Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
Options
  • Mark all as New
  • Mark all as Read
  • Float this item to the top
  • Subscribe
  • Bookmark
  • Invite a Friend
  • Threaded format
  • Linear Format
  • Sort by Topic Start Date
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • Smart-UPS & Symmetra LX | RM 4,611
  • UPS Management Devices & PowerChute Software 2,913
  • Racks, Rack Accessories, & Cooling 955
  • Data Center & Facility 3 Phase UPS 605
  • General Questions & Suggestions 240
  • Getting Started 166
  • Datacenter UPS 131
  • Server Room & Data Center Design Best Practices 106
  • Smart-UPS & Symmetra LX-RM 97
  • Other Environmental Monitoring Products & Questions 48
  • Business Power UPS 36
  • Datacenter Racks & Cooling 28
  • Rack Accessories & Cooling 16
  • Business Power Software & NMC 15
  • Home & Office - UPS & Software 15
  • Datacenter Accessories 15
  • Datacenter Netbotz & Monitoring 9
  • Network Management Card 6
  • Data Center Expert 6
  • Racks 6
  • power monitoring expert 5
  • IT Expert 5
  • Data Center Operation 4
  • Back-UPS & Surge Protectors 3
  • DCIM Support 2
  • apc 2
  • firmware 2
  • UPS 2
  • Home & Office - Accessories 2
  • Product Feedback 2
  • UPS Network Management Card 2
  • SMARTCONNECT 2
  • NetBotz 2
  • EcoStruxure IT Design CFD 1
  • Smart-750 1
  • Smart Design & Engineering 1
  • srt5000 1
  • detected 1
  • AP9210 1
  • Legacy Gateways & Energy Servers 1
  • symmetra 1
  • AP9619 1
  • 240v 1
  • spit phase 1
  • Certicate 1
  • AP7750A 1
  • Datacenter Forum 1
  • managedservices 1
  • dedicatedserver 1
  • managedserver 1
  • Electrical Calculation Tools 1
  • Tips and ideas 1
  • Building Operations 1
  • DDF 1
  • IT Advisor 1
  • Battery life 1
  • Safety 1
  • ssl 1
  • SERVER 1
  • Previous
  • 1 of 6
  • Next
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All
Related Products
Thumbnail of EcoStruxure™ IT SmartConnect
Schneider Electric
EcoStruxure™ IT SmartConnect
32
Thumbnail of Smart-UPS
Schneider Electric
Smart-UPS
29
Thumbnail of Uninterruptible Power Supply (UPS)
Schneider Electric
Uninterruptible Power Supply (UPS)
25
Load more

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

APC UPS Data Center & Enterprise Solutions Forum

Start a Topic
  • All
  • Solved
  • Unsolved
  • Unanswered
Solved
Anonymous user
Anonymous user

Can extended AVR Trim damage a Smart-UPS 1500 RM?

I have 10 Smart-UPS 1500 RM's in a building where the supply voltage has risen to 126.7 VAC due to recently decreased load in the building. AVR trim is being engaged for long durations on these UPS's....
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
930 0 2
Latest Reply: BillP

Solved
BillP
Administrator BillP Administrator

UPS IBM XHV 10000

Hello World, One of our customer came to our workshop with an IBM UPS. The UPS seems to be an APC 10000RMXLI rebadged for IBM. May be the electronic is a little bit different. The UPS is down: no light...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
806 0 3
Latest Reply: Erasmus_apc

Solved
Anonymous user
Anonymous user

SSL Certificate SubjectAlternateName and Bulk CSR Generation

Using the APC Security Wizard I have been able to upload an enterprise signed SSL certificate successfully. The FQDN for the UPS was set as the Common Name during the CSR generation. When browsing to...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1664 0 4
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

Network Managment Card does a warm restart when enabling/disabling SNM...

Hi Guys I've got an application that monitors the status of two ups's on our network. I'm using SNMP to do this. It works fine for a while, but after some time, usually a few hours, the network managem...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1001 0 3
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

Installing AP9512THBLK

All I have bought 2x AP9512THBLK sensors to replace the temperature only ones which came with out AP9619 Network Management Cards. I assume i can just remove the old ones and plug the new ones in. This...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
761 0 1
Latest Reply: BillP

Solved
BillP
Administrator BillP Administrator

PowerChute Business Edition and NMC...

Hello there. Let me introduce some information : we have 4 UPS (1 SRT10KRMXLI, 2 SRT8KRMXLI and 1 SRT6KXLI). Each of them has its own NMC card. Unfortunately, only 2 UPS's are connected to a server, th...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1978 0 6
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

Monitoring more tan one UPS with one Server

Hi, I have 2 smart-UPS 3000RM 2U with USB connector and one 3U 3000 with only serial connector. Only one is used for the server, the two other provide power to PC's installed elsewhere. Powerchute reco...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
679 0 1
Latest Reply: Techie_apc

Solved
Anonymous user
Anonymous user

Longer Run Time on lower rated models?

Wondering if someone can explain how a slightly higher rated UPS model has a lower run time capability vs. a lower rated model. Tried asking a couple of my peers but none of them seemed to know. [APC S...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
629 0 1
Latest Reply: upsguy_apc

Solved
Anonymous user
Anonymous user

3000-5000VA UPS w/ both 120 & 240V Input?

I've been browsing the web for the past few days trying to track down if there is any product offered that would match the requirements I have. Are there any UPS's that offer both 120 & 240V input ...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1906 0 1
Latest Reply: Techie_apc

Solved
Anonymous user
Anonymous user

Communication Lost from UPS

We have 3 x SC1000i UPS and each one is plugged into it's own server via the supplied Serial > USB lead (940-0272A). The servers at varying times lose communication with the UPS. I have contacted AP...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1150 0 5
Latest Reply: Anonymous user

Solved
JcMac_apc
Crewman JcMac_apc

Shutting off PDU outlets to shutdown ESXi servers and Appliances

Hi, We have two (2) Dell 2950 III running ESXi 3.5 U4 connected to two (2) APC switched AP7940 PDUs which are in turn connected to an 8 KVA APC UPS with a AP9619 card. My to install APC PCNS on the VMs...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1130 0 2
Latest Reply: JcMac_apc

  • « Previous
    • 1
    • …
    • 783
    • 784
    • 785
    • …
    • 1078
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore