Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,826
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 509
  • Next »

Central I/O Input and Output Specifications

Issue Questions regarding specifications of Central I/O Inputs and Outputs Product Line EcoStruxure Building Operation Environment SmartStruxure I/O Modules: AO-8, AO-8-H AO-V-8, AO-V-8-H DI-16 DO-FA-12, DO-FA-12-H DO-FC-8, DO-FC-8-H RTD-DI-16 UI-8-AO-4, UI-8-AO-4-H, UI-8/AO-4-2, UI-8/AO-4-H-2 UI-8-AO-V-4, UI-8-AO-V-4-H, I/O UI-8/AO-V-4-2, UI-8/AO-V-4-H-2 UI-8-DO-FC-4, UI-8-DO-FC-4-H, UI-8/DO-FC-4-2, UI-8/DO-FC-4-H-2 UI-16 Cause Different I/O modules have varying electrical specifications Resolution Universal Input Specifications Universal inputs can be configured as voltage, current, thermistor, resistance, digital or supervised inputs.   Voltage Input Specifications: Range: 0 to 10 VDC Resolution: 12-bit (UI-8 v2: 16-bit) Accuracy: ±(0.7mV + 0.2% of reading) Current Input Specifications: Range: 0 to 20 mA Resolution: 12-bit (UI-8 v2: 16-bit) Accuracy: ±(0.03 mA + 0.4% of reading) Resistance Input Specifications: 10 Ohm to 10 kOhm 10 kOhm to 60 kOhm Thermistor Input Specifications: Range: -50 to 150° C (-58 to 302° F) Supported Types: 10k Type I (Continuum) 10k Type II (I/NET) 10k Type III (Satchwell) 10k Type IV (FD) 1.8k (Xenta) 10k Linearized (Satchwell DRT) 10k Type V (FD w/ 11k shunt) 1k (Balco) 20k (Honeywell) 2.2k (Johnson Controls) Digital Output Specifications Form C Relay: Terminals: Common (C), Normally Open (NO), Normally Closed (NC) Minimum Pulse Width: 100 ms Isolation: 1500 VAC (coil to contact) Cycle Life: ≥100,000 cycles Contact Rating: 250 VAC, 30 VDC, 3 A Form A Relay: Terminals: Common (C), Normally Open (NO) Minimum Pulse Width: 100 ms Isolation: 1500 VAC Cycle Life: ≥100,000 cycles Contact Rating: 250 VAC, 30 VDC, 2 A LED Indicators: Polarity: Reflects actual output state (ON = active, OFF = inactive) Color: Green Analog Output Specifications Analog outputs can be configured as voltage or current. Voltage Output: Range: 0 to 10 VDC Resolution: 50 mV Accuracy: ±100 mV Terminals: Voltage (V), Return Minimum Load: Source 2 mA, Sink -1 mA Current Output: Range: 0 to 20 mA Resolution: 0.1 mA Accuracy: ±0.2 mA Terminals: Current (I), Return Max Load: ≤650 Ohms Supervised Input Specifications Supervised inputs detect sabotage via resistor monitoring. Detected Conditions: Open circuit, short circuit, contact open/closed Circuit: 5V, 1 or 2 resistors Configurations: Series only, parallel only, series + switch Resistor Range: 1k to 10k Ohms (must be equal values) Note: Resistor value must be defined in the system. RTD Input Specifications RTD-DI-16 specifications are extensive. Refer to the official datasheet: RTD-DI-16 Specification Sheet  
View full article
Picard Product_Support
‎2018-09-11 01:25 PM

Last Updated: Administrator CraigEl Administrator ‎2025-08-22 08:24 PM

Labels:
  • EcoStruxure Building Operation
3626 Views

Replace an old Xenta 301 system version 1 with a new controller

Issue You need to replace a faulty Xenta 301 controller. However, the existing unit is running System Version 1, and the network comprises approximately 12 Xenta controllers on a Menta-only network using the .nwc and .ndb configuration tools. Product Line TAC Vista Environment TAC Xenta 300 Cause New Xenta 301 controllers are shipped with System Version 3 by default. System Versions 1 and 3 are incompatible on the same network. Resolution To ensure compatibility, downgrade the new Xenta 301 controller to System Version 1.17 before installation. Steps to Downgrade and Replace: Download TAC Xenta 300 system program version 1.17 Use the Download Wizard as usual. Important: When downgrading from Version 3 to Version 1, do NOT retain the old application in the Download Wizard. Select "Clear Application" during the process. Manually Download the Menta Application and Network Configuration Use a serial cable to perform the manual download. Apply the appropriate TAC Menta versions for your network setup. Additional Notes Mixing different system versions on the same network can lead to unpredictable behavior and communication issues. Always verify the version compatibility before deploying new hardware.
View full article
Picard Product_Support
‎2018-09-11 12:51 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-22 07:22 PM

Labels:
  • TAC Vista
2223 Views

Summary page or List of All Forced Variables in version 1.4.1 and older

Issue Users need a way to identify all Forced Variables without manually inspecting each point. The goal is to have a summary view—not via Reports Server—but directly accessible on the Automation Server (AS) or Enterprise Server (ES). Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause There is no built-in summary page in versions 1.4.1 and older that lists all Forced Variables. This makes it time-consuming to locate which points are currently forced. Resolution You can locate Forced Variables using the system tree in the Workstation. Navigate to: ES/Servers/AS/System/Modules/RuntimeDBManager/VariableManager/Variables Ensure the isForced column is enabled to view which variables are forced. Additional Notes: This method provides a quick overview without needing to open each individual point. It is especially useful for troubleshooting and auditing system behavior.
View full article
Picard Product_Support
‎2018-09-11 04:00 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-22 07:13 PM

Labels:
  • EcoStruxure Building Operation
1913 Views

Xenta controller Universal Inputs

Issue What does it mean when a TAC controller is said to have a Universal Input? Product Line TAC Vista Environment Xenta Programmable Controllers Xenta I/O modules Cause The term “Universal” is commonly interpreted to mean compatibility with all types of inputs. However, this definition does not accurately apply to TAC Xenta controllers. Resolution In the context of TAC Xenta controllers, the term “Universal Input” refers to compatibility with multiple types of input signals, but not necessarily all types.   Key clarification: It is essential for project planners and system designers to consult the specific device’s datasheet to understand the exact definition of “Universal” as it applies to the particular TAC Xenta model in use. This ensures proper configuration and avoids misinterpretation during system design and implementation.
View full article
Picard Product_Support
‎2018-09-06 03:24 PM

Last Updated: Administrator CraigEl Administrator ‎2025-08-22 07:06 PM

Labels:
  • TAC Vista
2246 Views

LMADMIN.exe - Application Error

Issue After the "Windows is shutting down" message, Windows displays a non-specific memory error: lmadmin.exe - Application Error The instruction at "0x00000000" referenced memory at "0x000000". The memory could not be read. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Cause This issue is caused by Flexera Software, the licensing software used within Building Operation. Flexera does not support Windows XP, which leads to this error during system shutdown. This is a known limitation and will not be addressed in future updates. Resolution There are no known operational impacts associated with this error. It only occurs during shutdown of a Windows XP machine. Upgrading the operating system to a supported version will eliminate this error. Additional Notes This issue is cosmetic and does not affect system performance or licensing functionality. Users are encouraged to migrate away from Windows XP due to broader security and compatibility concerns.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-22 07:01 PM

Labels:
  • EcoStruxure Building Operation
2934 Views

Identifying Security Expert Smart Card Readers firmware

Issue How can the firmware version of Security Expert Smart Card Readers be determined. Product Line EcoStruxure Security Expert Environment Security Expert Smart Card Readers Cause It is not possible to easily identify the firmware which a reader has been shipped with. Serial Numbers are not sequential and cannot be used as general guide. Resolution There are two supported methods to determine the firmware version of a Security Expert Smart Card Reader: 1. Via Product Support If you need to identify the original firmware version shipped with a reader: Raise a case with Schneider Electric Product Support. Include the reader’s serial number in your request. Product Support will contact Manufacturing to obtain confirmation of the firmware version originally installed on the reader. 2. Via Controller Web Interface (Requires Reader Expander Firmware 1.12.605 or later, Security Expert Controller Firmware 2.08.1498 or later, SP-C-WEB Firmware 4.00.2261 or later) From firmware version 1.12.605 and above, the Security Expert Controller’s web interface displays the serial numbers and firmware versions of connected card readers via RS-485 or OSDP. Steps to View Firmware Version: Log in to the Controller Web Interface. Navigate to Application Software. Open the Module dropdown to view connected readers. Important Notes: Wiegand-connected readers are not displayed in the web interface. If the Reader Expander address has changed, a power cycle is required for the readers to reappear in the interface.  
View full article
Admiral RyanSuar Admiral
‎2019-04-03 09:30 AM

Last Updated: Ensign AndreasP Ensign ‎2025-08-19 10:28 PM

Labels:
  • EcoStruxure Security Expert
2714 Views

Security Expert Database Table Sizes

  Issue Understanding the size of individual tables within the Security Expert databases is essential for effective database management. This insight helps optimize system performance and supports archiving strategies. Product Line EcoStruxure Security Expert Environment EcoStruxure Security Expert Microsoft SQL Server Cause Managing SQL database size is critical to maintaining system performance. Identifying which tables consume the most space provides actionable data for optimization and archiving. Resolution To determine table sizes in the Security Expert and Security Expert Events databases, follow these steps using SQL Server Management Studio (SSMS): Open SSMS Right-click on the relevant database (e.g., Security Expert or Security Expert Events). Navigate to: Reports > Standard Reports > Disk Usage by Table Review the report to identify tables with the largest data footprint. Examples: Security Expert DB Security Expert Events DB Exporting the Report You can print or export the report for documentation or analysis: Print Export to Excel, PDF or Word Right-click on the data results and select Export Note: The “Disk Usage by Table” report is available in SQL Server 2008 and later.
View full article
Admiral Alan_Wood Admiral
‎2024-10-10 12:08 PM

Last Updated: Administrator CraigEl Administrator ‎2025-08-22 06:50 PM

Labels:
  • EcoStruxure Security Expert
875 Views

EBO SAML Single Sign On(SSO) Reverse Proxy support

Issue Fail to setup reverse proxy for SAML SSO. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Webstation Cause EBO doesn't support reverse proxy configuration for SSO. Resolution The current version of EBO (7.0) does not support reverse proxy for SSO. An enhancement idea has been submitted to the Idea Forum. Please click the thumbs-up icon to help increase its visibility to product management.   Idea forum: SAML reverse proxy support  
View full article
Admiral StephenYang Admiral
‎2025-08-20 10:18 AM

Labels:
  • EcoStruxure Building Operation
95 Views

WebReports/Report Server discontinuation in EBO 2022 or higher (Migration to External Log Storage)

Issue Sites using Report Server need to upgrade to EcoStruxure Building Operation (EBO) 2022 or higher, where WebReports/Report Server is no longer supported. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Report Server Building Operation Timescale Database Cause WebReports/Report Server is not supported in EBO 2022 (version 4.0) or higher. Resolution To address this, Schneider Electric provides a Data Migration Assistant (DMA) tool that: Reads data from WebReports 3.x Writes data to External Log Storage Download the DMA Tool External Log Storage Overview Stores historical data from EcoStruxure BMS Storage capacity is limited only by your hardware Historical data is displayed in WorkStation and WebStation (event and trend views) Any server can be configured to write data to TimescaleDB   Any server in the system can be configured to write historical data to the TimescaleDB database. Licensing Requirements External Log Storage requires a license Refer to: Software and Features that Require Licenses Part Number Summary and Hardware Software Matrix Hardware & Software Requirements Ensure compatibility with: TimescaleDB PostgreSQL Recommended specs for large systems (e.g., 100 BMS servers): High-performance SSD Minimum 64 GB RAM Additional CPU capacity Refer to: IT System Planning Guide Merging Log Data External Log Storage reduces extended trend logs on BMS servers You can merge extended trend logs into source logs in External Log Storage See: Merging of Trend Log Data Enhanced Reporting (XLSX Templates) EBO servers (v3.2 or higher) support native reporting with: Text and XLSX formats Advanced XLSX features: formulas, conditional formatting, charts, sparklines Historical data pulled from External Log Storage (PostgreSQL/TimescaleDB) Refer to: Examples for Native EBO Notification Reports
View full article
Kirk Mahmoud_Sayed Kirk
‎2022-06-22 01:54 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-15 06:38 PM

Labels:
  • EcoStruxure Building Operation
5028 Views

How BACnet controllers are established as being Online / Offline

Issue How are BACnet controllers established as being Online / Offline? Product Line EcoStruxure Building Operation Environment BACnet Cause BACnet controllers may appear offline in the system, even though they can still be communicated with. This raises questions about how their online/offline status is determined. Resolution The online/offline status of BACnet devices is managed by the BACnet device manager plugin, which processes BACnet I-Am messages to maintain a device table.   The following rules and mechanisms are used to determine the status of BACnet controllers: Device Discovery and Initial Probing When a new device is discovered, an entry is added to the device table. The system probes the new entry up to four times at 5-second intervals. If the device does not respond within this time, it is declared offline. Offline Detection via MSTP Driver Building Operation uses the MSTP dev driver to monitor token passing. If three consecutive tokens are missed, the device is marked as offline. Probing Offline Devices Once a device is offline, the system sends a Who-Is message every 60 seconds. Offline devices are probed indefinitely at 60-second intervals until they respond. Online devices are never probed. Status Transition A device is considered online once it responds to a request. If it fails to respond, its status is updated to offline, and probing resumes.
View full article
Picard Product_Support
‎2018-09-06 09:47 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-13 05:47 PM

Labels:
  • EcoStruxure Building Operation
2734 Views

Getting data from Rayleigh Instruments RI-78-80-C kWh Meter

Issue How to get data from Rayleigh Instruments RI-78-80-C kWh power meters Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Automation Server (ASP/ASB) Modbus RTU Interface Cause The RI-78-80-C meter provides a single 48-bit Modbus RTU word representing energy in kWh. This word spans three 16-bit registers (registers 0, 1, and 2). The meter: Only responds to a valid 48-bit read Does not return exceptions for invalid or partial register reads Resolution To successfully read the 48-bit value: Step-by-Step Instructions Create a Modbus Group Set an appropriate polling interval. Add Registers Add three 16-bit unsigned registers to the group: ModReg0 (Register 0) ModReg1 (Register 1) ModReg2 (Register 2) Create an Analog Value Example name: kWReading Script Program Use the following calculation: kWReading = ((256 * 256 * ModReg0) + (256 * ModReg1) + ModReg2) / 100 ​ This formula accounts for the fact that each register only uses half of its 16-bit range (values from 0 to 255). The register values represent 1/100 of a kWh, so a scaling factor of /100 is applied. Bind Points Bind the Modbus registers and analog value to the script program. Example Calculation If: ModReg0 = 3 ModReg1 = 167 ModReg2 = 59 Then: kWReading = ((3 × 256 × 256) + (167 × 256) + 59) / 100 = 239419 / 100 = 2394.19 kWh ​   Additional Notes The device may appear online in EcoStruxure even if it’s not responding correctly. This is because the online poll interval mechanism expects a response from a 16-bit register. Since the RI-78-80-C doesn’t respond to invalid reads, it may falsely appear online. To avoid this, set the online poll interval mechanism to “Inhibit”. Compatibility Warning: This device may not function correctly in v2.0 and v3.0 due to changes in offline detection. This issue is resolved in v3.1. Resources Example Modbus Objects and Script RI-78-80-C Exports.zip Numeric Output kWReading   Line Calc1 kWReading = ((256*256*ModReg0) + (256*ModReg1) + ModReg2)/100
View full article
Picard Product_Support
‎2018-09-11 07:08 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-13 05:24 PM

Labels:
  • EcoStruxure Building Operation
3294 Views

Esmi Ultima Input Module Trouble

Warning Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source. Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.   Issue The panel displays an Address 1 has a wiring trouble condition. This is accompanied by a General Trouble alert. Product Line ESMI Fire Detection. Environment FFSULH2007. Cause The system is showing a wiring trouble condition at Address 1. To view more details, press the “More Details” button on the panel. This issue originates from the Input Module (FFSULH2007). Resolution The Input Monitor Module provides contact monitoring circuits for equipment that uses a dry contact signal. Typical Connection Diagram The diagram below shows a typical connection of the input module with the monitored equipment. The circuit is monitored for wiring faults using an End-of-Line (EOL) resistor, which should be installed at the last point of the circuit. Note: The EOL resistor is supplied inside the module box. Troubleshooting Steps If the EOL resistor is removed or discarded, or if the wiring is broken, the module will detect a loss of resistance and generate a wiring trouble alert. The installer must ensure: The EOL resistor is properly connected at the last point of the equipment. Any broken wires are repaired or rejoined. Once the wiring and resistor are correctly installed, the trouble condition will automatically clear.
View full article
Ensign Sandeep_Kumar006 Ensign
‎2025-08-12 09:17 PM

on ‎2025-08-12 09:17 PM

Labels:
  • ESMI Fire Detection
129 Views

MPM Daylight Saving Time (DST)

Issue The MPM controller does not adjust the clock automatically when Daylight Saving Time (DST) period occurs. Product Line EcoStruxure Building Expert Environment SmartStruxureLite Multi-Purpose Manage Cause DST settings in the MPM are configured for North America. Canada and United States: Daylight saving time begins on the second Sunday of March and ends on the first Sunday of November Europe: Daylight saving time begins on the last Sunday of March and ends on the last Sunday of October Resolution In Firmware 2.15, DST properties can be configured in the Controller Configuration Object (CFG1) and/or configuration page. DST start and end configuration on month, week, weekday, hour and offset can be set. If using a firmware version older than 2.15, a script can be used to correct the issue. The script can be found here: Daylight_Saving_Time_DSC.lua
View full article
Picard Product_Support
‎2018-09-11 01:57 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:15 AM

Labels:
  • EcoStruxure Building Expert
2083 Views

Sigma programmable object bit mask to decode Modbus register

Issue How to use bit masking to decode on/off states from a Modbus analogue registers e.g. Holding or Input registers. Where each bit is required to be read individually to indicate the status of a coil. Product Line Satchwell Sigma Software Environment Sigma IC Modbus and IC3 Modbus controllers Cause Configuration technique to read 16-bit Modbus registers for on/off states. Resolution Each modbus holding or input register is 16 bits, where each bit can be on or off i.e. 0 or 1. For example the Sigma analogue input value of 901 represents the state of a number of coils where each bit indicates the on or off.  Hence, this translates to the 16-bit binary value  0000001110000101  where 1 = on and 0 = off Create a Sigma analogue input object to read the Modbus value. Click here for the  Sigma Modbus 4.06 release Note Create a programmable object for each of the required bits (max of 16 for each register) to be read as below.  (Highlight, copy and paste into each programmable object). For Example starting with the Least Significant Bit (LSB) and where point 0|222 is the Modbus value created, the programmable objects are; Bit 1 (LSB) 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 1 ) 30 IF YINT = 1 THEN RETURN TRUE "Bit 1 = on" 40 RETURN FALSE "Bit 1 = off" Bit 2 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 2 ) 30 IF YINT = 2 THEN RETURN TRUE "Bit 2 = on" 40 RETURN FALSE "Bit 2 = off" Bit 3 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 4 ) 30 IF YINT = 4 THEN RETURN TRUE "Bit 3 = on" 40 RETURN FALSE "Bit 3 = off" Bit 4 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 8 ) 30 IF YINT = 8 THEN RETURN TRUE "Bit 4 = on" 40 RETURN FALSE "Bit 4 = off" Bit 5 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 16 ) 30 IF YINT = 16 THEN RETURN TRUE "Bit 5 = on" 40 RETURN FALSE "Bit 5 = off" Bit 6 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 32 ) 30 IF YINT = 32 THEN RETURN TRUE "Bit 6 = on" 40 RETURN FALSE "Bit 6 = off" Bit 7 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 64 ) 30 IF YINT = 64 THEN RETURN TRUE "Bit 7 = on" 40 RETURN FALSE "Bit 7 = off" Bit 8 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 128 ) 30 IF YINT = 128 THEN RETURN TRUE "Bit 8 = on" 40 RETURN FALSE "Bit 8 = off" Bit 9 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 256 ) 30 IF YINT = 256 THEN RETURN TRUE "Bit 9 = on" 40 RETURN FALSE "Bit 9 = off" Bit 10 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 512 ) 30 IF YINT = 512 THEN RETURN TRUE "Bit 10 = on" 40 RETURN FALSE "Bit 10 = off" Bit 11 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 1024 ) 30 IF YINT = 1024 THEN RETURN TRUE "Bit 5 = on" 40 RETURN FALSE "Bit 6 = off" Bit 12 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 2048 ) 30 IF YINT = 2048 THEN RETURN TRUE "Bit 12 = on" 40 RETURN FALSE "Bit 12 = off" Bit 13 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 4096 ) 30 IF YINT = 4096 THEN RETURN TRUE "Bit 13 = on" 40 RETURN FALSE "Bit 13 = off" Bit 14 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 8292 ) 30 IF YINT = 8292 THEN RETURN TRUE "Bit 14 = on" 40 RETURN FALSE "Bit 14 = off" Bit 15 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 16384 ) 30 IF YINT = 16384 THEN RETURN TRUE "Bit 15 = on" 40 RETURN FALSE "Bit 15 = off" Bit 16 (MSB) 10 XINT = INT POINT 0|222 20 YINT = XINT MASK ( 32768 ) 30 IF YINT = 32768 THEN RETURN TRUE "Bit 16 = on" 40 RETURN FALSE "Bit 16 = off"
View full article
Picard Product_Support
‎2018-09-07 08:21 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:15 AM

Labels:
  • Satchwell BAS & Sigma
4616 Views

Installing and Configuring Email Service Accounts in Niagara G3

Issue Installing and Configuring Email Service Accounts in Niagara G3 Environment Niagara G3 Cause The need for a quick reference guide Resolution The following document can be found at Niagara-Central.com as well.
View full article
Picard Product_Support
‎2018-09-11 06:29 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:15 AM

Labels:
  • TAC IA Series
2217 Views

How to configure a LON router in Niagara R2.

Issue How to configure a LON router in Niagara R2. Environment Niagara R2 LON Cause Troubleshooting Resolution Review / download documentation here.
View full article
Picard Product_Support
‎2018-09-11 06:12 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:15 AM

Labels:
  • TAC IA Series
1703 Views

Schlage Lock Configuration

Issue Schlage step by step configuration. Environment Windows Xp, 7,  2008, 2008R2 Continuum 1.94 Cause Single Door set Up examples. Resolution Schlage Door setup examples attached.   Download here
View full article
Picard Product_Support
‎2018-09-11 06:01 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:15 AM

Labels:
  • Andover Continuum
1712 Views

How to setup automatic table truncation on Single-User SQL Express systems

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue How to setup automatic table truncation on Single-User SQL Express systems. Product Line Andover Continuum Environment Continuum Cyberstation Single-User SQL Express SQL Server 2005 Cause Only the ExtendedLog table is automatically truncated on an Single-User SQL Express Continuum system. The other tables that can fill up quickly and need to be truncated regularly are not catered for (accessevent, activityevent, alarmevent, and errorevent). Resolution IMPORTANT: Make sure to perform a full SQL Database backup before attempting to make any changes to the database. (See Move / Backup / Restore a database on a Single User SQL2005 Express system for details on how to backup your database and, if not already installed, where to get Management Studio from) Use the attached file SQLExpress to add table truncations.zip, to configure your Single-User SQL Express system to automatically truncate these tables when it does the ExtendedLog truncation. After downloading the file, follow the steps below. There are three files in the archive, these need to be copied to your Continuum folder on your Single-User system running SQLExpress as the database engine. LogTruncate.SQL This file is the SQL script that performs the truncation of the four tables (accessevent, activityevent, alarmevent, and errorevent) to the number of days you specify - I have selected 90 days as my default but you can change this to whatever you require for each table. CS_LogTruncate_OneOff.bat This batch file will run the LogTruncate.sql script once when manually executed. You will need to change the server name "PC3" to whatever your PC's name actually is on your system. CS_Hrly - with LogTruncat.bat This is the batch file that will be renamed and replace the existing "CS_Hrly.bat" file currently located in your Continuum folder. This is the same as your current file except it has added the LogTruncate.sql script so that this will now be executed every hour along with the rest. Backup "CS_Hrly.bat" file in Continuum folder by renaming the file to something like "CS_Hrly ORIGINAL.bat". Rename "CS_Hrly - with LogTruncat.bat" to "CS_Hrly.bat", copy into (overtop the existing file if you haven't renamed it) the Continuum folder, and change the server name "PC3" to your PC's name. This should now execute this table truncation script along with the other database maintenance scripts every hour.
View full article
Picard Product_Support
‎2018-09-10 10:05 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:15 AM

Labels:
  • Andover Continuum
1995 Views

Documentation for the Huba 692 differential pressure sensor

Issue Documentation for the Huba 692 differential pressure sensor is not available on the Extranet or other Schneider Electric web sites. Environment Part no 6552050000, Huba 692 Differential pressure sensor Cause This is a Class 3 product that is sold by Schneider Electric, but documentation is provided by the manufacturer. Resolution Data sheet is available here, or on the manufacturer web site: http://www.hubacontrol.com/en/products/
View full article
Picard Product_Support
‎2018-09-10 08:54 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:15 AM

Labels:
  • Field Devices
1996 Views

Webstation static graphics viewer doesn't work in Chrome, FireFox or smart phones

Issue Webstation static graphic viewer no longer works in Chrome, FireFox or on smart phones. The "Loading..." image never goes away. Environment Webstation Cause The file "xmlHttpImageLoader.js" located in "C:\inetpub\wwwroot\TACVistaWeb519\Modules\Graphics\ImageLoader" (519 being the version of TAC Vista installed) uses the name "status" for a variable in the script. This variable name is a reserved word. The name is actually not a reserved JavaScript word, but a reserved Windows word: http://www.w3schools.com/js/js_reserved.asp Resolution As only Internet Explorer is supported, this is not going to be fixed. There is however a workaround that will enable viewing graphics in static mode. 1. Rename the file C:\inetpub\wwwroot\TACVistaWeb519\Modules\Graphics\ImageLoader\xmlHttpImageLoader.js 2. Paste this corrected file to the same location
View full article
Picard Product_Support
‎2018-09-11 11:35 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:15 AM

Labels:
  • TAC Vista
1444 Views
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of