Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2197 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 78
    • 79
    • 80
    • …
    • 110
  • Next »
Label: "Andover Continuum" Show all articles

Unknown model number error when learning I2/b3 device

Issue Performing an automatic learn or manually commissioning i2/b3 device results in the error "Unknown model number" ACCTrace shows a model number zero Product Line Andover Continuum Environment CyberStation CX/bCX I2/B3 Cause This error can be caused by communication issues. Resolution Verify field bus is properly terminated if required. Follow standard Infinet/MSTP troubleshooting techniques to solve any communication problems inducing the unknown model error.
View full article
Picard Product_Support
‎2018-09-06 01:12 PM

Labels:
  • Andover Continuum
2049 Views

Drop down fields are no longer showing in Personnel Manager

Issue Drop down fields are no longer showing the drop down menu or any fields to select in Personnel Manager Environment Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause There is a limitation set for the number of entries and if this is exceeded they will no longer show. Resolution By default the number of drop down entries is set to a maximum number of entries of 1000. This is usually an ample number of these types of fields, but if more are needed then do the following: Find the file PersonnelManagerCtrl.dll.config in C:\program files\Continuum\Common Edit this file in a text editor and find the entry called GridComboMaxEntries="1000" Restart Cyberstation for this setting to take affect, repeat for each Cyberstation. Caution: This is not an unlimited number and can affect system performance, increase this in small increments i.e. 10-25.
View full article
Picard Product_Support
‎2018-09-06 01:12 PM

Labels:
  • Andover Continuum
1035 Views

Triac output of i28xx controller gets damaged when controlling the TriState Triac output.

Issue PE program in i28xx controller controls the VAV with TriState Triac output, and the Triac output gets damaged randomly. Environment i2 controller ( i28xx , i28xx-V ) with Triac output. Cause The output channel can get damaged / burned when Triac output value is changed to +ON from -ON ( or to -ON from +ON ) without setting the output value to OFF before the change. Resolution Check the VAV control PE program and make sure the program sets the Tri-state Triac output value to OFF before changing it to the opposite value.
View full article
Picard Product_Support
‎2018-09-06 01:12 PM

Labels:
  • Andover Continuum
945 Views

Triac outputs on b3867.

Issue Customer has an application to control a heat pump and would like to use the b3867. The concern is that the triac outputs switch the 24v common, not the 24v hot. Most heat pumps will expect the 24v hot to be switched not the 24v common that is grounded. An interposing relay could be used on these outputs but it is more cost effective (both labor and materials) if the relay could be eliminated.   Environment b3867 Cause Customer has an application to control a heat pump and would like to use the b3867. The concern is that the triac outputs switch the 24v common, not the 24v hot. Most heat pumps will expect the 24v hot to be switched not the 24v common that is grounded. An interposing relay could be used on these outputs but it is more cost effective (both labor and materials) if the relay could be eliminated. Resolution In this case a relay will be required.   The i2 controller technical reference does not specifically mention that you cannot switch X1 (hot) but the output terminal block on the controller itself has the following label: "Note: Triac outputs must switch the grounded leg only. See manual." If the load was wired on the X2, the hot leg (X1) would be shorted to ground and the load would not see 24V.
View full article
Picard Product_Support
‎2018-09-06 01:12 PM

Labels:
  • Andover Continuum
1619 Views

How to mass change object attributes with dump file import.

Issue Need to change the same attributes of a large number of the same object class all at once. Environment Continuum Cause Some object attributes are not able to be modified from a Listview. What is a method to change these attributes? Resolution In the example below we will be modifying the InfinityInput objects LogType, Size, and LogIntervalSecs attributes to change the logging parameters using the "Import from Dump File" method. Before importing anything backup the database, do this now. Go into Offline Mode. Use a ListView to get all the inputs you want to modify. This could be All_Inputs but I'd suggest creating a new one that has the same fields and maybe a filter to weed out the inputs you do not want to change. (you can also use the default listview and just select the inputs you want to modify) In the Listview; select "Edit -> Select All" and the "Object -> Send To -> Text File...". Give the file a name and press Save. Edit your Dump file with Notepad++ or similar text editor and change the fields that you want to change. Search and Replace may save time. Save the file. In ContinuumExplorer; go to the Root, Right-click and select "Import Into..." and select the file you just modified. This will import the Dump file and overwrite the objects with your changes. Checking the Distribution Properties window you will find that there may be errors about duplicate channel numbers - disregard this for now. Go back into Online mode. Confirm the changes have been applied by rerunning the ListView. Select your inputs that were changed and Right-click "Send to -> Controller" to send these changes down to the controller.
View full article
Picard Product_Support
‎2018-09-06 01:12 PM

Labels:
  • Andover Continuum
1712 Views

Controller reload only takes a few seconds, does not work but generates no error.

Issue When reloading a controller the Distribution Properties displays: timestamp "The operation 'Reloading objects to Controllers' is starting. then just 5-10 seconds later timestamp "The operation 'Reloading objects to Controllers' is finished. The reload is not successful. Environment CyberStation All controllers Cause The "Send to Controller" Options are not set correctly. Resolution In ContinuumExplorer select  Options >> Send to Controller Options... In the Send to Controller Options dialog box change the Source Object Options from "Do not reload attached objects" to either of the other two choices, depending on whether or not you want to reload just the network controller (Reload attached objects, but not attached controllers) or you want to reload the network controller and all of its field controllers (Reload attached objects and controllers). Note: The last choice may take a long, long time depending on the size of the system. That option is rarely used as it resets all field controllers at once, and then reloads them one at a time.  The first option (Do not reload attached objects) only reloads the controller's dictionary - not the full objects/attributes. 
View full article
Picard Product_Support
‎2018-09-06 01:11 PM

Labels:
  • Andover Continuum
1139 Views

Maximum Cable Length Between ACX and Card reader

Issue What is the maximum cable length between a card reader and an ACX controller?   Environment Continuum ACX controllers (all versions) Cause -none- Resolution The ACX controllers support Wiegand, ABA, or CardKey readers, and the maximum cable lengths are 500 ft. (152.4 m) using 18 AWG cable or 200 ft. (60.96 m) using 22 AWG cable.
View full article
Picard Product_Support
‎2018-09-06 01:11 PM

Labels:
  • Andover Continuum
1820 Views

Exclamation point on a Continuum BACnet controller object indicates 'requires flash backup'

Issue The Save to Flash exclamation point (bang) shows on a Continuum BACnet controller object. Hovering over the icon, a tooltip comes up indicating that the controller 'requires flash backup'. However when performing a backup to flash, a result comes back that the 'controller doesn't need flash backup' and the exclamation icon remains. Re-loading the controller and performing a send to database have no effect. Product Line Andover Continuum Environment bCX4000 bCX4040 B3 Field Devices Cause Controller's restart mode not configured to use cool start (cool start = restoring DB from flash backup) Resolution Set controller's ACCRestartMode system variable to one of the modes below that includes cool start. The available re-start modes are (except in the b3885 and b3885-V): ACCWarmStartOnly (0) ACCCoolStartOnly (1) ACCWarmToCool (2)
View full article
Picard Product_Support
‎2018-09-06 01:11 PM

Labels:
  • Andover Continuum
1462 Views

How to stop a Workstation from receiving Device Offline alarms.

Issue Do not want a particular Workstation to receive Device Offline alarms. Environment Continuum Cyberstation Cause Device offline alarms are not to be delivered to specific Workstations. Resolution There are a couple methods that can stop these alarms from being delivered: You can stop all alarms from being delivered temporarily by; R-click Continuum icon in task bar, select Properties, and un-tick "I want this Workstation to receive alarms in this session". This will stop all alarms from being delivered to this Workstation until it is re-enabled or you log off then back on. Stop this Workstation from receiving just Offline alarms. Browse to the Templates folder and open the ControllerStatus EventNotification, remove this Workstation from the Delivery tab. It will no longer receive any alarms from offline Devices (this included Workstations and Controllers).
View full article
Picard Product_Support
‎2018-09-06 01:11 PM

Labels:
  • Andover Continuum
1330 Views

Getting error "Unable to lock an object because it is already locked" when saving a workstation program.

Issue Unable to save any program in a workstation giving error  "Unable to lock an object because it is already locked"   Environment Cyberstation Programs Cause This is usually caused by the FiringOrder attribute being locked, often due to a PC crash or other unexpected operating system shutdown. Resolution This is due to the firingorder attribute being locked, start the Continuum Command Line application, select the problem workstation from the network button. At the R> enter: firingorder editlock = false This should clear the edit lock and allow the programs to be saved. **Check to make sure that another program that accesses this program is not disabled.
View full article
Picard Product_Support
‎2018-09-06 01:10 PM

Labels:
  • Andover Continuum
1674 Views

How many indexes are used in SQL versions for Continuum?

Issue Certain versions of Cyberstation use a different number of indexes by default. Environment Continuum Microsoft SQL Server Cause Some IT departments like to know how many indexes are used in their application databases Resolution 1. The amount of indexes used is based on Cyberstation version To see the number of indexes and additional information use Enterprise Management Studio to run a query on the Continuumdb select * from sys.indexes 2. Additional indexes can be created by DBAs for optimization and performance reasons, but these are not the defaults.
View full article
Picard Product_Support
‎2018-09-06 01:10 PM

Labels:
  • Andover Continuum
1237 Views

Logging and Alarms are not working on Modbus RTU X Driver points

Issue When creating Modbus RTU X Driver points any alarms attached to them or logging set up do not operate at all. Environment Modbus RTU X Driver All  XDriver enabled controllers Cause The Modbus RTU X Driver is a Poll on demand X Driver which means it is not within the normal Controller Scan process, so alarms and logging will not update. Resolution As these points are outside of the controller Object Management System (OMS) these functions do not update. Built into the X Driver is the capability to put an Annex point in the parameter 6 that will be updated along with the X Driver point, these annex points can then be alarmed or have logging attached as they are within the OMS and the controller scan process. See the Modbus RTU manual for full details on setting up annex points.
View full article
Picard Product_Support
‎2018-09-06 01:10 PM

Labels:
  • Andover Continuum
1337 Views

bCX goes offline when trying to reload (transaction timeout)

Issue bCX4040 has trouble staying online, taking a reload. Environment bCX4040 Cause BCX4040 is shown online in web browser but offline in Continuum. When resetting the controller from web browser, the controller comes online for a short time in Continuum but unable to take a reload (transaction time out). Also, it's not showing up when performing find new BACnet device. Resolution There's more than one issue that can cause this symptom. In this case the controller error log had over 5000 entries in less than 2 days. All the same error: 1 W 10/09/2011 22:26:55.26 0x00001408 0x04e51900 0x02111cfe 0x000001fc 0x00000e48 The '1408' corresponding error text is 'Not enough memory'. There was a T-tap on the bCX's MSTP -  for another enclosure with b38xx controllers, approximately 25 meters away. Once reconnected as a daisy-chain the problem was solved.
View full article
Picard Product_Support
‎2018-09-06 01:10 PM

Labels:
  • Andover Continuum
2167 Views

SiteScan schedule configuration.

Issue Several fields appear edit locked or grayed out in SiteScan schedules. Environment SiteScan Cause Schedules are operating as designed. Resolution The fields that are grayed out appear so because of the event type selected. Each event type selected in a SiteScan schedule restricts or allows specific combinations of data to be manipulated.  
View full article
Picard Product_Support
‎2018-09-06 01:10 PM

Labels:
  • Andover Continuum
1138 Views

Using an Xdriver on comm4 of a CX 9200 may not work

Issue CX 9200 comm4 has 5 wires instead of 3, so the wires have to be jumpered to work with RS-485 Environment CX 9200 Xdriver Cause The issue with comm4 is that it is a 4 wire RS-485 interface and the xdriver ends up attempting to decode its own messages Resolution Sometimes this scenario will work, but other times values do not come across properly. Alternatives for this would be:  Use a media converter which may do a better job of jumpering the signal Move the xdriver to a different port
View full article
Picard Product_Support
‎2018-09-06 01:10 PM

Labels:
  • Andover Continuum
1208 Views

Can Personnel Manager profiles be linked to Personnel objects

Issue A university customer has two personnel "types" - faculty/staff and student. They would like to link a different Personnel Manager profile to each type of personnel so that when the record is edited it opens using that profile. Can this be done? Environment CyberStation Personnel Manager Cause A university customer has two personnel "types" - faculty/staff and student. They would like to link a different Personnel Manager profile to each type of personnel so that when the record is edited it opens using that profile. Can this be done? Resolution Unfortunately, this is not a feature in the current (v1.93) or older CyberStation versions. You can open the Personnel Manager and then switch to a different profile and enter the personnel data, but that profile is not linked to the saved record. So, subsequent editing of the record will open in the default (current) profile.
View full article
Picard Product_Support
‎2018-09-06 01:10 PM

Labels:
  • Andover Continuum
1127 Views

Fields are grayed out in object's editor and there is an asterisk between the class name and the object name.

Issue Unable to edit an object because fields are grayed out. Environment CyberStation Cause Object is edit locked. When an object is opened for edit the object is locked in order to give the process editing the object exclusive access to it. If an object editor shows an asterisk next to the name it indicates that the object is current under editing by another process. Resolution Wait for the process that has a lock on the object to complete. If the object is locked because of an unexpected Continuum shutdown while the object was under edit follow these steps to unlock it: In the Continuum Explorer right click the object's name and select properties. In the Current Status tab, click on the 'Force Object to Unlocked' button. Click OK to exit.
View full article
Picard Product_Support
‎2018-09-06 01:09 PM

Labels:
  • Andover Continuum
1415 Views

Database Initialization Program Cannot Create a Database on the Server.

Issue Database Initialization Program Cannot Create a Database on the Server. Environment CyberStation v1.93 SQL Server 2008 R2 Windows 7 Pro Workstation Cause Database Initialization Program Cannot Create a Database on the Server. Resolution Server install went fine. CyberStation install went fine on new Windows 7 Pro Workstation. Could "see" server from the workstation. One or more of the items listed below maybe necessary to solve the problem: -Configure Write permissions on the server, specifically the folder where SQL server was installed.  -Make the workstation and the database server members of the same domain. -If using Windows Workgroup make sure the Workgroup in both the SQL server and the workstation machine have the same name, also make sure the user name and password is the same on both machines. -In the Continuum Database Initialization, in the server name field, enter the server's IP address instead of the name. -Also try creating another Windows user
View full article
Picard Product_Support
‎2018-09-06 01:09 PM

Labels:
  • Andover Continuum
1191 Views

Controller locks up when trying to update OS on CX9640

Issue Tried to flash uprev the controller.  Continuum indicates "Initializing" but will go no further.  Environment BCX9640 Cause Unknown Resolution Method 1 Upgrade controller firmware using a RoamIO Method 2 Create a test Stand Alone Continuum DB. Bring the problem controller online on the test cyberstation. Flash uprev controller.
View full article
Picard Product_Support
‎2018-09-06 01:09 PM

Labels:
  • Andover Continuum
1011 Views

What are the card number restrictions associated with various access card types.

Issue Personnel distributions failing due to illegal card numbers configured in personnel objects. Environment CyberStation Personnel Objects Cause Each card type has restrictions as to what site codes can be used and the maximum card number that can be used.  Resolution  The following is a summary of card types and the site codes and card numbers that are available to each. Card Format Site Code Card Number Wiegand26 0 – 255 (8-bit) 0 – 65535 (16-bit) Infinity_37 0 – 4095 (12-bit)    0 – 524287 (19-bit) HIDCorp1000_35 0 – 4095 (12-bit)  0 – 1048575 (20-bit) CustomWiegand 0 - 65535 (16-bit)    0 – 4294967295 (32-bit)   Note: Site codes of 0 cannot be entered through the old style Personnel Editor, use Personnel Manager or set attributes through a list view.
View full article
Picard Product_Support
‎2018-09-06 01:08 PM

Labels:
  • Andover Continuum
1104 Views
  • « Previous
    • 1
    • …
    • 78
    • 79
    • 80
    • …
    • 110
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore