Exclamation point on a Continuum BACnet controller object indicates 'requires flash backup'
  • Exclamation point on a Continuum BACnet controller object indicates 'requires flash backup'
  • AbeMeran
    AbeMeran
‎2018-09-06 01:11 PM
The Save to Flash exclamation point (bang) shows on a Continuum BACnet controller object. Hovering over the icon, a tooltip comes up indicating that the controller 'requires flash backup'. However when performing a backup to flash, a result comes back that the 'controller doesn't need flash backup' and the exclamation icon remains. Re-loading the controller and performing a send to database have no effect.
Andover Continuum
  • bCX4000
  • bCX4040
  • B3 Field Devices
Controller's restart mode not configured to use cool start (cool start = restoring DB from flash backup)
Set controller's ACCRestartMode system variable to one of the modes below that includes cool start.
The available re-start modes are (except in the b3885 and b3885-V):
  • ACCWarmStartOnly (0)
  • ACCCoolStartOnly (1)
  • ACCWarmToCool (2)
  • 6384
100% helpful (1/1)