the color. Open the "File" menu and "Save My Program Settings"
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • TAC Vista
1248 Views

Trendlogs don't work after changing PC.

Issue PC was changed - for example because of a PC crash. Restored Vista and log backups. After that, logged data can be read, but no new values are logged. Environment Vista 5.1.7 Cause Vista 5.1.7 was installed and started on the new computer then the time on the computer was set to a future date by the IT department. During the time the PC clock was set to the future date values were logged. Then the time was set back to present time. The problem now is that "Next log time" will be potentially far in the future so no log will be logged until that date.   Resolution Correct the PC time Restore the log backup and Vista backup again Start Vista
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • TAC Vista
971 Views

Xenta Servers use a 10 Base T network port at 10Mbits/sec, half duplex

Issue Some managed switches have settings that have to be configured to match the communications type and speed of the connected devices. Environment Xenta 511, 527, 527-NPR, 555, 701, 711, 721, 731, 911, 913 Cause Some managed switches have to be configured to match the communications type and speed of the connected devices. Resolution Most switches automatically detect the speed and configuration of the connected devices. However, for those site where these configurations must be manually configured, the specs below should be noted. All Xenta Servers use a standard 10 Base T network port. These ports operate at 10 Mbits/sec. and are half duplex.
View full article
Picard Product_Support
‎2018-09-06 12:09 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
1584 Views

Vista Report not saving on hard disk when scheduled to run

Issue When you setup a time event object to run a Vista report and save it to the hard drive on the local PC no file is saved, even though you can run the report manually. Environment Vista Reports Cause In the report the path to where the report needs to be saved is incorrect. The report will not create a new directory if the directory does not exist. A error will be logged in the $log folder of the database in the b0warlog.txt file. The text will look like this Tue Jun 26 10:28:46 2012 report  >>could not be saved Report report-report,  hRes=[-2146827284} Resolution Correct the path to were the report is to be saved or create the folder that matches the report save path.
View full article
Picard Product_Support
‎2018-09-06 12:09 PM

Labels:
  • TAC Vista
974 Views

Vista - User Group Alarm

Issue No alarms when specific users are logged in No alarms from specific Change of State Environment Vista Cause User Group Alarm are used when you want specific users to be able to see specific alarms.  For an example a Alarm control bound to a specific User Group - Alarm will only send its alarm to users added to User Group Alarm. Resolution To create a User group Alarm right click on root and choose add Add object User Group Alarm Add object User Group Add a Vista User Right click on the created User group and add the Vista user Right click on the User Group - Alarm and add the User Group. At Root right click on the Alarm control object and navigate to tab "user" and add the User group Alarm Now only the users added to the User Group - Alarm can see the alarm handled by this Alarm control object.
View full article
Picard Product_Support
‎2018-09-06 12:09 PM

Labels:
  • TAC Vista
1065 Views

No alarm file is created when an alarm is trigged in Vista.

Issue The system is set up to create an alarm file when certain alarms is trigged but no file is created. Environment TAC Vista 5.1.7 Cause For a alarm file to be created when an alarm is set a object called "Alarm Receiver - File" must be created that object must be connected to a "Alarm Control" object, then the alarm which should trigger the file must be connected to that  "Alarm Control" object. The alarm was connected to the wrong "Alarm Control" object.   Resolution Make sure the alarm is connected to the correct "Alarm Control" object.
View full article
Picard Product_Support
‎2018-09-06 12:08 PM

Labels:
  • TAC Vista
1289 Views

When previously offline BACnet devices go back online, will the Xenta 913 try to poll them again?

Issue When previously offline BACnet devices go back online, will the Xenta 913 try to poll them again? How does Xenta 913 poll BACnet devices that have been offline? The Xenta 913 doesn't poll all the BACnet objects when previously offline BACnet devices go back online Environment Xenta 913 BACnet Cause All objects the BACnet objects that can't be polled (are offline) during a poll are moved to a "failed queue". " Every 30 seconds a task moves one input and one output object from the "failed queue" to a different queue so that they will be retried next poll. This is all hardcoded and the 30 seconds timer cannot be changed.   Resolution If you wait long enough, all of the BACnet objects will be polled again. If many devices have been offline, this will take a while though.
View full article
Picard Product_Support
‎2018-09-06 12:08 PM

Labels:
  • TAC Vista
1167 Views

"Not set" shown in the name column after upgrading to database layout version 2.

Issue "Not set" shown in the name column after upgrading to database layout version 2. Environment TAC Vista 5.1.7 or newer SQL taclogdata database layout version 2.0 Cause The "Name" column is a new column introduced in Vista 5.1.7 with the new database layout, so when a database is upgraded no name is added as there is no contact with Vista. Once Vista is running and a value is logged to the trendlog the name will be updated in the "Name" column to the same name as shown in Vista. Resolution No resolution required as the name will be updated once a log value is logged to the log database.
View full article
Picard Product_Support
‎2018-09-06 12:08 PM

Labels:
  • TAC Vista
1006 Views

What mode should be used in a zone when the area is not in use?

Issue What operation modes should be used in zone control then the area is not being used? Environment Xenta 121 FC Xenta 121 HP Cause The TAC Xenta 120 device does not have any internal clock. The actual operation modes has to be sent from another device such as a Xenta 401. The following values could be sent to the nviManOccCmd SNVT: 0=OC_OCCUPIED 1=OC_UNOCCUPIED 2=OC_BYPASS 3=OC_STANDBY other values=OC_NUL 255=OC_NUL Resolution Normally, OCCUPIED mode is used when there are people in the zone. During night time, or short periods without people in the zone STANDBY may be used. If someone enters the area and triggers a motion detector or presses the Bypass button, the mode changes to BYPASS. UNOCCUPIED mode is most appropriate if the area is no longer rented or during some other long period without anyone in the area.
View full article
Picard Product_Support
‎2018-09-06 12:08 PM

Labels:
  • TAC Vista
1086 Views

Does TAC Vista Support for trending based on the COV (Change of Value)?

Issue Does TAC Vista Support for trending based on the COV (Change of Value)? Environment TAC Vista Cause Other BMS systems support COV for trending. Does TAC Vista support the same? Resolution No, TAC Vista do not have any provision to trend based on COV. It is only possible based on time interval.
View full article
Picard Product_Support
‎2018-09-06 12:07 PM

Labels:
  • TAC Vista
971 Views

Setpoint value changed after performing a download of a XBuilder project into a Xenta Server.

Issue A change is made to a public signal in TAC Vista Workstation, which was created in a Xenta Server XBuilder project, changed back to the initial value after performing a download to this Xenta Server. Environment Xenta Servers (Xenta 511, Xenta 515, Xenta 555, Xenta 527, Xenta 701, Xenta 711, Xenta 721, Xenta 731, Xenta 913) XBuilder Tested with Windows Server 2003, Window XP SP3 Cause If a path name is changed of a signal, for example, change the "the site name" folder name to another name, Vista consider this change as a major change, and Workstation will not be able to find the new path of the signal. Therefore, the signal will return to the initial value which is initialized in the Menta object. Resolution Suggestion is making all the infrastructure change at the beginning if you can. If there is a need to change the path, make sure all the initial values are reflect to the current values in Workstation. Then, make the download to the Xenta Server.
View full article
Picard Product_Support
‎2018-09-06 12:07 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
2040 Views

Some users are unable to see I/NET values on a graphics page displayed in a 527

Issue Some users are unable to see I/NET values on a graphics page displayed in a 527 Environment Xenta 527 TGML Cause User permissions on the 527 must allow the user to access the I/NET links that are being displayed Resolution Log out of the 527 Log in as the root user In the Configuration folder, select User administration Modify the user that was having issues. Click on the ".." link at the top of the folder list till you are in the root folder Click on the "inet" link to modify permissions of the I/NET folder Give the user read and read/write access Save changes
View full article
Picard Product_Support
‎2018-09-06 12:07 PM

Labels:
  • TAC INET
  • TAC Vista
1324 Views

How do TAC Vista server logs affect the performance of the server?

Issue How do TAC Vista server trend logs affect the performance of the server and LON network? Environment TAC Vista server LON Network Cause The bandwidth of the LON network is for all communication on the LON wires to share. This includes all graphics, object transfers, etc. Resolution The bottleneck is the communication to the lon network. Depending on what interface (LTA) you are using Vista can handle about 15-40 read/writes per second. Many Vista Server trend logs would increase the amount of information being sent out on the wire and if there is a sufficient number of them, you may see some delays on other forms off communication: i.e., graphics, object transfers, etc.
View full article
Picard Product_Support
‎2018-09-06 12:07 PM

Labels:
  • TAC Vista
1270 Views

How many characters can a comment field in TAC Menta have?

Issue How many characters can a comment field in TAC Menta have? Environment TAC  Menta Cause How many characters can a comment field in TAC Menta have? If you exceed this length, the application may not work as expected. Resolution There can be 30,000 characters.
View full article
Picard Product_Support
‎2018-09-06 12:07 PM

Labels:
  • TAC Vista
1319 Views

Is it possible to send the reports by email based on schedule.

Issue Is it possible to send the reports by email based on time schedule. Environment TAC Vista Reports Cause Vista does not provide any email functionality for sending Reports.  Some third party applications may exist to do this but have not been tested. Resolution There is no provision in Vista to send reports by email, it is only possible to generate the reports manually or based on schedule which is available within the Vista Reports function.
View full article
Picard Product_Support
‎2018-09-06 11:13 AM

Labels:
  • TAC Vista
1384 Views

Xenta 102-AX displaying strange data in Vista 5.1.6

Issue When creating a Xenta 102-AX in Vista 5.1.6 the UCPTprogramversn and UCPTapplicVersn is ignored and all SNVT/SCPT PROPERTY_OFFSET values have incorrect values causing incorrect value readings and incorrect default values.  The PROPERTY_OFFSET value is offset by 12. Xenta 102-AX devices that are in LNS networks display correct values in LonMaker or NL-220 and only display incorrectly in Vista. Environment Vista Workstation LonMaker NL-220 102-AX Cause A change in the way Vista handles XIFs in Vista 5.1.6 inadvertently caused it to display incorrect values. Resolution Hotfix 12 for TAC Vista 5.1.6 should be downloaded from the Extranet and installed. From the Buildings Business Extranet Navigate to Products > TAC Vista > Vista Software > TAC Vista 5.1.6 > Hotfixes. Hotfix 12 can be applied following the steps below: Before installing the hotfix, Vista Workstation and Server should be shut down. Double-click the hotfix executable file to install. Once the hotfix is installed rebrowse the 102-AX XIF file into any devices that were experiencing the issue by right-clicking the 102-AX device in Vista Workstation and selecting Properties. Then select the XIF File tab and click the ellipses next to the source file. Reselect the 102-AX XIF file and click OK. It may be necessary to refresh the screen to begin seeing correct values.
View full article
Picard Product_Support
‎2018-09-06 11:13 AM

Labels:
  • TAC Vista
1311 Views
  • « Previous
    • 1
    • …
    • 93
    • 94
    • 95
    • …
    • 102
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore