Triac output of i28xx controller gets damaged when controlling the TriState Triac output.
  • Triac output of i28xx controller gets damaged when controlling the TriState Triac output.
  • SangKim
    SangKim
‎2018-09-06 01:12 PM
PE program in i28xx controller controls the VAV with TriState Triac output, and the Triac output gets damaged randomly.
i2 controller ( i28xx , i28xx-V ) with Triac output.
The output channel can get damaged / burned when Triac output value is changed to +ON from -ON ( or to -ON from +ON ) without setting the output value to OFF before the change.
Check the VAV control PE program and make sure the program sets the Tri-state Triac output value to OFF before changing it to the opposite value.
  • 6357
100% helpful (1/1)