Issue
The Save to Flash exclamation point (bang) shows on a Continuum BACnet controller object. Hovering over the icon, a tooltip comes up indicating that the controller 'requires flash backup'. However when performing a backup to flash, a result comes back that the 'controller doesn't need flash backup' and the exclamation icon remains. Re-loading the controller and performing a send to database have no effect.
Product Line
Andover Continuum
Environment
- bCX4000
- bCX4040
- B3 Field Devices
Cause
Controller's restart mode not configured to use cool start (cool start = restoring DB from flash backup)
Resolution
Set controller's ACCRestartMode system variable to one of the modes below that includes cool start.
The available re-start modes are (except in the b3885 and b3885-V):
- ACCWarmStartOnly (0)
- ACCCoolStartOnly (1)
- ACCWarmToCool (2)