Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,840
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 329
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 505
    • 506
    • 507
  • Next »

TS-57XX-85X and TS-67XX-85X 10K thermistor with 11 K shunt resistance table

Issue TS-57XX-85X and TS-67XX-85X 10K thermistor with 11 K shunt resistance table Environment Unknown Environment Cause Unknown Cause Resolution Temp (°C) Temp (°F) Ohms (11K shunt)   -40.0°     -40.0°   10,517   -39.0°     -38.2°   10,489   -38.0°     -36.4°   10,460   -37.0°     -34.6°   10,430   -36.0°     -32.8°   10,397   -35.0°     -31.0°   10,364   -34.0°     -29.2°   10,329   -33.0°     -27.4°   10,292   -32.0°     -25.6°   10,254   -31.0°     -23.8°   10,214   -30.0°     -22.0°   10,172   -29.0°     -20.2°   10,129   -28.0°     -18.4°   10,084   -27.0°     -16.6°   10,037   -26.0°     -14.8°   9,988   -25.0°     -13.0°   9,938   -24.0°     -11.2°   9,885   -23.0°     -9.4°   9,830   -22.0°     -7.6°   9,773   -21.0°     -5.8°   9,715   -20.0°     -4.0°   9,654   -19.0°     -2.2°   9,592   -18.0°     -0.4°   9,527   -17.0°     1.4°   9,460   -16.0°     3.2°   9,391   -15.0°     5.0°   9,320   -14.0°     6.8°   9,247   -13.0°     8.6°   9,171   -12.0°     10.4°   9,094   -11.0°     12.2°   9,015   -10.0°     14.0°   8,933   -9.0°     15.8°   8,850   -8.0°     17.6°   8,764   -7.0°     19.4°   8,677   -6.0°     21.2°   8,587   -5.0°     23.0°   8,495   -4.0°     24.8°   8,402   -3.0°     26.6°   8,307   -2.0°     28.4°   8,210   -1.0°     30.2°   8,111   0.0°     32.0°   8,012   1.0°     33.8°   7,910   2.0°     35.6°   7,807   3.0°     37.4°   7,702   4.0°     39.2°   7,595   5.0°     41.0°   7,489   6.0°     42.8°   7,380   7.0°     44.6°   7,270   8.0°     46.4°   7,160   9.0°     48.2°   7,048   10.0°     50.0°   6,937   11.0°     51.8°   6,825   12.0°     53.6°   6,711   13.0°     55.4°   6,597   14.0°     57.2°   6,483   15.0°     59.0°   6,369   16.0°     60.8°   6,255   17.0°     62.6°   6,141   18.0°     64.4°   6,027   19.0°     66.2°   5,912   20.0°     68.0°   5,798   21.0°     69.8°   5,686   22.0°     71.6°   5,572   23.0°     73.4°   5,460   24.0°     75.2°   5,348   25.0°     77.0°   5,238   26.0°     78.8°   5,127   27.0°     80.6°   5,018   28.0°     82.4°   4,909   29.0°     84.2°   4,802   30.0°     86.0°   4,696   31.0°     87.8°   4,591   32.0°     89.6°   4,487   33.0°     91.4°   4,385   34.0°     93.2°   4,284   35.0°     95.0°   4,184   36.0°     96.8°   4,086   37.0°     98.6°   3,989   38.0°     100.4°   3,894   39.0°     102.2°   3,800   40.0°     104.0°   3,707   41.0°     105.8°   3,617   42.0°     107.6°   3,528   43.0°     109.4°   3,441   44.0°     111.2°   3,355   45.0°     113.0°   3,271   46.0°     114.8°   3,189   47.0°     116.6°   3,107   48.0°     118.4°   3,028   49.0°     120.2°   2,951   50.0°     122.0°   2,875   51.0°     123.8°   2,801   52.0°     125.6°   2,729   53.0°     127.4°   2,658   54.0°     129.2°   2,588   55.0°     131.0°   2,521   56.0°     132.8°   2,455   57.0°     134.6°   2,390   58.0°     136.4°   2,327   59.0°     138.2°   2,266   60.0°     140.0°   2,206   61.0°     141.8°   2,148   62.0°     143.6°   2,091   63.0°     145.4°   2,036   64.0°     147.2°   1,982   65.0°     149.0°   1,929   66.0°     150.8°   1,878   67.0°     152.6°   1,827   68.0°     154.4°   1,779   69.0°     156.2°   1,732   70.0°     158.0°   1,685   71.0°     159.8°   1,640   72.0°     161.6°   1,597   73.0°     163.4°   1,554   74.0°     165.2°   1,513   75.0°     167.0°   1,472   76.0°     168.8°   1,433   77.0°     170.6°   1,395   78.0°     172.4°   1,359   79.0°     174.2°   1,322   80.0°     176.0°   1,287   81.0°     177.8°   1,253   82.0°     179.6°   1,220   83.0°     181.4°   1,188   84.0°     183.2°   1,157   85.0°     185.0°   1,126   86.0°     186.8°   1,097   87.0°     188.6°   1,068   88.0°     190.4°   1,040   89.0°     192.2°   1,013   90.0°     194.0°   987   91.0°     195.8°   961   92.0°     197.6°   936   93.0°     199.4°   912   94.0°     201.2°   888   95.0°     203.0°   865   96.0°     204.8°   843   97.0°     206.6°   821   98.0°     208.4°   800   99.0°     210.2°   780   100.0°     212.0°   760   101.0°     213.8°   741   102.0°     215.6°   722   103.0°     217.4°   704   104.0°     219.2°   686   105.0°     221.0°   669   106.0°     222.8°   652   107.0°     224.6°   636   108.0°     226.4°   620   109.0°     228.2°   605   110.0°     230.0°   590   111.0°     231.8°   576   112.0°     233.6°   561   113.0°     235.4°   548   114.0°     237.2°   534   115.0°     239.0°   521   116.0°     240.8°   509   117.0°     242.6°   496   118.0°     244.4°   484   119.0°     246.2°   473   120.0°     248.0°   462   121.0°     249.8°   451
View full article
Picard Product_Support
‎2018-09-06 02:31 PM

on ‎2018-09-06 02:31 PM

Labels:
  • Field Devices
1510 Views

Which NEMA 4 classed DuraDrive actuators can be used with the VB-7323 diverting valves

Issue NEMA 4 classed DuraDrive actuators cannot be used with the VB-7323 diverting valves Environment NEMA 4 DuraDrive actuators VB-7323 diverting valves Cause Which NEMA 4 classed DuraDrive actuators can be used with the VB-7323 diverting valves Resolution There are no NEMA 4 solutions available. Consider using the MA-318 or 481 for two position applications. No modulating spring return options are available but non-spring return gear train actuators with AV-391 (150 pound plungers) can be used when the AM-363 gasket is added.
View full article
Picard Product_Support
‎2018-09-06 02:30 PM

on ‎2018-09-06 02:30 PM

Labels:
  • Field Devices
1493 Views

Having set Link Addressing in a Sigma DNN3 can no longer communicate to the DNN3 and Link Addressing does not work.

Issue Set-up the Link Addressing using the Pocket Terminal (LA +) for port 1 via the DNN3 service port and set port 2 on the DNN3 to be Serial PPP.  Can't communicate to the DNN3 from the Sigma server and global data is not being passed between the two VLAN's. Environment Multiple Sigma controllers across at least two Ethernet VLAN's.  DNN3's (version 1.h) connected to each VLAN. Each DNN3 is connected to the VLAN via port 1 and port 2 is configured as a 'virtual' serial PPP port but not connected to a device. Cause No routing information (static routes) entered into the DNN3's.   Although Link Addressing can be correctly configured the DNN3 devices also need to know where to transmit the point to point global data, that is the router device for the local Ethernet VLAN or default gateway. By having two ports configured on the DNN3 network routing messages RIP will be enabled and broadcast and will advertise the port 2 address as a potential but false route off the network, therefore RIP must also be disabled.  Resolution Using Pocket Terminal or Windows Hyperterminal enter a default Static Route to the DNN3 via its service port.  Use the generic entry 0.0.0.0/0 for the destination sub-LAN and mask.  For example; SR+ 0.0.0.0/0 192.168.1.253   1      (Where 192.168.1.253 is the default gateway and 1 is the DNN port number). RIP must also be disabled on the DNN3 port 1.  For example; RIPD 1
View full article
Picard Product_Support
‎2018-09-06 02:19 PM

on ‎2018-09-06 02:19 PM

Labels:
  • Satchwell BAS & Sigma
1684 Views

A new lookup table used on a Sigma Analogue Output (AO) Object does not work

Issue Created a new lookup table for an analogue output (AO) object to provide 10% steps and not 1% steps.  Displaying the object value always shows 1% steps. Environment Sigma Controller (All Versions) Cause The analogue output object value is the input value for the lookup table and the output of which is then passed to the A to D converter and then to the physical output. Resolution The value can be seen by a multimeter connected to the physical output. If the value of the output needs to be displayed via the Sigma front end then a programmable object is required to process the lookup table and then cross referenced to a standard analogue output object (with the default lookup table). Example of programmable object: 10 Xflo = POINT 0|51 20 YFLO = LOOKUP (1812, XFLO) 30 RETURN VIA TEXT 92 VALUE YFLO Where POINT 0|51 is the control/input object and 1812 is the lookup table number.
View full article
Picard Product_Support
‎2018-09-06 02:16 PM

on ‎2018-09-06 02:16 PM

Labels:
  • Satchwell BAS & Sigma
1297 Views

ModBMS will not allow an OPC Client to write OPC DA values to Sigma.

Issue ModBMS will not allow an OPC Client to write OPC DA values to Sigma. But, reading the ModBMS/Sigma values does work. Environment Sigma 4.04 and below ModBMS OPC Client Cause ModBMS uses the DDE functions to read/write data to the Sigma server.  A Sigma release 4.04 and below the write function was not supported and was fixed in Sigma release 4.05 onwards. Resolution Upgrade to Sigma 4.05 (onwards) where the DDE write function has been fixed.
View full article
Picard Product_Support
‎2018-09-06 02:07 PM

on ‎2018-09-06 02:07 PM

Labels:
  • Satchwell BAS & Sigma
1440 Views

How to select a platinum sensor compatible with the Analog Input (AI) object in WorkPlace Tech.

Issue How to select a platinum sensor compatible with the Analog Input (AI) object in WorkPlace Tech. Environment WorkPlace Tech I/A Series Lon (MNL) controllers I/A Series BACnet (MNB) controllers Cause Sensor manufacturers provide platinum sensors with different Temperature Coefficient of Resistance (TCR). Resolution The Analog Input (AI) object supports 1Kohm platinum sensor with Temperature Coefficient of Resistance (TCR) equal to 0.00385 OHM/OHM @ °C. Check manufacturer's datasheet and select sensor with TCR of  0.00385 OHM/OHM @ °C
View full article
Picard Product_Support
‎2018-09-06 02:07 PM

on ‎2018-09-06 02:07 PM

Labels:
  • TAC IA Series
1537 Views

Replacement of Satchwell ALX series Linear Actuator by S-E MV15B-24 Linear Actuator due to obsolescence. (Actuator Selection)

Issue Satchwell ALX series Linear Actuator requires replacement. Environment Satchwell ALX series Linear Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body. Cause Obsolescence of Satchwell ALX series Linear Actuator. Resolution Replace Satchwell ALX series Linear Actuator with MV15B-24 Linear Actuator and Linkage Kit :-  ALX = MV15B-24 + L7SV (880-0662-000). Note: this part no. is for both actuator and linkage kit.  N.B.  Should the Satchwell ALX series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the MV15B-24 Actuator as appropriate :-  S2 – MV15B = Two independent 250 volt 10 amp / 3 amp rated SPDT Auxiliary End Point Switches.    Particular care should be taken when selecting an S-E Forta MV15B-24 Actuator to replace an existing Satchwell ALX series Actuator. The S-E MV15B-24 Actuator may be used to replace an existing Satchwell ALX series Actuator but it should be noted that where an existing Satchwell ALX series Actuator has been connected directly to a Satchwell Controller, an independent Transformer rated to provide the greater level of power required by a single S-E MV15B -24 Actuator (12VA) will also be required. (e.g. S-E Transformer Type TR32)  Where an existing Satchwell ALX series Actuator has been connected via an independent Transformer, it is possible that the Transformer may have been rated to provide the level of power required by a single ALX series Actuator (3.5VA) only. In such circumstances the existing independent Transformer may also require replacement by another independent Transformer, rated to provide the greater level of power required by a single S-E MV15B-24 Actuator (12VA) (e.g. S-E Transformer Type TR32)
View full article
Picard Product_Support
‎2018-09-06 02:06 PM

on ‎2018-09-06 02:06 PM

Labels:
  • Field Devices
1598 Views

Replacement of Satchwell ALM series Linear Actuator by S-E MV15B-230 Linear Actuator due to obsolescence. (Actuator Selection)

Issue Satchwell ALM series Linear Actuator requires replacement. Environment Satchwell ALM series Linear Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF Series Plug and Seat Valve Body. Actuator type :- ALM series Cause Obsolescence of Satchwell ALM series Linear Actuator. Resolution Replace Satchwell ALM series Linear Actuator with MV15B-230 Linear Actuator and Linkage Kit :-  ALM = MV15B-230 + L7SV (880-0126-000) Linkage Kit N.B.  Should the Satchwell ALM series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the MV15B-230 Actuator as appropriate :-  S2 – MV15B = Two independent 250 volt 10 amp / 3 amp rated SPDT Auxiliary End Point Switches.
View full article
Picard Product_Support
‎2018-09-06 02:06 PM

on ‎2018-09-06 02:06 PM

Labels:
  • Field Devices
1599 Views

The Sigma default user name TAC USER does not work with Sigma 4.05 SEB

Issue 1. The Sigma default user name TAC USER does not work with Sigma 4.05 SEB 2. Tried the user access password and could not logon Environment Sigma 4.05 SEB Cause The default user name changed at Sigma 4.05 SEB Resolution From Sigma 4.05 SEB onwards the default user name is SIGMA USER. The password remains unchanged.
View full article
Picard Product_Support
‎2018-09-06 02:02 PM

on ‎2018-09-06 02:02 PM

Labels:
  • Satchwell BAS & Sigma
1475 Views

Replacement of Satchwell AR Series 1 or AR Series 2 Rotary Actuator by S-E MD Series Rotary Actuator due to obsolescence. (Actuator Wiring)

Issue Satchwell AR Series 1 or AR Series 2 Rotary Actuator requires replacement Environment Satchwell AR Series 1 or AR Series 2 Rotary Actuators installed on Satchwell MB Series or MBF Series Rotary Shoe Valve Bodies. Satchwell ARE ARM & ARX Series 1 and Series 2 Rotary Actuators Cause Obsolescence of Satchwell AR Series 1 or AR Series 2 Rotary Actuators Resolution Replace Satchwell AR Series 1 or AR Series 2 Rotary Actuators with appropriate S-E MD Series Rotary Actuators and wire as follows: Satchwell AR Series 1 or AR Series 2 Rotary Actuators installed on Satchwell MB Series Screwed Rotary Shoe Valve Bodies ARE ARE Series 1 & 2 Wire Colour BLUE  =  MD10A-24 or MD20A-24 Wire Number 2 ARE Series 1 & 2 Wire Colour RED  =  MD10A-24 or MD20A-24  Wire Number 3 ARE Series 1 & 2 Wire Colour BLACK  =  MD10A-24 or MD20A-24  Wire Number 1 ARE Series 2        Wire Colour WHITE  =  MD10A-24 or MD20A-24  Wire Number 5  ARX ARX Series 1 & 2 Wire Colour RED  =  MD10B-24 or MD20B-24 Wire Number 3 ARX Series 1 & 2 Wire Colour BLUE  =  MD10B-24 or MD20B-24  Wire Number 2 ARX Series 1 & 2 Wire Colour BLACK =  MD10B-24 or MD20B-24  Wire Number 1  ARM – UP TO MARCH 2006 ARM Series 1 & 2 Wire Colour RED  =  MD10B-230 or MD20B-230 Wire Number 3 ARM Series 1 & 2 Wire Colour BLUE  =  MD10B-230 or MD20B-230 Wire Number 2 ARM Series 1 & 2 Wire Colour BLACK  =  MD10B-23 or MD20B-230 Wire Number 1  ARM – SINCE MARCH 2006 ARM Series 1 & 2 Wire Colour BROWN  =  MD10B-230 or MD20B-230 Wire Number 3 ARM Series 1 & 2 Wire Colour BLACK  =  MD10B-230 or MD20B-230 Wire Number 2 ARM Series 1 & 2 Wire Colour BLUE  =  MD10B-230 or MD20B-230 Wire Number 1  Note: Should the Satchwell AR Series Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the S-E MD Actuator as follows: MD – S1  One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch  AR COMMON Wire Colour ORANGE  =  MD-S1 COMMON Wire Number S1 AR N/O contact Wire Colour BROWN  =  MD-S1 N/O contact Wire Number S3      AR N/C contact Wire Colour WHITE  =  MD-S1 N/C contact Wire Number S2  MD – S2  Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches  AR COMMON Wire Colour ORANGE  =  MD-S2 COMMON Wire Number S1 AR N/O contact Wire Colour BROWN  =  MD-S2 N/O contact Wire Number S3 AR N/C contact Wire Colour WHITE  =  MD-S2 N/C contact Wire Number S2  AR COMMON Wire Colour BLACK  =  MD-S2 COMMON Wire Number S4 AR N/O contact Wire Colour RED  =  MD-S2 N/O contact Wire Number S6 AR N/C contact Wire Colour BLUE  =  MD-S2 N/C contact Wire Number S5   Satchwell AR Series 1 or AR Series 2 Rotary Actuators installed on Satchwell MBF Series Flanged Rotary Shoe Valve Bodies ARE ARE Series 1 & 2 Wire Colour BLUE  =  MD20A-24 Wire Number 2 ARE Series 1 & 2 Wire Colour RED  =  MD20A-24 Wire Number 3 ARE Series 1 & 2 Wire Colour BLACK  =  MD20A-24 Wire Number 1 ARE Series 2        Wire Colour WHITE  =  MD20A-24 Wire Number 5  ARX ARX Series 1 & 2 Wire Colour RED  =  MD20B-24 Wire Number 3 ARX Series 1 & 2 Wire Colour BLUE  =  MD20B-24 Wire Number 2 ARX Series 1 & 2 Wire Colour BLACK =  MD20B-24 Wire Number 1  ARM – UP TO MARCH 2006 ARM Series 1 & 2 Wire Colour RED  =  MD20B-230 Wire Number 3 ARM Series 1 & 2 Wire Colour BLUE  =  MD20B-230 Wire Number 2 ARM Series 1 & 2 Wire Colour BLACK  =  MD20B-230 Wire Number 1  ARM – SINCE MARCH 2006 ARM Series 1 & 2 Wire Colour BROWN  =  MD20B-230 Wire Number 3 ARM Series 1 & 2 Wire Colour BLACK  =  MD20B-230 Wire Number 2 ARM Series 1 & 2 Wire Colour BLUE  =  MD20B-230 Wire Number 1  Note: Should the Satchwell AR Series Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the S-E MD Actuator as follows: MD – S1  One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch  AR COMMON Wire Colour ORANGE  =  MD-S1 COMMON Wire Number S1 AR N/O contact Wire Colour BROWN  =  MD-S1 N/O contact Wire Number S3 AR N/C contact Wire Colour WHITE  =  MD-S1 N/C contact Wire Number S2  MD – S2  Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches  AR COMMON Wire Colour ORANGE  =  MD-S2 COMMON Wire Number S1 AR N/O contact Wire Colour BROWN  =  MD-S2 N/O contact Wire Number S3 AR N/C contact Wire Colour WHITE  =  MD-S2 N/C contact Wire Number S2  AR COMMON Wire Colour BLACK  =  MD-S2 COMMON Wire Number S4 AR N/O contact Wire Colour RED  =  MD-S2 N/O contact Wire Number S6 AR N/C contact Wire Colour BLUE  =  MD-S2 N/C contact Wire Number S5
View full article
Picard Product_Support
‎2018-09-06 02:01 PM

on ‎2018-09-06 02:01 PM

Labels:
  • Field Devices
1603 Views

Graphic not updating programmable (prog) objects

Issue The text on the prog object does change but the graphic does not show the same change. Environment Sigma all versions BAS all versions Cause Controller only update server graphics when the object changes state or exceeds the set tolerance.  If prog objects are written with the same condition but different texts in the return statements then the correct text may not be displayed until the whole graphic is updated.  For example 10 If P0|1 on then return true "Object 1 on" 20 if P0|2 on then return true "Object 2 on" 30 if p0|3 on then return true "Object 3 On" Resolution Write the programmable object to that will change state to update the graphic.  This may well have to be a dedicated object for the graphic.  For example using a time statement to check for a change; 10 if not time left then goto 50 20 If P0|1 on then return true "Object 1 on" 30 if P0|2 on then return true "Object 2 on" 40 if p0|3 on then return true "Object 3 on" 50 set timer 10 60 If P0|1 on then return false "Object 1 on" 70 if P0|2 on then return false "Object 2 on" 80 if p0|3 on then return false "Object 3 on"
View full article
Picard Product_Support
‎2018-09-06 02:00 PM

on ‎2018-09-06 02:00 PM

Labels:
  • Satchwell BAS & Sigma
1679 Views

Replacement Digital Clock for Satchwell SVT4251 or CSC2726 and CSC2727 Controller.

Issue Need to replace Digital Clock for SVT4251 or CSC2726 and CSC2727 Controller. Environment SVT4251  CSC2726 CSC2727 Cause Faulty Clock Resolution Replacement Digital Clock for SVT4251 or CSC2726 and CSC2727 Controller is part number 561-9-261
View full article
Picard Product_Support
‎2018-09-06 02:00 PM

on ‎2018-09-06 02:00 PM

Labels:
  • Field Devices
1173 Views

Automatic and manual Sigma data backup

Issue Which files can be backed up safely with an automatic/manual method. Environment Sigma (All) Cause Backing up a live Sigma system is not a recommend as copying ‘live open’ files can not guarantee the integrity of the data. Resolution For either backup method (automatic or manual) those files which could be potentially 'open' by Windows should not be backed up unless the Sigma server and clients have been shut down.  1. Those data locations that can be backup safely while the Sigma is running are those in which archive data is stored, namely; a.  C:\Sigma\Data\ArchivedAlarms b. C:\Sigma\Data\ArchivedLogs c. C:\Sigma\Data\ArchivedTransactions Removing the files from these locations should only be done as a space saving measure as Sigma can be configured to view these data files by the user. 2. For all other files the recommendation is to shut the system down (clients and server) before taking the backup. 3. Restoring data must only be performed after shutting down the system first.
View full article
Picard Product_Support
‎2018-09-06 01:58 PM

on ‎2018-09-06 01:58 PM

Labels:
  • Satchwell BAS & Sigma
1766 Views

DC1100 / DC1400 Boiler output does not energize during HWS time schedule ON periods

Issue DC1100 / DC1400 Boiler output does not energize during HWS time schedule ON periods Environment DC1100 / DC1400 Discrete Controller installations. Cause DC1100 / DC1400 HWS time schedule is not Boiler Linked. Resolution Please check the catalog for current equipment Check Hot Water Link Option is set to Boiler Linked by following Controller access procedure :- Override Setting Switch :- select SET position. Display Screen / Navigation Buttons :- select parameters SYSTEMS MENU / ALTER SETTINGS / ENTER PASS No. (0112) HOT WATER / LINK OPTION Check LINK OPTION setting If LINK OPTION is set to INDEPENDENT then amend to BOILER LINKED If LINK OPTION is set to BOILER LINKED then PUMP RUN ON may be active If PUMP RUN ON  is active then Boiler outputs will be disabled until PUMP RUN time expires To amend PUMP RUN ON time :- select parameters SYSTEMS MENU / ALTER SETTINGS / ENTER PASS No. (0112) COMPENSATOR / SET-UP MENU / PUMP RUN-ON Amend Pump Run-On time period to 1 MINUTE and observe BOILER No.1 LED status should change from OFF to ON DC1100 / DC1400 Boiler No. 1 output (Terminal 10) should now be energised.
View full article
Picard Product_Support
‎2018-09-06 01:55 PM

on ‎2018-09-06 01:55 PM

Labels:
  • Field Devices
1337 Views

Can I/A ENC-520 interface to a Honeywell Q7700 Network Interface for boiler/burner monitoring?

Issue Can I/A ENC-520 interface to a Honeywell Q7700 Network Interface for boiler/burner monitoring? Environment I/A Series G3 (Niagara) ENC-520 Cause Driver for Interface Resolution Tridium reports that there is no G3 driver to support an interface with this product.
View full article
Picard Product_Support
‎2018-09-06 01:49 PM

on ‎2018-09-06 01:49 PM

Labels:
  • TAC IA Series
1496 Views

How to identify the DMS (MicroSmart) MSC-P1502 Enhanced from the non- Enhanced version.

Issue How to identify the DMS (MicroSmart) MSC-P1502 Enhanced from the non- Enhanced version. Environment DMS MicroSmart MSC-P1500 series Cause Controller version identification Resolution The MSC-P1502 controller came in two versions, non-Enhanced and Enhanced. The Enhanced version had the feature for AI 5 & 6 to be configured (jumpers J1 & J2) for a Voltage/mA input or resistance input.  Non-Enhanced version: Using OPRIF to communicate to the controller, the controller greeting screen would display PCB as the Controller Type. Visual identification would be that the circuit board has a label with the p/n MSCA-6160.  Enhanced version: : Using OPRIF to communicate to the controller, the controller greeting screen would display PCB as the Controller Type.  Visual identification would be that the circuit board has a label with the p/n MSCA-6161.  If there is no p/n label on the board, another way to identify an enhanced version is by looking at the circuit board. Above the inputs AI5 & AI6 there would be a white box with the wording ENHANCED AI.
View full article
Picard Product_Support
‎2018-09-06 01:49 PM

on ‎2018-09-06 01:49 PM

Labels:
  • TAC IA Series
1337 Views

Is MNL-V2RV3-APP the actual controller hardware or is it an application for the actual physical controller?

Issue Is MNL-V2RV3-APP the actual controller hardware or is it an application for the actual physical controller? Environment I/A MicroNet LonMark series controllers. MNL-5RF3-APP, MNL-5RH3-APP, MNL-5RR3-APP, MNL-5RS3-APP, MNL-5RS4-APP MNL-10RF3-APP, MNL-10RH3-APP, MNL-10RR3-APP, MNL-10RS3-APP, MNL-10RS4-APP MNL-11-RF3-APP MNL-13-RF3-APP MNL-20RF3-APP, MNL-20RH3-APP, MNL-20RR3-APP, MNL-20RS3-APP, MNL-20RS4-APP MNL-V1RV3-APP, MNL-V2RV3-APP, MNL-V3RV3-APP Cause Part Number description Resolution The MNL-V2RV3 is the actual controller; the extension -APP is an option for factory to install customer's in-house engineered application. Contact Customer Service for details.
View full article
Picard Product_Support
‎2018-09-06 01:48 PM

on ‎2018-09-06 01:48 PM

Labels:
  • TAC IA Series
1752 Views

IC GEN -XLATE table settings for digital objects

Issue What entries are needed in the INPUT_XLATE table for the Sigma digital input to work? Environment Sigma gateway.txt IC GEN DDE IC GEN OPC Cause The Sigma digital inputs operate a reverse logic of 100.0 = off and 0.0 = on.  This needs to be reflected in the IC GEN Gateway.txt file XLATE table Resolution 1.  For the IC GEN gateway.txt input XLATE table when mapping to digital input objects; [INPUT_XLATE] count=2 Item0=1 / 0.0      ;DDE input of 1 = DI on Item1=0/ 100.0  ;DDE input of 0 = DI off 2. For the IC GEN gateway.txt output XLATE table when mapping from digital output objects; [OUTPUT_XLATE] count=2 Item0=0.0/ 0        ;D0 off = DDE output of 0 Item1=100.0/ 1   ;D0 on = DDE output of 1
View full article
Picard Product_Support
‎2018-09-06 01:46 PM

on ‎2018-09-06 01:46 PM

Labels:
  • Satchwell BAS & Sigma
1522 Views

SVT Optimiser Controller Time Switch settings should allow for selected Design Preheat Hours in order to enable the controlled space to recover to the required day temperature af...

Issue SVT Optimiser Controller does not enable the controlled space to recover to the required day temperature after an unoccupied period during which the inside air temperature has fallen to 12°C. Environment SVT4201 Optimiser Controller fitted with Analogue Time Switch. SVT4251 Optimiser Controller fitted with Digital Time Switch. Cause SVT Optimiser Controller Time Switch settings do not allow for selected Design Preheat Hours (DPH) Resolution SVT Optimiser Controller Time Switch settings should allow for selected Design Preheat Hours (DPH) SVT Optimiser Controller Time Switch settings should be carried out as follows :- Set Td to "Day" temperature required during occupancy. Set Tn to minimum "Night" temperature required during unoccupied periods. Set DPH to design preheat time. DPH is the maximum time required in order to enable the controlled space to recover to the required day temperature after an unoccupied period during which the inside air temperature has fallen to 12 deg. C. Select the approximate time in whole hours on the rotary switch (1 to 5 hours) Fine trim +/- 1/2 hour on the associated setting potentiometer. Note.  ALL "ON" times must be set earlier than the start of occupancy by the selected pre-heat time (DPH) set at (3) above. Example : DPH = 2 hours Occupancy time = 8.00 a.m. Set Time Switch "ON" time to 6.00 a.m. Setting the Time Switch "ON" time to 6.00 a.m. will enable the SVT Optimiser Controller to switch the plant ON at any time between 6.00 a.m. and 8.00 a.m. depending on the heating loss experienced in the controlled space during the preceding plant OFF period. N.B. The setting method detailed in the example above applies equally to both SVT4201 Analogue Time Switch and SVT4251 Digital Time Switch versions of the SVT Optimiser Controller.
View full article
Picard Product_Support
‎2018-09-06 01:46 PM

on ‎2018-09-06 01:46 PM

Labels:
  • Field Devices
1359 Views

DMS MicroSmart, Global point passing (broadcast) not working.

Issue DMS MicroSmart, Global point passing (broadcast) not working. Environment MSC-L1000 MSC- MPC-001 MSC-P-751, MSC-P-752, MSC-P-753, MSC-P-754 MSC-P-1501, MSC-P-1502, MSC-P-1503, MSC-P-1504 MSC-V-510, MSC-V-511, MSC-V-521, MSC-V-522 MSC-V-751, MSC-V-752, MSC-V-753, MSC-V-754 Cause The number of TXD and RXD broadcast channels are limited per controller type. Resolution The Level 11. controllers' MicroSmart Global Data Broadcasting capabilities are as follows: MSC-L1000: TXD and RXD on 1-122 channels MSC- MPC: TXD and RXD on 1-122 channels MSC-P-75x: TXD on 1-122 channels. RXD on 1-24 channels. MSC-P-150x: TXD on 1-122 channels. RXD on 1-24 channels. MSC-V-51x: TXD on 1-122 channels. RXD on 1-24 channels. MSC-V-52x: TXD on 1-122 channels. RXD on 1-24 channels. MSC-V-75x: TXD on 1-122 channels. RXD on 1-24 channels.  
View full article
Picard Product_Support
‎2018-09-06 01:46 PM

on ‎2018-09-06 01:46 PM

Labels:
  • TAC IA Series
1432 Views
  • « Previous
    • 1
    • …
    • 505
    • 506
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of